Solar Panel Circuit Breaker Wiring

I've got some new panels I'm installing, each is around ~7.6 amps (Kyocera 135's). It says the short circuit current is 8.37 amps and the "series fuse rating" is 15 amps.

Now these aren't like batteries in that they can only produce a maximum (I'm guessing) of 8.37 amps in full sunshine with no wiring other than enough to short circuit.

So I guess my questions are:

a) What's the "series fuse amp" rating of 15 amps for?

b) I want to get a breaker like this one, for each panel (they're running in parallel to a bus before going into a charge controller):

10 Amp Din Rail Mount Breaker - Circuit Breakers @ AltE

Is a 10 amp circuit breaker going to cause excess resistance on something that regularly can be hovering in the 7.5 amp range, and if so based on the numbers here what size breaker should I use?

There's a second bus after the charge controller (combining the outputs of all the charge controllers) that also runs through a 50a breaker on its way to the battery terminals.

I've done some pretty cheap solar installs before where I've just run the wires directly from the panel to the battery posts, but I'm trying to do this the right way.

Where I'm at so far:

Rebel Heart - Sailing, cruising, liveaboard blog and website - Eric's Blog - finally mounted the solar*panels
rebel heart is offline   Reply With Quote
Old 10-10-2010, 13:26   #2
Long Range Cruiser
 
MarkJ's Avatar

Join Date: Dec 2007
Location: Australian living on "Sea Life" currently in England.
Boat: Beneteau 393 "Sea Life"
Posts: 12,822
Images: 25
I just a 20 amp auto fuse holder & fuse. Just goes in line.
$4





Mark
PS I wonder what grief I will cop for this? I DON'T use Paper charts either!
Attached Thumbnails
Click image for larger version

Name:	20a-fuse.jpg
Views:	607
Size:	13.9 KB
ID:	19993  
__________________
Notes on a Circumnavigation.
OurLifeAtSea.com

Somalia Pirates and our Convoy
MarkJ is offline   Reply With Quote
Old 10-10-2010, 13:35   #3
Registered User
 
sabray's Avatar

Join Date: Aug 2008
Location: Wash DC
Boat: PETERSON 44
Posts: 3,165
Don't feal bad mark. I died last week because I use something like this. Yours should work just fine. Wow you did something right. Now about that anchor...
Attached Images
 
sabray is offline   Reply With Quote
Old 10-10-2010, 13:39   #4
Registered User
 
rebel heart's Avatar

Join Date: Oct 2005
Posts: 6,185
Images: 3
I'm fine with something like that too, but I'm just trying to get the numbers right. If the panel wiring will be destroyed at 12 amps, I don't want to put a 15 amp circuit breaker in, you know?

I can't even find anything online about damage coming from a short circuiting solar panel. I guess it's only going to be able to generate a fixed amount (in this case 8 and some change amps), so as long as everything internal to the panel can handle 8 amps, there's no risk of "damaging" the panel with a short circuit.

?
rebel heart is offline   Reply With Quote
Old 10-10-2010, 13:50   #5
Registered User
 
sabray's Avatar

Join Date: Aug 2008
Location: Wash DC
Boat: PETERSON 44
Posts: 3,165
You might check what the manufacturer says. but if max rated out put is 8 amps the 10 amp breaker would be fine. I like marks solution if the wire leads are in line with the wire sizes for the run. If the 10 amp blows you up to a 12 amp. I dont think that will happen if you wire everything with good awg.
sabray is offline   Reply With Quote
Old 10-10-2010, 14:22   #6
Marine Service Provider
 
witzgall's Avatar

Join Date: Oct 2006
Location: Eastern Shore, MD
Boat: Camper Nicholson 44 Ketch
Posts: 2,060
Reb,

Why not wire them in series to a controller that can handle the 24v, and then fuse them on one wire right before the controller, and then 8 inches from the batteries? Simpler, more efficient.

Chris
witzgall is offline   Reply With Quote
Old 10-10-2010, 14:28   #7
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,159
Quote:
Originally Posted by rebel heart View Post
I'm fine with something like that too, but I'm just trying to get the numbers right. If the panel wiring will be destroyed at 12 amps, I don't want to put a 15 amp circuit breaker in, you know?

I can't even find anything online about damage coming from a short circuiting solar panel. I guess it's only going to be able to generate a fixed amount (in this case 8 and some change amps), so as long as everything internal to the panel can handle 8 amps, there's no risk of "damaging" the panel with a short circuit.

?
I have 3 solar panels, 2 32 watt flexible (one on each ama) and a 120 watt on the arch. They all feed a BlueSky MPPT controller which then goes through a 20 amp marine circuit breaker to feed the batteries.

