CNG in a Sealed, Vented Locker

In the August, 2014 BoatUS magazine, a writer asked about CNG on a boat he was looking to buy, and was wondering if he needed a sealed locker.

The response was technically accurate, but highly misleading and very unnerving for any of us that use CNG (and probably soured the deal for the reader).

The response stated that CNG must be in a sealed locker if the capacity is over 100CF, and the insurance company may well enforce that requirement. An accurate statement, for sure.

The problem is that 99.99% of CNG tanks out there, the standard white SCUBA size tanks that are available for exchange, are about 73CF.

Bottom line, contrary to what the BoatUS article implies, or CNG lockers are compliant without being sealed and vented.

I hate misleading and inflammatory "news" stories....
sailingharry is offline   Reply With Quote
Old 19-10-2014, 10:58   #2
Registered User
 
S/V Illusion's Avatar

Join Date: Oct 2007
Location: Lakewood Ranch, FLORIDA
Boat: Alden 50, Sarasota, Florida
Posts: 3,472
Re: CNG in a sealed, vented locker

You might write the editor informing him/ her of the disservice the author has done and suggest that, in a future edition, they post a clarification if they really want to serve of value to their subscribers.

The problem is ubiquitous as we often read here in this forum when people write opinion as fact or perpetuate bad info by repeating it simply because some jerk wrote a book or claimed some non-existent expertise.
S/V Illusion is offline   Reply With Quote
Old 19-10-2014, 14:25   #3
Moderator
 
Jim Cate's Avatar

Join Date: May 2008
Location: cruising SW Pacific
Boat: Jon Sayer 1-off 46 ft fract rig sloop strip plank in W Red Cedar
Posts: 21,195
Re: CNG in a sealed, vented locker

Just curious: how can a locker be both vented and sealed?

Jim
__________________
Jim and Ann s/v Insatiable II, lying Port Cygnet Tasmania once again.
Jim Cate is offline   Reply With Quote
Old 19-10-2014, 15:23   #4
Registered User
 
lonesoldier0408's Avatar

Join Date: Jun 2013
Boat: Luger, Southwind, 21
Posts: 428
Quote:
Originally Posted by Jim Cate View Post
Just curious: how can a locker be both vented and sealed?

Jim
CNG being heavy, Will settle in the bilge if not vented via hose to the outside. The hatch may be watertight yet not airtight. Best interpretation is, a bowl to catch leaking CNG and plumbing to vent that CNG from the bottom of that bowl to overboard.
lonesoldier0408 is offline   Reply With Quote
Old 19-10-2014, 15:38   #5
Registered User
 
Tayana42's Avatar

Join Date: Nov 2012
Location: Long Beach, CA
Boat: Tayana Vancouver 42
Posts: 2,804
Re: CNG in a sealed, vented locker

I thought CNG (methane) was lighter than air and would dissipate in air, unlike LPG (propane ) which is heavier than air and will sink to the low point waiting for a spark.
Tayana42 is offline   Reply With Quote
Old 19-10-2014, 16:42   #6
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,060
Re: CNG in a sealed, vented locker

CNG is lighter than air. That is why it is promoted as safer than propane. At normal temperatures it has to be stored at high pressures in heavy tanks.

Large quantities of propane can be stored in light tanks because it turns into a liquid at low pressures and normal temperatures.
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 19-10-2014, 16:51   #7
Registered User
 
Island Time O25's Avatar

Join Date: Sep 2014
Posts: 3,053
Re: CNG in a sealed, vented locker

Quote:
Originally Posted by lonesoldier0408 View Post
CNG being heavy, Will settle in the bilge if not vented via hose to the outside. The hatch may be watertight yet not airtight. Best interpretation is, a bowl to catch leaking CNG and plumbing to vent that CNG from the bottom of that bowl to overboard.
You are confusing CNG with LPG. CNG, when out of the cylinder, is lighter than air and will dissipate if it leaks. The only danger is to have a spark or other source of ignition right next to it at the time of a massive leak. And unlike LPG it does not accumulate in the bilge. Therefore CNG is much safer than LPG most of the time. And this is the main reason I'm not converting for now from CNG as it is plentiful, although not cheap, where I am based.
Island Time O25 is offline   Reply With Quote
Old 19-10-2014, 16:55   #8
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,706
Re: CNG in a sealed, vented locker

HopCar is right. Man, there are sooooooooo many CNG vs Propane discussions, it is remarkable.

