Six-pac = OUPV= Operator of Uninspected Passenger Vessel= no requirement

33CFR183 subpart J is only for gasoline powered boats
__________________

__________________
donradcliffe is offline   Reply With Quote
Old 19-11-2009, 10:42   #17
Senior Cruiser
 
Sailmonkey's Avatar

Cruisers Forum Supporter

Join Date: Sep 2009
Location: Houston
Boat: '76 Allied Seawind II, 32'
Posts: 5,770
I pulled the engine on a boat that had suffered from a minor case of alternatorflameritis, compounded by a case of foaminsulationburnerus. The flame sheilded filter bowl had melted. The flame shield was intact.
__________________

__________________
Sailmonkey is online now   Reply With Quote
Old 20-11-2009, 18:52   #18
Eternal Member
 
Chief Engineer's Avatar

Join Date: Aug 2006
Location: North of Baltimore
Boat: Ericson 27 & 18' Herrmann Catboat
Posts: 3,798
Ah yes.....reminds me of a case of

Vetusmufflerus meltii due to Thruhullinum closedofferus.

replaced unit and da-da-da DAAAAAAAAAAAAAAHHH(trumpet sound)

Customer melted it the following week....again......

Quote:
Originally Posted by Sailmonkey View Post
I pulled the engine on a boat that had suffered from a minor case of alternatorflameritis, compounded by a case of foaminsulationburnerus. The flame sheilded filter bowl had melted. The flame shield was intact.
__________________
Chief Engineer is offline   Reply With Quote
Old 20-11-2009, 19:04   #19
Senior Cruiser
 
Sailmonkey's Avatar

Cruisers Forum Supporter

Join Date: Sep 2009
Location: Houston
Boat: '76 Allied Seawind II, 32'
Posts: 5,770
at least the vetus melts before the hose.........centek mufflers tend to hold in there after the hose has gone south.
__________________
Sailmonkey is online now   Reply With Quote
Old 20-11-2009, 20:19   #20
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Toronto, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 2,593
Neither the CFR's, Canada Shipping Act or ABYC standards refer to "Heat shields" in any way.
Below is the standard comment I make in my surveys in this regard. Note that all referenced standards refer to pleasure craft.


"Canada Shipping Act – TP1332E 7.7.1 and the US Code of Federal Regulations Title 33 183.590 requires every fuel filter or strainer shall meet the fire resistance requirements for fuel systems set forth in ABYC Standards for Small Craft H-24.5.7 unless the filter or strainer is inside the fuel tank".

None of the Racors with plastic bowls and without heat shields meet this requirement.
__________________
That hysterical laughter you hear as you sail a way in your "new" boat ..... is the seller.
boatpoker is offline   Reply With Quote
Old 20-11-2009, 20:37   #21
Eternal Member
 
Chief Engineer's Avatar

Join Date: Aug 2006
Location: North of Baltimore
Boat: Ericson 27 & 18' Herrmann Catboat
Posts: 3,798
The Point is that Subpart J applies to Gasoline Engines

Subpart J—Fuel Systems


Source: CGD 74–209, 42 FR 5950, Jan. 31, 1977, unless otherwise noted.
General


§ 183.501 Applicability.

(a) This subpart applies to all boats that have gasoline engines, except outboard engines, for electrical generation, mechanical power, or propulsion.


Quote:
Originally Posted by boatpoker View Post
Neither the CFR's, Canada Shipping Act or ABYC standards refer to "Heat shields" in any way.
Below is the standard comment I make in my surveys in this regard. Note that all referenced standards refer to pleasure craft.


"Canada Shipping Act – TP1332E 7.7.1 and the US Code of Federal Regulations Title 33 183.590 requires every fuel filter or strainer shall meet the fire resistance requirements for fuel systems set forth in ABYC Standards for Small Craft H-24.5.7 unless the filter or strainer is inside the fuel tank".

None of the Racors with plastic bowls and without heat shields meet this requirement.
__________________
Chief Engineer is offline   Reply With Quote
Old 20-11-2009, 20:41   #22
Senior Cruiser

Cruisers Forum Supporter

Join Date: Dec 2006
Location: Seattle
Boat: Cal 40
Posts: 2,401
Images: 7
You mean refer to pleasure craft with gasoline engines?

Subpart J—Fuel Systems

S
OURCE: CGD 74–209, 42 FR 5950, Jan. 31,

1977, unless otherwise noted.
G


ENERAL

§ 183.501 Applicability.
(a) This subpart applies to all boats
that have gasoline engines, except outboard
engines, for electrical generation,

mechanical power, or propulsion.

