Registered User

Join Date: May 2006
Posts: 629
Victron Multiplus in Parallel

This is really only interesting if you have one multi or multiplus already and then a few years later, decide to buy another...........
Victron units cannot be paralleled unless they are identical in hardware and also in software release, even though there is some leeway with the software release.
When paralleled, some flexibility and redundancy is lost and if any unit fails you could lose your shore or generator power as the AC is passing through the unit.

But there is a bit of a workaround that worked for me.....
I ended up using the multi as input into the multiplus... Both with their own remote panels so amps can be regulated... and a bypass switch possibility for the multiplus when on shore power.

This gave me the flexibility to use both chargers at the same time or individually...To be able to have up to (2x2.5kw) 5kw through the inverters if needed, a max of (2x70a) 140 charging amps and to be able to bypass the multiplus shore power management if on a stable shore power circuit.
This also gives a redundancy backup in case one of the units stops working.

This setup enabled me to use 2 inverters that are not the same with many of the benefits of the paralleled system with more redundancy and flexibility.
__________________

Fuss is offline   Reply With Quote
Old 07-02-2013, 05:20   #2
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 908
Re: Victron multiplus in parallel

I am very familiar with both the Multi and the Multi Plus and using them in parallel.

Quote:
I ended up using the multi as input into the multiplus... Both with their own remote panels so amps can be regulated...
This lost me. Perhaps a one-line sketch would help.
__________________

__________________
Charlie Johnson
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 08-02-2013, 03:15   #3
Registered User

Join Date: May 2006
Posts: 629
Re: Victron multiplus in parallel

This works well if the installation basis for AC source is a 3 way selection of either shore power, generator or inverter.

The output from the switch goes into the AC input for the new multiplus.
So this means that shore power, generator and inverter have their AC amps supplemented by the new multiplus. Which is a great feature of the multiplus.

So, in the case of the original multi inverter (or any sine wave inverter) .... The AC output from the multi goes into the input on the multiplus (as the multiplus does not care what the input is, shore power, generator or inverter). The multiplus then supplements the amps if necessary.

The 2 remote panels enable control of the DC charging rates into the batteries as now you have 140a available instead of 70.

The other thing I would recommend is to have a bypass switch so the AC input can bypass the multiplus. This gives 2 advantages...
1- the AC relay in the multiplus has the possibility to be rested when on a strong shore power connection.
2- if the multiplus ever gets a techical problem then you will still have shore power/generator power. Without this bypass then your shore power/generator power will only be available if your multiplus is both on and functioning properly.
Fuss is offline   Reply With Quote
Old 08-02-2013, 03:24   #4
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Cowes (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 25,151
Re: Victron multiplus in parallel

I think it is an excellent idea!

A weak point of the Multiplus is that, with all your AC running through it, you are really stuffed when (not if) it fails -- you lose all AC power on top of your charging and inverting capability

This happened to me. Mine was repaired under warranty, but I spent a total of three or four whole days (two of them two people) getting the unit out and shipping it, then putting it back in and installing it, due to awkward mounting position inside my engine space.

I don't think that it is really acceptable for such an expensive and such a mission-critical piece of hardware to be so failure-prone. I'm wondering if Mastervolt is more reliable? It's lighter, that's for sure.

The AC bypass switch is a good idea. I also have a backup battery charger on board now.
Dockhead is offline   Reply With Quote
Old 08-02-2013, 03:26   #5
Nearly an old salt
 
goboatingnow's Avatar

Cruisers Forum Supporter

Join Date: Jun 2009
Posts: 13,360
Images: 3
Re: Victron multiplus in parallel

Quote:
I don't think that it is really acceptable for such an expensive and such a mission-critical piece of hardware to be so failure-prone. I'm wondering if Mastervolt is more reliable? It's lighter, that's for sure.
I used to sell Mastervolt, its about the same, in both these makes , you get unexplained premature failures that are difficult to accept, given the enormous price premiums.


Dave
__________________
Check out my new blog on smart boat technology, networking and gadgets for the connected sailor! - http://smartboats.tumblr.com
goboatingnow is offline   Reply With Quote
Old 08-02-2013, 03:32   #6
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Cowes (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 25,151
Re: Victron multiplus in parallel

Quote:
Originally Posted by Fuss View Post
This works well if the installation basis for AC source is a 3 way selection of either shore power, generator or inverter.

