Cruisers Forum
 

Go Back   Cruisers & Sailing Forums > Engineering & Systems > Electrical: Batteries, Generators & Solar
Cruiser Wiki Click Here to Login
Register Vendors FAQ Community Calendar Today's Posts Log in

Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 23-08-2012, 02:48   #1
Registered User

Join Date: Feb 2010
Location: Vancouver, BC
Posts: 33
Voltage Drop From Battery To Main Breaker Panel

Hello. I have a 2003 Beneteau 50 and we're having some undervolt problems. We replaced the three house batteries with new lead-acid filled 135AH batteries a month or so ago. The starter battery is isolated, though it shares a common ground with the house batteries.

If I measure voltage at any one of the the house batteries with no load it reads say 12.3 volts -- but the voltage at the panel is 11.7. As I turn on different loads there is a marked voltage loss at the panel ... If I turn on everything at the same time pulling some 20AH of load on my amp-meter, the voltage drop at the panel is to something like 10.8 or so volts -- I have verified this as well by several means -- the Garmin chartplotter says the same voltage as the voltmeter at the breaker panel ... also my digital voltmeter says the same thing. and my inverter starts an audible alarm below 11.0 volts.

When I measured the volts at the battery instead of losing nearly 2 volts when everything is turned on, the voltage loss at the battery is only 0.1 or 0.2 volts.

We are not particularly careful in terms of battery usage -- we are anchored out about 3/4 of the time but run a generator to charge batteries and our computeres for a few hours at least a couple of times a week. We are often charging computers via the inverter but have a policy that they can only charge when the engine is running.

We have an 80amp Hitachi alternator ... with the battery charger on we get 13.25 volts at the house and starter batteries and about the same with the engine running and alternator charging. At the breaker panel we get about 12.5-12.7 when the engine or charging system is running.

My guess is that we might have some corrosion in the system somewhere -- either that or the wire from the house batteries to the breaker panel is too small.

We haven't added too much in terms of load from the original delivery manifest from Beneteau and recent replacements of RADAR, Chartplotter and going LED for mooring and navigation lights has taken off more for more load than anything we have adding.

So ... what I was planning to do is to chase each connection from the batteries on out to the breaker panel and clean and measure the resistance across each of these wires as power makes its way from the batteries to the breaker panel. (e.g., battery connections -- fusible link, battery switch, breaker panel wire, etc.)

I doubt it is in the ground circult as the starter battery is not affected ... but will probably check there first anyway as that would be a likely problem area.

Any ideas or recommendations would be appreciated. Does anyone else have some direct experience in this or advice that we can use? Thanks for the assistance.
marina.alex is offline   Reply With Quote
Old 23-08-2012, 02:58   #2
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Voltage Drop from Battery to Main Breaker Panel

Checking all the connections from the house battery bank to the panel is where I would start. I would look first at the connections on the battery itself. Get a wire brush and clean all the connections both on the terminals and on the cables.

If that doesn't fix it I would next check all the connections to see if any are loose. If no then start checking these.

You might also want to track the voltage through the system to see if you can isolate where the voltage drops, starting at the batteries where the voltage is good.

It also sounds like your charging voltages are on the low side so you may be dropping voltage in the charging circuits as well.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 23-08-2012, 03:01   #3
Registered User

Join Date: Dec 2009
Posts: 2,959
Images: 4
Ya. A bad connection somewhere. Probably warm or hot to the touch. Maybe melted. Trace it with the voltmeter. Put one lead on the battery terminal then the other on each terminal between there and the load panel. You'll find it easy.
daddle is offline   Reply With Quote
Old 23-08-2012, 03:26   #4
Marine Service Provider
 
edsailing's Avatar

Join Date: Apr 2009
Location: Devon, UK
Boat: Sailing vessels up to 200 tons
Posts: 388
Images: 1
Re: Voltage Drop From Battery To Main Breaker Panel

Charging voltages seem very low - should be getting 14+V to get the batteries fully charged. I would go over all connections, take them off, clean and refix.
__________________
Regards, Ed

Delivering boats for a living - no more!
edsailing is offline   Reply With Quote
Old 23-08-2012, 03:55   #5
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Voltage Drop From Battery To Main Breaker Panel

As others have noted, your charging voltages are WAY low, and those new batteries aren't going to last long at this rate.

