Solar directly to batteries to equalize them

My boat is always on the hook. Neither the engine or my solar panels through the regulators will generate more than 14.4V, so I cannot equalize my battery bank.

My old battery bank died to what I think was due to sulfation. At 14.4 V they only took a low (sub 10A) current, but with only 10% charge taken out, the voltage dropped to below 12V.

New battery bank purchased (Trojan &-105s), but as I never stay at the dock, I cannot equalize them to prevent sulfation.

I have 500W of solar panels. They deliver around 17-18V (I think), and it gets regulated down to lower voltages.

Idea: To equalize the batteries. For a short time connect some of the solar panels (200W maybe) directly to the battery bank. Monitor the voltage and battery temperature, and if voltage goes much above 16V or too hot, disconnect the panels.

Is this a good idea or will I likely destroy something.

I read a statement from Trojan that most batteries which prematurely died was due to undercharging and hardly ever by overcharging.
Sail IC is offline   Reply With Quote
Old 02-01-2016, 14:11   #2
Registered User
 
svmariane's Avatar

Join Date: May 2007
Location: On the hard due to wife's medical condition.
Boat: Sold, alas, because life happens.
Posts: 1,829
Re: Solar directly to batteries to equalize them

Just my 2 pence worth, but...

500 W seems enough solar to do the job so I'm suspicious of your solar regulator. Is it an MPPT type?

If not..... Maybe check into the likes of this: TS-MPPT-60
TriStar MPPT » Morningstar Corporation

I've about 350 W solar and have no problems using our TS-MPPT-60 to equalize our 600 A/H house bank.

Better results if the (free) software is utilized from a laptop (or similar).

Note: We run our boat with solar & wind power - no genset, no shore power, and not using motor except to maneuver.

{Our TS-60 allows for future solar expansion vice being limited by a TS-30.
No affiliation with the company except as happy customer. }
__________________
"Being offended is not the same thing as being right." Dave Barry.
Laughter is the salve that keeps reality from scaring.
¯\_(ツ)_/¯
svmariane is offline   Reply With Quote
Old 02-01-2016, 14:11   #3
Registered User
 
pcmm's Avatar

Join Date: May 2014
Location: Whitby, Canada
Boat: Morgan Out Island 41
Posts: 2,267
Images: 2
Re: Solar directly to batteries to equalize them

What regulator are you using? most modern MPPT controllers have the ability to run an equalization program. some can even do it on a monthly equalization cycle.
pcmm is offline   Reply With Quote
Old 02-01-2016, 14:20   #4
Registered User
 
svmariane's Avatar

Join Date: May 2007
Location: On the hard due to wife's medical condition.
Boat: Sold, alas, because life happens.
Posts: 1,829
Re: Solar directly to batteries to equalize them

Quote:
Originally Posted by Sail IC View Post

Idea: For a short time connect some of the solar panels (200W maybe) directly to the battery bank. Monitor the voltage and battery temperature, and if voltage goes much above 16V or too hot, disconnect the panels. Is this a good idea or will I likely destroy something.
Did exactly that when our old non-TriStar solar controller died enroute Tonga / New Zealand. We lived. The batteries lived another two years. Why they died is another story.....
__________________
"Being offended is not the same thing as being right." Dave Barry.
Laughter is the salve that keeps reality from scaring.
¯\_(ツ)_/¯
svmariane is offline   Reply With Quote
Old 02-01-2016, 14:21   #5
Registered User

Join Date: Apr 2012
Location: Winter Germany, Summer Med
Boat: Lagoon 380 S2
Posts: 1,923
Re: Solar directly to batteries to equalize them

Our regulators do that automatically once month. Maybe yours too?
rabbi is offline   Reply With Quote
Old 02-01-2016, 16:31   #6
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Solar directly to batteries to equalize them

Quote:
Originally Posted by rabbi View Post
Our regulators do that automatically once month. Maybe yours too?
IMHK automatic "equalization" is one of the dumbest ideas that seduce buyers of boat equipment. I have seen enough examples of equipment fried by unattended equalization at about 15.5V.

Sent from my GT-I9192 using Cruisers Sailing Forum mobile app
svlamorocha is offline   Reply With Quote
Old 02-01-2016, 16:45   #7
Registered User

Join Date: Jul 2015
Location: Orential N.C.
Boat: 1981 Morgan OI 41
Posts: 162
Re: Solar directly to batteries to equalize them

There is a discussion on here about battery orientation IIRC the plates should run side to side not front to back. if one side is allowed to stay dry too long as in when you are running heeled over on a long tack it is bad on them.

Sent from my RCT6077W22 using Tapatalk
Salty Mike is offline   Reply With Quote
Old 02-01-2016, 17:17   #8
Registered User
 
zboss's Avatar

Join Date: Sep 2011
Location: On a boat
Boat: 1987 Cabo Rico 38 #117 (sold) & 2008 Manta 42 #124
Posts: 4,174
Re: Solar directly to batteries to equalize them

I am going to be (shortly) selling 4 Genasun solar controllers that have been custom programmed by the factory specifically for charging Trojan batteries. They have a built in equalization mode... they automatically equalize every 30 days.

