Hello, Richard,
Quote:
Originally Posted by Richard Kollmann
Skip, I am
trying to follow your refrigeration troubles but lack the normal information
needed to formulate an opinion that might help you. Information on Seafrost
12/24 volt units I have heard from boaters has been good although this is
only three or four Emails. Your first system was a Frigoboat keel cooler
with a BD50 compressor that performed well at freezer and refrigerator
temperatures until system failed. You now report new SeaFrost air and water
cooled unit with a 30% larger BD80 compressor will not maintain previous
Frigoboat BD50 compressor box temperatures with either air or water
cooling.
|
Almost right - there is no way to do water-only cooling. However, even on
high, non-stop (I looked up some prior correspondence with Cleave - Sea
Frost, and Clay - Hansen Marine), air cooling only will not succeed in
cycling the freezer, and temperatures gradually rise to barely frozen; as a
result, also, my reefer rises and can't keep up with the near-freezing input
vs the usual well-under-freezing input..
Quote:
Originally Posted by Richard Kollmann
dd
As I understand it your new BD80 system is
powering two or three evaporator thermo plates not holding plates or
roll-bond thin plate evaporators.. Refrigerant flow control is accomplishes
by one or more evaporator pressure regulators instead of a capillary tube or
TXV.
|
Yes. My system is like as shown in their website, with, in our case,
instead of the two larger plates which, in the end, didn't fit due to the
slight tapering between top and bottom, originally ordered, Clay went with 3
slightly smaller plates, which are mounted on the walls not of the spillover
divider. Without doing the math, I expect that this coverage meets the
specified minimum of 60% coverage of the available wall surfaces, as the
plates could have been longer if needed. As it is, they extend well under
the shelf position we have.
BD Series
We have the largest model, the BDXPXAW System. As you can see in their
brochure, and the link to the condenser test (which presumes to demonstrate
the superiority of air over
keel cooling, and describes their water cooling
system, which appears to be merely a
single loop), we have an oversized air
condenser, and a water jacket condenser. I confess to not having
taken detailed pictures of the unit when it was open during
installation, so
I don't really remember the layout in it. During
installation, it was
presumed that we would be operating on air cooling only, but Clay ordered
the water option unit which now has a rocker rather than the shown toggle
switch for enabling the
pump, presumed changed for durability reasons.
The main page also has amp draws for each of their units, as well as the
available BTUs removed. Note that it's either at -10F or -30F plate
temperatures. Given that in my conversations with Cleave, wherein he
suggested using whatever would produce something in the +20F range (which
would mean plate temperatures of about a 15F shutoff), I think that's a bit
disingenuous. The BEST, with water and air, that I could not-quite reach is
a plate temp of +2.5.
The anectdotal claims of too many to count here in CF of box temperatures of
zero or lower make me think it must be possible. Just not with my
system/installation/environment, because we've been having this discussion
since we left St. Augustine, with the above results.
Our system has an AEO which - if you can believe the literature, is very
smart, adjusting
RPM by 400 per time, up or down as needed to achieve a 52%
run time. Regardless of setting (low, medium, high, automatic), I've never
experienced a 52% runtime. As you know, for a while I was being entirely
anal - well over a thousand readings - about recording times and
temperatures of on-off moments (one reading when it went off, one when it
restarted) for both the refrigerator and freezer; about the best I achieved
was a 2/3, and more like 80% runtime vs offtime. Our control is the ETT.
In conversation during Clay's fiddling with the system, he told me that
Cleave recommended not using the ETT in automatic, and that he just left HIS
on low all the time. Eventually, recently, I got the system to - at least -
cycle reliably (with water cooling working) on medium. In conversation with
Cleave, about using automatic, which was presumed to be the most efficient,
he suggested running it on medium, as that setting used a bit less
power
than automatic. The inference was that this was overall - that using
automatic cost more than straight medium, which, by extrapolation, was way
more than straight low (which can't keep up running full time). As this was
all by
phone, I have no written confirmation of that, but it appears moot,
as low only won't cut it.
I haven't, in a great while, done overnight calculations of draw. I guess
it's time to do that again. What I do is note our
current AH deficiency when
we turn off the light (two 0.5A fans and miscellaneous overhead the only
load, dark and still so no
wind or
solar contribution), and again when we
get up, before turning on any other loads. For weeks on end, the AH
consumed were consistent when regarded as an average over the hours
measured.
From that I infer - without having a dedicated amphour recorder attached to
the unit/breaker - that our system behaves consistently and that I can rely
on those figures.
