Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 25-10-2015, 14:02   #46
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Which Brand of Inverter?

The problem I'm running into is I can't find a 2KW or ideally smaller inverter that has a way to connect into the ships power system, all I have found have plugs only, I want a way to connect a 10Ga wire to it, then to a switch that will prevent shore power combining with the inverter, just exactly like I have with my built in generator, I want to wire the inverter just like I did the generator.
Anyone know of a brand that has studs I can connect to instead of the regular three prong plug?
I'm not interested in an inverter / charger, just an inverter.
I only need a few hundred watts, I want to be able to run a few AC only things I have on the boat, without having to crank the generator to do so.


Sent from my iPad using Cruisers Sailing Forum
a64pilot is offline   Reply With Quote
Old 25-10-2015, 14:14   #47
Registered User

Join Date: Apr 2012
Location: Winter Germany, Summer Med
Boat: Lagoon 380 S2
Posts: 1,924
Re: Which Brand of Inverter?

Quote:
Originally Posted by hellosailor View Post

The inverter is easy enough to find, but the feeding and care of it, and ensuring it gets enough power from a big enough battery bank and cables, that's the really expensive part of things.
You are right but the comexities depend on the needs and the exisitng setup. At least in our case it was quite simple. The inverter sits 40cm from the main fuse next to the battery. But of course one needs big wires with appropriately crimped terminal connectors. I happened to have these tools but otherwise any chandlery can do that.

But of course we can't use the inverter like power at home. No problem to use a toaster, microwave or power grinder for a minute or two but two ladies with long hair and a 1500w hairdryer could draw the batteries down. So anything big that runs longer than a few minutes requires an engine to run. Happens very rarely so not a problem for us.

Anyway its nice to have the possibility to use big applances and tools should the need arise.
rabbi is offline   Reply With Quote
Old 25-10-2015, 14:22   #48
֍֎֍֎֍֎֍֎֍֎

Join Date: Apr 2006
Posts: 15,136
Re: Which Brand of Inverter?

"I want a way to connect a 10Ga wire to it,"
And the ampacity of a 10 AWG wire is going to limit the size of your inverter, even if your wire is only a yard long, to how many watts? Maybe 10-20 amps, depending on the voltage drop you want to suffer. So maybe a two hundred watt inverter?
Or did I get my math all wrong again?
hellosailor is offline   Reply With Quote
Old 25-10-2015, 14:23   #49
Registered User
 
SailRedemption's Avatar

Join Date: Feb 2014
Location: New Orleans
Boat: Kaufman 47
Posts: 1,184
Re: Which Brand of Inverter?

Quote:
Originally Posted by rabbi View Post
The comment about charging devices was for the OP. Really these USB charging sockets are excellent.

If I'm not mistaken we have a Sterling Pro Power S 1500 pure sine inverter. Now that I looked it up I realize that we got it for next to nothing. We paid 180 euro for a brand new item. Seems these went for around 900 euro normally.
Oh nice, I was looking at that one. Yea, you definitely got it for a steal! I'm holding off now for the inverter to see what my actual needs are when we start sailing in spring. I just bought a Victron Phoenix charger for that reason.

A Plus that no one has mentioned about having separate units I that a standalone charger can accept different input voltages and hz. At least the option is there. A inverter /charger doesn't do that, at least non I have found.

For me at least, I need a charger more than an inverter at this time so... Viola

Sent from my VS986 using Tapatalk
SailRedemption is offline   Reply With Quote
Old 25-10-2015, 14:44   #50
Registered User

Join Date: Apr 2012
Location: Winter Germany, Summer Med
Boat: Lagoon 380 S2
Posts: 1,924
Re: Which Brand of Inverter?

Quote:
Originally Posted by SailRedemption View Post
A Plus that no one has mentioned about having separate units I that a standalone charger can accept different input voltages and hz. At least the option is there. A inverter /charger doesn't do that, at least non I have found.
Clayton power g3 combi does 45-65hz and 110-265v.
Our previous boat came with such a beauty but i have no clue how much the prhious owner paid for that.
rabbi is offline   Reply With Quote
Old 25-10-2015, 14:59   #51
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Which Brand of Inverter?

Quote:
Originally Posted by hellosailor View Post
"I want a way to connect a 10Ga wire to it,"
And the ampacity of a 10 AWG wire is going to limit the size of your inverter, even if your wire is only a yard long, to how many watts? Maybe 10-20 amps, depending on the voltage drop you want to suffer. So maybe a two hundred watt inverter?
Or did I get my math all wrong again?