The other day I noticed no charging at all. The starboard flexible panel had been damaged and had water intrusion.

After disconnecting it, everything worked normally. The panel measured zero volts output and depending on where I pressed on it, measured between a few hundred and zero ohms. Water and a little rust could be seen under the clear plastic cover.

Unisolar no longer makes them, but for direct replacement reasons I found one reasonably priced on Ebay.
__________________
The question is not, "Who will let me?"
The question is,"Who is going to stop me?"


Ayn Rand
senormechanico is offline   Reply With Quote
Old 10-10-2010, 14:31   #8
Registered User
 
ShipShape's Avatar

Join Date: May 2010
Posts: 267
Use the auto-style fuse like Mark says. "Series fuse rating" means the 15 amp fuse is in series, aka in-line. I installed my two Kyocera 135's a year ago, here is a pic of how I did it:

Click image for larger version

Name:	solar and <a title=wind.JPG Views: 793 Size: 78.9 KB ID: 19997" style="margin: 2px" />

I have my wind gen using the same charge controller so there are some extra things here. The two red boxes are auto-style fuse holders, the top left is for the wind gen and the bottom right for the solar panels. For the bottom bar on the bus bar, the port panel comes in on the left and the stbd panel comes in on the center. They both leave on the right, go through a 30 amp fuse, and enter the top bus bar on the top right.

The wind gen comes in from its fuse on the left of the top bus bar. Both solar and wind leave the top bus bar from the center and go to the charge controller. I also took the cover off the negative stud so you would have a complete picture - the three skinny wires are the two panels and the wind gen, and the fat wire goes to ... well, it gets complicated after this because I set things up so that I can separate the battery banks.

BTW, the wiring is hugely over-sized to keep resistance to a min. The skinny wires are 10 AWG.

So for your set-up, if you want to use two 15 amp fuses, put them in-line on each panel, then you can either cram both wires into your charge controller, or use a step-down butt connector or a post and just send one wire to the charge controller.

Another pic because it is Sunday.

Click image for larger version

Name:	bus bar.JPG
Views:	722
Size:	83.7 KB
ID:	19996
ShipShape is offline   Reply With Quote
Old 10-10-2010, 14:46   #9
Registered User

Join Date: Aug 2008
Location: St. Martin
Boat: St. Francis 43 Brisa
Posts: 333
Rebel, I think I see what you're asking... Not how to do it but why is there a series fuse rating of 15 amps and what happens if you put two fuses instead of one.....correct?

Ok serries fuse is there to protect three or more panels. With two you are fine.

heres how that wokrs

1 shorted panel.... = no amps
2 panels 1 shorts out the other sends over 8.37 amps ( the specs on your solar panel ISC ) the other panel sends the short max of 8.37 amps.. the same as the panel was designed to handle so no worries yet.
If you install a third panel now the short gets 2 x 8.37 = 16.74 amps. This exceeds the rating on the panel and needs the 15 amp breaker for protection... so with only 2 panels you don't need a series fuse.
Heres how that works....

http://www.nmsu.edu/~tdi/pdf-resources/CC125.pdf

Now for the fuses... you ned one between the controller and the batteries.... you only need 1 for every string of solar panels inline....at the end of the positive wires between the last panel and the controller. If you put two little fuses you will be able to trouble shoot the system if there is a problem, but you will get more drop than just putting one bigger breaker for both panels.

Most MPPT controllers have a fail no flow sensor and system that acts as additional protection.... for future reference.

Hope that helps mate!
sailingaway221 is offline   Reply With Quote
Old 10-10-2010, 14:57   #10
Registered User
 
cuthbert's Avatar

Join Date: Oct 2010
Boat: Catalina 350
Posts: 145
I would go with a fuse over a circuit breaker.

In a general (non marine) sense, a fuse is far more robust to short spikes and surges (in the boating application, not necessarily from the panels but elsewhere on the boat).

Again in the general sense and this also applies in marine applications the advantage of a circuit breaker is that it requires no skill or knowledge to fault find and reset. The downside of this is that it will be prone to trip on a spike that a fuse would be unaffected by and worse still a circuit breaker is far slower to trip than a fuse is to blow in a worse case scenario.

Since you are fitting it on your boat (and hence know what is where and why) put a fast blow fuse in.

