Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Hi Guys,

Hoping that you can help. Since we are having some mild December days on the Chesapeake, I decided to de-winterize my freshwater system for a 2 day visit to the boat to tackle some projects.

I filled my freshwater tank and then switched on my fw pump and waited until my hot water heater (Atwood ehm6) filled and the motor turned off once properly pressurized. Everything seemed as normal.

I then turned on my water heater and waited about an hour. I turned on my kitchen faucet (to hot) and noticed something weird. There was plenty of hot water coming out but the freshwater pump was not coming on. It ran for a good 7-8 seconds and then the pump came on. Closing the faucet, the pump remained on for another good 7-8 seconds and then shut off. My FW system has never acted like this before in my 3 seasons on the boat. There is no expansion tank (that I know of).

I then turned off the circuit and drained the hot water heater, refilled it with cold tank water and tried again. Same thing. This made me very worried that my tank is somehow over-pressurized.

I checked my pressure relief valve and it seems to be working properly. Draining water into the bilge when pressed.

Any ideas of what could be causing this? Thanks in advance for any insight or diagnoses.

Joe
JoeDoc is offline   Reply With Quote
Old 16-12-2019, 18:27   #2
Registered User
 
DeepFrz's Avatar

Cruisers Forum Supporter

Join Date: Mar 2006
Location: Winnipeg
Boat: None at this time
Posts: 8,462
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Air in the water system acting as an expansion tank. Possibly air trapped in the hot water tank or elsewhere. Did you make sure the air was out of all the lines?
DeepFrz is offline   Reply With Quote
Old 17-12-2019, 07:02   #3
Registered User
 
CaptTom's Avatar

Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,119
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

This is pretty normal. There can be a "bubble" of air in the top of the water heater, or as DeepFrz points out, in the lines.

With use, the bubble shrinks and the air works its way out of the lines, and you'll notice less time between opening the hot tap and hearing the pump.

My water heater is plumbed into the engine coolant, so when running the mains it gets really hot. I try to remember to open a hot water tap about an hour after getting underway to release the built-up pressure.

Water expands when heated, but it can't be compressed. That extra volume has to go somewhere. If there's no air above the water in the tank to compress, it'll force its way back through the cold water inlet. That's why many boats have expansion tanks and/or one-way valves.
CaptTom is offline   Reply With Quote
Old 17-12-2019, 07:25   #4
Moderator
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,084
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Your pressure controlled pump is a wonderful gauge of what's happening in your freshwater system. It pressurizes the system, including any air, such as you just discovered. If pressure ramains up, nothing then happens, but if you have a leak or left something turned on, the pump will cycle, bumping along for a few revolutions, and then off as pressure is restored. With no air in the system, the pump will cut off just after you close a valve, because it is just pressurizing the expansion of your hoses and pipes. Being able to hear the pump lets you know what is going on.
__________________
Never let anything mechanical know that you are in a hurry.
tkeithlu is offline   Reply With Quote
Old 17-12-2019, 09:36   #5
Registered User
 
sailone3032's Avatar

Join Date: May 2011
Location: Ottawa, Canada
Boat: Contest 50CS
Posts: 59
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

If you noticed that the water was too hot and the pressure was high, perhaps there is an issue with the thermostat and the water is boiling creating the pressure. I would check the temperature of the pipes at the exit of the tank they should be below 150 deg F
sailone3032 is offline   Reply With Quote
Old 17-12-2019, 09:41   #6
Registered User

Join Date: Feb 2019
Posts: 70
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

PV = nRT

You increased the temperature of a closed system. Of course pressure increased as a result.
SwellGuy is offline   Reply With Quote
Old 17-12-2019, 13:43   #7
Registered User

Join Date: Mar 2011
Location: fl- various marinas
Boat: morgan O/I 33' sloop
Posts: 1,447
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

probably not a problem. there is normally a lag between turning the hot tap and the pump sensing a pressure loss. a few seconds is no cause for concern unless your hot water is substantially hotter than it should be but that seems unlikely.
Dave22q is offline   Reply With Quote
Old 17-12-2019, 14:14   #8
Registered User

