State-of-charge automatic "full" synchronisation

Over the previous winter I installed a new house battery bank on this ship (St. Lawrence II - Brigantine Inc.). The work was triggered by the existing batteries being toast and a switch to DC refrigeration. The bank comprises 4 x Trojan L16H-AC with a total rated capacity of 12V @ 740 AH (20 hour rate). I also installed a Victron BMV-702 battery/temperature monitor and a Victron CCGX for data logging. The battery bank is typically charged on a daily basis by an on-board generator or shore power; both feed into a Xantrex TrueCharge 40.

The attached graphs show a couple of examples of the actual charging profile, specifically the relationship between voltage, current, and the calculated state-of-charge. I find it very interesting to view what actually happened during the charge cycles.

One can clearly see where the BMV makes the decision to perform its auto-synchronisation with the battery bank, and assume that the bank is at 100% capacity. Given the subsequent voltage rise, and continued high current, I question whether the bank is really even close to 100% at this point. The BMV default configuration is:

Quote:
the BMV resets to ‘fully charged’ when the following ‘charged parameters’ are met: the voltage exceeds 13.2V and simultaneously the (tail-) charge current is less than 4.0% of the total battery capacity
My friends at Victron came back with this suggestion:


Quote:
Just adjust the “Tail Current” setting in the BMV set-up menu to a lower value.It is meant to be adjustable for situations like this.
I would tend to agree that makes sense, as the "100% charge" is somewhere on the downward current slope while the voltage is at 14.4V.

Does this make sense to other folk, or am I missing something? What would be a good tail current setting to use? I can adjust the tail current in a range of 0.5 – 10% of the battery capacity in 0.1% steps.


Thanks,

Allan.
Attached Thumbnails
Click image for larger version

Name:	SLII - Combined #1.png
Views:	193
Size:	64.6 KB
ID:	156934   Click image for larger version

Name:	SLII - Combined #1 - Zoom.png
Views:	190
Size:	57.8 KB
ID:	156935  

Click image for larger version

Name:	SLII - Combined #2.png
Views:	172
Size:	36.3 KB
ID:	156936  
ayates is offline   Reply With Quote
Old 30-09-2017, 08:05   #2
rom
Registered User

Join Date: Mar 2016
Boat: Lagoon 440
Posts: 736
Re: State-of-charge automatic "full" synchronisation

I have set mine to 1%. Most of the time I can tell the batteries have already reached 100% SOC while the SOC reading on the BMV is say close to 99%.

Problem is if you don't get back to 100% regularly the reading slowly goes away from what's real. On rare occasions it happens that my SOC reading get as low 95% while the batteries have actually reached 100%.

I can not see how this equipment can stay totally in line with the truth, so we have to accept the slight difference.
rom is offline   Reply With Quote
Old 30-09-2017, 10:25   #3
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,706
Re: State-of-charge automatic "full" synchronisation

Been down this road years ago:

Reset the fault values.

*********************************************
For everyone installing a battery monitor: The "Gotcha Algorithm" thread, a "MUST READ"

Link-series Charging Algorithms -- The "Gotcha" Factor!

DEFAULTS are factory settings that are made to be modified to suit your setup.

Also read this one:

Programming a Battery Monitor (by Maine Sail)

Keeping Your Battery Monitor More Accurate Photo Gallery by Compass Marine How To at pbase.com
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 30-09-2017, 11:33   #4
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: State-of-charge automatic "full" synchronisation

Your first issue is charging a 740ah bank with a 40a charger. You should be 100A+

It looks like only 20a is going to the batteries. So you probably have a 20a load on the boat. Effectively leaving you with a 20a charger to charge a 740ah bank.

In 3rd pic I wonder when the current drops more (10a at 13.5v at 80% soc) Is it actually the bank taking less. Or more loads put on, and the charger is still maxed?

The meter thinks your batteries are taking small amps at a float voltage. When in reality the batteries want more. But your charger is maxed out and can't even hit its bulk voltage. In the 3rd graph. The one I looked at. The meter reset before the charger even hit absorption. While the meter probaby thinks you're in float.

