Re: Electric hot water heater / Legionella bacteria concerns

Thanks guys, valuable input.
__________________
www.ladyrover.com
Franziska is offline   Reply With Quote
Old 12-01-2021, 06:11   #107
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,431
Images: 241
Re: Electric hot water heater / Legionella bacteria concerns

Quote:
Originally Posted by rslifkin View Post
If you're willing to run a few pre filters, you can handle most types of contamination. Something along the lines of a fine sediment filter, then a carbon block filter, then something like GAC+KDF, then an oil/hydrocarbon removal filter [2]. Of course, all the extra filters starts to get expensive, especially the more specialized ones. So I wouldn't bother with it unless you really needed to.
Indeed.
Activated Granular Activated Carbon [coconut shell] , GAC, is used, in combination with KDF* media, to significantly extend the life of filtre cartridges.
KDF-55 media is a redox media, that removes chlorine, and reduces heavy metals.
KDF-85 removes hydrogen sulfide, and reduces iron, by the redox process and filtration. Both KDF®* redox media are bacteriostatic, and inhibit the growth of microorganisms in the filter.
* Patented by KDF Fluid Treatment, Inc.

https://www.home-water-purifiers-and...ter-filter.php


[2] Are you aware of a flow-through oil/petroleum filtre, suitable for use on a typical cruising boat? I'm not.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 12-01-2021, 06:19   #108
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,302
Re: Electric hot water heater / Legionella bacteria concerns

Quote:
Originally Posted by GordMay View Post
[2] Are you aware of a flow-through oil/petroleum filtre, suitable for use on a typical cruising boat? I'm not.

Pentek lists their OAC-20BB (only comes in the one giant size) as removing glycol and hydrocarbons. There are also those filters meant for removing oil from bilge water discharge, so the stuff is definitely out there.
rslifkin is offline   Reply With Quote
Old 12-01-2021, 11:44   #109
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,431
Images: 241
Re: Electric hot water heater / Legionella bacteria concerns

Quote:
Originally Posted by rslifkin View Post
Pentek lists their OAC-20BB (only comes in the one giant size) as removing glycol and hydrocarbons. There are also those filters meant for removing oil from bilge water discharge, so the stuff is definitely out there.
I'd be pleased to be exposed as ignorant, but the Pentek OAC-20BB won’t provide adequate pre-filtering, for an R/O watermaker:

ONLY Up to 90% of total hydrocarbons are removed in a single pass
BIG For use in 20 inch Big Blue® filter housings
LOW Flow Rate 5-10 gpm (19-38 L/min)
https://www.thewaterguy.ca/catalog/v...8aAj7LEALw_wcB
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 17-01-2021, 16:31   #110
Registered User
 
Buzzman's Avatar

Join Date: Mar 2011
Location: New South Wales, Australia
Boat: Still building
Posts: 1,557
Re: Electric hot water heater / Legionella bacteria concerns

Quote:
Originally Posted by Franziska View Post
That's a different game. Home water cylinders are permanently attached to electricity and the heater kicks in when the water gets below a certain heat.

Not necessarily.....

In Oz, we have an electrically heated HWS power supply colloquially called 'off peak hot water supply'.

Essentially, many years go, it was noticed that there was little demand for electricity over night, and so the generators had to run down, which was not good for them, so the 'authorities' came up with a plan to utilise the excess power being produced by the idling generators at night.

'Peak power' was when lots of demand was on the grid, 'off peak' when demand was low. So to better utlise the 'off peak' supply, they enabled a system whereby water heaters ran ONLY at night. This supply is separate to the 'main' supply, and can only be utilised by the water heater, which is the only appliance legally allowed to be connected to it. The carrot was that such 'off-peak' power was one third the price of the regular 'mains peak' supply cost.

So each house was fitted with a 'ripple switch' - which detected a radio signal sent along the power lines by the power distributor, that then 'switched on' the "off peak hot water supply".

Now these ripple switches were only able to activate after 11.00pm and usually switched off before 7.00am.

The element in the heater tank was also thermostatically controlled, so would turn itself off once water in the tank reached a set temperature. So an insulated tank might only switch on and run up to temp once per night.

This temperature was usually set at 60 deg C, as this was the optimum temp for killing Legionella but not scalding users.

In very recent times it has been mandated that such water heaters be now fitted with a compulsory tempering valve, to mix the 60 deg C water from the tank with cold water supply to reduce faucet/tap temperature to 45 deg C, as this is considered a 'non-scalding' temperature and is thus safer for babies, the elderly, and the idiots who jump into a hot bath and scald themselves. But the temp in the tank will still kill the Legionella.

The POINT is that once the tank reaches 60 deg C it cuts power to the element, so probably is only at 60 deg C for an hour or too, enough to kill the Legionella, apparently, and perhaps only once a night at best.

My conclusion from this practice - that demonstrably does not lead to legionella outbreaks - is that an occasional burst to 60 deg C is probably sufficient on a boat.

