Re: Starter Cable Size Question

Quote:
Originally Posted by Terra Nova View Post
...the TOTAL distance from battery + all the way back to battery -. That is what determines cable size.
Quote:
Originally Posted by Frankly View Post
I don't understand the thinking that the starter positive conductor should be the same size as the return (negative)...
See above.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 18-11-2016, 10:33   #32
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Starter Cable Size Question

Quote:
Originally Posted by Frankly View Post
I don't understand the thinking that the starter positive conductor should be the same size as the return (negative). ..............
I already answered this once but here it is again:

The current through the entire circuit is the same. For example, if the starter draws 200 amps then 200 amps must flow through the positive conductor, the motor and the negative conductor.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 18-11-2016, 10:49   #33
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Starter Cable Size Question

Quote:
Originally Posted by S/V Alchemy View Post
Correct. There is some logic in keeping the cable sizes identical and of equal length, as well..........
Again, the same current flows through the entire circuit. There is absolutely no electrical difference between having a one foot positive conductor and a ten foot negative conductor compared to a ten foot positive conductor and a one foot negative conductor. It's eleven feet of cable either way.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 18-11-2016, 11:33   #34
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Starter Cable Size Question

Quote:
Originally Posted by a64pilot View Post
OK a boat that is used in salt water and not the vacuum of space the wire may increase resistance as the wire ages, .......

Again, nope. The connections may oxidize and increase resistance if not properly done but the resistance of the wire will not change.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 18-11-2016, 11:55   #35
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Starter Cable Size Question

I guess you have never stripped wire back and found it black well away from the ends?
OK, so the terminal ends increase in resistance, how does that not increase the resistance of the circuit?

I stand by that your circuit is the best it will ever be the day its new, and only one thing can happen, and that is it will increase in resistance.
What do you think often cause fires in old wiring systems ?

Why do people rewire old boats if the wire lasts forever?
a64pilot is offline   Reply With Quote
Old 18-11-2016, 12:52   #36
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Starter Cable Size Question

I understand Ohm's law, Kirchoff's Current Law, and Kirchoff's Voltage Law (MSEE). There is no prostitution of those laws that would indicate that both the positive and negative starter motor cables should be the same size.

They should be able to safely carry the current, and the voltage delivered to the motor terminals should be at an acceptable level. That the positive and negative cables be the same size is pure BS (that was the question by the OP).
Frankly is offline   Reply With Quote
Old 18-11-2016, 13:30   #37
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Starter Cable Size Question

Quote:
Originally Posted by Frankly View Post
I understand Ohm's law, Kirchoff's Current Law, and Kirchoff's Voltage Law (MSEE). There is no prostitution of those laws that would indicate that both the positive and negative starter motor cables should be the same size.

They should be able to safely carry the current, and the voltage delivered to the motor terminals should be at an acceptable level. That the positive and negative cables be the same size is pure BS (that was the question by the OP).
Here is the OP's post:
Quote:
What size negative cable should I be running from my starter back to my house bank if the run from the house bank requires 2/0 on the positive side? Can it be 1/0?
So the cables don't have to be the same size but if the positive cable needs to be 2/0, the negative cable cannot be smaller.

There is never any harm (electrically) in using a larger cable or wire than needed but there could be a problem with physical size.

Quote:
There is no prostitution of those laws that would indicate that both the positive and negative starter motor cables should be the same size.
I'm not sure what you are trying to say or who you are trying to impress with that statement, but in this series circuit, there is no advantage to using different sized cables so a normal person would use the same size cable throughout the circuit.

Would you make up an anchor rode with half 1/2" chain and half 1/4" chain?
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 18-11-2016, 20:06   #38
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Starter Cable Size Question

Quote:
Originally Posted by Marqus View Post
To illustrate using Maine Sail's conservative 370A starter current (if your starter current is higher, the voltage drop will increase):

6 feet of 1/0 copper cable will have a voltage drop of 0.21volt
6 feet of 2/0 copper cable will have a voltage drop of 0.17volt

So, hypothetically, if you have one 6ft link of 2/0 followed by a 6ft link of 1/0, the total voltage drop (due to wire length) to the starter will be around 0.4volt.

If both links were 2/0 copper, the total drop will reduce to around 0.34volt.
The wire gauge calculator I use is here: AWG by wire length/amps calculator

Assuming a 12' total run with battery voltage at 12.7 and 370 amp load it gives 3/0 wire size for a 3% drop. 3% of 12.7 is .38 volts.
mitiempo is offline   Reply With Quote
Old 19-11-2016, 03:30   #39
Registered User

Join Date: Feb 2011
Location: South-East Australia coast
Boat: 40ft fibreglass sloop
Posts: 201
Re: Starter Cable Size Question

Quote:
Originally Posted by Frankly View Post
I understand Ohm's law, Kirchoff's Current Law, and Kirchoff's Voltage Law (MSEE). There is no prostitution of those laws that would indicate that both the positive and negative starter motor cables should be the same size.