Edit: I see I spend too much time with my posts, I have repeated Chief's post.
John



Quote:
Originally Posted by boatpoker View Post
Neither the CFR's, Canada Shipping Act or ABYC standards refer to "Heat shields" in any way.
Quote:
Originally Posted by boatpoker View Post

Below is the standard comment I make in my surveys in this regard. Note that all referenced standards refer to pleasure craft.


"Canada Shipping Act – TP1332E 7.7.1 and the US Code of Federal Regulations Title 33 183.590 requires every fuel filter or strainer shall meet the fire resistance requirements for fuel systems set forth in ABYC Standards for Small Craft H-24.5.7 unless the filter or strainer is inside the fuel tank".


None of the Racors with plastic bowls and without heat shields meet this requirement.


__________________
cal40john is offline   Reply With Quote
Old 20-11-2009, 21:02   #23
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Toronto, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 2,593
Clarification .....

CFR's refer only to gasoline engines.

ABYC H-33, Diesel Fuel systems 33.5.6 requires " all individual components of the fuel distribution system, as installed in the boat, shall be capable of withstanding a 2 1/2" minute exposure to free burning fuel (N-Heptane), or No.2 diesel fuel without leakage, when tested in accordance with Title 33 CFR, Section 183.590, Fire Test.

My correspondence with Racor indicates that none of their plastic bowl filters without heat shields have ever been tested to this standard, therefore do not meet ABYC Standards or Transport Canada TP1332E Standards for placement in compartments containing diesel engines or fuel tanks.

My ABYC Standards Certification course is coming up in two weeks, I'll raise the issue again. I have had this discussion with Transport Canada Department of Marine Safey and they agree with my position. Eight of their investigators will be attending the same course here at Port Credit Yacht Club ( where I live on my boat).
__________________
That hysterical laughter you hear as you sail a way in your "new" boat ..... is the seller.
boatpoker is offline   Reply With Quote
Old 20-11-2009, 21:59   #24
Eternal Member
 
Chief Engineer's Avatar

Join Date: Aug 2006
Location: North of Baltimore
Boat: Ericson 27 & 18' Herrmann Catboat
Posts: 3,798
ABYC wants $25.00 for their book of standards. You would think they would have it in the public domain

CFR 33 Subpart J refers to Gasoline Engines only.

If the Racor Turbine Series Filters with heat shields are not approved, why are they sold with the "MA" designation?
__________________
Chief Engineer is offline   Reply With Quote
Old 21-11-2009, 09:24   #25
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Toronto, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 2,593
I think your $25.00 price for the standards is little out of date. You must be an ABYC member to purchase them. I think this years invoice (membership at latest issue of standards) was $500.00 (converted to Canadian).
__________________
That hysterical laughter you hear as you sail a way in your "new" boat ..... is the seller.
boatpoker is offline   Reply With Quote
Old 21-11-2009, 10:05   #26
Senior Cruiser

Cruisers Forum Supporter

Join Date: Dec 2006
Location: Seattle
Boat: Cal 40
Posts: 2,401
Images: 7
Quote:
Originally Posted by Chief Engineer View Post
ABYC wants $25.00 for their book of standards. You would think they would have it in the public domain

CFR 33 Subpart J refers to Gasoline Engines only.

If the Racor Turbine Series Filters with heat shields are not approved, why are they sold with the "MA" designation?
Like NFPA, ABYC is a business, though not for profit businesses.

John
__________________
cal40john is offline   Reply With Quote
Old 21-11-2009, 16:50   #27
Eternal Member
 
Chief Engineer's Avatar

Join Date: Aug 2006
Location: North of Baltimore
Boat: Ericson 27 & 18' Herrmann Catboat
Posts: 3,798
Things must be bad in Canada

The Lowest priced memberships is $275,00 USD

Quote:
Originally Posted by boatpoker View Post
I think your $25.00 price for the standards is little out of date. You must be an ABYC member to purchase them. I think this years invoice (membership at latest issue of standards) was $500.00 (converted to Canadian).
__________________

__________________
Chief Engineer is offline   Reply With Quote
Reply

Tags
racor

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cleaning Racor 500 FG Filter - Problem ! MarkJ Engines and Propulsion Systems 36 16-02-2012 12:56
Racor Filters - Thank You clausont Engines and Propulsion Systems 0 28-09-2008 19:44
Racor 500 MINIMUM flow Whimsical Engines and Propulsion Systems 6 24-06-2008 02:49
Racor 500 Element Warning Pete the Cat Engines and Propulsion Systems 33 10-11-2006 03:55



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 12:15.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.