Re: Coldplate Reefer Questions for the Pro's!

Well guru Rich...

Your check is in the mail...

Seems as though we're going to be just fine with this setup... Cycle times may be a little longer with the smaller compressor... AND... I have not achieved sweet spot conditions... BUT... We're out of the yellow danger zone, and smack dab in the reefer zone!

Box=34.2637f
(picture verification attached)

No frost any line inside or outside the box

Plate is completely frozen except the top 1.5".... Weird as I burped the air outta this thing filing it with your recommended mix??? No leakage... bah..

Low is high @ 8
High is low @ 120

Imma put the shelves back in this baby... and tweak if you think I need to... Not sure I do...

Ever grateful... Ed
Attached Thumbnails
Click image for larger version

Name:	Thermo 34 .jpg
Views:	28
Size:	65.6 KB
ID:	129758  
__________________

__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is online now   Reply With Quote
Old 18-08-2016, 18:18   #17
Liveaboard Cruiser
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: Morro Bay, CA
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,217
Send a message via Skype™ to SV THIRD DAY
Re: Coldplate Reefer Questions for the Pro's!

Bingo Ed....

Now 8PSI is ok but if it was me (a techy nerd who likes to fine tune things) now that you are cycling, I would give the TXV just a little tweak (like a 45-degs turn) closed (Righty Tighty). This will slightly decrease the amount of refrigerant being injected into the holding plate and allow for your compressor to pull the low side pressure down to 0-5psi, with 2-3psi being perfect. That's the sweet spot and can save you a little on the power usage and will get your holding plate just a little colder.

Keep me updated amigo, but it sure sounds like I need to send you a Marine Refrigeration Merit Badge!

You could have a little air gap in the top of your holding plate, OR it could be a combination of these two things.
1. not having refrigeration coils up in the top of the plate to hit the colder temps on the eutectic solution
and
2. the top of your box being warmer so more heat is being added to the top of your plate.
__________________

__________________
Rich Boren Living Aboard in Morro Bay, CA and the owner of:
Cruise RO Water High Output Water Makers
Technautics CoolBlue Refrigeration

SV THIRD DAY is offline   Reply With Quote
Old 18-08-2016, 18:28   #18
Liveaboard Cruiser
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: Morro Bay, CA
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,217
Send a message via Skype™ to SV THIRD DAY
Re: Coldplate Reefer Questions for the Pro's!

Quote:
Originally Posted by Rorzech View Post
I've been using leak stoppers for a couple of years now without any failures so far , so until I have a problem with them , i'll continue using them. I've seen some miracles with that stuff that was hard to believe. I've never seen it ever plug anything up. Oxygen and water combined with refrigerant causes the stuff that blocks things up.The proof is in the pudding.
I'm in the process of re-building a system now that was contaminated and gummed up with leak stopper and I have seen many systems damaged by using it. We don't say not to use it because we own stock in a Non-leak stop maker company, but because we have seen the damage they can cause. Proof isn't in the pudding, its in the wreaked systems we have had the unfortunate experience of helping clients fix to have cold beer again over the years.

So from the manufacturer and from someone who takes the sad phone calls on weekends from those that didn't believe the bold print in our manual, please don't use Leak Stoppers in your system.
__________________
Rich Boren Living Aboard in Morro Bay, CA and the owner of:
Cruise RO Water High Output Water Makers
Technautics CoolBlue Refrigeration

SV THIRD DAY is offline   Reply With Quote
Old 18-08-2016, 23:49   #19
Moderator
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: North Mississippi
Boat: 48 Wauquiez Pilot Saloon-C22 Chrysler Sunpiper- 19 Potter-Preparing to cruise w/my girl
Posts: 5,978
Re: Coldplate Reefer Questions for the Pro's!

Quote:
Originally Posted by SV THIRD DAY View Post
Bingo Ed....

Now 8PSI is ok but if it was me (a techy nerd who likes to fine tune things) now that you are cycling, I would give the TXV just a little tweak (like a 45-degs turn) closed (Righty Tighty). This will slightly decrease the amount of refrigerant being injected into the holding plate and allow for your compressor to pull the low side pressure down to 0-5psi, with 2-3psi being perfect. That's the sweet spot and can save you a little on the power usage and will get your holding plate just a little colder.

