Reg Sense +/- to #1 House when House failed

When I have wired the Regulator sensing wires + and - to respective House Battery terminals, what happens when the House battery fails?

Assuming House Panel and Starter are connected to the "C", Alt power (+) is direct to #1 house and the echocharger is not going to connect because the charger field is not activated and there is not adequate voltage to cause the echocharger to "combine".

1. Switch to #2 Bat Reserve to start engine. No problem.
2. Alternator Field - will not be activated if #1 Bat is 10.5vdc
3. Nothing will charge.

Yet we are told not to switch to "Both" as it may kill both batteries.
(If Both is selected, and if Batt #1 has enough partial charge current to activate the alternator field, then alternator may be put on a full load, pumping into both batteries.)

Do I have to move the Regulator Sensing wires to Battery #2 Reserve to get the alternator charging?
or reconnect the + / - sensing wires at the alternator?
rgleason is offline   Reply With Quote
Old 21-06-2018, 22:51   #2
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,662
Re: Reg Sense +/- to #1 House when House failed

the reg power still needs to come from the battery that starts the motor. a reg should have a b+ and a sense + like a balmar mc 614 does. (as well as ign wire)

the reg will power up off the engine battery. read 10v on the sense. and start charging the house full blast. once the house bank gets high enough the echo charger will kick in.

if you have an old reg that uses the power wire as the sense. consider replacing it. also consider replacing the 1,2, all switch. and separate the house and engine battery properly.

with a 1,2,all swtich I would likly have the sense, alt + and reg + all to the common. at bare min the reg b+ needs to.

get a blue sea add a battery kit. run the alt to the house, reg sense to the house batt, and reg power to the engine batt.
smac999 is offline   Reply With Quote
Old 22-06-2018, 01:47   #3
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Reg Sense +/- to #1 House when House failed

You can use a pos dist busbar at the bank to connect to. You can then use a wrench to pull the banks main fuse or put a Blue Sea mSeries ON/OFF between the busbar and bank. In the event of an actual bank failure turn off the ON/OFF or pull the fuse then set to BOTH. These failures are extremely rare if practicing good battery care and you're replacing the bank before SOH gets too bad.
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 22-06-2018, 17:23   #4
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,632
Images: 2
Re: Reg Sense +/- to #1 House when House failed

Thank you, both.

I failed to state that the regulator is a Balmer ARS-5 which does not have a separate power + wire (sense and power + are the same wire).

I think I learned that:

1. If a #1 bank is at 10.5 volts (not entirely dead) that the alternator field will still be activated and the Alt will be able to fully charge.

2. If #1 bank is entirely dead, I will have to change the power & sense wire + to #2 bank reserve to get the alt charging. I should also probably move the - sense to #2 bank.

3. That if I select Both banks and just want #2 bank to be active, disconnect the #1 with a wrench or Switch.

4. This is a rare case.

5. I don't believe it is cost effective to replace the new balmar ARS-5 and I am continuing to use my 12Both switch with the starter and house panel on the "C" terminal.

Thanks for confirming that this could be an issue if you run your batteries way down.
rgleason is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
UK Reg - in NZ - Need Call Sign? Jdiamond Marine Electronics 11 08-06-2009 07:58
I a stock Yanmar 55a Alternator "heavy-duty" enough to be changed to external reg? Northeaster Engines and Propulsion Systems 11 01-03-2009 13:28
New Reg's for Aus. GordMay Rules of the Road, Regulations & Red Tape 10 05-06-2008 02:56
Newbie... saying hello and asking for advice reg RYA and YA certificates... svass Meets & Greets 5 12-09-2007 01:34
cruzpro alternator reg problem southernman Electrical: Batteries, Generators & Solar 15 20-02-2006 19:49

Advertise Here


All times are GMT -7. The time now is 10:21.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.