Diesel generator starting issue

I have a westerbeke 8K diesel generator and has developed a problem while starting. The starting procedure is to hold the switch for the glow plugs for 10 seconds or so and then hit the starter switch. The problem that has just developed is when the motor starts it barely wants to run for the first 15 seconds or so then it seems to straighten out and run normally for hours. Power production from the generator is fine. This problem just started a few days ago and no work has been recently performed just looking for a direction on where to start looking
motion30 is offline   Reply With Quote
Old 09-12-2017, 14:13   #2
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Diesel generator starting issue

Are your glow plugs working?

When you’re operating the glow plugs can you hear the electric fuel pump running?

I’d start with the glow plugs, be sure they’ve got voltage, and that each one has continuity.

Then move to fuel if the glow plugs check out. It’s possible you’ve got an air leak into the fuel that takes some time to clear out.
Sailmonkey is offline   Reply With Quote
Old 09-12-2017, 14:25   #3
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Re: Diesel generator starting issue

In order: Verify that the preheat/prime relay is working (using voltmeter): then verify that the fuel pump is getting power (same voltmeter); verify that fuel pump works from direct 12v connection; then check the glow plugs for power (same volt meter). If they have power check resistance (pull one for best reading; should be 1-6 ohms or so... one of these is probably it.
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 09-12-2017, 14:28   #4
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,407
Re: Diesel generator starting issue

I concur with Sailmronkey, check to see if all the glow plugs are working - one or more may have failed.

For a quick and dirty glow plug check, try putting the glow plugs back on immediately after starting (but during the first 15 seconds of poor running). If the engine immediately picks up, then perhaps it isn't a glow plug issue, rather perhaps a low compression issue. If so, always start with the easiest checks like valve lash etc.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 09-12-2017, 14:34   #5
Registered User

Join Date: Feb 2009
Posts: 2,409
Re: Diesel generator starting issue

Yea I was thinking glow plugs it's a 3 cylinder so should not be a big deal to check. If the glow plug is good the terminals will have continuity through the terminals yes?
motion30 is offline   Reply With Quote
Old 09-12-2017, 14:44   #6
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Diesel generator starting issue

Quote:
Originally Posted by motion30 View Post
Yea I was thinking glow plugs it's a 3 cylinder so should not be a big deal to check. If the glow plug is good the terminals will have continuity through the terminals yes?


Correct, but you’ll need to remove the bus bar connecting all the plugs and measure continuity to ground for each one.

Check for voltage before going this far though
Sailmonkey is offline   Reply With Quote
Old 10-12-2017, 12:37   #7
Registered User

Join Date: Feb 2007
Location: Live in Boise, boat is in the Rio Dulce
Boat: 56' CNSO Mikado Cutter Ketch
Posts: 367
Re: Diesel generator starting issue

Quote:
Originally Posted by motion30 View Post
I have a westerbeke 8K diesel generator and has developed a problem while starting. The starting procedure is to hold the switch for the glow plugs for 10 seconds or so and then hit the starter switch. The problem that has just developed is when the motor starts it barely wants to run for the first 15 seconds or so then it seems to straighten out and run normally for hours. Power production from the generator is fine. This problem just started a few days ago and no work has been recently performed just looking for a direction on where to start looking
I have a Westerbeke 7.6 BTD and had the exact same issue. Turned out it was picking up a small amount of air at a fuel fitting. Once it started it barely ran for 10-15 seconds while it burned thru the accumulated air. Once it got past it then it would run perfectly until the next time that I started it cold.

