I thought that the short lengths of wire that attached to appliances were
Inconsequential because they were too short to increase resistance? That could just be something that I read somewhere.
__________________

sully75 is offline   Reply With Quote
Old 13-05-2016, 15:19   #32
Registered User
 
CarinaPDX's Avatar

Join Date: Jan 2010
Location: Portland, Oregon, USA
Boat: 31' Cape George Cutter
Posts: 1,755
Re: USB jacks phantom loads

Sully75- there are two issues relating to wire size, voltage drop and ampacity. A short piece of small wire will probably not result in significant voltage drop. However, it will have a lower current limit (ampacity) and will require a smaller circuit breaker or fuse to protect against fire. To explain, the smaller wire will heat up from the relatively large current that could easily be conducted through the larger supply cable, and if this heat exceeds the temperature rating of the wire's insulation it can melt the insulation or even start a fire. Thus the circuit breaker must be sized to protect at the maximum current allowed through the smaller wire, no matter how short. This will limit the current that can be allowed on the entire branch, unless the device has its own fuse or breaker.

Greg
__________________

CarinaPDX is offline   Reply With Quote
Reply

Tags
loa

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
opencpn linux mint 13 and GPS USB SKYTRAQ GM 65 Skytraq - chipset Venus 6 USB - NMEA archimede OpenCPN 2 18-02-2013 03:04
Garmin USB-USB Cable + Windows7? HamishB OpenCPN 4 24-05-2011 02:13
How to Handle USB GPS and NMEA to USB Inputs sailracer OpenCPN 16 16-04-2011 07:22
Isolate Shore Power Loads from Inverter Loads RoyHB Electrical: Batteries, Generators & Solar 4 19-04-2010 05:02
Powered USB Hub vs Powered USB Cables Bryan Kemler Monohull Sailboats 2 20-01-2010 15:24



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 22:21.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.