Keep me updated amigo, but it sure sounds like I need to send you a Marine Refrigeration Merit Badge!

You could have a little air gap in the top of your holding plate, OR it could be a combination of these two things.
1. not having refrigeration coils up in the top of the plate to hit the colder temps on the eutectic solution
and
2. the top of your box being warmer so more heat is being added to the top of your plate.
Ya know it's kinda silly when I think about it... I've probably hooked up a manifold 500x to various thingamajigs... big environmental chambers to reefers n freezers n OMG can't count the cars... Plus dealer ac installs...

Sometimes a little talking down from the ledge helps immensely... Gracias!

Box did well today... left it completely off 12hrs, and went from 34 to 40.... And 40to 38 in an hour running... Imma tweaker too..., I'll give that superheat screw a 45 right, and see how she does... (sounds like it's going to bump my hi a smidge too?)

No way I could have an air gap in the top of the plate... But then again... There was that time I was wrong back in '74

We'll see how badly we need to sit at the keyboard when my buddy brings over a couple o BDFiddys for the DC side!

Thanks again Hero... I'll update with the new specs after the tweak!
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is online now   Reply With Quote
Old 19-08-2016, 21:18   #20
Registered User

Join Date: Oct 2014
Boat: Morgan, West Indies 38 Ketch
Posts: 70
Re: Coldplate Reefer Questions for the Pro's!

Got a fan in there?


Sent from my iPhone using Cruisers Sailing Forum
__________________
akopac is offline   Reply With Quote
Old 20-08-2016, 06:06   #21
Moderator
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: North Mississippi
Boat: 48 Wauquiez Pilot Saloon-C22 Chrysler Sunpiper- 19 Potter-Preparing to cruise w/my girl
Posts: 5,978
Re: Coldplate Reefer Questions for the Pro's!

Quote:
Originally Posted by akopac View Post
Got a fan in there?


Sent from my iPhone using Cruisers Sailing Forum
Not yet, but I'm soon to add one... I know it would help a ton! Right now I think I have a big variation in zones... It's a big box
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is online now   Reply With Quote
Old 20-08-2016, 06:22   #22
Moderator
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: North Mississippi
Boat: 48 Wauquiez Pilot Saloon-C22 Chrysler Sunpiper- 19 Potter-Preparing to cruise w/my girl
Posts: 5,978
Re: Coldplate Reefer Questions for the Pro's!

Quote:
Originally Posted by SV THIRD DAY View Post
Now 8PSI is ok but if it was me (a techy nerd who likes to fine tune things) now that you are cycling, I would give the TXV just a little tweak (like a 45-degs turn) closed (Righty Tighty). This will slightly decrease the amount of refrigerant being injected into the holding plate and allow for your compressor to pull the low side pressure down to 0-5psi, with 2-3psi being perfect. That's the sweet spot and can save you a little on the power usage and will get your holding plate just a little colder.
First time double quoting! Kinda fun...

Did the 'ol 1/8th turn, and waited 2 hrs... = no change in pressures...
repeat... repeat... repeat... You get the idea... 1.5 total in, plate started to sweat from frozen near the top... Danger Will Robinson!

Backed out 1.5 to original... I'm guessing that our lack of refinement is because some asshat installed an R12 TXV in a 134 system...

I can see now the thought process for the original install... Let's blow this candle out with a leaf blower...

Ah well... I'll refine as we go along... maybe swap TXV's or install a bigger compressor... Now it's time to hit the DC side... This I think should be easy as it's just another compressor issue, and once I stabilize my voltage with a new house bank I'll tackle it !

Thanks a ton Rich!
E
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is online now   Reply With Quote
Old 20-08-2016, 08:54   #23
Liveaboard Cruiser
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: Morro Bay, CA
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,217
Send a message via Skype™ to SV THIRD DAY
Re: Coldplate Reefer Questions for the Pro's!

