Upgraded thermostat options

My carver originally came with a 1986 16000 btu marine air. When I bought the boat I was told that it was just low on Freon...but the boat came with a 2006 18000 btu marine air, but no controls. I had my a/c guy wire my old controls to the new system. I’m wondering if I could upgrade to a thermostat that will turn the unit off and on like a house
Attached Thumbnails
Click image for larger version

Name:	9F0F2F72-CB0C-49D0-BB17-D3456518CA49.jpeg
Views:	280
Size:	60.4 KB
ID:	213321   Click image for larger version

Name:	3BC3BA62-03B4-4411-966E-01EDD368C5E1.jpeg
Views:	119
Size:	108.8 KB
ID:	213322  

gotjeepzj is offline   Reply With Quote
Old 21-04-2020, 03:26   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 51,347
Images: 241
Re: Upgraded thermostat options

Greetings and welcome aboard the CF, gotjeepzj.

Yes.
Marine Air (now Dometic) Systems Air Conditioning Air Conditioning Controls
Marine Air Systems Air Conditioning Controls | Tropical Marine AC
https://citimarinestore.com/citiguid...ntrols-for-ac/
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 21-04-2020, 09:54   #3
Registered User

Join Date: Dec 2019
Location: on our boat cruising the Bahamas and east coast
Boat: 2000 Catalina 470 #058
Posts: 1,339
Re: Upgraded thermostat options

They make control pads (digital) where you can setup temp setpoints. Some models also allow automatic fan settings so it owuld then operate just like home.
GreenWave is offline   Reply With Quote
Old 21-04-2020, 14:53   #4
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Upgraded thermostat options

That unit came with a Passport I/O control.
Coolerking is offline   Reply With Quote
Old 21-04-2020, 14:59   #5
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,348
Re: Upgraded thermostat options

In order for you to upgrade one so that it will operate like a house I.E. fan only comes on with the compressor, you need a thermostat that senses the air temp at the thermostat, like a house does.
All Marine AC’s that I am familiar with sense the room air temp in the return air grill, so that it takes constant air flow to continuously know what the room air temp is.
That’s not an insolvable problem of course and I have seen some window units for houses solve that issue by running the fan for 5 min every 30 min or so.
a64pilot is offline   Reply With Quote
Old 21-04-2020, 15:33   #6
Registered User

Join Date: Apr 2020
Boat: Amel 53, Super Maramu
Posts: 428
Re: Upgraded thermostat options

Quote:
Originally Posted by a64pilot View Post
In order for you to upgrade one so that it will operate like a house I.E. fan only comes on with the compressor, you need a thermostat that senses the air temp at the thermostat, like a house does.
All Marine AC’s that I am familiar with sense the room air temp in the return air grill, so that it takes constant air flow to continuously know what the room air temp is.
That’s not an insolvable problem of course and I have seen some window units for houses solve that issue by running the fan for 5 min every 30 min or so.
It is most certainly not insoluable, at least two builders of small yacht AC units have solved it.

MarineAire AC units have both options. A remote themostat, or a fan that runs 30 sec every 10 minutes to sense air temperature at the return grill.

Mermaid AC units dispense with the whole problem by using a standard 4-wire household thermostat, which of course includes the temperature sensor. A much better solution, IMO, since controller issues are frequent sources of trouble, and you can swap out one of their thermostats at any hardware store with what ever controller options you might want to spend money for.

For sophisticated air conditioners, I have never understood the rational for the return air grill sensor--other than it is cheaper and ties the customer to your spare parts forever.
SVHarmonie is offline   Reply With Quote
Old 21-04-2020, 19:21   #7
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Upgraded thermostat options

Are you cooling part of the room where the sensor/display is at?
Or are you cycling the air through coils and reading the effect over time?
The AC only knows what you are telling it, that means you pretty much need to measure the air temp at the return air path, and the fan needs to run to do this.
This becomes very apparent when you are trying to cool a pilot house with lots of glass on a sunny day.

Many of the marine hvac systems we install will default to the display to read the air temps if possible when the alt-air tsep is removed from the board.
These can be influenced by it's position in the boat, ie..in the sun.
Keep in mind that there are many many different ways to do marine hvac, in the end, its all about removing heat.
Coolerking is offline   Reply With Quote
Old 22-04-2020, 11:22   #8
Registered User

Join Date: Apr 2020
Posts: 10
Re: Upgraded thermostat options

Thanks all. First let me clarify my original post. The boat had the optional 16000 btu unit installed when I bought it. It didn’t work. I was told it uses a can of Freon every 2 years and it was time to refill. Bad news. That was not the case. As soon As I put Freon in it, and turned to start, it would trip the breaker. Locked compressor. Good news...when I bought it he had given me a 2006 18000 btu unit. He was told it was good, but had never hooked it up, and it didn’t have any controls. I had our marina a/c expert check it out and he said the compressor was free and it had Freon. We hooked it up and he used my old controls on the newer a/c. I haven’t had problems in the year it’s been done.