Our system has something not shown in the brochure - an
accumulator/filter/dryer with a sight glass. When the system was first
charged, there were bubbles; Clay said that was of no event. However,
eventually, during a roadtrip where we were gone for a month, he continued
to attempt to get performance from the system. The constant pressure valve,
on which more later, along with both temperature probes, were replaced. We
even tried using box temperature as the trigger, rather than plate
temperature, for a bit, during the early days, when I was still aboard.
While we were gone, apparently Clay capitulated, and installed the water
cooling
pump and lines, eventually pronouncing it good, and increased the
charge to where there were only the most infrequent and minor bubbles in the
glass.
Finally, we have a constant pressure valve, nominally set (see below) for
4PSI, with which Clay fiddled fairly extensively before replacing the first
one, considering that to be defective.
I don't - and guess that Clay didn't, either - know whether our probes which
were the first defective
replacements were, indeed, defective. Perhaps we
simply were not getting to temperatures. Both Clay and I have IR
guns; they
don't agree with each other, or with indicated box temps. Out of
frustration, Clay bought a simple mechanical thermometer, and mounted it in
various places around the box during testing. If THAT could be believed,
the actual temperatures AT THE PROBE (hung it on the wire right before the
probe) were between 8-10 degrees colder than indicated on the ETT. Shooting
the probe temp supported that distinction.
So, I'm left with slowly raising the cutoff (now at +6.5 and a hystersis
of - also - 6.5), to achieve a box temperature which is nominally warmer
(nominally as we don't have the previous Carel thermostat and probe
installed for reference) than what the Frigoboat system did at half the
amps. During Clay's test, he bought some ice cream; until he fiddled some
more, it was not firm - which means, to me, that what I see for temperatures
on the ETT cannot be relied upon, and I'm constrained to dead reckoning to
attempt a box temperature which I used to be able - warm loading aside - to
keep within 2 degrees (8 cutoff, 2 hysterisis) in my prior system.
Granted, that was box, and not plate temperature, as I understand to be the
industry norm, so I have no idea what my actual plate temps were. However,
as it was of the thinwall (with a SS front for longevity) variety, I
speculate it changed temps rather more swiftly than the
current plates,
which act a bit like cold plates; there's something inside the box, it
seems, which acts a bit as a thermal flywheel. If so, the plate temps, when
not
charging, likely were very similar to box temps (of course, I could be
entirely mistaken, but logic suggests), and the ability to quickly remove
heat (because of the speed of decline in temps during evaporation) seems
like it would be more effective at maintaining that narrow hysterisis.
By contrast, my ETT box probe readings run about 13 or so cutoff, and low
20s restart, a huge swing by comparison. In one of the other threads,
someone suggested going to a 2-3° hysteresis for improvement - do you agree?
Finally, this increase in my cutoff temps has meant that my reefer actually
cycles - in rough approximation with the freezer, because when the spillover
fan engages, it blows the warmer air into the freezer, causing it to
energize soon after the reefer has shut off, usually - rather than was the
case when we were a couple of degrees lower. In that lower freezer temps,
the reefer was able to get by with convection, running the spillover fan
only when warm loaded, and, occasionally, the temp would drop below our
desired level.
So, from that (our temps are such that we actually have to use the spillover
fan on a regular basis), I infer that our system is reasonably balanced in
temperature terms. In addition, both boxes cycle reliably (the freezer
actually - if the water is working properly - gets to turn off on a regular
basis), albeit at a much higher energy cost than I'm happy about.
Quote:
Originally Posted by Richard Kollmann
The poorer performance change from the new
BD80 compared to the old BD50 Must result from one of the
following:- Insulation has lost some of its original R
value. After 10 years this is possible on open cell insulation without
moisture shielding but not a problem on your Extruded Polystyrene board.
Morgan OI boas did have a problem with moisture interring insulation from a
leaking deck seal this question can be eliminated by drilling a small hole
inside box near bottom of liner. If dry behind liner moisture is not a
performance problem.
|
- When the first plates were found to be too large to fit both into the box,
we had a hole at the bottom of the first one mounted (and three others, too,
of course) which was open. No water. We epoxy/cabosil filled those holes
and started over for the new plates ordered. FWIW, Clay was able to sell
those larger plates for an installation before we returned from our road
trip, so he was particularly pleased at not having to have dead inventory...
Quote:
Originally Posted by Richard Kollmann
- Under the summer climate conditions where
the boat is now ambient water and air temperatures are about the same so why
is it this unit with an oversize fan condenser is not performing as well or
better with air cooling? Normally boaters find keel coolers are less energy
efficient in seawater above 85 degrees F over a 24 hour day than air fan
cooled?
|
That is, to put it mildly, the question of the day.