Quote:
Originally Posted by HappyMdRSailor View Post
I'm guessing that our lack of refinement is because some asshat installed an R12 TXV in a 134 system...
Bingo....
You will never get it dialed in tight with an R12 TXV running on R134a and here's why.

The sensing bulb that controls the actuation of the TXV is gas filled, this gas (either R12, R134a or what ever refrigerant the TXV is made to function with) needs to expand and have the same properties as the refrigerant in the system. So the sensing bulb is basically sending slightly false information back to the TXV. So it will never be "perfect" but you can take close enough.

Now on more thing, I think you are working under a false assumption that your compressor is too small...but from your cycle time of bounce back when you did the testing...I don't have any data/gut feel that is the case, so I think you could run that compressor until it dies, which could be long after you have sold the boat! Now what DOES need to be changed is the old R12 TXV....you should get a new R134a valve on there for better/more efficient performance.

Oh and on the circulation fan.
Don't make the common mistake of thinking "Bigger is Better".
All you need is a 10CFM fan to just gently move air around in the box.
I've seen people put in Gigantic fans like they are trying to make a blast freezer...ha ha ha. 10CFM is all you need plus it will use so little power you won't even know it is there.
__________________
Rich Boren Living Aboard in Morro Bay, CA and the owner of:
Cruise RO Water High Output Water Makers
Technautics CoolBlue Refrigeration

SV THIRD DAY is offline   Reply With Quote
Old 20-08-2016, 09:37   #24
Moderator
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: North Mississippi
Boat: 48 Wauquiez Pilot Saloon-C22 Chrysler Sunpiper- 19 Potter-Preparing to cruise w/my girl
Posts: 5,978
Re: Coldplate Reefer Questions for the Pro's!

Quote:
Originally Posted by SV THIRD DAY View Post
Bingo....
You will never get it dialed in tight with an R12 TXV running on R134a and here's why.

The sensing bulb that controls the actuation of the TXV is gas filled, this gas (either R12, R134a or what ever refrigerant the TXV is made to function with) needs to expand and have the same properties as the refrigerant in the system. So the sensing bulb is basically sending slightly false information back to the TXV. So it will never be "perfect" but you can take close enough.

Now on more thing, I think you are working under a false assumption that your compressor is too small...but from your cycle time of bounce back when you did the testing...I don't have any data/gut feel that is the case, so I think you could run that compressor until it dies, which could be long after you have sold the boat! Now what DOES need to be changed is the old R12 TXV....you should get a new R134a valve on there for better/more efficient performance.

Oh and on the circulation fan.
Don't make the common mistake of thinking "Bigger is Better".
All you need is a 10CFM fan to just gently move air around in the box.
I've seen people put in Gigantic fans like they are trying to make a blast freezer...ha ha ha. 10CFM is all you need plus it will use so little power you won't even know it is there.
Well... I suppose when I get the freezer going... I guess I could paste the fridge bulb to the DC freeze evap with a regulating heat sink...

Wait??? Nix that... 134 pressures are lower than 12... so the bulb temp needs to be warmer... ***ebays tiny heating blankets***
Or... a 134 TXV...

Great input on the compressor!!!
If the original (french) asshats (butt-chapeau's?) put in the wrong TXV, what would make me think they picked the correct compressor???
(sometimes I catch up...)

Roger on the tiny fan... 2.5" computer/electronics?

You obviously know this would be nowhere near as fun if I was staring at a warm box...
__________________

__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is online now   Reply With Quote
Reply

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Reefer Questions norules Construction, Maintenance & Refit 15 23-03-2015 13:52
For Sale: Liferaft. Viking Rescyou Pro 4UKSL. 4 Man pro valise. Self righting. Brisbane AU dennisail Classifieds Archive 4 29-03-2013 19:06
Hello, I Am a Pro Boater with Dumb Questions! whiteH2Okayaker Meets & Greets 20 14-04-2010 15:17
12 Volt Reefer Electronic Noise jan bogart Plumbing Systems and Fixtures 7 22-03-2009 20:31
Chemical smell in reefer boxes chienbizarre Construction, Maintenance & Refit 7 19-09-2008 13:22


Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 20:38.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.