Re: Small battery bank running an inverter

Quote:
Originally Posted by GILow View Post
I also gave voltage ranges that were consistent with TXG's experience of running a practically identical system. So I think it is pretty clear this is an internal battery resistance/chemistry issue and all that remains is to speak to the manufacture's technical representative and get his opinion on whether treating the batteries in this way will damage them.
With the length of time that you are drawing the high Amps from a "dual purpose" battery, I wouldn't be too concerned about damaging them.

After all, it's only a couple of Ah each time and I doubt that they would experience much heating.

But as you've discovered, it will cause a fairly large temporary voltage drop. If you've got instruments running at the same time, don't be surprised if they decide to reset themselves
StuM is offline   Reply With Quote
Old 10-12-2016, 00:03   #62
Registered User
 
TeddyDiver's Avatar

Join Date: Aug 2010
Location: Arctic Ocean
Boat: Under construction 35' ketch (and +3 smaller)
Posts: 2,761
Images: 2
Re: Small battery bank running an inverter

Quote:
Originally Posted by GILow View Post
.
I also stated that I ASSUMED I had a bad contact somewhere but I was able to rule it out using that very simple test.


I am starting to worry if anyone is actually reading what I posted.
I feel your pain :-( Way too common problem.

BR Teddy
TeddyDiver is offline   Reply With Quote
Old 10-12-2016, 01:51   #63
txg
Registered User

Join Date: Oct 2014
Location: Berlin - Germany
Boat: Dufour 35
Posts: 199
Re: Small battery bank running an inverter

I'm still waiting for any proof or experiences from all the guys who told us that this load is too high for a 220Ah bank?

Regarding battery heating: At least with our AGM bank that's not a problem even with longer times at high loads. 60kg of mostly lead is just such a big thermal mass that it takes a very long time to heat it up. I could only once feel that our batteries heated up a little bit, and this was only about 5-10 deg. C about ambient temp. This happened when i did some tests to our alternator which meant discharging from full to 50% at 120A continuously, and then directly recharging up to 80% beginning at 90A.
txg is offline   Reply With Quote
Old 10-12-2016, 04:36   #64
Registered User
 
Boatwright's Avatar

Join Date: Jul 2016
Location: Traverse City, Michigan
Boat: Hinterhoeller Niagara 35
Posts: 289
Re: Small battery bank running an inverter

The reason your inverter is tripping is the huge DC current required to operate ANY appliance that produces heat - coffee maker, hair dryer, toaster, etc. - is pulling the system voltage down to the trip voltage.

Inverters are a great convenience for operating smaller intermittent loads such as an electric drill, or a small continuous load such as a TV or stereo.

In practice no matter what the inverter rating, intermittent loads should be no greater than 500 watts, continuous loads should be limited to 100 watts. Any more than this will overload the DC system, overheat wires, shorten battery life, blow alternator diodes, etc..

We all love our coffee. There are good alternatives. We use an old-fashioned whistling tea kettle and a Melitta brand insulated drip coffee pot.

http://www.amazon.com/Melitta-Coffee...tta+coffee+pot

The coffee is great -- the only disadvantage is one of us has to get out of bed to fire up the kettle.
Boatwright is offline   Reply With Quote
Old 10-12-2016, 05:05   #65
Registered User
 
Boatwright's Avatar

Join Date: Jul 2016
Location: Traverse City, Michigan
Boat: Hinterhoeller Niagara 35
Posts: 289
Re: Small battery bank running an inverter

I should add:

The only practical way to have a 120 volt system on a yacht that will run an electric kitchen is to have a genset that produces multiple KW of AC power. If you are under sail and smaller than 40', forget the electric coffee pot.

There just isn't a DYI battery powered solution to power heat producing electric appliances for the average cruiser.
Boatwright is offline   Reply With Quote
Old 10-12-2016, 05:20   #66
txg
Registered User

Join Date: Oct 2014
Location: Berlin - Germany
Boat: Dufour 35
Posts: 199
Re: Small battery bank running an inverter

Quote:
Originally Posted by Boatwright View Post
I should add:

The only practical way to have a 120 volt system on a yacht that will run an electric kitchen is to have a genset that produces multiple KW of AC power. If you are under sail and smaller than 40', forget the electric coffee pot.

