Old 28-02-2023, 12:23   #16
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 9,965
Re: Kidde smokers run amuk

Quote:
Originally Posted by CaptTom View Post
Usually on a boat, false smoke alarms are due to Hydrogen Sulfide from battery charging. Were you plugged in at the time?

Another possibility is condensation inside the detector. We all know how condensation can form on the hull or anything metal when temperatures drop. Even if that doesn't set it off, it can cause dust to stick to the detector.

It's never good to ignore an alarm, but the fact is there are a number of causes for false alarms. The trick is being sure you know the cause.

Hydrogen, not hydrogen sulfide (batteries also do not give off hydrogen sulfide, only H2 and H2SO4). See post 6.
__________________
Gear Testing--Engineering--Sailing
https://sail-delmarva.blogspot.com/
thinwater is online now   Reply With Quote
Old 28-02-2023, 17:30   #17
Registered User
 
CaptTom's Avatar

Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,296
Re: Kidde smokers run amuk

Quote:
Originally Posted by thinwater View Post
Hydrogen, not hydrogen sulfide (batteries also do not give off hydrogen sulfide, only H2 and H2SO4). See post 6.
Live and learn! I knew about Hydrogen, I've watched it bubble out. So what is that "rotten egg" smell when a battery is overcharging? I just assumed that was what was causing the detector to alarm. Hydrogen rises in air. I know at least once I've heard the CO detector go off due to battery charging, when the detector wasn't on the overhead, or near or above the battery compartment, so it wouldn't have "seen" much Hydrogen.
CaptTom is offline   Reply With Quote
Old 28-02-2023, 18:25   #18
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,381
Re: Kidde smokers run amuk

Quote:
Originally Posted by CaptTom View Post
I know at least once I've heard the CO detector go off due to battery charging, when the detector wasn't on the overhead, or near or above the battery compartment, so it wouldn't have "seen" much Hydrogen.
How much does it need to "see" ?
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 28-02-2023, 19:13   #19
Registered User
 
capn_billl's Avatar

Join Date: Aug 2010
Location: Naples, FL
Boat: Leopard Catamaran
Posts: 2,581
Re: Kidde smokers run amuk

Quote:
Originally Posted by thinwater View Post
CO sensors with alarm on many other gases, because that is how the technology works. The cross interferences are well known.


They are very sensitive to hydrogen gas, a common source of "false alarms" on boats that have been closed up.


https://sps-support.honeywell.com/s/...sitivity-to-H2


https://www.senvainc.com/catalog/doc...sitivities.pdf
If there is a flammable gas buildup, I still want to know about it. That's more of a feature, than a bug.
capn_billl is offline   Reply With Quote
Old 01-03-2023, 05:38   #20
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,518
Kidde smokers run amuk

Still a mystery. Have had 8 hatches open for over a month now. No L/A charging for weeks. I blasted both suspect alarms with breathing quality air. Back in service.

Too bad the gas chromatograph was left behind. The job i left was designing parts of those.
Cross sensitivity was a spec we dealt with. Target gases included hydrogen, methane, heptane, ethane, and acetylene. Your basic explosive gas mix for transformer oil.
team karst is offline   Reply With Quote
Old 03-03-2023, 07:37   #21
Registered User

Join Date: Mar 2007
Boat: Privilege 482
Posts: 527
Re: Kidde smokers run amuk

We had the same issue with a couple of Kidde smoke detectors when we got deep into the tropics and the humidity levels soared. Intermittent going off, etc. Can't prove it was just the humidity, but it only seemed to affect the ones in the cabins with less air movement.
__________________
Boats, kids, and all that jazz.
teneicm is offline   Reply With Quote
Old 03-03-2023, 07:42   #22
Registered User

Join Date: Apr 2020
Posts: 4
Re: Kidde smokers run amuk

I had a failing house bank battery set off the CO detector. The battery was very hot and gave off an odor.
Jackpmyers1948 is offline   Reply With Quote
Old 03-03-2023, 14:13   #23
Registered User

Join Date: Mar 2013
Location: me US, CO. boat Sweden
Boat: Malö 42, 43.1ft
Posts: 21
Re: Kidde smokers run amuk

In the early years of owning and refitting our previous sailboat, we had the smoke and gas alarm go off repeatedly moored in a marina. Sometimes but not always, after coming back to the boat after some hiking. Hatches closed, because you never know when the next shower is gonna hit in the Scandinavian summer.

