Safely Testing Large Solar

I am ready to test-install my 4 large 327 Watt Sunpower Solar panels on the Bimini rack.
This is for final adjustment prior to painting the racks and detailing the Bimini material.

Each Panel’s Rated Voltage=54.7 V; Rated Current= 5.98 A; Voc 64.9 V.

I also wanted to individualy test each panels output, in case there is a bad panel that would still be covered under warranty…
Each panels junction box comes with 1m of output cable MC4 Connectors

My working Plan is to mount 2 panels on each rack in shade…. Tape output cables secure…. Then physically mount on Bimini and confirm fit and output of each panel

My Solar newbie questions:
1… Any dangers or concern with that plan?
2… Using my AC/DC Clamp meter what is the best way of measuring each panels output?
__________________

__________________
Pelagic is offline   Reply With Quote
Old 02-06-2015, 04:26   #2
CF Adviser
 
Pelagic's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 6,890
Re: Safely Testing Large Solar

Some Photos of the instalation design
Attached Thumbnails
Click image for larger version

Name:	1 DSC_3019.jpg
Views:	92
Size:	324.4 KB
ID:	103068   Click image for larger version

Name:	1 DSC_3020.jpg
Views:	97
Size:	343.8 KB
ID:	103069  

Click image for larger version

Name:	1 hinge down .jpg
Views:	97
Size:	255.7 KB
ID:	103070   Click image for larger version

Name:	1 hinge up .jpg
Views:	96
Size:	276.7 KB
ID:	103071  

Click image for larger version

Name:	1 hinged up .jpg
Views:	97
Size:	259.2 KB
ID:	103072  
__________________

__________________
Pelagic is offline   Reply With Quote
Old 02-06-2015, 06:15   #3
Don't ask if you can't handle it
 
sailorboy1's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Location: On the boat somewhere
Boat: Hunter 410
Posts: 12,312
Re: Safely Testing Large Solar

Would seem to me that all you need to do to check the panels is to check the open circuit voltage as I don't understand how in your plan you are going to check amperage.
__________________
jobless, houseless, clueless, living on a boat and cruising around somewhere
sailorboy1 is offline   Reply With Quote
Old 02-06-2015, 06:46   #4
Registered User

Join Date: Jun 2009
Location: still in a roll of fiberglass around Cape Town
Boat: Leopard 40 (new model)
Posts: 1,201
Re: Safely Testing Large Solar

Quote:
Originally Posted by Pelagic View Post
I am ready to test-install my 4 large 327 Watt Sunpower Solar panels on the Bimini rack.
This is for final adjustment prior to painting the racks and detailing the Bimini material.

Each Panel’s Rated Voltage=54.7 V; Rated Current= 5.98 A; Voc 64.9 V.

I also wanted to individualy test each panels output, in case there is a bad panel that would still be covered under warranty…
Each panels junction box comes with 1m of output cable MC4 Connectors

My working Plan is to mount 2 panels on each rack in shade…. Tape output cables secure…. Then physically mount on Bimini and confirm fit and output of each panel

My Solar newbie questions:
1… Any dangers or concern with that plan?
2… Using my AC/DC Clamp meter what is the best way of measuring each panels output?
This is what I have done to test panels:

- Start with all panels disconnected
- Cover one of the panels with something
- Connect that panel to the controller but insert an amp meter in one of the wires just before the controller and another one just after the controller. (In your case the panel makes more than 140W so it will make more than 10A after the controller, hence don´t insert a regular 10A series ammeter in there and use a clamp instead) . Set the series ammeter to the 10A scale.
- Connect enough DC loads to consume more watts than your panel´s rating. This is to make sure battery voltage will stay low to prevent the controller from constraining the power output of the panel. If you have difficulty in lining up enough load then it is time for the "inverter plus hair dryer" combo.
- Uncover the panel and read volts and amps before and after the controller.

I do not use a current clamp because I have never found one that is precise for loads of a few amps. I like to install a permanent A and Ah meter like the US$59 Watts Up downstream of the controller.
For one-off testing , the amp meter of most multitesters (that works in series) should be fine because they are precise enough (say to a few percentage points of scale) . Your panels are so big that a clamp may be good enough at least for after the controller.

Cheers
C
__________________
svlamorocha is offline   Reply With Quote
Reply

Tags
solar

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Load Testing and Conductance Testing Joe500 Electrical: Batteries, Generators & Solar 0 02-12-2009 16:12
Using flares safely Boracay Health, Safety & Related Gear 5 03-01-2009 07:39
Can cats be safely hove to? prout35 Multihull Sailboats 8 23-02-2008 07:54
Diving safely from your boat. 2divers Fishing, Recreation & Fun 3 27-02-2006 18:28
New Boat how to do the pay off, safely? Ram Construction, Maintenance & Refit 8 24-01-2006 09:01



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 19:48.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.