Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by Dave Lochner View Post
Also, AC and DC are not entirely equivalent in these calculations. AC travels through wires much more efficiently than DC which tends to heat up wires more quickly than AC causing more resistance in the wire and subsequently more heat and power loss.
This is not correct. The standard practice in AC systems is to describe AC currents by the "root mean square" average of the waveform, which is a long way of saying that one amp of DC creates the same heat as one amp of AC, provided the length and cross section of the wire are the same.

Quote:
Originally Posted by Dave Lochner View Post
Since shore power is essentially an extension of the power grid to your boat, using NEC sizes for the AC system is OK. But, do not use household wire or automotive wire on the boat. Stick with marine grade wire.
.
I disagree. NEC ampacity tables are based on an ambient temperature (30C) that is appropriate for houses, not engine rooms. ABYC assumes that engine room temperatures are higher and there is good reason for that.
30C. In addition, the NEC ampacity tables do not include a column for insulation rated for 105C, which is common on boats.

Quote:
Originally Posted by Dave Lochner View Post
For DC wiring use the ABYC guidelines and marine grade wire.
I will not argue with that.
__________________

__________________
svlamorocha is online now   Reply With Quote
Old 12-08-2015, 10:51   #17
Registered User

Join Date: Nov 2013
Location: Homeport: Oswego, NY
Boat: 1993 Sabre 362 #113
Posts: 351
Re: Wire Ampacity - NEC or ABYC?

Attached is a page from Charlie Wing's Book on Marine Electrical Systems

The chart shows AC wire sizes to be roughly the same as the NEC standards. The over current protection should be lower than the wire's capacity in order to protect the wire.

"This is not correct. The standard practice in AC systems is to describe AC currents by the "root mean square" average of the waveform, which is a long way of saying that one amp of DC creates the same heat as one amp of AC, provided the length and cross section of the wire are the same. "

Yes, provided that the voltage is the same. 1 amp at 120 Volts has more energy than 1 amp at 12 V. You would need to have 10 amps at 12v to have the same energy as 1 amp at 120. (assuming resistive loads and not inductive loads) Thus we have very high voltage lines on the power grid.
Attached Thumbnails
Click image for larger version

Name:	AC-wire-size.jpg
Views:	65
Size:	441.9 KB
ID:	107185  
__________________

__________________
Dave Lochner is offline   Reply With Quote
Old 12-08-2015, 10:59   #18
Registered User

Join Date: Jun 2009
Location: still in a roll of fiberglass around Cape Town
Boat: Leopard 40 (new model)
Posts: 1,202
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by Dave Lochner View Post
1 amp at 120 Volts has more energy than 1 amp at 12 V. You would need to have 10 amps at 12v to have the same energy as 1 amp at 120. (assuming resistive loads and not inductive loads) Thus we have very high voltage lines on the power grid.
All that is great stuff but has nothing do with with ampacity-based wire sizing.

If you have one wire carrying 1A of AC and another wire carrying 1A of DC in the same environment then both will have the same temperature. Therefore the ampacity-based gauge is the same.

Another story is that AC usually uses higher voltages, and higher voltages let you carry more power with the same current (say 1A). In other words, at usual AC voltages (higher than usual DC voltages) you need smaller currents for the same appliance.

Still, the formulas to determine ampacity-base gauge from current at a point in a circuit are the same for AC and DC and have nothing to do with voltage between ends of a circuit. It is all about heat generation and dissipation!
__________________
svlamorocha is online now   Reply With Quote
Old 12-08-2015, 12:00   #19
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 4,030
Re: Wire Ampacity - NEC or ABYC?

So is the consensus that ABYC ampacity tables are not substantially more liberal than NEC for like cable and environmental conditions? I would be surprised if ABYC allowed way higher current than NEC. Both bodies give a lot of deference to NFPA so it would not make sense for them to arrive at completely different recommendations.
__________________
transmitterdan is offline   Reply With Quote
Old 12-08-2015, 13:45   #20
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 809
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by transmitterdan View Post
So is the consensus that ABYC ampacity tables are not substantially more liberal than NEC for like cable and environmental conditions? I would be surprised if ABYC allowed way higher current than NEC. Both bodies give a lot of deference to NFPA so it would not make sense for them to arrive at completely different recommendations.

I am not yet convinced of that.

First, despite efforts in the past by NFPA to form (or threaten to form) a model building code, the NEC, NFPA and I assume the ABYC, give no deference to anyone, and that includes especially when they feel someone is stepping on their turf. The battle amongst the various model building codes (ICBO, BOCA, SBC, etc.) in the past have been downright silly.

