First you need to compare apples to apples. Meaning, count the entire
power consumption that comes from your DC supply (batteries/solar).
We have two Mabru 12v units that we bought from The Yacht Rigger. I'm glad we did! Both are DC12V 12K btu/hr units. Running both at maximum
cooling, maximum fan speed combined they draw right at 90A from our 12v nominal
LiFePO4 bank.
This inludes the seawater
pump.
So when you make your comparisons, be sure to include the seawater
pump and any
inverter losses. The pump will be 50-200w and the inverter losses will be 6-7% at an absolute minimum and can be much higher depending on what part of the efficiency curve your load ends up being. Your Multiplus 3KVA is 93.9% @ 800W, 91.5% @ 1600W, 88.3% @ 2500W.
Remember, you'll pay for efficiency one way or the other. More
solar and
batteries if you use more energy.
Boats only hold so much
solar.
There are other advantages too, like no wear and tear on your inverter. You don't have to turn off aircon to run your
galley device, etc.