So, sometimes it alarms, sometimes no alarm and none for our noses discernible smell, not even my wife's nose! I thought, very annoying this thingy, and I have to hinder wife using it as a frisbee. After a few days I realize it only goes off when we have the wind in from stern. I had also upgraded the propane locker to a for purpose built "airtight" gas bottle container, with drainage out at bottom through assigned throughhull, and air-inlet from top to outside. I also had electrical remote switch on the bottle, always off when not using stove (a must security feature I think).

So, I was in denial! There could not be any unwanted gases, right? Shame on me!

My annoyance threshold was finally reached, and I realized there must be something with the gas container set-up! Lo and behold, after following the out-drainage under a lot of stuff and under the floorboards to the through hull I see that the valve was in the CLOSED postion (do not ask me why)!!

So, the very tiny amount of gas diffusing out from the couplings on the gasbottle, had no way to go, and with wind in from stern into the air intake, it was enough pressure to force out a tiny amount of gas (bottle shut off by remote when not in use) and waft it forwards into the living quarters with air from the stern dorades (again, we did not smell anything)!

Since then, I NEVER ignore any gas alarms. Especially not if they would go off repeatedly! They might actually do their job and warn you correctly! We lived to learn!
Photonsailor is offline   Reply With Quote
Old 03-03-2023, 14:17   #24
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,534
Re: Kidde smokers run amuk

Quote:
Originally Posted by Photonsailor View Post
In the early years of owning and refitting our previous sailboat, we had the smoke and gas alarm go off repeatedly moored in a marina. Sometimes but not always, after coming back to the boat after some hiking. Hatches closed, because you never know when the next shower is gonna hit in the Scandinavian summer.

So, sometimes it alarms, sometimes no alarm and none for our noses discernible smell, not even my wife's nose! I thought, very annoying this thingy, and I have to hinder wife using it as a frisbee. After a few days I realize it only goes off when we have the wind in from stern. I had also upgraded the propane locker to a for purpose built "airtight" gas bottle container, with drainage out at bottom through assigned throughhull, and air-inlet from top to outside. I also had electrical remote switch on the bottle, always off when not using stove (a must security feature I think).

So, I was in denial! There could not be any unwanted gases, right? Shame on me!

My annoyance threshold was finally reached, and I realized there must be something with the gas container set-up! Lo and behold, after following the out-drainage under a lot of stuff and under the floorboards to the through hull I see that the valve was in the CLOSED postion (do not ask me why)!!

So, the very tiny amount of gas diffusing out from the couplings on the gasbottle, had no way to go, and with wind in from stern into the air intake, it was enough pressure to force out a tiny amount of gas (bottle shut off by remote when not in use) and waft it forwards into the living quarters (again, we did not smell anything)!

Since then, I NEVER ignore any gas alarms. especially not if they would go off repeatedly! They might actually do their job and warn you correctly! We lived to learn!
Hear hear! I have always been saying that these are not false alarms and I’m usually ridiculed for it. But there’s something triggering the sensor so it’s not a false alarm. For new boats it’s out gassing from materials or even paint still curing etc.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 03-03-2023, 22:33   #25
Registered User

Join Date: Jan 2015
Posts: 124
Re: Kidde smokers run amuk

doesn’t help in this case as the OP has a fire alarm problem but domestic CO alarms are susceptible to damp and that’s why they sell different ones for boats.
paul2884 is offline   Reply With Quote
Old 05-03-2023, 08:23   #26
Registered User

Join Date: Sep 2009
Location: Niagara on the Lake Canada
Posts: 188
Re: Kidde smokers run amuk

Quote:
Originally Posted by team karst View Post
We have 5 CO/smoke detectors on board. All new in 2022. Two have gone off in smoke detect mode. Inconsolable, have permanent batteries. Put them in zip locks to shut them up.
Not cooking, nothing unusual going on. Genset, both engines off. Unit one was in a berth a couple weeks ago, this last one in the saloon.
Any history with these?