Get a bigger charger.
smac999 is offline   Reply With Quote
Old 30-09-2017, 12:14   #5
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: State-of-charge automatic "full" synchronisation

Keep an eye on the performance of these and if one starts to show low specific gravity and the bank won't stay charged you could have a bad battery. I say this because I think that some of the L16 ac Trojans are defective and if you can catch it in time you might get Trojan to honor the warranty. I had one go bad after two years with no abuse and there is a recent thread here where someone else had the same problem.
Thumbs Up is offline   Reply With Quote
Old 01-10-2017, 13:55   #6
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: State-of-charge automatic "full" synchronisation

Quote:
Originally Posted by smac999 View Post
Your first issue is charging a 740ah bank with a 40a charger. You should be 100A+

It looks like only 20a is going to the batteries. So you probably have a 20a load on the boat. Effectively leaving you with a 20a charger to charge a 740ah bank.

In 3rd pic I wonder when the current drops more (10a at 13.5v at 80% soc) Is it actually the bank taking less. Or more loads put on, and the charger is still maxed?

The meter thinks your batteries are taking small amps at a float voltage. When in reality the batteries want more. But your charger is maxed out and can't even hit its bulk voltage. In the 3rd graph. The one I looked at. The meter reset before the charger even hit absorption. While the meter probaby thinks you're in float.

Get a bigger charger.
Agree 100%.

Get a larger charger. Your 40 amp charger is only capable of just over 5% of the bank size - and this is without any loads on the boat. That is basically a float voltage for a battery bank of that size.
mitiempo is offline   Reply With Quote
Old 01-10-2017, 14:49   #7
Registered User
 
DeepFrz's Avatar

Cruisers Forum Supporter

Join Date: Mar 2006
Location: Winnipeg
Boat: None at this time
Posts: 8,462
Re: State-of-charge automatic "full" synchronisation

Isn't your bank really 870 Ah? Maybe you have set the Ah rating to low.
DeepFrz is offline   Reply With Quote
Old 01-10-2017, 17:49   #8
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: State-of-charge automatic "full" synchronisation

Quote:
Originally Posted by DeepFrz View Post
Isn't your bank really 870 Ah? Maybe you have set the Ah rating to low.
Good catch. Trojan's spec sheet does state 435 AH @ the 20 hour rate.

http://www.trojanbattery.com/pdf/dat...ata_Sheets.pdf
mitiempo is offline   Reply With Quote
Old 01-10-2017, 20:23   #9
Registered User

Join Date: Dec 2016
Posts: 255
Re: State-of-charge automatic "full" synchronisation

Quote:
Originally Posted by Stu Jackson View Post
For everyone installing a battery monitor: The "Gotcha Algorithm" thread, a "MUST READ"

Link-series Charging Algorithms -- The "Gotcha" Factor!

DEFAULTS are factory settings that are made to be modified to suit your setup.

Also read this one:

Programming a Battery Monitor (by Maine Sail)

Keeping Your Battery Monitor More Accurate Photo Gallery by Compass Marine How To at pbase.com
Brilliant information! I have devoured many article's on Maine Sail's site, I am surprised I missed that one.


Thanks,

Allan.
ayates is offline   Reply With Quote
Old 01-10-2017, 20:31   #10
Registered User

Join Date: Dec 2016
Posts: 255
Re: State-of-charge automatic "full" synchronisation

Quote:
Originally Posted by mitiempo View Post
Quote:
Originally Posted by DeepFrz View Post
Isn't your bank really 870 Ah? Maybe you have set the Ah rating to low.
Good catch.
Very good point. I had stuck in my mind the capacity of the L16RE-B which was my original plan. I'll double check the BMV configuration.