Charge absorption/acceptance levels for flooded batteries should be 14.4VDC at a minimum. Trojan recommends 14.8VDC and my own research confirms that this level is highly desirable.

Your alternator should be putting out 14.4 or higher.

Appropriate float level voltage (when the batteries are nearly full) are 13.2-13.8VDC.

I'd certainly agree that you have bad connections somewhere with the voltage drop you're seeing. And, it's very likely to be more than one problem connection. CHECK ALL OF THEM on both the positive and negative side.

If you have a diode isolator in the circuit, that can account for a modest drop, but nothing like you're seeing.

Also, check voltage drop across battery switches. I've seen some large drops due to bad switch contacts.

It's important to check the end connectors on each wire to be sure they are properly fitted. If there's any doubt, renew them (cut them off and put on new ones, properly, using the right crimper for the terminals you're using).

Sound like a lot of work? Yes, it can be. But your electrical problems are likely to persist if you don't nail this problem now. And, you'll go broke trying to keep your batteries in good condition.

Bill
btrayfors is offline   Reply With Quote
Old 23-08-2012, 04:15   #6
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,394
Images: 241
Re: Voltage Drop From Battery To Main Breaker Panel

Quote:
... My guess is that we might have some corrosion in the system somewhere -- either that or the wire from the house batteries to the breaker panel is too small ...
Indeed.

To test the voltage drop of any length of wire, do the following:
1. Set the voltmeter to read millivolts or on the lowest volt scale.
2. Put the voltmeter positive lead on the end of the wire closest to the battery.
3. Put the voltmeter negative lead on the other end of the wire.
4. Operate the circuit.
5. If the voltage drop is more than 0.200V* (200mV), the wire, or connections are bad.
6. If excessive, remove the wire at both ends and clean the connections, retest.
7. If still excessive*, replace the wire.

* 0.00V across a connection
Maximum 0.375V across an entire run of wire (3% of 12.5V)
0.30V across a switch
0.10V at a ground

See ➥ Diagnosing Voltage Drops - Electrical Automotive Troubleshooting

And ➥ http://assets.fluke.com/appnotes/aut...e/beatbook.pdf
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 23-08-2012, 04:17   #7
Registered User

Join Date: Mar 2012
Location: On board in Leros, Greece
Boat: Hunter Legend 420 Passage
Posts: 863
Re: Voltage Drop From Battery To Main Breaker Panel

Quote:
Originally Posted by btrayfors View Post
Also, check voltage drop across battery switches. I've seen some large drops due to bad switch contacts.
+1

Instead of checking the resistance at each connection or across each switch check the voltage, at say 20 amps. The larger the current flowing the larger the voltage drop. (Ohms law V=IxR) If you get more than 3% loss = 0.4 volts then you have a problem at that connection. This happened on my master house battery switch which never gets turned off. Turned it on/off 50 times and the volt drop when down to 0.1v. Took it to pieces and cleaned all the corrosion and the volt drop went down to 0.01v.
sailinglegend is offline   Reply With Quote
Old 23-08-2012, 04:50   #8
Marine Service Provider
 
edsailing's Avatar

Join Date: Apr 2009
Location: Devon, UK
Boat: Sailing vessels up to 200 tons
Posts: 388
Images: 1
Re: Voltage Drop From Battery To Main Breaker Panel

Another thought. I had battery charging problems on a Jeanneau 45 last year. The output off the alternator was low, 13.5 volts and the electrician I got in reckoned there was a small mod needed to to the regulator to up it to 14.8. Not sure what he did as this was at the end of the delivery but believe he fixed it.
__________________
Regards, Ed

Delivering boats for a living - no more!
edsailing is offline   Reply With Quote
Old 23-08-2012, 05:44   #9
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Voltage Drop From Battery To Main Breaker Panel

Another way to do this is to rent a thermal camera for checking your electrical system, to find warm or hot spots.