There was a thread just yesterday on another boating forum where someone suggested he was considering switching from propane to CNG even though he already had a legal propane system. Weirdos strike again. I guess it's OK, though, it's boating, right?

The ONLY thing one should do is to vent the CNG regulator overboard. There is a connection to do so right on the regulators. Most folks don't.
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 19-10-2014, 19:05   #9
Registered User
 
FSMike's Avatar

Join Date: Aug 2009
Location: Bahamas/Florida
Boat: Solaris Sunstar 36' catamaran
Posts: 2,686
Images: 5
Re: CNG in a sealed, vented locker

Quote:
Originally Posted by sailingharry View Post
----
The response stated that CNG must be in a sealed locker if the capacity is over 100CF, and the insurance company may well enforce that requirement. An accurate statement, for sure.

The problem is that 99.99% of CNG tanks out there, the standard white SCUBA size tanks that are available for exchange, are about 73CF.

Bottom line, contrary to what the BoatUS article implies, or CNG lockers are compliant without being sealed and vented.
I wonder if the "capacity" refers to the total of CNG aboard, rather than one tank. Most cruisers I know carry two tanks of their fuel of choice to prevent running out in remote locations.
__________________
Sail Fast Live Slow
FSMike is offline   Reply With Quote
Old 19-10-2014, 19:18   #10
Registered User
 
Cuttyhunk's Avatar

Join Date: Nov 2008
Location: northeast USA
Boat: EndeavourCat 36
Posts: 372
Re: CNG in a sealed, vented locker

Quote:
Originally Posted by FSMike View Post
I wonder if the "capacity" refers to the total of CNG aboard, rather than one tank. Most cruisers I know carry two tanks of their fuel of choice to prevent running out in remote locations.
ABYC A22.7.4.7 says "attached combined capacity of greater than 100 cubic feet" ... "shall be located on the exterior of the boat where escaping gases can flow directly into the atmosphere outside the boat, or

22.7.4.7.1 "the cylinders and connected devices hsall be installed in a dedicated locker"

If you have less than 100 CF in cylinders "attached" to the system, you are ok with

A22.7.4.6: "For CNG installations that include cylinders with an attached combined capacity of 100 cubic feet or less, cylinders, cylinder valves, regulating equipment, and safety devices shall be:

22.7.4.6.1 readily accessible, secured for sea conditions, and protected from the weather and against mechanical damage" and there are a couple of other more stringent options listed, as well.

The above is from the July 2014/2015 edition of the ABYC Standards.
Cuttyhunk is offline   Reply With Quote
Old 19-10-2014, 19:21   #11
Registered User
 
Dsanduril's Avatar

Join Date: Aug 2011
Location: Petersburg, AK
Boat: Outremer 50S
Posts: 4,229
Re: CNG in a sealed, vented locker

From the source (at least in the US):

Quote:
22.12.1 CNG systems with connected capacity greater than 100 cubic feet shall provide for storage lockers (see A-22.13S2).
Quote:
22.13.5 If the CNG installation includes attached cylinders of greater than 2.8 cubic meters (100 cubic feet) combined capacity, the cylinders shall be:

22.13.5.1 located on the exterior of the boat where escaping gases can directly escape into the open air, or

22.13.5.2 installed in a locker which shall be:
a. vapor tight to the hull interior,
b. vented to the open atmosphere outside the boat,
c. constructed of or lined with corrosion resistant materials,
d. equipped with a means to discharge incidental accumulated water,
e. equipped with a cover which
i. opens directly to the atmosphere,
ii. latches tightly,
111. is capable of being quickly and conveniently opened without tools and for operating the cylinder valves, testing the system for leakage and viewing the
pressure gauge.
Both of those seem to indicate that it is only the capacity of "connected" or "attached" cylinders that is counted, although there is no definition of either term in the document. And or course, to my mind conflicts with:

