Old 22-07-2018, 13:47   #76
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Sizing Main Battery Cables

Quote:
Originally Posted by rgleason View Post
Maine Sail,

Can a person using a DC Clamp/Volt meter capture these values?

For a Yanmar 3YM30 starter (64amp, 400cca) (While searching I found a forum email from you with these values, after your inquiry to Yanmar). Should I use:
  1. 200 amp fuse + awg 1 (existing wires) 12 feet full length.
  2. 225 amp fuse + awg 1/0 12 feet
  3. 250 amp fuse + awg 2/0 12 feet

For any battery than can be called on to start a motor I recommend a 250A fuse as a minimum. A 200A can work for many, many starts, I've experimented with one on my own boat, but it also may eventually nuisance trip if long cranking is required such as a fuel bleeding event. When possible I like to see a fuse rated at about 55% - 70% of in-rush. At this ratio I have never seen a nuisance trip.



Anyone can measure the in-rush or peak low/high voltage with the correct instruments such as a Fluke 376 (in-rush) or a Fluke 289 (peak voltages) a Midtronics analyzer (in-rush, average cranking load etc.), an oscilloscope and some other good quality tools...



It's not going to be very accurate with most cheap instruments, even cheap clamp meters that claim in-rush. A typical 1kW starter can draw about 370A for in-rush and about 100A continuous with ZERO LOAD and decent voltage... Add cranking an engine to it and the load is higher because we have moved from no load to loaded..


The YM starter has a "no load" rating of 90A at 11 volts. No load means spinning in free air.


It has a "loaded" spec (cranking an actual motor) of 250A at 8.4V. If you have a big bank and terminal voltage does not drop that much that 250A loaded rating can easily go higher..


Yanmar also specs a maximum allowable wiring voltage drop to the starter of 0.2V @ 100A (odd way to rate it). For 1AWG wire this would mean a max total circuit length, using 1AWG, of 8'..
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 22-07-2018, 14:14   #77
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,523
Images: 2
Re: Sizing Main Battery Cables

Rod, Thank you! That resolves one of my problems. It appears that AWG #1 is too low just from calculation (with the right 90a starter amperage and 370a inrush) without a load, and that from your experience it is best to use at least a 250a fuses.


Your video Voltage Transients in A Marine Battery System
is hugely helpful to just understand the issues with large loads.
If I understood correctly the starter being used is for a Westerbeke 30hp motor, so it is a comparable starter to a 3YM30 engine.


I had not known about voltage transients and the necessary wiring considerations to protect instruments.
rgleason is offline   Reply With Quote
Old 22-07-2018, 15:00   #78
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Sizing Main Battery Cables

Quote:
Originally Posted by rgleason View Post
Rod, Thank you! That resolves one of my problems. It appears that AWG #1 is too low just from calculation (with the right 90a starter amperage and 370a inrush) without a load, and that from your experience it is best to use at least a 250a fuses.


Your video Voltage Transients in A Marine Battery System
is hugely helpful to just understand the issues with large loads.
If I understood correctly the starter being used is for a Westerbeke 30hp motor, so it is a comparable starter to a 3YM30 engine.


I had not known about voltage transients and the necessary wiring considerations to protect instruments.

90A is not the starter amperage it is the NO LOAD amperage rating. Meaning if you ran it on a bench not connected to a motor at 11V it would spin and pull 90A just top spin the motor into free air.. When you connect it to your engine, and the voltage of the battery sags to 8.4V, it should not pull more than 370A unless your starter terminal voltage is higher. In that case it could easily exceed 400A for short duration's.
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 22-07-2018, 17:02   #79
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Sizing Main Battery Cables

Quote:
Originally Posted by rgleason View Post
Changes:
  1. Moved the 24hr Battery Fuse Panel AWG 6 to direct to Battery Positive + Post (less than 7" away)
  2. Moved the SW#1 AWG 1/0 to be direct to Battery 225a (eliminating two connections).
  3. Moved the Alternator AWG 1/0 to be direct to Battery 225a (eliminating two connections).
Is the Emergency Battery switch still meaningful?
There should not be more than one positive and one negative outgoing wire on a battery or battery bank. Use a bus.

Your emergency switch is not necessary and as with any connection it contributes to voltage drop.
mitiempo is offline   Reply With Quote
Old 22-07-2018, 17:11   #80
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,523
Images: 2
Re: Sizing Main Battery Cables

Using Blue Seas Circuit Wizard
12v, 370 amp, 12', 3% voltage drop, variable load, engine room, terminated on fuse.
I get 4/0 wire and wire capacity of 378 amps.
This seems way too big. What am I doing wrong?

#1 works ok, engine starts right away.