Thanks,

Allan.
ayates is offline   Reply With Quote
Old 01-10-2017, 20:38   #11
Registered User

Join Date: Dec 2016
Posts: 255
Re: State-of-charge automatic "full" synchronisation

Quote:
Originally Posted by mitiempo View Post
Quote:
Originally Posted by smac999 View Post
Your first issue is charging a 740ah bank with a 40a charger. You should be 100A+
Agree 100%.

Get a larger charger. Your 40 amp charger is only capable of just over 5% of the bank size - and this is without any loads on the boat. That is basically a float voltage for a battery bank of that size.
Totally agree. Unfortunately I couldn't fit in that upgrade last year. My thoughts are to upgrade to 2 x Victron Skylla 12/60 running in parallel. That will give me 120A of charging capacity, along with redundancy in the event one unit fails.

That would cover generator and shore power driven charging. Ideally a high output alternator would also be used, so as to get similar capacity for engine driven charging.


Thanks,

Allan.
ayates is offline   Reply With Quote
Old 10-10-2017, 09:15   #12
Registered User

Join Date: Dec 2016
Posts: 255
Re: State-of-charge automatic "full" synchronisation

Quote:
Originally Posted by Stu Jackson View Post
DEFAULTS are factory settings that are made to be modified to suit your setup.
Greating reading.

My Trojan rep came back with (for the L16-HC):
  • Peukert factor is 1.79
  • Charge efficiency is 85%

Thanks,

Allan.
ayates is offline   Reply With Quote
Old 30-12-2017, 08:13   #13
Registered User

Join Date: Dec 2016
Posts: 255
Re: State-of-charge automatic "full" synchronisation

FYI... Found an nice instance of a complete charge cycle in the logged data. See attached graph. The Xantrex charger is putting out its full output of 40A (29A+12A; the dips lower than 12A are from the fridge which runs on 120V when available). Not actually sure what triggered the switch from absorption to float, as neither the time nor the current line up with the published Xantrex algorithm.

I will definitely be updating the battery monitor configuration parameters.


Allan
Attached Thumbnails
Click image for larger version

Name:	Untitled.png
Views:	105
Size:	63.4 KB
ID:	161257  
ayates is offline   Reply With Quote
Old 30-12-2017, 19:52   #14
Registered User

Join Date: Oct 2015
Posts: 2,007
Re: State-of-charge automatic "full" synchronisation

I am going back to repeat what has already been said: The battery charger is woefully inadequate for both your battery bank and your rate of power use.

Let's do just a little arithmetic:

***You frequently pull power of of the batteries at a pretty constant 20 amp rate. If you do that for 12 hours, then you have withdrawn 240 amp-hrs.

***If you then start to charge with your 40 amp charger, you only have 20 amps available to feed to the batteries, the rest gets used by your loads.

***If your charging was 100% efficient (and it is nowhere close) you would need 12 hours of charging to replace the 240 amp-hrs you pulled out in the previous 12 hours!

Basically, you need to run this charger at least 18 hours a day just to keep up. Look at the voltage your batteries are dropping to: less than 12V! Ouch... they are nearly dead already.
billknny is offline   Reply With Quote
Old 30-12-2017, 20:02   #15
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: State-of-charge automatic "full" synchronisation

As above. At under 12v. With a 10-20a load. You are under 50% soc. either the meter is way off. Or you have already toasted the new bank. 12.8v full battery. 12v 50% battery.

Get a bigger charger.
smac999 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
When is "Full" really "Full" SV Sedna Construction, Maintenance & Refit 8 27-06-2017 08:15
Automatic Charge Relays - Good or Bad mlibkind Electrical: Batteries, Generators & Solar 54 10-10-2014 14:10
Blue sea automatic charge relay cutlass Product or Service Reviews & Evaluations 16 17-04-2012 07:26
Washington State purchase with out-of-state residence cyclepro Dollars & Cents 7 06-06-2011 08:55
State by State Nonresdient Regs Stoney Rules of the Road, Regulations & Red Tape 2 10-06-2008 08:52

Advertise Here


All times are GMT -7. The time now is 11:59.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.