We had 390w of solar with a 2412(?) Blue Sky controller - we started with 260w and when we added a 3 panel I contacted Blue Sky and they said I could go over but absolutely do not add another panel. As we were sailing in the southern part of the Caribbean we exceed the controllers capacity many many days. We added a 4th panel but also upgraded to 3024 Blue Sky controller -
we have 2 more 6v Trojans than you do.
__________________
just our thoughts and opinions
chuck and svsoulmates
Somewhere in the Eastern Caribbean
chuckr is offline   Reply With Quote
Old 20-12-2016, 06:09   #17
Registered User

Join Date: Jul 2016
Location: Anguilla
Boat: CheoyLee Offshore 33
Posts: 644
Images: 1
Send a message via Skype™ to masonc
Re: Solar panel controller question.

Quote:
Originally Posted by chuckr View Post
We had 390w of solar with a 2412(?) Blue Sky controller - we started with 260w and when we added a 3 panel I contacted Blue Sky and they said I could go over but absolutely do not add another panel. As we were sailing in the southern part of the Caribbean we exceed the controllers capacity many many days. We added a 4th panel but also upgraded to 3024 Blue Sky controller -
we have 2 more 6v Trojans than you do.
Exceeding the input capacity of the solar charge controller is no big deal as long as you don't exceed the voltage rating. The current generating capacity is a resource, it will take current it wants.
Voltage is a different animal, you must not exceed the rating. If you do and there is a problem, you will lose any warranty, especially if the unit has logging and the manufacturer can check.
You are unlikely to exceed the voltage rating in the Caribbean as the voltage drops with temperature. The problem comes with very cold weather when the voltage output of the panels climbs and exceeds the rating.
masonc is offline   Reply With Quote
Old 20-12-2016, 06:14   #18
Registered User

Join Date: Jul 2016
Location: Anguilla
Boat: CheoyLee Offshore 33
Posts: 644
Images: 1
Send a message via Skype™ to masonc
Re: Solar panel controller question.

Quote:
Originally Posted by carlo de leo View Post
It's strongly recommended to install a bipolar DC circuit breaker just before the controller. So my suggestion: install this DC breaker rated at 20A, then install your new solar panel and see what happens. The controller itself may deal with an eventual extra load, you would be wasting some power if your panels exceed 20A, but you'd be safe.
This is a really bad idea. The breaker is not a current limiter, it is a safety device. The breaker for a charge controller should be rated at 125% of rated output to allow for constant current. You should not plan for the breaker to trip. If the breaker trips, it can damage your charge controller. For a 20A ma output charge controller, you need a 25A breaker, unless the breakers are constant current rated (some Midnight solar breakers).
If your solar panel rated output is more than the charge controller rating, it will not harm the controller, as long s the voltage remains within rating. You might lose some output at peak production but that's not a big deal.
masonc is offline   Reply With Quote
Reply

Tags
solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combining a diversion controller with a MPPT Solar controller GILow Electrical: Batteries, Generators & Solar 6 19-01-2016 04:45
VHF interference from BZ MPPT solar panel controller sailrj Marine Electronics 8 14-11-2012 07:45
For Sale: Uni- Solar 68w panel w/ controller sailandfish Classifieds Archive 0 20-06-2012 15:55
Solar Panel Charge Controller lannen Electrical: Batteries, Generators & Solar 15 12-06-2009 02:34

Advertise Here


All times are GMT -7. The time now is 14:29.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.