They should be able to safely carry the current, and the voltage delivered to the motor terminals should be at an acceptable level. That the positive and negative cables be the same size is pure BS (that was the question by the OP).
Strongly articulated perhaps, but you just can't fault that statement.

If you know the overall voltage drop you can or want to tolerate, feel free to use different cable lengths and/or cables of different thicknesses.

Just sum your voltage drops - calculation can be quite easy as Mitiempo well illustrates.
Marqus is offline   Reply With Quote
Old 21-11-2016, 10:07   #40
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Starter Cable Size Question

Quote:
Originally Posted by mitiempo View Post
The wire gauge calculator I use is here: AWG by wire length/amps calculator

Assuming a 12' total run with battery voltage at 12.7 and 370 amp load it gives 3/0 wire size for a 3% drop. 3% of 12.7 is .38 volts.
10% voltage drop tables are acceptable for starter circuits.

Will reduce voltage to the starter slightly, but will cost much less, for negligible difference in performance.
ramblinrod is offline   Reply With Quote
Old 21-11-2016, 10:09   #41
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Starter Cable Size Question

Quote:
Originally Posted by Marqus View Post
Strongly articulated perhaps, but you just can't fault that statement.

If you know the overall voltage drop you can or want to tolerate, feel free to use different cable lengths and/or cables of different thicknesses.

Just sum your voltage drops - calculation can be quite easy as Mitiempo well illustrates.
With the exception that one cannot exceed the maximum current carrying capacity of any wire.

But, for all intents and purposes, it is generally easiest to just calculate the round trip cable run distance and pick the size off the table for the max current expected.
ramblinrod is offline   Reply With Quote
Old 21-11-2016, 21:18   #42
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Starter Cable Size Question

Quote:
Originally Posted by ramblinrod View Post
10% voltage drop tables are acceptable for starter circuits.

Will reduce voltage to the starter slightly, but will cost much less, for negligible difference in performance.
Stick with the 3% table of values.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 21-11-2016, 22:21   #43
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Starter Cable Size Question

Quote:
Originally Posted by Terra Nova View Post
Stick with the 3% table of values.
I agree. I believe ABYC requires 3% drop for motors. Even if they don't it is the better choice as the losses from connections will add to the drop.
mitiempo is offline   Reply With Quote
Old 21-11-2016, 22:51   #44
Registered User

Join Date: May 2010
Posts: 673
Re: Starter Cable Size Question

Quote:
Originally Posted by a64pilot View Post
I guess you have never stripped wire back and found it black well away from the ends?
OK, so the terminal ends increase in resistance, how does that not increase the resistance of the circuit?

I stand by that your circuit is the best it will ever be the day its new, and only one thing can happen, and that is it will increase in resistance.
What do you think often cause fires in old wiring systems ?

Why do people rewire old boats if the wire lasts forever?
I think the poster was saying that the flow of 'electricity' is in the core of the copper wire and not on the surface. oxidation on the surface of a wire will make little difference to the resistance of the wire. Corrosion that eats into the wire, reducing its diameter significantly and destroying the conductivity of the circuit does have an impact. That corrosion is most likely to occur where there is a 'mechanical' connection and where there is moisture and air. A poorly crimped terminal connector will readily corrode on a boat.
dlymn is offline   Reply With Quote
Old 21-11-2016, 23:17   #45
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Starter Cable Size Question

Quote:
Originally Posted by dlymn View Post
I think the poster was saying that the flow of 'electricity' is in the core of the copper wire and not on the surface. oxidation on the surface of a wire will make little difference to the resistance of the wire. Corrosion that eats into the wire, reducing its diameter significantly and destroying the conductivity of the circuit does have an impact. That corrosion is most likely to occur where there is a 'mechanical' connection and where there is moisture and air. A poorly crimped terminal connector will readily corrode on a boat.
Skin effect only pertains to AC.
ramblinrod is offline   Reply With Quote
Reply

Tags
size


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
More than one Cable in a Cable Clam? sully75 Electrical: Batteries, Generators & Solar 19 17-11-2022 04:42
Coupler for Middle of Outboard Starter Cable HJ51 Monohull Sailboats 7 18-11-2015 03:21
Recessed Starter Switch or Stop-Cable Panel petedd Construction, Maintenance & Refit 4 13-05-2010 17:04
For Sale: 50' Telephone/Cable TV Combo Cable off-the-grid Classifieds Archive 5 27-10-2009 12:00

Advertise Here


All times are GMT -7. The time now is 19:12.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.