What is your max alternator output?
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 26-08-2012, 08:43   #10
Registered User

Join Date: Feb 2010
Location: Vancouver, BC
Posts: 33
Re: Voltage Drop From Battery To Main Breaker Panel

Thanks for all the replies. I have done some more problem determination. Based on the input I have received so far I think the data shows my big problem is at the battery isolator where there is about a 1.5 volt drop. Then each of the switches seem to lose between 0.1 and 0.3 volts, then further down the line it is fairly consistent throughout the rest of the circuits.
I wasn’t able to get inside the battery charger to figure out its starting voltage, but I measured the voltages across the other elements the same as with the alternator.
My course of action will be to disassemble and clean all battery connections between the isolator, switches and batteries, then re-measure what we have. While I am doing this I will also measure any drop across the switches & depending on time might dismantle and clean them as well.
Any other recommendations would be appreciated …. Thx
Here’s the data
Alternator Batt Charger
Voltage out of Alternator 14.21
Voltage at Starting Battery 12.98 13.98
Voltage at House Battery 12.85 13.39
Voltage at Garmin 12.70 13.00

Battery Isolator middle -- directly from Alternator 14.28 13.03
Batt Isolator Top -- to Starter Batt 13.12 -
Batt Isolator Bot -- to House Batteries 12.94 13.30

Battery Switch 1 (Starter) Top 13.22 13.90
Battery Switch 1 (Starter) Bot 13.10 13.95

Battery Switch 2 (House) Top 12.95 13.36
Battery Switch 2 (House) Bot+A16 12.90 13.37

425 Amp inline Fuse In 12.95
425 Amp inline Fuse Out 12.95

At 70amp DC Circuit Breaker in Panel In 12.98 13.18
At 70amp DC Circuit Breaker in Panel Out 12.98

Volts at largest Red Wire coming into Panel 13.00 13.39
marina.alex is offline   Reply With Quote
Old 26-08-2012, 09:33   #11
Marine Service Provider
 
edsailing's Avatar

Join Date: Apr 2009
Location: Devon, UK
Boat: Sailing vessels up to 200 tons
Posts: 388
Images: 1
Re: Voltage Drop From Battery To Main Breaker Panel

Your voltage out of the alternator is way low, should be 14.8.... what's the shore power voltage showing? Looks like you have dirty/poor contacts through most of system as well so cleaning looks like a good move. I would be concerned to get charging voltage up to right level as otherwise your batteries won't be getting above 85% charge.
__________________
Regards, Ed

Delivering boats for a living - no more!
edsailing is offline   Reply With Quote
Old 26-08-2012, 10:22   #12
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Voltage Drop From Battery To Main Breaker Panel

Good thoughts from everyone.
The only bit I would add is when measuring voltage drop make sure there is a reasonable power draw in the system. Turn on enough equipment so 10A,or so, are drawn from the batteries.
noelex 77 is offline   Reply With Quote
Old 10-11-2021, 12:09   #13
Marine Service Provider

Join Date: Oct 2012
Location: San Francisco Bay Area
Boat: Beneteau 43
Posts: 81
Re: Voltage Drop From Battery To Main Breaker Panel

This is a very old post, but I have a very similar issue with my Beneteau 43:

With approx 16 A of current, I have a 0.9 V drop between the house battery bank and my electrical panel. The batteries would be at a healthy 12.3 V under load (no engine, no charger), but the panel meter shows ~11.4 V, enough to cause my low voltage alarm to go off, and some sensitive electronics to stop working correctly.

I traced the drop back to two spots:
- 0.3 V across two the main battery switches (red and black, 0.15 V each)
- 0.6 V across the wires between the switches and the panel.

The latter can be explained by the fact that there are about 40' of 6 AWG cables (round trip, black and red), which at 16 A would yield about that voltage drop based on the AWG specs. Why Beneteau would use 6 AWG wire for that long a stretch on a most critical connection is hard to understand. I think my only workaround is to add a supplemental pair of 6 AWG wires to that same connection.