Can I use an old ZapStop (I currently have on my Alternator) between DC Panle +/- to suppress transients? Would it work? Isn't ZapStop also a diode?... I saw the "...Sterling APD is not just limited to clamping transients from an alternator load dump it can also be placed across a DC electronics circuit or across the DC Panels B+ & B- feeders for added insurance," https://marinehowto.com/voltage-tran...rical-systems/
rgleason is offline   Reply With Quote
Old 22-07-2018, 17:36   #81
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,523
Images: 2
Re: Sizing Main Battery Cables

Quote:
Originally Posted by mitiempo View Post
There should not be more than one positive and one negative outgoing wire on a battery or battery bank. Use a bus.
Your emergency switch is not necessary and as with any connection it contributes to voltage drop.

Thank you for your thought and response.


Yes I understand that standard. Here is a wiring diagram with the main pos bus. This is a small boat with little room for wiring. See Existing

I am going use Trojan T105 batteries with EUT connections, with an MRBF fuse holder Blue Seas dual fuse holder 2151 or single 5191 turned on its side attached to the post to save space. It is kind of hard to see the drawing.

The 24hr Battery Fuse Panel is attached direct to the positive post with a #6 wire within 7", just as the many small + sensor and power leads would have been attached, with exactly the same number of connections, but consolidated in a single fuse panel.

The cables from the 1both2 switch and the alternator would be attached on the load side of the main battery fuse (not battery side) to reduce connections.

As far as the rest of the main + busway (Charger and ACR Combiner) I think those would be handled by a MRBF 5196.

John had suggested the emergency switch as good to have so I had shown it in earlier diagrams.
rgleason is offline   Reply With Quote
Old 22-07-2018, 18:47   #82
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Sizing Main Battery Cables

The emergency switch is good to have so you can take power completely away from the starter in case of a serious fault, like the starter not disengaging.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 22-07-2018, 20:16   #83
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,523
Images: 2
Re: Sizing Main Battery Cables

Thanks Terra Nova for the explanation for the switch.

From the Yanmar Manual pages 183, 184 through 188
Page 184, 12'=3.65m so 50mm(sq) is needed.
Page 185, 6'=1.8m so 20mm(sq) is needed.
Page 185, 12'=3.65m (if full length is intended), so 40mm(sq)

Looks to me like AWG 1 = 42mm(sq) will work for comply with pg185,
However complying with pg 184 AWG 1/0=53mm(sq) is needed.

From American Wire Gauges AWG sizes and cross sections
1 42mm(sq)
1/0 53mm(sq)
2/0 67mm(sq)
3/0 85mm(sq)
4/0 107mm(sq)

When I look at page 186 Chart 12.3.2
1. I know the engine starts at under 1000 rpm, say 800 rpm
2. On the torque curve 800 rpm is about 200amps
3. On the speed curve 1500rmp is about 200amps
4. On the volt curve 8.4v is about 250amps where the specs say current is 250 and rmp is 1000.

Why wouldn't a 200 amp or 250 amp fuse work?
AWG 1/0, would be 200amp or 225amp fuse
AWG 2/0, would be 250 amp fuse
rgleason is offline   Reply With Quote
Old 22-07-2018, 22:18   #84
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Sizing Main Battery Cables

Quote:
Originally Posted by Terra Nova View Post
The emergency switch is good to have so you can take power completely away from the starter in case of a serious fault, like the starter not disengaging.
You can do that just as well with the main switch.

My preference is a simple on/off for start and another for house.
mitiempo is offline   Reply With Quote
Old 22-07-2018, 22:25   #85
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,874
Re: Sizing Main Battery Cables

Quote:
Originally Posted by rgleason View Post
Thank you for your thought and response.


This is a small boat with little room for wiring.
Lots of room for a 6" bus. It is common sense to keep battery wiring to a minimum and simplifies battery maintenance as well.

First thing I look at on a battery bank is the number of wires on the bank. More than 2 load carrying wires is sloppy.

Positive post to bus. MRBF fuses on the bus for individual loads. This way a blown fuse does not kill everything unless it is the main fuse.
mitiempo is offline   Reply With Quote
Old 23-07-2018, 07:38   #86
Registered User

Join Date: Feb 2015
Location: Segundo, Colorado
Boat: 1975 Ta Chaio CT41
Posts: 71
Re: Sizing Main Battery Cables

Use 1/0 or 2/0 for all of your heavy load circuits. You should size these wire runs for a worst case scenario. A starter going bad, an inverter shorting, etc. Often battery cables are undersized due to cost and are insufficient to properly carry loads causing cables to get hot. When calculating loads add at least 30% safety factor for catastrophic failure. Once past the breakers or fuses normal sizes can be run since these circuits are protected.
curtis742 is offline   Reply With Quote
Old 23-07-2018, 08:37   #87
Registered User

Join Date: Oct 2010
Location: Blue Mountain Ont
Boat: Beneteau Oceanis 400 40 ft "Camp David
Posts: 608
Re: Sizing Main Battery Cables

One other issue is how you are charging your batteries.

If you have an inverted in the system you want to size the conductors properly.