10 Ga on the 110V side, although it's overkill, I have it, and like oversizing wire.
2 Ga on the low volt side, total run about 6', inverter within 3' of the house bank. Gauge is again overkill, but I have 2 ga.

So what I'm looking for is an ideally a 1 - 2 KW inverter, that is capable of being wired directly to, I dislike the plug idea although I guess you can easily get 1,000W through a plug, but not 2,000W.


Sent from my iPad using Cruisers Sailing Forum
a64pilot is offline   Reply With Quote
Old 25-10-2015, 15:34   #52
Registered User
 
SailRedemption's Avatar

Join Date: Feb 2014
Location: New Orleans
Boat: Kaufman 47
Posts: 1,184
Re: Which Brand of Inverter?

Quote:
Originally Posted by a64pilot View Post
10 Ga on the 110V side, although it's overkill, I have it, and like oversizing wire.
2 Ga on the low volt side, total run about 6', inverter within 3' of the house bank. Gauge is again overkill, but I have 2 ga.

So what I'm looking for is an ideally a 1 - 2 KW inverter, that is capable of being wired directly to, I dislike the plug idea although I guess you can easily get 1,000W through a plug, but not 2,000W.


Sent from my iPad using Cruisers Sailing Forum
You can get watts through the plug it's the amps that gets things heated up.. Take a hair dryer, most are 1500 Watt or more but the typical house bathroom outlets does just fine. But I'm not an electrician, just what I have absorbed working with my dad.

But I agree, I'm looking for the same as you, same size and installation. I have found the victron Phoenix inverters are wire up in the size you look for. I think the biggest 120v they make is a 1500w for about $700 on Jamestown.

Sent from my VS986 using Tapatalk
SailRedemption is offline   Reply With Quote
Old 25-10-2015, 16:41   #53
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,706
Re: Which Brand of Inverter?

Quote:
Originally Posted by a64pilot View Post
The problem I'm running into is I can't find a 2KW or ideally smaller inverter that has a way to connect into the ships power system, all I have found have plugs only, I want a way to connect a 10Ga wire to it, then to a switch that will prevent shore power combining with the inverter, just exactly like I have with my built in generator, I want to wire the inverter just like I did the generator.
Anyone know of a brand that has studs I can connect to instead of the regular three prong plug?
I'm not interested in an inverter / charger, just an inverter.
I only need a few hundred watts, I want to be able to run a few AC only things I have on the boat, without having to crank the generator to do so.
a64,

What you're looking for is a stand alone inverter that has an automatic transfer switch (ATS) inside it. Most all combined I/Cs do have this feature. I KNOW you are not looking for a combined I/C.

There are two choices:

1. Get a standalone inverter without an ATS and buy a manual switch and install and use it. If you're away from shorepower anyway, it will almost always be on inverter, but you HAVE TO make sure you don't plug in to shorepower with it on inverter.

2. Find a standalone inverter WITH an ATS. On another boating forum I had this same discussion recently and IIRC Maine Sail said they now make standalone inverters with an ATS. I'll see if I can find that discussion. And, if I may suggest, you could do some Google homework yourself, knowing they do exist.
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 25-10-2015, 17:36   #54
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,162
Re: Which Brand of Inverter?

You can also do what I did, split the duplex outlets and wire one for the inverter and the other for the shorepower.
Take a look at the side of any USA style duplex socket and you will see where it can be cut for that purpose.
That way, shore cannot mix with inverter, even if both are electrically live at the same time.
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 25-10-2015, 18:30   #55
Registered User

Join Date: Aug 2013
Posts: 431
Re: Which Brand of Inverter?

I have a Kisae 55amp/2000 watt true sine I/C. Inexpensive, Works well and very good service when i needed it (See my previous posts on this site re Inverter issue). My only complaint is that the DC ground screw is way too small and it's difficult to access the mounting bracket once the wiring is in place. Otherwise works great.
osprey877 is offline   Reply With Quote
Old 25-10-2015, 19:18   #56
Registered User
 
SailRedemption's Avatar

Join Date: Feb 2014
Location: New Orleans
Boat: Kaufman 47
Posts: 1,184
Re: Which Brand of Inverter?

Quote:
Originally Posted by Stu Jackson View Post
a64,

What you're looking for is a stand alone inverter that has an automatic transfer switch (ATS) inside it. Most all combined I/Cs do have this feature. I KNOW you are not looking for a combined I/C.