The drop that I can't explain is that on the switches. Does it seem reasonable that at only 16 A a big, bulky switch would drop that much voltage? Is there any maintenance that needs to be done to the switch? (cleaning it etc..I am not sure one can even open the switch to clean it). Or just replace both of them?

Thanks for any insight!

coupdemistral is offline   Reply With Quote
Old 11-11-2021, 08:40   #14
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,317
Re: Voltage Drop From Battery To Main Breaker Panel

Quote:
Originally Posted by coupdemistral View Post
This is a very old post, but I have a very similar issue with my Beneteau 43:

With approx 16 A of current, I have a 0.9 V drop between the house battery bank and my electrical panel. The batteries would be at a healthy 12.3 V under load (no engine, no charger), but the panel meter shows ~11.4 V, enough to cause my low voltage alarm to go off, and some sensitive electronics to stop working correctly.

I traced the drop back to two spots:
- 0.3 V across two the main battery switches (red and black, 0.15 V each)
- 0.6 V across the wires between the switches and the panel.

The latter can be explained by the fact that there are about 40' of 6 AWG cables (round trip, black and red), which at 16 A would yield about that voltage drop based on the AWG specs. Why Beneteau would use 6 AWG wire for that long a stretch on a most critical connection is hard to understand. I think my only workaround is to add a supplemental pair of 6 AWG wires to that same connection.

The drop that I can't explain is that on the switches. Does it seem reasonable that at only 16 A a big, bulky switch would drop that much voltage? Is there any maintenance that needs to be done to the switch? (cleaning it etc..I am not sure one can even open the switch to clean it). Or just replace both of them?

Thanks for any insight!

Oh my,, #6 wire for that run is bordering on criminal.
Do you have any info about the specs of the "big bulky" switch, (that link wouldn't allow me to enter without a password).
Many so called "heavy duty" switches use brass contacts and the oxide that forms on brass has lower conductivity than the base metal.
The best switches use copper, or copper/silver, which not only have much better conductivity, but any oxide that forms will not have as much resistance.
I've always recommended the use of the heavy duty switches from Cole-Hersee,, they seem to know what the term "heavy duty" entails.
This is but one of their products;
Battery and Field Master Silver On/Off – Cole Hersee
Or, perhaps this type;
Dual Battery Switch Selector And Alt Field – Cole Hersee
Bowdrie is offline   Reply With Quote
Old 11-11-2021, 09:31   #15
Marine Service Provider

Join Date: Oct 2012
Location: San Francisco Bay Area
Boat: Beneteau 43
Posts: 81
Re: Voltage Drop From Battery To Main Breaker Panel

Quote:
Originally Posted by Bowdrie View Post
Oh my,, #6 wire for that run is bordering on criminal.
Do you have any info about the specs of the "big bulky" switch, (that link wouldn't allow me to enter without a password).
Many so called "heavy duty" switches use brass contacts and the oxide that forms on brass has lower conductivity than the base metal.
The best switches use copper, or copper/silver, which not only have much better conductivity, but any oxide that forms will not have as much resistance.
I've always recommended the use of the heavy duty switches from Cole-Hersee,, they seem to know what the term "heavy duty" entails.
This is but one of their products;
Battery and Field Master Silver On/Off – Cole Hersee
Or, perhaps this type;
Dual Battery Switch Selector And Alt Field – Cole Hersee
this is really useful. I wasn't aware of the use of bronze (always assumed it was copper) and attendant oxidation problems.
Sorry about the link not working. Try this one. It's the most common type on Beneteaus and the like.

If I were to replace the switch with a different model/brand I would want to , of course, minimize rewiring and changes to the mounting. The first one of your links seems closer to the original. I will have to check dimensions etc. but it may be a solution

Do you know if these types of switches can be disassembled and cleaned from oxidation? I have seen contact cleaners work miracles in other, though more low-amp, situations.

Thanks!
coupdemistral is offline   Reply With Quote
Reply

Tags
battery


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 15:31.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.