Also how is the alternator wired? If you have a high output Balmar wired to the house battery bank ( directly) then you maybe able to use smaller cables. If you are using the starting circuit as the charge circuit be sure you are getting every amp. Bigger is better.
CampDavid is offline   Reply With Quote
Old 23-07-2018, 08:42   #88
Registered User
 
AKA-None's Avatar

Join Date: Oct 2013
Location: Lake City MN
Boat: C&C 27 Mk III
Posts: 2,647
Re: Sizing Main Battery Cables

For future edification http://www.usawire-cable.com/pdfs/nec%20ampacities.pdf

There is a lot more to wire sizing than just grabbing a number. Temp, bundling, connections, etc to name a few.

Any wire will handle any current but the key is for how long and under what conditions. To much and the delta t is very short.
__________________
Special knowledge can be a terrible disadvantage if it leads you too far along a path that you cannot explain anymore.
Frank Herbert 'Dune'
AKA-None is offline   Reply With Quote
Old 23-07-2018, 11:06   #89
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,523
Images: 2
Switches: Emergency Switch, DCPanel and Starter, etc

Quote:
Originally Posted by mitiempo View Post
You can do that just as well with the main switch.
My preference is a simple on/off for start and another for house.
I think we have that ability with the proposed wiring:
1. DC Panel has its own switch and main Circuit Breaker.
2. DC Panel and Starter are on the "C" of the 1both3 switch and can be disconnected from any battery (off) or use House or Reserve battery sources.
3. Alternator has a safety disconnect switch as shown.
4. Charger does not have a dedicated switch on the dc side, but does have internal fuses, is also fused at the main positive busbar, and can also be shut off at the new 120v AC panel using the 15a Charger circuit breaker.
5. Battery 24hr Fused Panel has no switch and is wired direct to the positive battery post. It is the only thing other than the batteries that is not easily switched off. However the fuses can be removed.

Not including the Emergency Switch will make connections more direct with less voltage drop, which is good. The cons are that disconnecting the House batteries might require unbolting the terminal wires, and if there is some electrical problem that is not as quick or as safe. I currently have no emergency switch, and have not missed one, but that is no example to follow necessarily.

On the other hand, everything except the batteries and the Battery 24hr Fused Panel can be easily switched off. I am torn about whether to include the emergency switch or not, as I don't understand all the forces at work. Could the battery run away somehow and would an Emergency Switch help somehow?
rgleason is offline   Reply With Quote
Old 23-07-2018, 12:01   #90
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,523
Images: 2
Size conductors properly

Quote:
Originally Posted by CampDavid View Post
One other issue is how you are charging your batteries. If you have an inverted in the system you want to size the conductors properly. Also how is the alternator wired? If you have a high output Balmar wired to the house battery bank ( directly) then you maybe able to use smaller cables. If you are using the starting circuit as the charge circuit be sure you are getting every amp. Bigger is better.

CampDavid see the most current wiring diagram

  1. Charger -40a Stirling wired to the MRBF 5196 Positive Busbar + 80amp fuse. Wiring diagram shows AWG #6 and length of circuits.
  2. Currently the Alternator jumps over to the starter with a short 8" small cable and it uses the starter cable, clever, but that will be changed.
  3. Alternator -Currently Balmar 90-65, but will be changed to Balmar 60-120 or similar. Will be wired direct to main House Battery Fuse (250a to 300a). Alternatively direct to MRBF 5196 Positive Busbar (but using the main battery fuse 250a-300a). -On second thought maybe we do need a 150a fuse on the alternator at the positive busbar, my head is spinning after focus on the starter and learning about voltage transients and sizing from MaineSail. What a help that was!
  4. Do I need a fuse on the Alternator if the cable is sized conservatively?
  5. All the negative cables go to the shunt near the house battery bank rather than the engine ground to try to suppress voltage transients from the starter.
  6. I was thinking of using the old ZapStop that is on my Alternator now, to reduce voltage transients at the DC Panel. I think it is a diode and it might work (after I rewire the alternator).
  7. Solar - The other source is going to be Solar PV about 280-300 watts, wired through controllers to the Battery 24hr Fused Panel which is wired direct to the positive house battery post bypassing the main battery fuse. This panel also has all the voltage sensor fuses for the Smartgauge, Link, ACR Combiner, so it has to have no voltage drop from the battery.
Any further thoughts would be appreciated.
rgleason is offline   Reply With Quote
Reply

Tags
battery, cables

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Battery switch & neg bus bar sizing masca Electrical: Batteries, Generators & Solar 32 17-06-2018 16:00
Sizing main halyard sailingunity Deck hardware: Rigging, Sails & Hoisting 11 07-08-2017 14:43
Battery cable sizing sailorboy1 Electrical: Batteries, Generators & Solar 5 26-06-2011 05:50
Battery Bank Interconnect Cable Sizing? Catamount Electrical: Batteries, Generators & Solar 7 10-04-2010 08:03
Battery Cables Cheechako Construction, Maintenance & Refit 1 03-02-2010 15:55

Advertise Here


All times are GMT -7. The time now is 04:22.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.