Join Date: Jan 2016
Location: Beaufort, NC, USA
Boat: Ta Chiao 56
Posts: 753
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Adding an expansion tank might be a good idea.
Brewgyver is offline   Reply With Quote
Old 17-12-2019, 15:05   #9
Registered User

Join Date: Nov 2013
Location: Nice, France
Boat: Hunter Marine 38
Posts: 1,342
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Did you open the through-hull of the pressure relief valve? Every hot water tank has a pressure relief valve, to the outside or in the bilge. You were lucky that there was air in the system to compensate for the increase in water volume.
Without air the increase in water volume could have split your tank.
sailormed is offline   Reply With Quote
Old 17-12-2019, 15:27   #10
Registered User
 
CaptTom's Avatar

Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,119
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Quote:
Originally Posted by sailormed View Post
Did you open the through-hull of the pressure relief valve? Every hot water tank has a pressure relief valve, to the outside or in the bilge. You were lucky that there was air in the system to compensate for the increase in water volume.
Without air the increase in water volume could have split your tank.
Interesting, I'd never heard of plumbing the P/T relief valve to a through-hull.

But you make a good point. If there's too much pressure, that valve should release it. Likewise if it overheats, which can happen if you have an engine jacket water loop connected. Those valves are pretty reliable. The usual failure mode is to start leaking, not fail to open.
CaptTom is offline   Reply With Quote
Old 17-12-2019, 15:56   #11
Registered User
 
NYSail's Avatar

Join Date: Jan 2012
Location: Long Island, New York
Boat: Beneteau 423 43 feet
Posts: 851
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

There s assumed pressure with hot water. System is normal.
NYSail is offline   Reply With Quote
Old 17-12-2019, 23:58   #12
Registered User

Join Date: Nov 2013
Location: Nice, France
Boat: Hunter Marine 38
Posts: 1,342
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Quote:
Originally Posted by CaptTom View Post
Interesting, I'd never heard of plumbing the P/T relief valve to a through-hull.

But you make a good point. If there's too much pressure, that valve should release it. Likewise if it overheats, which can happen if you have an engine jacket water loop connected. Those valves are pretty reliable. The usual failure mode is to start leaking, not fail to open.
My 2005 Hunter 38 has the pressure relief valve going to a mid-ships through hull. My neighbour has the same boat and had the pressure relief TH closed. He had to replace his hot water tank
sailormed is offline   Reply With Quote
Old 18-12-2019, 03:44   #13
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,440
Images: 241
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

Quote:
Originally Posted by CaptTom View Post
... Water expands when heated, but it can't be compressed. That extra volume has to go somewhere. If there's no air above the water in the tank to compress, it'll force its way back through the cold water inlet. That's why many boats have expansion tanks and/or one-way valves.
And your tank has a pressure release valve.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 18-12-2019, 15:19   #14
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Water Heater suddenly over-pressurized? Hot water flowing w/o FW pump

You should see what happens to the psi of a tempered water system when the expansion tank's internal bladder fails and the crew, seeing the drop in loop psi, naturally add water to compensate....works great until winter when the whole thing blows up while running in heat mode...
Coolerking is offline   Reply With Quote
Reply

Tags
heater, pump, water


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pressurized fresh water pump triggered every 2 hours BrettB Plumbing Systems and Fixtures 30 07-04-2018 20:58
Fresh Water pump draws power when pressurized & causes LED lights to flicker... Duece Construction, Maintenance & Refit 0 16-03-2018 11:10
For Sale: Bulkhead-Mount Force10 Kerosene Heater with Pressurized Fuel Tank LekiM Classifieds Archive 0 18-03-2015 08:15
Hot Water Heater / Block Heater? - 3GM30 BareProductions Engines and Propulsion Systems 9 23-02-2013 18:12
Ohhhhh Hot! Hot! Hot! knottybuoyz Marine Electronics 6 01-06-2007 07:43

Advertise Here