It is also my understanding (mate who works for Zip instant-boiler maker) that instantaneous hot water heaters are designed to kill Legionella, so even though of shorter duration (water heated to req temp for less time) it is done to an 'adequate' level.

I conclude there is nothing to worry about if you have a heater on the boat, *provided* it is cycled occasionally to kill any outbreaks that might have somehow survived the last heating cycle.

Another point: that article on copper silver filtration linked to by Franziska is quite clear that carbon-activated filters are a *known* breeding ground for such parasites and clearly therefore require regular cleaning and or flushing to remove the biofilms that support the microbes. They actually stated that up to a month after the 'testing' process Legionella were still apparent in pretty regular concentrations in the effluent from the filters.

They concluded that, while it appeared from the results that combining the carbon and silver seemed to lead to a reduction in Legionella bypassing the filter, compared to the non-silver carbon filtration, that it was not a 100% removal, so could not conclude that using such a combo was advisable.

Ergo, reliance on any sort of carbon-filtration system might be risky, if Legionella, giardia or cryptosporidium were the targets. Fine for removing chlorine (what kills everything else) and other 'odours' but not so great for removing organisms.

Heat to 60 deg C kills the Legionella; mechanical filtration below 0.5 microns takes out the others.
Buzzman is offline   Reply With Quote
Old 17-01-2021, 18:23   #111
Registered User

Join Date: Jul 2018
Location: NZL - Currently Run Aground Ashore..
Boat: Sail & Power for over 35 years, experience cruising the Eastern Caribbean, Western Med, and more
Posts: 2,129
Re: Electric hot water heater / Legionella bacteria concerns

Yes, my home in France had a similar setup with the electric hot water heater.

It had a special breaker at the circuit board which could be set to Off / Auto / Manual.

Auto would run the hot water heater only during off peak electricity times, so in general that meant only at night.

As you said, this was to utilise the off peak power generation excess, which was also cheaper per kW too.

(it was also common for dishwashers, washing machines, etc, to have programmable timers, and it was encouraged to run these at night as well).

This all worked on the logic that most people had a shower when they got up in the morning before going to work so that's when most of the water needed to be hot.

And it did mean that it in Auto the hot water would only be heated to maximum temperature once per day.

jmh2002 is offline   Reply With Quote
Old 18-01-2021, 02:45   #112
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,431
Images: 241
Re: Electric hot water heater / Legionella bacteria concerns

Quote:
Originally Posted by Buzzman View Post
... My conclusion from this practice - that demonstrably does not lead to legionella outbreaks - is that an occasional burst to 60 deg C is probably sufficient on a boat.
It is also my understanding (mate who works for Zip instant-boiler maker) that instantaneous hot water heaters are designed to kill Legionella, so even though of shorter duration (water heated to req temp for less time) it is done to an 'adequate' level.
I conclude there is nothing to worry about if you have a heater on the boat, *provided* it is cycled occasionally to kill any outbreaks that might have somehow survived the last heating cycle ...
On-demand, instant, water heaters don’t necessarily kill Legionella, but neither do they store water, allowing time for the bacterium to grow to toxic/ virulent numbers - hence are “safe”. Neither do conventional water heaters.
The danger lies (mostly) in stored water.

As previously noted:
"Legionella, the bacterium that causes Legionnaires’ disease, occurs naturally in freshwater environments, like lakes and streams. Generally the low amounts of these bacteria in freshwater do not lead to disease. However, Legionella can pose a health risk when it gets into water storage systems.
To do this, Legionella first has to grow (increase in numbers). Then it has to spread through small water droplets (aerosolization) that people can breathe in.
After Legionella grows, and multiplies, in a water system, water containing Legionella then has to spread in droplets small enough for people to breathe in. People can get Legionnaires’ disease or Pontiac fever when they breathe in small droplets of water in the air that contain the bacteria.
Less commonly, people can get sick by aspiration of drinking water containing Legionella. This happens when water accidently goes into the lungs while drinking.
So, treated water (chlorinated muni', or R/O) is highly unlikely to contain Legionella, and our storage tanks aren't likely large enough to retain water long enough to grow significant numbers of bacterium, to cause illness."

Here https://www.cruisersforum.com/forums...ml#post3315052

Alsohttps://www.cruisersforum.com/forums...ml#post3315062
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Reply

Tags
electric, heater, water


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fecal Bacteria Unsafe Levels On 33% of Beaches TigerPaws Emergency, Disaster and Distress 68 15-08-2019 05:44
HOT HOT HOT! running AC on Honda generator sailorboy1 Plumbing Systems and Fixtures 79 27-06-2019 07:21
Hot Water Heater / Block Heater? - 3GM30 BareProductions Engines and Propulsion Systems 9 23-02-2013 18:12
RO Water Quality and Bacteria phorvati Plumbing Systems and Fixtures 15 17-07-2010 14:37
Ohhhhh Hot! Hot! Hot! knottybuoyz Marine Electronics 6 01-06-2007 07:43

Advertise Here


All times are GMT -7. The time now is 22:13.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.