More Dometic aircon HP errors

We have 4 dometic aircon units and one shuts off with a HI PS error every once in a while.

There is good flow. I also hooked a dock hose up to the line and flushed it out. The strainer screen is clean and I’ve cleaned the air filter. I’m also leaving the compartment the compressor is in open so there is good airflow.

The unit blows nice cold air.

Sometimes it will run for days without any issue then it errors on high pressure. I’ll try to restart it and it errors again. Then, I’ll hit the power button and away it goes for hours or days.

It was flushed with barnacle buster last year and has only run for a few months after that.

It is hot here (80-100) and the marina water is about 85. I have the set point set to 76.

Anything else I should check?
crayiii is offline   Reply With Quote
Old 26-06-2022, 12:16   #2
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: More Dometic aircon HP errors

The high pressure switches are known to occasionally go bad
Sailmonkey is offline   Reply With Quote
Old 26-06-2022, 12:21   #3
Registered User

Join Date: Apr 2019
Posts: 614
Re: More Dometic aircon HP errors

Quote:
Originally Posted by Sailmonkey View Post
The high pressure switches are known to occasionally go bad
It looks like the unit would need to be recharged after changing the switch. Is that correct?
crayiii is offline   Reply With Quote
Old 26-06-2022, 12:25   #4
Registered User

Join Date: May 2022
Posts: 760
Re: More Dometic aircon HP errors

HP Failures are only caused by insufficient cooling in the condenser. Maybe a bad pressure switch, but this is very rare, and would be very unlikely to give the symptoms you describe.

You say the flow is "good." "Good" is not a number. Get a number.

Collect it in a bucket and calculate how many gallons per hour are flowing and compare this the the manufactuers specification. What might be just fine when seawater temps are in the 70s might not work when they are in the high 80s

If possible, check the temperature of the water coming out of the AC unit. Hopefully you can find a specification for this. If this is above specification, you need more flow.

Lastly, a check for possible fouling of the interior of the condenser: You can do this by hand, but a IR temp meter is more precise: Check the temperature of the line carrying refrigerant out of the condenser. It should be very close to the temperature of the incoming water.

If the refrigerant is still hot coming out of the condenser, there are only three possibilities:
1. water flow is not sufficient. Clean circuit or get bigger pump.
2. the condenser is fouled. Clean it.
3. the condenser is undersized for the incoming seawater temperature. You are stuck...

[Edit]
One more thing I saw once on an owner installed AC unit. The water connections were BACKWARDS. This provided sufficient cooling at low seawater temperatures, but not when they climbed... Worth a quick check as an easy fix...
ItDepends is offline   Reply With Quote
Old 26-06-2022, 12:46   #5
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: More Dometic aircon HP errors

Quote:
Originally Posted by crayiii View Post
It looks like the unit would need to be recharged after changing the switch. Is that correct?


They’re screwed onto a schrader valve (normally) so a small puff is all that escapes.
Sailmonkey is offline   Reply With Quote
Old 26-06-2022, 12:48   #6
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: More Dometic aircon HP errors

Quote:
Originally Posted by ItDepends View Post
HP Failures are only caused by insufficient cooling in the condenser. Maybe a bad pressure switch, but this is very rare, and would be very unlikely to give the symptoms you describe.


8 out of 10 times I’ve seen the behavior described it was a failings HP switch. The others were attributable to a failing pump trigger.

When the seawater flow is insufficient a repeatable pattern appears.
Sailmonkey is offline   Reply With Quote
Old 26-06-2022, 12:50   #7
Registered User

Join Date: Apr 2019
Posts: 614
Re: More Dometic aircon HP errors

The water temp here is actually hitting at and just below 90. The manual does say that at and above 90, we could see these errors.

This unit is on a pump that it servicing two other units and they aren’t getting the error. They also have a bit more flow than this unit so the manifold must be imbalanced.