There are two choices:

1. Get a standalone inverter without an ATS and buy a manual switch and install and use it. If you're away from shorepower anyway, it will almost always be on inverter, but you HAVE TO make sure you don't plug in to shorepower with it on inverter.

2. Find a standalone inverter WITH an ATS. On another boating forum I had this same discussion recently and IIRC Maine Sail said they now make standalone inverters with an ATS. I'll see if I can find that discussion. And, if I may suggest, you could do some Google homework yourself, knowing they do exist.
If you wire the inverter to where you can only do one or the other then you don't need a ATS. Blue Sea makes a AC rotary https://www.jamestowndistributors.co...otary+Switchesswitch for this application. One side for shore and the other for inverter and off. When you are plugged in set it on shore when away put it on inverter. If not leave it on off. This way you can't blow the inverter by having the shore power back feeding.

Am I thinking this correct? It makes sense to me, but I've been wrong before.

Sent from my VS986 using Tapatalk
SailRedemption is offline   Reply With Quote
Old 25-10-2015, 19:42   #57
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 33,873
Re: Which Brand of Inverter?

Quote:
Originally Posted by hellosailor View Post
A unit that is a shorepower charger/inverter implies there is shorepower, in which case an inverter isn't going to be needed... .




Erm, it inverts when there's no shore power, and charges when there is shower power.

If it has power boost, it will invert even when there is shore power -- to make up the difference when the loads exceed the shore power connection.
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is offline   Reply With Quote
Old 25-10-2015, 20:06   #58
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,706
Re: Which Brand of Inverter?

Quote:
Originally Posted by SailRedemption View Post
If you wire the inverter to where you can only do one or the other then you don't need a ATS. Blue Sea makes a AC rotary https://www.jamestowndistributors.co...otary+Switchesswitch for this application. One side for shore and the other for inverter and off. When you are plugged in set it on shore when away put it on inverter. If not leave it on off. This way you can't blow the inverter by having the shore power back feeding.

Am I thinking this correct? It makes sense to me, but I've been wrong before.
Yes, you're right. What you are describing is a MANUAL transfer switch. They make rotary and "straight" ones. They are used for inverters and for generators. a64 is looking for a standalone inverter with a built in ATS.
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 25-10-2015, 20:23   #59
Registered User

Join Date: May 2008
Posts: 3,536
Re: Which Brand of Inverter?

Well, here's a 300 watt inverter that can be wired directly. Don't know it but I know people like Morningstar solar controllers.

SureSine » Morningstar Corporation

But if the cost is not prohibitive for you, just get an inverter/charger made for marine use. You'll really be happier in the long run.

I'd pick the 2000 watt Victron inverter/charger that can be had for just over $1000. I've used Victrons in three boats over the last 15 years and been very happy. If you must, think of it as an inverter with a spare charger if your old charger breaks.You don't even need to connect shore power wires.

Or run both chargers to charge your batteries faster (depending on the battery type/banks size). Most boat's have a charger that is too small to put a proper load on the genset. The genset then wastes fuel and runs too cool idling along.
CarlF is offline   Reply With Quote
Old 25-10-2015, 20:38   #60
Registered User
 
SailRedemption's Avatar

Join Date: Feb 2014
Location: New Orleans
Boat: Kaufman 47
Posts: 1,184
Re: Which Brand of Inverter?

Quote:
Originally Posted by Stu Jackson View Post
Yes, you're right. What you are describing is a MANUAL transfer switch. They make rotary and "straight" ones. They are used for inverters and for generators. a64 is looking for a standalone inverter with a built in ATS.
Ah, I must have missed that he wanted the ATS on it.. Great.

Sent from my VS986 using Tapatalk
SailRedemption is offline   Reply With Quote
Reply

Tags
inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
420: 420 inverter issues. Our inverter is not working and we are not able to find a manual EW-WE Lagoon Catamarans 5 15-04-2020 07:04
Inverter Draw is it relative to the appliance using it or the wattage of the inverter felixqld66 Electrical: Batteries, Generators & Solar 5 06-06-2011 05:50
True (Pure) Sine Inverter vs Modified Sine Inverter Alecadi Electrical: Batteries, Generators & Solar 19 05-05-2011 06:19
Separate Charger and Inverter or Charger-Inverter ? SvenG Electrical: Batteries, Generators & Solar 14 15-10-2010 17:14
Calculating Amps Drawn Before Inverter and After Inverter ? impi Electrical: Batteries, Generators & Solar 23 26-09-2010 22:24

Advertise Here


All times are GMT -7. The time now is 17:45.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.