There just isn't a DYI battery powered solution to power heat producing electric appliances for the average cruiser.
This is just plain wrong. Obviously you haven't read anything in this thread except the first post. We are doing exactly what you describe as impossible and it works fine.
txg is offline   Reply With Quote
Old 10-12-2016, 05:46   #67
Registered User
 
StuM's Avatar

Cruisers Forum Supporter

Join Date: Nov 2013
Location: Port Moresby,Papua New Guinea
Boat: FP Belize Maestro 43 and OPBs
Posts: 12,891
Re: Small battery bank running an inverter

Quote:
Originally Posted by Boatwright View Post
In practice no matter what the inverter rating, intermittent loads should be no greater than 500 watts, continuous loads should be limited to 100 watts. Any more than this will overload the DC system, overheat wires, shorten battery life, blow alternator diodes, etc..
Guess I wasted my money putting a 2.5kW inverter in then

And if more than 500 Watts will overload a DC system, I'd better remove half of my solar panels and de-rate my alternators.

Darn it, I didn't realise that my battery system couldn't be drawn down at greater than C/25 or that I need to draw continuous loads below C/100.

Thanks for letting me know.
StuM is offline   Reply With Quote
Old 10-12-2016, 06:27   #68
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Small battery bank running an inverter

If it's only one minute, you should be fine. I due to my advanced age think Mr Coffee or similar device when someone says electric coffee maker.
I too am a a Coffee addict, something that 20 yrs in the Army did to me.
Please understand though that your 12VDC deep cycle batteries are really in fact starting batteries, not deep cycle, but no real matter as you have them.
I still think your undercharging them, long thread so I don't remember if they are AGM or not, but if not a hydrometer is inexpensive and an easy test that will tell if they are being undercharged or not.
a64pilot is offline   Reply With Quote
Old 10-12-2016, 06:49   #69
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Small battery bank running an inverter

Quote:
Originally Posted by Boatwright View Post
............ In practice no matter what the inverter rating, intermittent loads should be no greater than 500 watts, continuous loads should be limited to 100 watts. Any more than this will overload the DC system, overheat wires, shorten battery life, blow alternator diodes, etc......................
Well, that's just wrong!



You can run virtually any load with an inverter, provided the inverter and the battery system is adequate. Think of solar powered homes.

I have a 2000 watt inverter and a bank of four group 31 AGM batteries (roughly 400 AH). I routinely run a microwave oven that draws about 1400 watts and a single cup electric coffee maker (not at the same time). I get some voltage sag but it's temporary and it's no different than running the windlass or bow thruster.

The OP might solve his problem with true deep cycle batteries or he could just add one or two more batteries in parallel.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 10-12-2016, 06:56   #70
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Small battery bank running an inverter

Quote:
Originally Posted by txg View Post
I'm still waiting for any proof or experiences from all the guys who told us that this load is too high for a 220Ah bank? .
The fact that the inverter is sounding the low voltage alarm and the voltage at the battery terminals is dropping significantly is pretty much proof.

The voltage is dropping because there is too much internal resistance in the batteries.

Perhaps these are not true "deep cycle" batteries. Perhaps a different brand of batteries would work better. Certainly adding one or two more batteries in parallel would help.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 10-12-2016, 08:18   #71
Registered User
 
TeddyDiver's Avatar

Join Date: Aug 2010
Location: Arctic Ocean
Boat: Under construction 35' ketch (and +3 smaller)
Posts: 2,761
Images: 2
Re: Small battery bank running an inverter

Quote:
Originally Posted by rwidman View Post
The fact that the inverter is sounding the low voltage alarm and the voltage at the battery terminals is dropping significantly is pretty much proof.

The voltage is dropping because there is too much internal resistance in the batteries.

Perhaps these are not true "deep cycle" batteries.
Then it'd be starting batteries, they have smaller resistance.
TeddyDiver is offline   Reply With Quote
Old 10-12-2016, 08:35   #72
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,174
Re: Small battery bank running an inverter

Quote:
Originally Posted by Boatwright View Post
The reason your inverter is tripping is the huge DC current required to operate ANY appliance that produces heat - coffee maker, hair dryer, toaster, etc. - is pulling the system voltage down to the trip voltage.

