Re: Circuit breaker for a Lofrans Falkon

Quote:
Originally Posted by Paul L View Post
The breaker does NOT measure or trip based on the cable temperature. It trips based on the current passing through the breaker. So if the windlass motor draws in excess of the breaker rating for a period the breaker will trip.
Thanks Paul. I knew someone would explain better z
Pelagic is offline   Reply With Quote
Old 28-11-2017, 23:08   #17
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Circuit breaker for a Lofrans Falkon

Quote:
Originally Posted by Pelagic View Post
Thanks Paul. I knew someone would explain better z
Thanks for the correction. It should read as you edited NOT
__________________
Paul
Paul L is offline   Reply With Quote
Old 30-11-2017, 17:07   #18
Registered User

Join Date: Apr 2015
Location: Home port: Ft Lauderdale, Florida
Boat: VIA 42, aluminium cutter
Posts: 141
Re: Circuit breaker for a Lofrans Falkon

Yes, you need to upgrade the breaker to the recommended 125A.

And you also need to verify that the existing power cables will handle 125A. I suspect they will have to be upgraded.
Remember, when calculating the correct cable size, you must use DOUBLE the run from battery to windlass. Use the 10% voltage loss table.
blueazimuth is offline   Reply With Quote
Old 01-12-2017, 07:41   #19
Registered User
 
SVTatia's Avatar

Join Date: Jul 2007
Location: Toronto, Canada
Boat: Luders 33 - hull 23
Posts: 1,787
Re: Circuit breaker for a Lofrans Falkon

Quote:
Originally Posted by blueazimuth View Post
Yes, you need to upgrade the breaker to the recommended 125A.

And you also need to verify that the existing power cables will handle 125A. I suspect they will have to be upgraded.
Remember, when calculating the correct cable size, you must use DOUBLE the run from battery to windlass. Use the 10% voltage loss table.
As per post # 7.
SVTatia is offline   Reply With Quote
Old 01-12-2017, 07:56   #20
Registered User

Join Date: Apr 2012
Location: Currently in Spain
Boat: Island Packet 420
Posts: 419
Re: Circuit breaker for a Lofrans Falkon

What is weird is I can't find 125A, only 120A, even through Life and. I have battery cable for the run, so plenty thick cable.

Thank you all.
sailing_gal is offline   Reply With Quote
Reply

Tags
lofrans


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacing Seals in Lofrans Falkon 1500W Windlass marina.alex Anchoring & Mooring 5 08-12-2021 09:00
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Lofrans Falkon - convert to 2 chainwheels hpeer Deck hardware: Rigging, Sails & Hoisting 2 29-03-2015 08:49
Fuse or Circuit Breaker ? ggray Electrical: Batteries, Generators & Solar 5 15-10-2009 15:41
parallel a circuit breaker skyking2 Electrical: Batteries, Generators & Solar 13 03-11-2006 22:00

Advertise Here


All times are GMT -7. The time now is 10:49.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.