Duke 48, If you use wiring harnesses, don't forget to increase your wiring sizes per the guidelines for bundled wires. Using the Excel spreadsheet, it made these calculations almost automatic.
__________________

__________________
Roy M is offline   Reply With Quote
Old 13-09-2008, 09:02   #32
Registered User
 
Duke 48's Avatar

Join Date: Sep 2008
Location: Western KY
Boat: Morgan 321, BELIEVE
Posts: 203
Roy M: I had already planned to increase wire size - 14 instead of 16, 10 insead of 12, etc. just in case I decided to add a loads in the future.. You mentioned guidelines for bundeled wires. Is this ABYC or other?
__________________

__________________
Duke 48 is offline   Reply With Quote
Old 13-09-2008, 09:18   #33
Senior Cruiser
 
Roy M's Avatar

Cruisers Forum Supporter

Join Date: Feb 2007
Location: Southwestern Yacht Club, San Diego, CA
Boat: Searunner 40 trimaran, WILDERNESS
Posts: 3,042
Images: 4
Duke 48, Go to the West Marine Advisor page, look up their wire sizing pdf. Toward the bottom you will find the guidelines (ABYC???) for derating current capacity on bundles of wiring. At the risk of starting another flareup of the techies, electrons don't like the company of others, so they stage a work slowdown when forced to travel together in bundles of wires. It has to do with electrons punching their elbows into each others sides, crabbing about who's insulation is cooler, and gossiping about who is circulating around at CERN in Switzerland. Just size up accordingly and things move along with no heat generated or feelings hurt.
__________________
Roy M is offline   Reply With Quote
Old 13-09-2008, 09:37   #34
Moderator Emeritus
 
GordMay's Avatar

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 31,580
Images: 240
A good rule of thumb for “bundled” wires is to de-rate the individual ratings to 80% (or upsize to 125%).

See also:
"Ohm's Law & Boats"

And:
http://www.cruisersforum.com/gallery...r&imageuser=79
&
http://www.cruisersforum.com/gallery...r&imageuser=79
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 13-09-2008, 10:50   #35
Registered User
 
Duke 48's Avatar

Join Date: Sep 2008
Location: Western KY
Boat: Morgan 321, BELIEVE
Posts: 203
Roy M, Having checked out the West Marine sight as you suggested, I must admit the recommended current reductions are much larger than I expected. I'm sure there is some overkill for safety consideration, but I fully intend to follow the recommendations.

GordMay, The rule of thumb will help in my preliminary estimates. And, the article "Ohm's Law & Boats" has added even more dimension to my simple rewiring project. Fortunately, this "redesign" is one of the issues I plan to address during the winter.

Also, I really appreciate the input I have received on this thread.
__________________
Duke 48 is offline   Reply With Quote
Old 13-09-2008, 15:34   #36
Senior Cruiser
 
Roy M's Avatar

Cruisers Forum Supporter

Join Date: Feb 2007
Location: Southwestern Yacht Club, San Diego, CA
Boat: Searunner 40 trimaran, WILDERNESS
Posts: 3,042
Images: 4
Duke 48, My electrical panel covers a locker about 1 1/2 feet square and a foot deep. From this locker, several large conduits run to different areas of the boat, many through the engine room below it. Because of this limitation I knew I had to design a system that would be installed once, given how nasty it is to pull wire through conduits. After I had created the circuits and determined the wiring sizes and lengths, I started cutting different wires and cables, with some extra, and labelled both ends using the code I created. Then I could pull the Anaconda of copper through the conduit and bends, peeling off wires as they reached their individual distribution nodes. I was very pleased when it all worked out. I had the foresight to include some extra wires, of different gauges, for future, unknown, additions.
Attached Thumbnails
Click image for larger version

Name:	DSC08595-reduced.jpg
Views:	86
Size:	375.0 KB
ID:	5058   Click image for larger version

Name:	DSC05716-reduced.jpg
Views:	83
Size:	397.4 KB
ID:	5059  

__________________

__________________
Roy M is offline   Reply With Quote
Reply

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
6 volt vs 12 volt? mestrezat Electrical: Batteries, Generators & Solar 39 18-02-2009 00:33
Believe something similar posted before, here is tha sailor's Bible mickmul General Sailing Forum 6 28-02-2008 11:42
12 volt refrigeration Gallivanters Plumbing Systems and Fixtures 3 15-04-2007 09:11
6 volt batteries irwinsailor Electrical: Batteries, Generators & Solar 6 24-04-2005 03:15



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 13:02.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.