I dont know if they are the same as the KIDDE units in my home BUT my combos last just out the warrenty period and then start going crazy. I have hard wired my house 1 smoke in each bedrm, 1 in attached storage garage, 1 combo in the hall 1 combo in basement. (I also have a wired and battery smoke in the same rm in the basement because I dont trust these pos's.) At 60 bux when the combos go it is a pita. I have done away with battery types in the smokes. Only the combos have batts so when I shut the breaker they at least stop yelling. Ps I am a former Fire Alarm tech and know about smoke dets and these are crap. Like I said I dont trust them. Oh also a stand alone carbon in the hall by the bedrooms.
justlearnin is offline   Reply With Quote
Old 22-03-2023, 07:20   #27
Registered User

Join Date: Sep 2020
Location: Seabrook, TX
Boat: Catalina 30
Posts: 604
Re: Kidde smokers run amuk

Joining he fray:

-Dust as mentioned
-Mold on the sensor (gee, mold on a boat?...LOL)
-Cooked electronics form being in a closed boat in the sun...

cheers
sinnerman is offline   Reply With Quote
Old 22-03-2023, 07:28   #28
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 9,965
Re: Kidde smokers run amuk

Quote:
Originally Posted by CaptTom View Post
Live and learn! I knew about Hydrogen, I've watched it bubble out. So what is that "rotten egg" smell when a battery is overcharging? I just assumed that was what was causing the detector to alarm. Hydrogen rises in air. I know at least once I've heard the CO detector go off due to battery charging, when the detector wasn't on the overhead, or near or above the battery compartment, so it wouldn't have "seen" much Hydrogen.

The classic "rotten egg" smell is hydrogen sulfide (H2S), but a battery that is charging hard will emit H2SO4 (battery acid) fumes, which have a related smell.



H2 rises quickly, but in a closed cabin it does not really have a place to go. And like hot air, once it mixes in with the other air in the cabin, it does not separate, at all. That is myth. It only rises separately when there is no mixing, similar to how propane settles through air when undisturbed, but does not separate once mixed in. So the detector would NOT have to be over the battery. Another myth.
__________________
Gear Testing--Engineering--Sailing
https://sail-delmarva.blogspot.com/
thinwater is online now   Reply With Quote
Old 22-03-2023, 07:31   #29
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 9,965
Re: Kidde smokers run amuk

Quote:
Originally Posted by Photonsailor View Post
In the early years of owning and refitting our previous sailboat, we had the smoke and gas alarm go off repeatedly moored in a marina. Sometimes but not always, after coming back to the boat after some hiking. Hatches closed, because you never know when the next shower is gonna hit in the Scandinavian summer.

So, sometimes it alarms, sometimes no alarm and none for our noses discernible smell, not even my wife's nose! I thought, very annoying this thingy, and I have to hinder wife using it as a frisbee. After a few days I realize it only goes off when we have the wind in from stern. I had also upgraded the propane locker to a for purpose built "airtight" gas bottle container, with drainage out at bottom through assigned throughhull, and air-inlet from top to outside. I also had electrical remote switch on the bottle, always off when not using stove (a must security feature I think).

So, I was in denial! There could not be any unwanted gases, right? Shame on me!

My annoyance threshold was finally reached, and I realized there must be something with the gas container set-up! Lo and behold, after following the out-drainage under a lot of stuff and under the floorboards to the through hull I see that the valve was in the CLOSED position (do not ask me why)!!

So, the very tiny amount of gas diffusing out from the couplings on the gas bottle, had no way to go, and with wind in from stern into the air intake, it was enough pressure to force out a tiny amount of gas (bottle shut off by remote when not in use) and waft it forwards into the living quarters with air from the stern dorades (again, we did not smell anything)!

Since then, I NEVER ignore any gas alarms. Especially not if they would go off repeatedly! They might actually do their job and warn you correctly! We lived to learn!

^^^ And this!

Normally a gas locker drain does not have a valve, since it must be above the waterline. And so you can't close it!!


With several boats and many years in industry, I've seen very, very few true false alarms. Virtually every time there was something. Not always what was on the label, but something worth correcting.
__________________
Gear Testing--Engineering--Sailing
https://sail-delmarva.blogspot.com/
thinwater is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Weed Smokers on Your Boat Chotu Rules of the Road, Regulations & Red Tape 204 06-01-2023 21:08
Kidde Fire Extinguisher Recall Snore Product or Service Reviews & Evaluations 2 18-12-2014 03:01
Isotherm Freezer - Run, Stop, Run, Stop... Cruisin Cat Electrical: Batteries, Generators & Solar 8 24-04-2014 18:06

Advertise Here


All times are GMT -7. The time now is 18:04.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.