Quote:
22.13.3 Storage provisions for unconnected reserve cylinders, filled or empty, shall be the same as the provisions for the cylinder in use.
Dsanduril is offline   Reply With Quote
Old 19-10-2014, 19:30   #12
Registered User
 
Cuttyhunk's Avatar

Join Date: Nov 2008
Location: northeast USA
Boat: EndeavourCat 36
Posts: 372
Re: CNG in a sealed, vented locker

[QUOTE=Dsanduril;1658271]From the source (at least in the US):

You are quoting an old version of the standard. A-22 doesn't even go up to 13 anymore. Be careful getting the standards from the Internet. They are updated frequently. A-22 was last updated in 2012.
Cuttyhunk is offline   Reply With Quote
Old 19-10-2014, 20:34   #13
Registered User
 
Dsanduril's Avatar

Join Date: Aug 2011
Location: Petersburg, AK
Boat: Outremer 50S
Posts: 4,229
Re: CNG in a sealed, vented locker

Quote:
Originally Posted by Cuttyhunk View Post
You are quoting an old version of the standard. A-22 doesn't even go up to 13 anymore. Be careful getting the standards from the Internet. They are updated frequently. A-22 was last updated in 2012.
Not according to the ABYC themselves:

Standards Index - American Boat and Yacht Council

Scroll down and you'll see that they say 2012 is still the "current version". 2014/15 has not made it through legislation yet.

Minor point, as either way the text in question is pretty much identical, just a matter of numbering.
Dsanduril is offline   Reply With Quote
Old 19-10-2014, 22:35   #14
Registered User
 
lonesoldier0408's Avatar

Join Date: Jun 2013
Boat: Luger, Southwind, 21
Posts: 428
Re: CNG in a sealed, vented locker

Thanks to all those correcting my confusion on CNG and LPG.
Again, it must be sealed off from the interior of the vessel and vented overboard to dissipate. CNG above ignition sources and LPG below ignition sources. :thumbup:
lonesoldier0408 is offline   Reply With Quote
Old 01-11-2014, 14:29   #15
Registered User
 
sailingharry's Avatar

Join Date: Jun 2009
Location: Annapolis, MD
Boat: Sabre 34-1 (sold) and Saga 43
Posts: 2,318
Re: CNG in a sealed, vented locker

I got away from the internet a bit, and missed all the responses. Just read them, and have two comments.

With regard to Jim Cate's comment about "both vented and sealed," I'll admit my guilt. I should have said "sealed from the interior of the hull, and vented to the outside atmosphere." I hope that anyone who is struggling with fuel storage issues immediately understood the intent of my note. Regardless, I thank you for clearing this up for anyone not familiar with tank storage issues.

With regard to S/v Illusion's comment that I contact the author, I actually did. Her response was disappointing, as she made some sort of comment about "word limited column sizes" and seemed indifferent to the fact that her article was "accurate" but very misleading -- and in particular, left the person who asked the question with the wrong understanding.

Interesting, in the most recent BoatUS mag, she stated that a longer waterline boat, that increases hull speed from 7 to 8 (or so, I forget) allows a day sail to increase from 25 to 35 miles. Wow, a 15% increase in speed allows a 40% increase in distance? The standards for "Technical Editor" don't include "technical expertise."

Harry
sailingharry is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chain Locker Drain and Rode Spool inside Locker resilientg Construction, Maintenance & Refit 3 05-08-2012 18:02
Tubular Plate (Wet) or Sealed Spiral Cell (VRLA) for House Batteries, . . . or ? Pelagic Electrical: Batteries, Generators & Solar 20 18-02-2011 17:22
Sealed Wetcell batteries Joe500 Electrical: Batteries, Generators & Solar 2 11-02-2009 16:01
Valve Regulated Sealed Lead Acid Batteries Nauticatarcher Electrical: Batteries, Generators & Solar 5 25-03-2008 14:24

Advertise Here


All times are GMT -7. The time now is 02:59.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.