The output from the switch goes into the AC input for the new multiplus.
So this means that shore power, generator and inverter have their AC amps supplemented by the new multiplus. Which is a great feature of the multiplus.

So, in the case of the original multi inverter (or any sine wave inverter) .... The AC output from the multi goes into the input on the multiplus (as the multiplus does not care what the input is, shore power, generator or inverter). The multiplus then supplements the amps if necessary.

The 2 remote panels enable control of the DC charging rates into the batteries as now you have 140a available instead of 70.

The other thing I would recommend is to have a bypass switch so the AC input can bypass the multiplus. This gives 2 advantages...
1- the AC relay in the multiplus has the possibility to be rested when on a strong shore power connection.
2- if the multiplus ever gets a techical problem then you will still have shore power/generator power. Without this bypass then your shore power/generator power will only be available if your multiplus is both on and functioning properly.
You can also just pull both AC wires out of the Victron and connect them to each other with screw terminal blocks. That's what I did when mine failed. Saves some space on the instrument panel.

Reason 1 is good if you have the version of the Multiplus with a 16 amp transfer switch. I bought the 50 amp version since my genset produces more than 16 amps @ 240 volts.
Dockhead is offline   Reply With Quote
Old 26-03-2013, 15:35   #7
Registered User

Join Date: Mar 2013
Posts: 1
I have a multiplus 1600 that I have yet to wire into my battery bank. I have an offer of a 1200 multi. Will I be able to use the1200 with the multiplus wired into the same battery bank. The only thing I can think I might need them both for is to drive the washing machine to just get it turning which requires a bit of a surge. I imagine for the majority of the time I will only be using one of them.

This set up its in a remote building with no mains supply. I was thinking of getting a small generator to boost the multiplus if required but the multi would be cheaper and give me an inverter backup should one fail.
JonathanB is offline   Reply With Quote
Old 22-05-2013, 20:17   #8
Marine Service Provider
 
Emmalina's Avatar

Join Date: Jan 2012
Location: Thailand
Boat: Herreshoff Caribbean 50
Posts: 625
Re: Victron multiplus in parallel

I recently put a phoenix 2kw on my boat and a large solar array hoping to eliminate the need to start my gen-set. Is it feasible to get another 2kw phoenix and put it in parallel to get the start current I need? Its a half hp motor on the compressor I think and only draws 4a when running but the inverter just bombs when I try starting the compressor !! Thanks
__________________
Steve .. It was the last one that did this !
Emmalina is offline   Reply With Quote
Old 23-05-2013, 19:15   #9
Registered User
 
ebaugh's Avatar

Join Date: Dec 2011
Location: On the boat
Boat: DeFever 44
Posts: 292
Quote:
Originally Posted by Emmalina View Post
I recently put a phoenix 2kw on my boat and a large solar array hoping to eliminate the need to start my gen-set. Is it feasible to get another 2kw phoenix and put it in parallel to get the start current I need? Its a half hp motor on the compressor I think and only draws 4a when running but the inverter just bombs when I try starting the compressor !! Thanks
Probably assuming you have 220-240 VAC compressor. If 110-120VAC it should start on 2000 watt inverter.

Unless you have a huge battery bank, it won't run long though.
ebaugh is offline   Reply With Quote
Old 05-10-2017, 13:51   #10
rom
Registered User

Join Date: Mar 2016
Boat: Lagoon 440
Posts: 629
Re: Victron Multiplus in Parallel

I am considering the purchase of a second multiplus 12/3000/120 230VAC and found this old thread. I would like to know if others have setup theirs the way Fuss proposes. Any feedback ? I wonder which of the two solutions puts less stress on those equipments.
__________________

rom is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar Panels - Series or Parallel ? noelex 77 Electrical: Batteries, Generators & Solar 180 13-08-2016 01:48
Isolation Transformer: Victron vs Mastervolt vs Charles wilsodf Electrical: Batteries, Generators & Solar 87 07-07-2016 12:33
I've Had It With Victron Equipment Dockhead Electrical: Batteries, Generators & Solar 99 17-11-2014 13:04
Is My Victron Multi Dying ? Dreaming Yachtsman Electrical: Batteries, Generators & Solar 125 18-01-2013 08:06
Victron Multi 3000 US Not Working Anymore roetter Electrical: Batteries, Generators & Solar 5 01-11-2012 06:12



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 11:25.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.