Current situation is I run a 6000 btu window unit all day in the summer. Set on max cold and high fan it struggles to keep the boat about 84 degrees. I get home I turn on the main unit and the boat will cool off in about 10 mins. I don’t like having to leave the window unit on all day. And I don’t like the idea of leaving the blower and a/c water pump running on the main unit all day either. I was hoping I could use a thermostat of some sort that would kick on everything but then turns everything back off...cycling.

Currently the unit, return air, and biggest vent are located center of boat. I only have 2 vents and you wouldn’t believe how they ran the air to the bedroom.

I found the 3 knob conversions for $700+ but if I have to pay that much, I might as well pay $1700 and get a brand new one that comes with the modern digital thermostat. So I thought may I have other options and/or maybe I’m missing something.
gotjeepzj is offline   Reply With Quote
Old 22-04-2020, 12:22   #9
Registered User

Join Date: Aug 2018
Location: Hudson Valley, NY
Posts: 365
Re: Upgraded thermostat options

A regular home t-stat and a couple of relays ought to do the trick.
Pete17C is offline   Reply With Quote
Old 22-04-2020, 13:29   #10
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Upgraded thermostat options

On a factory original system,the water pump should only run when the compressor is running, i.e. the unit is cooling.
The fan will run all the time, as its designed to do, in auto modes, its speed will vary depending on the ambient/setpoint differential.
Coolerking is offline   Reply With Quote
Old 22-04-2020, 13:41   #11
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,627
Re: Upgraded thermostat options

Quote:
Originally Posted by Coolerking View Post
On a factory original system,the water pump should only run when the compressor is running, i.e. the unit is cooling.
The fan will run all the time, as its designed to do, in auto modes, its speed will vary depending on the ambient/setpoint differential.


I seem to remember the old three knob units running the water pump continuously.
Sailmonkey is offline   Reply With Quote
Old 22-04-2020, 13:46   #12
Registered User

Join Date: Apr 2020
Posts: 10
Re: Upgraded thermostat options

Quote:
Originally Posted by Sailmonkey View Post
I seem to remember the old three knob units running the water pump continuously.
That is correct sir. Continuous.
gotjeepzj is offline   Reply With Quote
Old 22-04-2020, 19:27   #13
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Upgraded thermostat options

Quote:
Originally Posted by gotjeepzj View Post
That is correct sir. Continuous.
Only when asking for cooling, ever.
It's triac is wired into the same circuit that is the compressor L-1.
Keep in mind that the older 3 knob control needed you to switch from "on" to "run".
If it runs all the time then the triac is shorted closed.
The same applies for the compressor and the fan...in the older units, if the triac shorted closed, then it would cause the corresponding device to run on power up/breaker on.
And if the triac has burnt through.. shorted open, then they would not run at all...
Coolerking is offline   Reply With Quote
Old 22-04-2020, 20:54   #14
Registered User

Join Date: Apr 2020
Posts: 10
Re: Upgraded thermostat options

Quote:
Originally Posted by Coolerking View Post
Only when asking for cooling, ever.
It's triac is wired into the same circuit that is the compressor L-1.
Keep in mind that the older 3 knob control needed you to switch from "on" to "run".
If it runs all the time then the triac is shorted closed.
The same applies for the compressor and the fan...in the older units, if the triac shorted closed, then it would cause the corresponding device to run on power up/breaker on.
And if the triac has burnt through.. shorted open, then they would not run at all...
That makes sense actually. One of my biggest issues is when the thermostat works and the compressor cycles off, it’s still pumping 90* lake water through it turning the ac into a heated...same thing in the winter.

Where is the triac located and can it be replaced?
gotjeepzj is offline   Reply With Quote
Old 23-04-2020, 15:47   #15
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Upgraded thermostat options

It's in the control box for the unit itself, usually mounted to the inside surface of the box itself, or, if you have multiple units running on one pump, it would be in the pump relay box.
Coolerking is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thermostat and thermostat housing pbmaise Engines and Propulsion Systems 22 13-01-2017 15:30
Anyone upgraded from ZF10 or HBW100 to larger hurth/ZF? sgtPluck Propellers & Drive Systems 11 01-04-2012 21:04
Upgraded my ICC to Sail . . . Wahoo ! simonmd General Sailing Forum 2 03-12-2010 14:53
Viability of Upgraded Engines on Catamaran WhataWorld! Multihull Sailboats 18 21-08-2010 04:34

Advertise Here


All times are GMT -7. The time now is 09:53.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.