Old 07-02-2019, 19:54   #1
Registered User

Join Date: Jan 2019
Posts: 78
Victron SmartSolar and BMV712 connections to shunt?

Hi all. I have a 100/50 Smart solar and a bmv712. Both are Bluetooth enabled and should talk to each other and both are from Victron. I've installed the BMV712 battery monitor successfully and it works fantastic. I'm about to install the 100/50 Smart solar controller but I have a question about wiring it to the BMV712 shunt or not.

I would think it makes sense to just do it, but I want to install the Smart solar controller about 2 meters from the shunt, but only about 500mm from the positive of the battery connection. I'm going to use 6AWG wiring as it's my understanding that this is the max you can fit into the Victron controllers.

Do I, or do I not need to connect the solar controller to the shunt? They are both Bluetooth enabled and I assume they talk to each other as this is advertised, therefore would the battery monitor know what the Smart solar is doing without the Smart solar being connected to the shunt? Ideally I would like to connected my solar controller directly to my battery negative and positive as then my wire runs would be no more than 500mm each to the battery.

If the above is not ok and communication won't work or won't be accurate between the 2 devices, do i need to get an even bigger cable (although im not sure how it would connect to the solar controller as ASH is the biggest it can take...) from the solar controller stretching 2 meters to the shunt?
If I do need to do this, then I may be forced to relocate the smart solar controller into the guest cabin instead of the storage cabin. Not ideal and would only decrease my cable run to the batteries from the solar controller to about 1 meter.

The problem arises as there is one house battery either side of the engine in my monohull. 2x260ah house batteries.

Am I over thinking this? Thanks in advance!
Scrimma is offline   Reply With Quote
Old 07-02-2019, 22:16   #2
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,634
Re: Victron SmartSolar and BMV712 connections to shunt?

of course it needs to go after the shunt. other wise the 712 will not work.

why is the shunt 2m from the battery? move the shunt beside battery. then solar will be close to shunt and pos battery.
smac999 is offline   Reply With Quote
Old 08-02-2019, 00:16   #3
Registered User

Join Date: Jan 2019
Posts: 78
Re: Victron SmartSolar and BMV712 connections to shunt?

Quote:
Originally Posted by smac999 View Post
of course it needs to go after the shunt. other wise the 712 will not work.

why is the shunt 2m from the battery? move the shunt beside battery. then solar will be close to shunt and pos battery.
Hi, thanks for the info. I have one battery on either side of my engine. One in each aft cabin. The cabin that's being used as storage is the one i want to put all that kind of thing into. The shunt is right next to the OTHER battery on the other side of the engine approx 600mm away (but approx 1700mm cable run away).
That's why I would love to have my MPPT on the STBD side, but have the negative run 1700mm-2000mm away to the shunt next to the batter on the other side. Will it be an issue do you think? Or should i just wire everything to the PORT sleeping cabine where the shunt is and deal with a flashing light and an ugly blue box in the bedroom? I'm not terrible opposed to that...it's the admiral that has other ideas!
Let me know your thoughts.
Thanks!
Scrimma is offline   Reply With Quote
Old 08-02-2019, 02:00   #4
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,398
Images: 22
Re: Victron SmartSolar and BMV712 connections to shunt?

We have the battery charger in the stern cabin but that has constant red and yellow lights. I think the yellow and green flashing lights would annoy me at night. Since you are using blue tooth to connect to the victron, can it live in a locker and still connect? worth a try.

Pete
Pete7 is offline   Reply With Quote
Old 08-02-2019, 02:41   #5
Registered User

Join Date: Jan 2019
Posts: 78
Re: Victron SmartSolar and BMV712 connections to shunt?

Quote:
Originally Posted by Pete7 View Post
We have the battery charger in the stern cabin but that has constant red and yellow lights. I think the yellow and green flashing lights would annoy me at night. Since you are using blue tooth to connect to the victron, can it live in a locker and still connect? worth a try.

Pete
That's what I'm hoping, but I'm reluctant to try it and it not work as it's quite the mission to set it up one way or the other. I'm hoping someone can tell me first. Haha. Also, I have a theory. If I situate the mppt next to the inverter and therefore connect to the inverter battery and shunt wires at the back of the inverter...would that cause any issues? The inverter wires are much bigger (2AWG) and can handle many many amps. I just don't know if it will effect the battery monitors readings if it passes through the inverter terminals on it's way to the battery and shunt, or if it will be less efficient even?! Thoughts?
Scrimma is offline   Reply With Quote
Old 08-02-2019, 03:49   #6
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Victron SmartSolar and BMV712 connections to shunt?

Every negative wire on the vessel, including your MPPT, and even a start or windalss bank, if they can be paralleld in to house, MUST be on the "load side" of the shunt.

The only negative lead, on the battery side of the shunt, should be the house battery. Any negative wire that sneaks past the shunt can not be measured. Ideally you shunt should be as close to the bank being measured as is possible so that anyone who comes along later knows not to connect anything directly to hosue bank negative..

Bluetooth can't correct or account for wiring mistakes....
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 08-02-2019, 04:36   #7
Registered User

Join Date: Jan 2019
Posts: 78
Re: Victron SmartSolar and BMV712 connections to shunt?

Quote:
Originally Posted by Maine Sail View Post
Every negative wire on the vessel, including your MPPT, and even a start or windalss bank, if they can be paralleld in to house, MUST be on the "load side" of the shunt.

The only negative lead, on the battery side of the shunt, should be the house battery. Any negative wire that sneaks past the shunt can not be measured. Ideally you shunt should be as close to the bank being measured as is possible so that anyone who comes along later knows not to connect anything directly to hosue bank negative..

