Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by Richard Kollmann View Post
IF new ground does not fix problem remove 2 seconds of small amounts of refrigerant with compressor stopped waiting 5 minutes each time after each start up test and try again.

If LED code displays 4 or 5 or 6 flashes every 4 seconds also run a new power wire with 15 amp fuse direct from battery to control module.
Thanks. How do I remove the refrigerant? With that bicycle type valve?

Thanks
SailorMcCruise is offline   Reply With Quote
Old 13-09-2020, 15:41   #17
Registered User

Join Date: Dec 2018
Location: Wichita/Pensacola
Boat: Lagoon TPI 37'
Posts: 560
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by Coolerking View Post
There is NOT a start or run cap on secop/danfoss 12/24vdc. units
Thanks, I never did see one but didn't know if internal or? I honestly didn't know.
sailingchiro is offline   Reply With Quote
Old 14-09-2020, 06:57   #18
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by SailorMcCruise View Post
Thanks. How do I remove the refrigerant? With that bicycle type valve?

Thanks
Yes, depress the Schrader valve, just like you were letting air out of a bike tire.
Make sure compressor has been off for at least 10 minutes before you do it, as you want to be sure you have positive pressure there.
Coolerking is offline   Reply With Quote
Old 14-09-2020, 23:02   #19
Registered User

Join Date: Jan 2016
Location: San Diego, CA
Boat: Beneteau 40.7
Posts: 343
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

For anyone looking to replace the fan itself, a 12 V computer fan works well. They are quiet, efficient and not expensive.
thunderhoof is offline   Reply With Quote
Old 14-09-2020, 23:43   #20
Registered User
 
Uncle Bob's Avatar

Join Date: May 2010
Location: Sydney Australia
Boat: Fisher pilothouse sloop 32'
Posts: 3,427
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Hi, had a similar problem with mine a few months back, chatted with Pete from ozefridge who suggested the addition of a relay in the cooling fan circuit and voila all is good, thanks Pete.
__________________
Rob aka Uncle Bob Sydney Australia.

Life is 10% the cards you are dealt, 90% how you play em
Uncle Bob is offline   Reply With Quote
Old 15-09-2020, 00:13   #21
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,466
Images: 22
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by Uncle Bob View Post
Hi, had a similar problem with mine a few months back, chatted with Pete from ozefridge who suggested the addition of a relay in the cooling fan circuit and voila all is good, thanks Pete.
How would a relay help?

The fridge was working and now it doesn't. The boat is damp. Jedi has suggested the likely problem is corrosion in the connections, the boat is after all damp. Fitting a relay may help in that making new connections resolves the problem for a while. The problem isn't the fridge, but a damp boat causing corrosion.

Pete
Pete7 is offline   Reply With Quote
Old 15-09-2020, 00:34   #22
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Wink Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by Uncle Bob View Post
Hi, had a similar problem with mine a few months back, chatted with Pete from ozefridge who suggested the addition of a relay in the cooling fan circuit and voila all is good, thanks Pete.
If you install a relay it eliminates the safety factor Danfoss designed into the system to prevent system damage due to excessive high pressure by limiting fan to 1/2 amp. When the trouble LED sends a two flash code replace the fan as all of the 6 LED code flashes are intended to keep these system reliable. Installing a relay on fan is like an electrical circuit without a current limiting fuse or breaker.
Richard Kollmann is offline   Reply With Quote
Old 15-09-2020, 00:41   #23
Registered User
 
Uncle Bob's Avatar

Join Date: May 2010
Location: Sydney Australia
Boat: Fisher pilothouse sloop 32'
Posts: 3,427
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by Pete7 View Post
How would a relay help?

The fridge was working and now it doesn't. The boat is damp. Jedi has suggested the likely problem is corrosion in the connections, the boat is after all damp. Fitting a relay may help in that making new connections resolves the problem for a while. The problem isn't the fridge, but a damp boat causing corrosion.

Pete
Pete, the cooling fan was running but the compressor would attempt to start and then wouldn't. The advice received was that the fan controller was conflicting with the compressor and they weren't playing nicely together, the addition of the relay in the cooling fan circuit bypassed this conflict and to date (touch wood ) all has been good.
As to the damp boat, I would suggest that sufficient forced air ventilation would go a long way to eliminating this problem. It is neither difficult nor expensive yet yields great results.
__________________
Rob aka Uncle Bob Sydney Australia.

