16-11-2018, 21:16
|
#31
|
Senior Cruiser
Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,755
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by john61ct
Nope, there is a spec'd min / max not to be messed with, needs to be in range for the **right** backpressure.
Use the one included, ask for specs, or use the spec from whomever they copied, Planar?
|
john back pressure has nothing to do with it . They are forced draft open burnpot systems.
__________________
Non illigitamus carborundum
|
|
|
16-11-2018, 21:36
|
#32
|
cruiser
Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Maybe crossed wires with Propex HS2211?
If so sorry, please ignore
|
|
|
16-11-2018, 22:22
|
#33
|
Senior Cruiser
Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,755
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by john61ct
Maybe crossed wires with Propex HS2211?
If so sorry, please ignore
|
entirely possible and personally I would not recommend the Propex HS2211
Due to it using propane as its fuel.
__________________
Non illigitamus carborundum
|
|
|
17-11-2018, 06:55
|
#34
|
Registered User
Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,342
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by newhaul
john back pressure has nothing to do with it . They are forced draft open burnpot systems.
|
Right. Mine came with a plastic hose for the combustion air intake. I think the idea is to quiet things down a little. I plan to remove mine, since the unit is behind some cabinetry anyway, and I suspect it's restricting the draft and contributing to overheating on "high."
If I had it to do again, I'd plan to minimize the exhaust hose run even if it meant longer hoses for the heated air discharge.
|
|
|
17-11-2018, 09:29
|
#35
|
Senior Cruiser
Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,755
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by CaptTom
Right. Mine came with a plastic hose for the combustion air intake. I think the idea is to quiet things down a little. I plan to remove mine, since the unit is behind some cabinetry anyway, and I suspect it's restricting the draft and contributing to overheating on "high."
If I had it to do again, I'd plan to minimize the exhaust hose run even if it meant longer hoses for the heated air discharge.
|
tom we don't actually need to use the intake air hose ( for the most part there are always exceptions.)
overheating ? Ok when was last cleaning ? Is there any restriction on the air runs ( cold or hot) ? How long is the exhaust line?
__________________
Non illigitamus carborundum
|
|
|
17-11-2018, 14:09
|
#36
|
Registered User
Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,342
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by newhaul
overheating ? Ok when was last cleaning ? Is there any restriction on the air runs ( cold or hot) ? How long is the exhaust line?
|
It's overheated (shut down with an error code) on anything much above half-way on the heat setting since it was first installed. The air intake and outlet are within a couple of feet of the unit, with only one 90 degree elbow each. The exhaust hose probably runs 7-8 feet, with some ups and downs along the way.
I suspect that length of exhaust hose, although within spec IIRC, is probably the problem. I'm planning to remove the combustion air intake hose and see if there's any improvement.
|
|
|
17-11-2018, 14:28
|
#37
|
Senior Cruiser
Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,755
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by CaptTom
It's overheated (shut down with an error code) on anything much above half-way on the heat setting since it was first installed. The air intake and outlet are within a couple of feet of the unit, with only one 90 degree elbow each. The exhaust hose probably runs 7-8 feet, with some ups and downs along the way.
I suspect that length of exhaust hose, although within spec IIRC, is probably the problem. I'm planning to remove the combustion air intake hose and see if there's any improvement.
|
your combustion exhaust is to long especially if it is lagged the full distance .
An improvement would be to just spot wrap and insert it into a 2 inch outer pipe . Allows for the exhaust to bleed off excess exhaust temperature.
__________________
Non illigitamus carborundum
|
|
|
21-11-2018, 11:13
|
#38
|
cruiser
Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by newhaul
john back pressure has nothing to do with it . They are forced draft open burnpot systems.
|
OK, but the right hose length **is** apparently important?
What is the underlying reason for that if I was wrong about it being back pressure?
|
|
|
21-11-2018, 11:24
|
#39
|
Senior Cruiser
Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,755
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by john61ct
OK, but the right hose length **is** apparently important?
What is the underlying reason for that if I was wrong about it being back pressure?
|
Its kinda wierd but it has to do with temperature of the exhaust if its to hot it will cause an overheat to cold and you get condensate that will eventually cause a blockage and overheat as well. So its not so much the length as the lay . The issue with it being longer usually means that at some point the exhaust does an upward turn . Hence my recommendation for a condensate drain being installed close to the unit.
__________________
Non illigitamus carborundum
|
|
|
21-11-2018, 15:15
|
#40
|
Registered User
Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,342
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Any chance that a small fan on the combustion air intake side would help?
|
|
|
21-11-2018, 15:36
|
#41
|
Registered User
Join Date: Jan 2015
Posts: 388
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by CaptTom
Any chance that a small fan on the combustion air intake side would help?
|
Go to.....
https://www.eberspaecher-na.com/file...10-29-2018.pdf
Page 61 >DUCTING RATING GUIDE
Hope it helps. You might is also orientation for other issues
__________________
Now or Never
|
|
|
21-11-2018, 15:58
|
#42
|
Senior Cruiser
Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,755
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by CaptTom
Any chance that a small fan on the combustion air intake side would help?
|
unfortunately tom no that won't do any good it will actually cause issues.
Adding a fan on the intake would cause an imbalance and combustion issues with the fuel to air ratios in the combustion chamber.
__________________
Non illigitamus carborundum
|
|
|
21-11-2018, 18:54
|
#43
|
Registered User
Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,342
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
All right, a fan on the combustion side is out.
The ducts are short and only use 2 el's and no significant obstructions. Using the numbers in the manual, I'd be maybe a "2." I don't think that's the problem.
Next step is to remove the combustion air intake hose (no real reason for it.)
Failing that, I'm thinking of moving the whole thing to another location to make the exhaust shorter, although that will make the ducting longer.
|
|
|
22-11-2018, 00:43
|
#44
|
Registered User
Join Date: Jul 2018
Posts: 18
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
When I started the thread I was thinking to install the heater in a way to reuse old exhaust and fuel lines from previously present and later removed generator. It had approximately 2.5 meters of the exhaust line ,which is still intact. With adapting fittings of cause.
Is that a bad idea?
|
|
|
22-11-2018, 00:54
|
#45
|
Senior Cruiser
Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,755
|
Re: Chineese or cheap forced air disel heaters vs expencive alternatives
Quote:
Originally Posted by navado
When I started the thread I was thinking to install the heater in a way to reuse old exhaust and fuel lines from previously present and later removed generator. It had approximately 2.5 meters of the exhaust line ,which is still intact. With adapting fittings of cause.
Is that a bad idea?
|
The fuel line would work just great
2.5 m is a long exhaust for a smaller air unit are we Talking1inch exhaust or 2 inch?
__________________
Non illigitamus carborundum
|
|
|
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Rate This Thread |
Linear Mode
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
Advertise Here
Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
Vendor Spotlight |
|
|
|
|
|