Bluetooth can't correct or account for wiring mistakes....
Hi! Thanks for the info. I feel like I understand the whole shunt idea and how everything needs to be on the load side and have conceded the fact that I need to connect the mppt to the shunt. My question now is if it's ok to connect to the inverter battery terminals and piggy back on those as my battery and shunt connection as the inverter cables are well oversized and it would save another cable run. I'm pretty sure it's fine. Just wondering if anyone had done It on here or can give me a definitive answer on that particular query. Any thoughts on that? I've heard of it done before, just never heard results back from anyone.
Scrimma is offline   Reply With Quote
Old 08-02-2019, 04:54   #8
Registered User
 
Suijin's Avatar

Join Date: Feb 2013
Location: Bumping around the Caribbean
Boat: Valiant 40
Posts: 4,625
Re: Victron SmartSolar and BMV712 connections to shunt?

I wired my MPPTs directly to the bank, bypassing the shunt. I knew that the BMV would not accurately show amps in from the controller but I get that from the MPPT interface. I really only use my BMV to monitor voltage and amps out anyway.
__________________
"Having a yacht is reason for being more cheerful than most." -Kurt Vonnegut
Suijin is offline   Reply With Quote
Old 08-02-2019, 05:08   #9
Registered User

Join Date: Jan 2019
Posts: 78
Re: Victron SmartSolar and BMV712 connections to shunt?

Quote:
Originally Posted by Suijin View Post
I wired my MPPTs directly to the bank, bypassing the shunt. I knew that the BMV would not accurately show amps in from the controller but I get that from the MPPT interface. I really only use my BMV to monitor voltage and amps out anyway.
Yeah, that's what I was trying with doing too. I just want to bake my cake and eat it too. Haha. It may come to this though and like you said, monitoring the mppt through Bluetooth can tell the story. The only question I have about that though, is doesn't the bmv have the ability to tell the mppt (through the Bluetooth communication to each other (both are Victron Bluetooth enabled)) SOC and all that jazz to effectively control the controller to maximize efficiency of the whole battery charging orocess?
Scrimma is offline   Reply With Quote
Old 08-02-2019, 05:49   #10
Registered User
 
Suijin's Avatar

Join Date: Feb 2013
Location: Bumping around the Caribbean
Boat: Valiant 40
Posts: 4,625
Re: Victron SmartSolar and BMV712 connections to shunt?

I have an older BMV with no Bluetooth. And I’m not sure the value of them communicating other than having everything in one interface, if that’s even possible.

I did what I did because it reduced the wire run by about 4’.

I suppose one benefit of having the controller before the shunt would be the BMV showing net power in but I generally don’t care about that given my user behavior.
__________________
"Having a yacht is reason for being more cheerful than most." -Kurt Vonnegut
Suijin is offline   Reply With Quote
Old 08-02-2019, 20:39   #11
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Victron SmartSolar and BMV712 connections to shunt?

Quote:
Originally Posted by Suijin View Post
I wired my MPPTs directly to the bank, bypassing the shunt. I knew that the BMV would not accurately show amps in from the controller but I get that from the MPPT interface. I really only use my BMV to monitor voltage and amps out anyway.
And the BMV will certainly not tell you the SOC of your battery bank wired that way either.
mitiempo is offline   Reply With Quote
Old 09-02-2019, 03:07   #12
Registered User

Join Date: May 2015
Location: Dubai
Boat: 450S
Posts: 188
Re: Victron SmartSolar and BMV712 connections to shunt?

I have both the 712 and smart solar and didnt know they communicated with each other? Not sure why you'd want that. The blue tooth is for remote monitoring via the app afaik.
Pascals Wager is offline   Reply With Quote
Old 09-02-2019, 03:42   #13
Registered User
 
Suijin's Avatar

Join Date: Feb 2013
Location: Bumping around the Caribbean
Boat: Valiant 40
Posts: 4,625
Re: Victron SmartSolar and BMV712 connections to shunt?

Quote:
Originally Posted by mitiempo View Post
And the BMV will certainly not tell you the SOC of your battery bank wired that way either.


I go by voltage. The BMV does a poor job of measuring SOC unless you stay on top of recalibrating it. Voltage never lies.
__________________
"Having a yacht is reason for being more cheerful than most." -Kurt Vonnegut
Suijin is offline   Reply With Quote
Old 09-02-2019, 03:56   #14
DK2
Registered User

Join Date: Dec 2018
Boat: Lagoon 440
Posts: 25
Re: Victron SmartSolar and BMV712 connections to shunt?

The BMV712 and the MPPT dont ‘talk’ to each other by Bluetooth. What would they say anyway? They talk individually to your VictronConnect monitoring app.
DK2 is offline   Reply With Quote
Old 09-02-2019, 04:00   #15
Registered User

Join Date: Jan 2019
Posts: 78
Re: Victron SmartSolar and BMV712 connections to shunt?

I read it somewhere that the battery monitor can control the solar charging or something to that effect. Don't quote me on that, but I read it in a couple places a few weeks ago. I'm with you though. Doesn't seem necessary.
Scrimma is offline   Reply With Quote
Reply

Tags
solar

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aternative Shunt for Victron Bat Mon 712? jbinbi Electrical: Batteries, Generators & Solar 11 09-05-2018 15:06
Strange shunt connections F51 Electrical: Batteries, Generators & Solar 1 28-06-2015 10:23
Terminals for Victron BMV-702 shunt svlamorocha Electrical: Batteries, Generators & Solar 6 23-02-2015 05:42
Solar Power and Battery Monitor Shunt Questions montenido Electrical: Batteries, Generators & Solar 31 13-12-2013 09:32
Victron 1000A Shunt quartones Electrical: Batteries, Generators & Solar 7 08-02-2012 08:31

Advertise Here


All times are GMT -7. The time now is 02:08.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.