One other unit that is on its own pump is also running fine.
crayiii is offline   Reply With Quote
Old 26-06-2022, 13:02   #8
Registered User

Join Date: Dec 2019
Location: on our boat cruising the Bahamas and east coast
Boat: 2000 Catalina 470 #058
Posts: 1,303
Re: More Dometic aircon HP errors

Water temps above 85 will cause all sorts of issues including this error and just generally insufficient cooling. Not too different from land based AC units that usually cannot cool more than 25 degrees below ambient.
__________________
Sailing a Catalina 470; now retired
GreenWave is offline   Reply With Quote
Old 26-06-2022, 13:03   #9
Registered User
 
stevec195's Avatar

Join Date: Oct 2011
Location: Fairhope, AL
Boat: Cabo Rico 45 build #005
Posts: 217
Send a message via Skype™ to stevec195
Re: More Dometic aircon HP errors

I had the same symptoms and found the problem to be a loose connection on the high pressure switch!
stevec195 is offline   Reply With Quote
Old 26-06-2022, 13:04   #10
Registered User

Join Date: May 2022
Posts: 760
Re: More Dometic aircon HP errors

If you are pushing the upper boundaries of the allowed seawater temperature, and an imbalance of water flow is giving this unit a bit less cooling I think you have your answer. It fits all the pieces.

It works OK, but is teetering on the edge of too hot. A bit of a longer than normal run, or hiccup in water flow, and it shuts down.

I would not go changing the pressure switch until I was SURE that cooling was sufficient and the exit temperature of the refrigerant was in spec. Even then, I'd probably make sure I was sure and put a gauge set on it before changing parts that are most liking doing exactly what they are supposed to do by shutting the compressor down when it occasionally rises over the max pressure because of the marginal cooling.
.
ItDepends is offline   Reply With Quote
Old 26-06-2022, 13:11   #11
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: More Dometic aircon HP errors

Quote:
Originally Posted by crayiii View Post
The water temp here is actually hitting at and just below 90. The manual does say that at and above 90, we could see these errors.



This unit is on a pump that it servicing two other units and they aren’t getting the error. They also have a bit more flow than this unit so the manifold must be imbalanced.



One other unit that is on its own pump is also running fine.


Ok, now I’ll second what itdepends is saying. With water temp that high, and multiple consumers on the same pump any small restriction in the system cooling circuit can cause this.

If you’re running constantly in really warm growth filled water you might even need to flush every three months of the flow rate is particularly slow through a single unit.
Sailmonkey is offline   Reply With Quote
Old 27-06-2022, 04:13   #12
Registered User

Join Date: Sep 2015
Location: East Coast Florida
Boat: Chris Craft 38 Commander 1965
Posts: 482
Re: More Dometic aircon HP errors

At my home dock here in south Florida my canal water temp gets to 90F or above each summer. The units will not run as stated in the manual.

Also, I had a pump that would run fine for about 30 minutes and then shut down from over heating reducing the water flow and HP error. New pump fixed the issue.Check the pump temperature with an infrared gun. I keep one onboard as they are about ten bucks and good for checking all sorts of temps on engines, freezers. etc.

My Depth sounders give me the water temp. I have a spare HP switch after one quit a few years ago in my small parts kit.
Squanderbucks is offline   Reply With Quote
Old 27-06-2022, 11:53   #13
Registered User

Join Date: Sep 2013
Posts: 14
Re: More Dometic aircon HP errors

I had a similar problem, turns out it was a loose electrical connection on the high pressure switch. Spade terminal had vibrated loose.
Escapaide is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aircon from Inverter from Batter Charger Agility Electrical: Batteries, Generators & Solar 70 03-02-2016 17:27
Server Errors on the Server Errors thread Tom Stormcrowe Forum Tech Support & Site Help 11 24-08-2012 06:51
Cost for Generator, Aircon, Davits ? FraidNot Electrical: Batteries, Generators & Solar 4 07-02-2011 08:45

Advertise Here


All times are GMT -7. The time now is 18:45.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.