Good luck,

Jeff
Mikado is offline   Reply With Quote
Old 10-12-2017, 13:24   #8
Registered User

Join Date: Feb 2009
Posts: 2,409
Re: Diesel generator starting issue

Jeff
I will look at the fuel fitings. Damn thing vibrates enough to shake anything loose
motion30 is offline   Reply With Quote
Old 15-12-2017, 16:30   #9
Senior Cruiser

Cruisers Forum Supporter

Join Date: May 2013
Location: Oregon to Alaska
Boat: Wheeler Shipyard 83' ex USCG
Posts: 3,510
Re: Diesel generator starting issue

When you start most generators, pressing the start button bypasses the coolant temperature and oil pressure safeties. Releasing the start button transfers the run condition to the safeties. A short or loose wire to the sensors or a weak sensor can also cause the problem.
But an air leak is where I would look first. Air entry into the fuel system while stopped can allow the fuel to drain away from the injector pump. The engine starts on the fuel in the pump and then the pump receives the air. Because air compresses, fuel in the injector line doesn't have enough pressure to allow the injector spray to overcome the thick, condensed, air in the cylinder. You get a partial ignition or no ignition at all in that cylinder.
Injectors I know have some mechanism to close off the injector from the ignition as soon as injection is complete. Usually spring closed needle valves. Without proper pressure the valve either doesn't open or open all the way.
Lepke is offline   Reply With Quote
Old 15-12-2017, 17:16   #10
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Diesel generator starting issue

On our Westerbeke I have to hold the glow plug switch engaged while cranking the engine. The glow plug switch bypasses the oil and temp switches so the fuel can flow during starting. If I let go of the glow plug switch too soon after it fires the engine stops.
transmitterdan is offline   Reply With Quote
Old 21-12-2017, 13:05   #11
Registered User

Join Date: Jun 2015
Location: Cruising Pacific Mexico and FP in 2024
Boat: Moody 49
Posts: 135
Re: Diesel generator starting issue

me thinks you are too warm a place for real glow plug issues!

Air leak, certainly a bleed will sort this out.
Mark Thurlow is offline   Reply With Quote
Old 21-12-2017, 13:12   #12
Registered User

Join Date: Feb 2009
Posts: 2,409
Re: Diesel generator starting issue

Quote:
Originally Posted by Mark Thurlow View Post
me thinks you are too warm a place for real glow plug issues!

Air leak, certainly a bleed will sort this out.
I am thinking an air leak as well. , as the problem has gotten worse. I'm going to try to check it out tomorrow. These westerbeke 8K generators are supposed to be self bleeding do they have electric fuel pump
motion30 is offline   Reply With Quote
Old 21-12-2017, 14:01   #13
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Diesel generator starting issue

Quote:
Originally Posted by motion30 View Post
I am thinking an air leak as well. , as the problem has gotten worse. I'm going to try to check it out tomorrow. These westerbeke 8K generators are supposed to be self bleeding do they have electric fuel pump


They will self bleed, but is the leak is far away from the generator there could be quite a bit of air in the line.
Sailmonkey is offline   Reply With Quote
Old 31-12-2017, 04:09   #14
Registered User

Join Date: Feb 2009
Posts: 2,409
Re: Diesel generator starting issue

Follow up..
Finally got the motivation to take the sound shield apart, there was diesel fuel on the bottom of the enclosure. So i tightened a couple fuel clamps and checked everything else ,everything seem tight. Still no change in the starting issue. So I cleaned up the mess then I went down in the bilge again today and tighten the clamps a little more and the three fittings that come out of the fuel injection pump. that was the issue. It starts right up there with no hesitation there runs great I'd like to thank everybody for their invoice and happy New Year's to you all
motion30 is offline   Reply With Quote
Reply

Tags
diesel, generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Another hard starting 3GM-30f hard starting issue phantomracer Engines and Propulsion Systems 29 17-05-2017 03:19
Farymann Diesel Starting Issue T27Sailor Engines and Propulsion Systems 16 19-08-2014 07:02
Vovlo MD2B starting/wiring issue. Ramblingman Engines and Propulsion Systems 7 06-06-2013 12:22
Yanmar 1GM10 starting issue StuartWeibel Engines and Propulsion Systems 15 15-05-2013 18:34
Diesel Starting Issue After Sailing GalvestonBay Engines and Propulsion Systems 19 05-12-2011 07:22

Advertise Here


All times are GMT -7. The time now is 14:14.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.