Quote:
Originally Posted by dearmstr
Refilled tank will not turn on. I disconnected the line and made sure that there was no residual propane in the lines reconnected and still will not turn on.
|
Assuming you turned the bottle valve to the fully opened position and you have a Solenoid Valve connected to the bottle, did you turn the solenoid on? Most Solenoid Valves are connected to a
control panel that is also connected to one or more gas sniffer/sensors and if one or more
sensor is detecting gas (propane or even hydrogen from a "bubbling"
battery being recharged) the Solenoid Valve will not open (although, normally, a audible
alarm will also sound). Of course, the foregoing also assumes there is
power to the
control panel and from there,
power to the Solenoid Valve. If so, the Valve itself may have failed or been damaged when you removed it to refill the bottle. Fortunately, failed valves remain "closed" as a
safety measure.
FWIW...