So far so good on our batteries. We are selling them because we are moving to carbon foam batteries and they have different charging voltages than the trojans. Let me know if you are interested.
zboss is offline   Reply With Quote
Old 03-01-2016, 00:24   #9
Registered User

Join Date: Apr 2012
Location: Winter Germany, Summer Med
Boat: Lagoon 380 S2
Posts: 1,923
Re: Solar directly to batteries to equalize them

Quote:
Originally Posted by svlamorocha View Post
IMHK automatic "equalization" is one of the dumbest ideas that seduce buyers of boat equipment. I have seen enough examples of equipment fried by unattended equalization at about 15.5V.

Sent from my GT-I9192 using Cruisers Sailing Forum mobile app
We can set the voltage for equation just like for the normal charging stages so no problem
rabbi is offline   Reply With Quote
Old 03-01-2016, 04:13   #10
Registered User

Join Date: Jun 2009
Location: BVI
Boat: Leopard 40 (new model)
Posts: 1,385
Re: Solar directly to batteries to equalize them

Quote:
Originally Posted by rabbi View Post
We can set the voltage for equation just like for the normal charging stages so no problem
The problem is that the voltage required to "equalize" most batteries ( say 15.5 volts) is more than enough to make it likely that you will fry certain devices. If the equalization is "attended" you can disconnect all loads, but that will not happen if the equalization happens once a month on a timer.

Sent from my GT-I9192 using Cruisers Sailing Forum mobile app
svlamorocha is offline   Reply With Quote
Old 03-01-2016, 04:56   #11
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Solar directly to batteries to equalize them

I've found through research and through personal experience that you don't need to equalize FLAs all that often -- maybe only once or twice a year -- provided that you frequently kick the voltage up to absorption level (14.6-14.8VDC) for a short time. This level avoids possible damage to onboard electronics and makes a measurable difference in battery capacity, electrolyte stratification and, presumably, in anti-sulfation.

My Victron is set to kick up to 14.8VDC for 30 minutes every other day before dropping back to resting voltages of 13.8VDC then 13.2VDC.

Given my druthers, I wish I could maintain 13.6-13.8VDC all the time, but my Victron automatically drops back to 13.2VDC after awhile and curiously that level is not programmable on my Multiplus.

Bill
btrayfors is offline   Reply With Quote
Old 03-01-2016, 05:21   #12
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Re: Solar directly to batteries to equalize them

Bill, are you sure about that float value?. We have a multi plus 3000 and the float value is certainly programmable on it.

Trojan recommends that batteries be equalized ONLY if the cell specific gravities are imbalanced, and to then equalize only until they rebalance. They don't think regular equalization is a good thing at all.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 03-01-2016, 05:36   #13
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Solar directly to batteries to equalize them

Hi, Mark...

Yes, I'm sure. On my Victron (Phoenix Multi Inverter/Charger 2500W/120A) the float value is also programmable. However, the so-called "storage value" is not. It's set at 13.2VDC and you can't change it. So the charger goes first to 13.8VDC (or whatever value you've programmed), then after a time of no activity it automatically drops down to 13.2VDC.

You're right about equalization (15.5VDC and above). I don't think it's required very often. And, I'd be leery about "automatic equalization", AKA uncontrolled equalization. With battery charging voltages that high, I'd wanna be right there to monitor/control what's going on.

Bill
btrayfors is offline   Reply With Quote
Old 03-01-2016, 06:08   #14
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Re: Solar directly to batteries to equalize them

I see that now. Ours is never operated such that we ever meet the conditions for switching to "storage" mode.

The "re-absorption" mode is programmable. You could set it to bump up every day for a few minutes, and that would probably have the same effect as sitting at 13.8V.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 03-01-2016, 06:55   #15
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Solar directly to batteries to equalize them

Mark,

Yes, that's what I've done since Feb 2012. The Victron is set to kick up to absorption voltage 14.8VDC every other day for 30 minutes.

Look at the yellow to green bars. That's the six-month period after I started using the every-other-day re-absorption voltage thing. A clear increase in measured capacity is seen in all batteries.

However, these batteries were already seven years old, and about 13 months later they all began to lose capacity (blue bars).

Battery #3 had clearly reached the end of it's lifetime. I removed it from the bank and went with the remaining house batteries for a few months until I replaced them all.

Click image for larger version

Name:	SixTrojans130424.jpg
Views:	275
Size:	101.2 KB
ID:	116066

Bill
btrayfors is offline   Reply With Quote
Reply

Tags
solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flexible Solar Panel mounted directly on Sunbrella banjoship Electrical: Batteries, Generators & Solar 95 30-05-2014 19:39
venting batteries during equalize sailorboy1 Electrical: Batteries, Generators & Solar 3 19-04-2014 19:49
Dead Batteries -- Blast Them or Coddle Them? Dockhead Electrical: Batteries, Generators & Solar 36 02-06-2012 17:07
I'm Afraid to Equalize Palarran Electrical: Batteries, Generators & Solar 24 13-09-2010 14:48
Use Solar Panel Output Directly? ciclon1942 Electrical: Batteries, Generators & Solar 7 23-05-2009 05:40

Advertise Here


All times are GMT -7. The time now is 12:41.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.