Life is 10% the cards you are dealt, 90% how you play em
Uncle Bob is offline   Reply With Quote
Old 15-09-2020, 05:08   #24
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by Uncle Bob View Post
Pete, the cooling fan was running but the compressor would attempt to start and then wouldn't. The advice received was that the fan controller was conflicting with the compressor and they weren't playing nicely together, the addition of the relay in the cooling fan circuit bypassed this conflict and to date (touch wood ) all has been good.
As to the damp boat, I would suggest that sufficient forced air ventilation would go a long way to eliminating this problem. It is neither difficult nor expensive yet yields great results.
It is always a risk and reword situation when you tamper with proven devices designed to prevent catastrophic equipment failures. The Danfoss BD compressor insures system's long life by testing six electrical function at control module during compressor start. The relay to reduce excessive fan amperage is much like those days when people put a copper penny behind a fuse that kept blowing.
Richard Kollmann is offline   Reply With Quote
Old 15-09-2020, 07:39   #25
Marine Service Provider

Join Date: Jun 2019
Location: Southern California
Posts: 317
Images: 2
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

The fans used on these systems draw .24 amps, they are 12vdc regardless of the input voltage to the unit.
When they begin to fail they begin to draw more, and this often will cause the start sequence to be interrupted.
I have replaced many dozens of them over the course of the last 17 years.
An easy way to check is to just disconnect the fan and see if the compressor will start, in fact, the compressor is so quiet that the fan noise can make it really hard to hear the compressor run.
Coolerking is offline   Reply With Quote
Old 21-09-2020, 12:11   #26
Registered User

Join Date: May 2019
Posts: 43
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Hello people.
Sorry I could not answer earlier. Was is a very remote spot, enjoying life without a fridge
So:
I did another test with proven to work thick cables running directly from the battery - no change.
I did release refridgerant with the schrader valve - no change.
Since "Jedi" mentioned corrosion: Is there any other element that coould be afflicted by corrosion inside of the element ( it looked quite ok to me on visual inspection - just the outside of the compressor is rusty at places )
SailorMcCruise is offline   Reply With Quote
Old 21-09-2020, 12:52   #27
Registered User
 
wingssail's Avatar

Join Date: Jan 2010
Location: On Vessel WINGS, wherever there's an ocean, currently in Mexico
Boat: Serendipity 43
Posts: 5,508
Send a message via AIM to wingssail Send a message via Skype™ to wingssail
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by SailorMcCruise View Post
Hello people.
Sorry I could not answer earlier. Was is a very remote spot, enjoying life without a fridge
So:
I did another test with proven to work thick cables running directly from the battery - no change.
I did release refridgerant with the schrader valve - no change.
Since "Jedi" mentioned corrosion: Is there any other element that coould be afflicted by corrosion inside of the element ( it looked quite ok to me on visual inspection - just the outside of the compressor is rusty at places )
Now that you have done all this testing and inspections (and wiring testing) and reported it all to us, I am going to venture to say that the compressor is bad. From every thing you describe the electronic module is doing is thing. The compressor just isn't starting.

I've had these exact symptoms with an exactly similar system, (BD35 /101N0210, air cooled condenser, etc, in June 2019, with a 9 year old system.

In my case I noticed the compressor attempting to start several times, then finally starting, for several days before it finally stopped for good.

I replaced the entire refer including the evaporator mainly because my quick connect fittings had been damaged previously (during the original installation) and I knew that I could not connect a new cooling unit to the existing evaporator. It gave me an opportunity to R&R the box and insulation.

The report is here: WINGSSAIL - Cruising Log of Wings - Serendipity 43 - Fred Roswold & Judy Jensen
Attached Thumbnails
Click image for larger version

Name:	80-180228-New Compressor.jpg
Views:	105
Size:	24.8 KB
ID:	223899  
__________________
These lines upon my face tell you the story of who I am but these stories don't mean anything
when you've got no one to tell them to Fred Roswold Wings https://wingssail.blogspot.com/
wingssail is offline   Reply With Quote
Old 27-02-2022, 00:30   #28
Registered User

Join Date: Feb 2019
Posts: 8
Re: Troubleshooting Danfoss BD35 / 101N0210 unit where compressor fails to start

Quote:
Originally Posted by Richard Kollmann View Post
If you install a relay it eliminates the safety factor Danfoss designed into the system to prevent system damage due to excessive high pressure by limiting fan to 1/2 amp. When the trouble LED sends a two flash code replace the fan as all of the 6 LED code flashes are intended to keep these system reliable. Installing a relay on fan is like an electrical circuit without a current limiting fuse or breaker.
I'm getting a 2 flash code without a fan connected. I run my fan 24/7 direct wired.
I can hear compressor kick for half a second and stop, 10 or so seconds later it tries again. I have 13.1 volts at controller. I've found a fellow in Melbourne, Australia that builds controllers at half the cost, he also sell originals so I'm getting a few brought over here to Portugal for spares.
Zencra is offline   Reply With Quote
Reply

Tags
compressor


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
[SOLD] Danfoss 101N0210 (NEW) s/v Jedi General Classifieds (no boats) 6 02-07-2022 16:49
Looking for help troubleshooting Danfoss BD35 on Norcold DE-0041R Irish Rover Plumbing Systems and Fixtures 17 15-09-2019 06:13
Troubleshooting a Danfoss BD35 Sonosailor Plumbing Systems and Fixtures 2 28-11-2015 12:23
Danfoss bd35 compressor economy mode Dod42 Electrical: Batteries, Generators & Solar 14 10-07-2014 06:18
240vac Danfoss Compressor to 12vdc Danfoss cat man do Plumbing Systems and Fixtures 15 30-05-2013 13:13

Advertise Here


All times are GMT -7. The time now is 13:08.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.