Second, and particularly for NFPA and ABYC, the fact that they seem to think their code documents need to be treated with secrecy and stealth to all but their members is asinine. This info is public and should be made so without subscription or burdensome costs. In the age of the internet this is stone age thinking. Their current business model sucks!

Third, with all the various data sources and conflicting information, posted primarily by third party commercial interests, spurious data is presented as fact, without context or clarification. At the very least we have should have a global source, readily accessible, for clear and concise factual data. Not a Wiki of data (I don't support crowd sourcing for electrical data), but a vetted, authoritative source.

Comparing NEC and ABYC is not apples to apples. THWM 90C rating cable is not the same as BC5-W2 cabling in an engine compartment. And SAE wiring, which you might encounter on propulsive machinery, is different entirely!!
__________________
redsky49 is offline   Reply With Quote
Old 12-08-2015, 14:25   #21
Registered User

Join Date: Jun 2013
Location: Indiana
Boat: Carver 450 voyager
Posts: 27
Re: Wire Ampacity - NEC or ABYC?

Boat wire is very fine strand with multiple smaller wires wrapped together to form I #12 wire. House wire has 1 solid wire. Electricity travels around the outside of each strand. Thus boat wire, like welders cable has a higher amp rating than solid #12 house wire.
__________________
Monepit is offline   Reply With Quote
Old 12-08-2015, 14:49   #22
Registered User

Join Date: Jul 2015
Posts: 30
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by Dave Lochner View Post
Attached is a page from Charlie Wing's Book on Marine Electrical Systems

Yes, provided that the voltage is the same. 1 amp at 120 Volts has more energy than 1 amp at 12 V. You would need to have 10 amps at 12v to have the same energy as 1 amp at 120. (assuming resistive loads and not inductive loads) Thus we have very high voltage lines on the power grid.
Dave you are confused, "wattage", the sum of volts times amps on DC system,has nothing to do with wire heating, the resistance of the wire impeding the flow of current is what causes heat.

Same is true for AC but it's volts times amps times power factor. On a true resistive load power factor would be 1.
Also listen to svlamorocha, he has it right. In AC it's the RMS current, the average current draw across the complete cycle of the sine wave. Peak to peak tends to be about 2.8 times the average or RMS.
__________________
dave948 is offline   Reply With Quote
Old 12-08-2015, 15:05   #23
Moderator
 
Paul Elliott's Avatar

Cruisers Forum Supporter

Join Date: Sep 2006
Posts: 3,888
Images: 4
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by Monepit View Post
Boat wire is very fine strand with multiple smaller wires wrapped together to form I #12 wire. House wire has 1 solid wire. Electricity travels around the outside of each strand. Thus boat wire, like welders cable has a higher amp rating than solid #12 house wire.
Not the case for DC. You are describing "skin effect", and this only applies for alternating current. It is actually quite minor at 50-60 Hz (8.5 mm at 60Hz, so for the sizes we are talking about effectively the entire wire is being used.) For DC current, skin effect is non-existent.

Also, to get around skin effect by using stranded wire, each individual strand must be insulated. This type of wire is called "Litz wire" and is sometimes done for wire used in high-frequency transformers and inductors.
__________________
Paul Elliott, S/V VALIS - Pacific Seacraft 44 #16 - Friday Harbor, WA
www.sailvalis.com
Paul Elliott is offline   Reply With Quote
Old 13-08-2015, 04:53   #24
Moderator Emeritus
 
GordMay's Avatar

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 31,592
Images: 240
Re: Wire Ampacity - NEC or ABYC?

Quote:
... the NEC, NFPA and I assume the ABYC, give no deference to anyone ...
FWIW: The National Electrical Code (NEC) IS NFPA 70
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 13-08-2015, 05:43   #25
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,432
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by Dave Lochner View Post
Attached is a page from Charlie Wing's Book on Marine Electrical Systems

The chart shows AC wire sizes to be roughly the same as the NEC standards. The over current protection should be lower than the wire's capacity in order to protect the wire.