To answer your questions as posted (and opinions here may vary)

a) Sufficient margin to not blow from the panel at
i) Maximum amperage from the panels and or "single fault" in the controller or wiring giving a short to ground (not a problem for the panel but the charge controller or other current source (e.g. battery) connected in the circuit
ii) Maximum amperage and the fuse being derated for temperature

b) If you want to go with the circuit breaker the unit that you posted would work in theory. But you have touched on a point that is fairly key, that amperage output given for the solar panel manufacturer is when the panel is operating on the "knee" in the voltage vs amperage graph of the panel, whatever is connected to the panel has to (ideally) present a resistance which is such that the panel is on that sweet spot. Hence the market for MPPT controllers (worth a wiki search/quick read).
cuthbert is offline   Reply With Quote
Old 10-10-2010, 16:19   #11
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
I hate inline fuses I remove all of them from my boats equipment I use suitably sized breakers instead. The last thing I need is to trying to remember where all those hidden inline fuses are.
goboatingnow is offline   Reply With Quote
Old 10-10-2010, 18:18   #12
Registered User

Join Date: Aug 2008
Location: St. Martin
Boat: St. Francis 43 Brisa
Posts: 333
I have to agree with goboating now. Fuses are old tech. At night in a dark boat, pitching and rocking at sea, it sucks to look for a fuse and replace.... its easy to throw a breaker back on.......sorry but all key systems on my boat have a breaker and no fuse.....The only fuseable advantage generally over a breaker is its cheap....
sailingaway221 is offline   Reply With Quote
Old 10-10-2010, 18:39   #13
Registered User
 
Caribsailors's Avatar

Join Date: Jun 2008
Location: Somewhere in the Caribbean
Boat: Beneteau First 38
Posts: 313
Images: 23
My Plan

Is to use a Bluesea http://bluesea.com/files/images/products/5028.jpg

and bring my solar and wind regulating devices through the fuse block to the battery, as well as feed the battery monitor.
__________________
As I sit, a swirling sea of passion gives it's poems in waves underneath me.
The whispers of the sun in my eyes, a silence within.
Rhythm of the surf, drums of the sea. Thoughts tumble and toss about the deep blue abyss inside me, where the love of you dwells.
I'm fighting currents to get back to you, listening to the flow of your liquid language as you beckon me, "Come Play"
Mariners Cove, CI. Anonymous.
Caribsailors is offline   Reply With Quote
Old 10-10-2010, 18:47   #14
Registered User

Join Date: Mar 2009
Posts: 223
To clear up a point: Fuse does not have to mean an inline fuse holder tucked away where you can’t get to it. This is bad engineering! Fuse panels put the fuse out where you can get to it and that is the professional way to install. For what it is worth, circuit breakers tend to drop more voltage across the protective device than a comparably sized fuse.

The over circuit protection protects both the wire and the device. In most low voltage dc the wire size is usually jacked up to prevent excessive voltage drop so the current handling capacity of the wire is quite high compared to the other weak links in the system. If you are using #10 wire in your runs you have a wire that will take 30 amps intermittent and 24 amps continuously, much higher than the panels current limits.

In the case of the Kyocera panel the maximum short circuit current is 8.37 amps and they want it protected at no more than 15 amps of reverse current in the panel. So how many panels do you have in parallel? If you have but two panels the maximum reverse current that could flow from an operating panel into a non operating panel is 8.37 amps, so there is no way you can hurt anything.

I still believe in fuses between the panel and controller to help protect against transients even if the potential reverse current is not an issue. Also a Schotke diode in each line to limit the current drain of a partially shaded panel. I don’t know if the panel is diode protected or not as it comes from the factory.

If you can wire the two panels in series and utilize the new type controllers, you will not only realize a higher power out but it gets easier to troubleshoot because the output is all or nothing, not so in the parallel circuit where a degraded condition is a more common occurrence.

Um Saudade
um saudade is offline   Reply With Quote
Old 10-10-2010, 19:04   #15
Registered User
 
Therapy's Avatar

Join Date: Jul 2007
Location: W Florida
Boat: Still have the 33yo Jon boat. But now a CATAMARAN. Nice little 18' Bay Cat.
Posts: 7,086
Images: 4
Rebel Heart,

I feel for you.

This stuff is complicated.
Therapy is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Earth Leak Circuit Breaker Wire Overheating...! raya Electrical: Batteries, Generators & Solar 8 27-05-2010 21:22
Fuse or Circuit Breaker ? ggray Electrical: Batteries, Generators & Solar 5 15-10-2009 15:41
Solar Panel wiring/charging options IslandHops Electrical: Batteries, Generators & Solar 5 17-02-2009 02:29
parallel a circuit breaker skyking2 Electrical: Batteries, Generators & Solar 13 03-11-2006 22:00

Advertise Here


All times are GMT -7. The time now is 07:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.