Quote:
Panel to controller 5.97x 2 = 11.94A
Controller to batteries 435 x 2 / 13 = 66.9A

If we work out the voltage drop with various wires:

Panel to controller
8AWG = 0.90 v
6AWG = 0.57 v
4AWG = 0.36 v

Controller to batteries
4AWG = 0.40 v
3AWG = 0.32 v
2AWG = 0.25 v

Well I would disagree , but essentially your doing what I said

Firstly if there is a short in the panel assy. The panel is theoretically capable of 6.43x2 , 13 amps, and I would size the mppt input wires as such

from the mppt to the battery, 435 x2 = 870 watts and in bulk you would anything down to 11.5V, so 75 amps which is the rated max output of the controller.

Hence i would size for those currents would be AWG #3 for about 2% drop round trip.

and #10 for the panel to mppt for a 1% drop

it would be unwise to size to less then max panel current IMHO
__________________

__________________
Check out my new blog on smart boat technology, networking and gadgets for the connected sailor! - http://smartboats.tumblr.com
goboatingnow is offline   Reply With Quote
Old 08-02-2015, 14:24   #17
Registered User
 
boatrips's Avatar

Join Date: May 2010
Location: SEATTLE
Boat: 42 US YACHT
Posts: 24
Re: Solar panel Installation and wire sizing from the solar panels to the mppt charge

I want to thank all who have contributed to this post.

I'm now waiting for confirmation from the charge controller mfgr regarding the max voltage of the panels vs the total volts of their charger before I purchase it.

Here's a picture of the solar panel installation on the new hardtop made specifically for the panels at a cost of about US$250.00 on top of the existing cockpit cover stainless steel bows

Fair winds,
Jim
Attached Thumbnails
Click image for larger version

Name:	870 watts of solar panels.jpg
Views:	158
Size:	43.3 KB
ID:	96847  
__________________

__________________
boatrips is offline   Reply With Quote
Old 08-02-2015, 19:25   #18
Registered User

Join Date: Feb 2015
Posts: 17
Re: Solar panel Installation and wire sizing from the solar panels to the mppt charge

use MC4 extension wire from your connectors comes in lengths 10 ft to 100 ft to your controller from controller to batteries use #4. solarsam
__________________

__________________
solarsam is offline   Reply With Quote
Reply

Tags
charger, installation, mppt, panels, solar, solar panels

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar panels with MPPT controller and 2 battery banks kevins Electrical: Batteries, Generators & Solar 11 17-09-2017 11:33
For Sale: 2 x 100 w 24 v Solar Panels and 30 Amp MPPT Controller Huggi21 Classifieds Archive 3 28-08-2013 16:32
solar wire sizing sailorboy1 Electrical: Batteries, Generators & Solar 5 27-03-2013 01:47
Wire Sizing for Installing Solar Panels / Wind Generator Eddie Electrical: Batteries, Generators & Solar 17 30-03-2010 20:06



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 06:05.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.