Inverters are a great convenience for operating smaller intermittent loads such as an electric drill, or a small continuous load such as a TV or stereo.

In practice no matter what the inverter rating, intermittent loads should be no greater than 500 watts, continuous loads should be limited to 100 watts. Any more than this will overload the DC system, overheat wires, shorten battery life, blow alternator diodes, etc..

We all love our coffee. There are good alternatives. We use an old-fashioned whistling tea kettle and a Melitta brand insulated drip coffee pot.

http://www.amazon.com/Melitta-Coffee...tta+coffee+pot

The coffee is great -- the only disadvantage is one of us has to get out of bed to fire up the kettle.
Just one question where did you get this information ?
I'm sure that the companies that make and sell bigger inverters (like just about all inverters. ). Would really like to know this information. I have no problems running either of my 750 watt inverters to power up to 700 watts draw. If any higher draw is needed I run both inverters in parallel. ( and yes it can be done and is actually quite easy to do)
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 10-12-2016, 09:47   #73
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Small battery bank running an inverter

Quote:
Originally Posted by Boatwright View Post
The reason your inverter is tripping is the huge DC current required to operate ANY appliance that produces heat - coffee maker, hair dryer, toaster, etc. - is pulling the system voltage down to the trip voltage.

Inverters are a great convenience for operating smaller intermittent loads such as an electric drill, or a small continuous load such as a TV or stereo.

In practice no matter what the inverter rating, intermittent loads should be no greater than 500 watts, continuous loads should be limited to 100 watts. Any more than this will overload the DC system, overheat wires, shorten battery life, blow alternator diodes, etc..
Totally depends on the battery bank size and the inverter size. As Newhaul posted you can parallel inverters for higher output. Some large boats parallel 4000+ watt inverters with a large battery bank. The most popular size of inverter is 2000 watts and is a good match for a battery bank of 450 AH or so, very common on cruising boats.
mitiempo is offline   Reply With Quote
Old 10-12-2016, 09:58   #74
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Small battery bank running an inverter

Quote:
Originally Posted by GILow View Post
So I think it is pretty clear this is an internal battery resistance/chemistry issue and all that remains is to speak to the manufacture's technical representative and get his opinion on whether treating the batteries in this way will damage them.


Seriously guys, I love the help, and I hate to sound ungrateful for the advice, but the whole "You are an idiot who does not know how to wire an inverter" thing is getting a bit thin.


As it is, I am probably just an idiot who did not know what to expect from batteries under this sort of load.


Matt
Nothing to do with "...an idiot who does not know how to wire an inverter." The best answers come after all the information is known though - wire gauge, distance, as well as battery size for example.

One thing we don't know is the brand of inverter. That and the low voltage cutout voltage - which should be stated in the manual - would help.

As far as inverters not being able to handle high loads when wired from smaller battery banks it is quite common. I had a customer a few years ago with 2 group 31 batteries and a 2000 watt inverter. As soon as he turned his coffee maker on the inverter shut down. Changed his battery bank to 4 golf carts for a total AH of 484 (double previous size) and no further issues.
mitiempo is offline   Reply With Quote
Old 10-12-2016, 10:20   #75
Registered User

Join Date: Jun 2010
Location: Easton, MD
Boat: 15' Catboat, Bristol 35.5
Posts: 3,510
Re: Small battery bank running an inverter

Quote:
Originally Posted by StuM View Post
Guess I wasted my money putting a 2.5kW inverter in then

And if more than 500 Watts will overload a DC system, I'd better remove half of my solar panels and de-rate my alternators.

Darn it, I didn't realise that my battery system couldn't be drawn down at greater than C/25 or that I need to draw continuous loads below C/100.

Thanks for letting me know.
kmacdonald is offline   Reply With Quote
Reply

Tags
battery, inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Single bank Battery Monitor with Automatic Charging Relay to starting bank as a load? Zach Marine Electronics 5 23-04-2016 15:26
Running a 240vac Motor off 48vdc Battery Bank Dame.n.Jess Electrical: Batteries, Generators & Solar 9 04-06-2010 05:55

Advertise Here


All times are GMT -7. The time now is 16:40.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.