Quote:
Originally Posted by Richard Kollmann
- It is possible that refrigerant is
contaminated. I found one boater that spent over $1,000 on service calls
because another manufacturer failed to remove test nitrogen from either the
new condensing unit or evaporator assembly.
|
I'm not in a position to judge - but I'm confident that Clay knows what he
was doing, and, this being a new system, I don't know that nitrogen was
involved in it, ever. Additionally, I did see him do the initial evacuation
test (leaving the gauges connected overnight), and since he replaced the
constant pressure valve, I assume he did so again at that time. So, I am
doubtful of that issue being the cause.
Quote:
Originally Posted by Richard Kollmann
- Refrigerant flow control is always a
possible destroyer of good refrigeration performance. Of all the different
refrigerant flow controls I find the suction pressure regulator devise the
most difficult to be precise with when balancing a boat refrigeration
system. These small pressure regulation devices were designed for drink
machines where ice was produced in one refrigerant circuit and cooling
liquid in another. When pressure regulator are used at freezer flow
temperatures valve adjustments are even more delicate. Capillary tubes have
a narrow flow control range, Thermo Expansion Valves used in mobile boat
refrigeration have a much wider flow control range while Suction Pressure
regulators are manually adjusted to produce a fixed flow control range like
4 psi to 10 psi.
|
Ours is the suction pressure regulator variety. At one point, after a
decommissioning (we have to decommission the system every time we're off the
boat, as it would flatten our
batteries in a few days without our being able
to recharge with the
Honda 2000), I noted that the bottom half of the third
plate wasn't frosted. Conversation with Cleave had me fiddling with this
regulator.
His initial instruction was to mark the start point and give it a half turn
CW. That very quickly not only frosted the plate, but the line all the way
to the compressor. Over a series of steps, I reduced that change by half
each time. When I got to where it HAD been, it was still over-frosted. So, I
gave it a quarter turn CCW, and the frost receded. Too far, I did the
same - restoring by halves - and wound up where I started, which was,
however, by this time, proper - the plate was fully frosted, and the line,
as well as the immediate area (less than 1/4") of the plate from which it
exited, wasn't.
However, I've since defrosted; the restart has the bottom third of the third
plate with no frost, again. So, I've again begun having to fiddle with that
valve. I am not at all pleased to think that I will have to do this every
time I defrost or decommission (next decommission coming in a couple of
months).
So, I confirm your opinion of delicacy. However, I fail to understand why,
once set, the regulator should require messing with again, let alone every
time.
Quote:
Originally Posted by Richard Kollmann
If you could find a qualified technician and
not one from HELL he will be able to analyze and see if high and low
pressures are in line with 134a refrigerants for desired evaporator
temperatures. Unfortunately these small pressure regulators do not have a
low pressure test port as do the larger valves, sometimes used on larger
holding plate systems. There are no two ice box conversion system installed
in exactly the same way so tubing lengths, number of bends will all change
the actual evaporator super heat by reading low pressure at compressor
service port instead of valve complicating fixed pressure valve
adjustments.
|
Would that be you? I will, eventually, get the rest of my game-stoppers
sorted out, and resume my shakedown; Lake Sylvia likely would be one of my
stops, as it was nearly 20 months ago when we started our shakedown from
hell. (Most of you don't know that EVERY time we moved the boat, there was
something which HAD to be resolved before we could continue. There have been
seven such
events since we launched, and more have arrived since we tied up
again here in Vero Beach last
Christmas...)
However, I can't get over the angui$h of losing a system which worked
perfectly until it didn't at all, and having $4K tied up in a system which
displays symptoms of not working properly. As seen in a different thread,
Cleave calculates that I have a BTU load well within the capability of our
system - but yet, suggests I'd have better results in total amp draw to
install yet another system for the reefer alone. Aside from the fact that I
can't afford it, I continue to be in the dark as to why a nominally higher
capacity system, using the vaunted, superior to water, air cooling, can't do
the job that a smaller compressor and inefficient keel cooler shrugged off.
Quote:
Originally Posted by Richard Kollmann
Skip, I do not have an answer to the question
about how to handle seawater cooling system flow restrictions.
Hopefully this new thread will get one or two responders with SeaFrost new
BD80 compressor systems to respond.
|
Thanks for your help, Richard, as always. Sorry we missed each other last
time around.
L8R
Skip