"This is not correct. The standard practice in AC systems is to describe AC currents by the "root mean square" average of the waveform, which is a long way of saying that one amp of DC creates the same heat as one amp of AC, provided the length and cross section of the wire are the same. "

Yes, provided that the voltage is the same. 1 amp at 120 Volts has more energy than 1 amp at 12 V. You would need to have 10 amps at 12v to have the same energy as 1 amp at 120. (assuming resistive loads and not inductive loads) Thus we have very high voltage lines on the power grid.
This is wrong. For power distribution applications, the required size of the wire is determined only by the amps to be carried by the wire. Voltage carrying capacity of the wire is determined by the insulation between it's source and return path. Hence, a 12 awg wire carrying 20 amps @ 1 volt delivers 20 watts of power. The same 12 awg wire carrying the same 20 amps @ 600 volts will deliver 12,000 watts. Both are acceptable for 12 awg (given the insulation material is rated @ 600 volts, typical in household romex type wire).
__________________
DotDun is offline   Reply With Quote
Old 13-08-2015, 06:27   #26
Registered User
 
Scout 30's Avatar

Join Date: Oct 2014
Location: Florida
Boat: Scout 30
Posts: 2,358
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by redsky49 View Post

Second, and particularly for NFPA and ABYC, the fact that they seem to think their code documents need to be treated with secrecy and stealth to all but their members is asinine. This info is public and should be made so without subscription or burdensome costs. In the age of the internet this is stone age thinking. Their current business model sucks!

Third, with all the various data sources and conflicting information, posted primarily by third party commercial interests, spurious data is presented as fact, without context or clarification. At the very least we have should have a global source, readily accessible, for clear and concise factual data. Not a Wiki of data (I don't support crowd sourcing for electrical data), but a vetted, authoritative source.

I agree. Great post!
__________________
Scout 30 is offline   Reply With Quote
Old 13-08-2015, 07:10   #27
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: San Francisco Bay
Boat: research vessel
Posts: 10,152
Re: Wire Ampacity - NEC or ABYC?

Tesla vs Edison. Tesla's idea eventually won out mostly because for the same gauge wire and the same current, AC can transfer power a greater distance.

https://en.wikipedia.org/wiki/War_of_Currents
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 13-08-2015, 07:23   #28
Certifiable Refitter/Senior Wannbe
 
Wotname's Avatar

Cruisers Forum Supporter

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: Van DeStat Super Dogger 31'
Posts: 7,336
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by dave948 View Post
Dave you are confused, "wattage", the sum of volts times amps on DC system,has nothing to do with wire heating, the resistance of the wire impeding the flow of current is what causes heat.
Exactly

Quote:
Originally Posted by dave948 View Post
.
Also listen to svlamorocha, he has it right. In AC it's the RMS current, the average current draw across the complete cycle of the sine wave. Peak to peak tends to be about 2.8 times the average or RMS.
Not quite but close
The relationship of AC currents in pure resistive loads are
RMS current = 0.707 times Peak current
Average current = 0.5 times Peak current

The RMS current is for all intends and purposes the "real" current as far as power and heating aspects are concerned.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 13-08-2015, 13:45   #29
Registered User

Join Date: Jul 2015
Posts: 30
Re: Wire Ampacity - NEC or ABYC?

Quote:
Originally Posted by Wotname View Post
Exactly


Not quite but close
The relationship of AC currents in pure resistive loads are
RMS current = 0.707 times Peak current
Average current = 0.5 times Peak current

The RMS current is for all intends and purposes the "real" current as far as power and heating aspects are concerned.
You may be right, I'm not sure but I think we are on the same page but thinking of different values. Your right about peak back to zero, a quarter of a sine wave. I was referencing a full cycle, zero to peak back to zero then zero to peak back to zero in the opposite direction. 2.8 peak to peak.
__________________
dave948 is offline   Reply With Quote
Old 13-08-2015, 17:30   #30
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 4,030
Re: Wire Ampacity - NEC or ABYC?

Dave,

You are right, the peak to peak voltage is 2.8 times the RMS voltage for a sinusoid.

It is important to consider the voltage drop because for 12V DC the percentage drop is much higher than for AC circuits for the same current and wire size. The current that causes a 1% voltage drop for 120V AC will cause a 10% drop on a 12V DC circuit even though the current and wire size are the same. The allowed ampacity is only one part of the system design. Voltage drop also has to factor into the decision about wire size. Similarly the size of the wire creates an upper limit on circuit breaker size but there is nothing wrong with using a smaller breaker/fuse.
__________________

__________________
transmitterdan is offline   Reply With Quote
Reply

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
wire rigging dyform, compact wire, rod RDW Deck hardware: Rigging, Sails & Hoisting 4 12-11-2014 03:51
What's the Best Way to Connect a 4mm Wire to the Middle of a 6mm Wire? mischief Electrical: Batteries, Generators & Solar 11 07-11-2013 10:31
New wire being made 5 foot battery wire to terminal strip sdowney717 Electrical: Batteries, Generators & Solar 3 20-08-2012 09:27
How to Wire a Battery Isolator with a Three Wire Alternator ? bazzer Electrical: Batteries, Generators & Solar 7 05-12-2010 13:47



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 02:17.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.