Okay so why is this on the West marine site. I always had the solenoid past the regulator. Just cause that's how I did it. Could be wrong,http://content.westmarine.com/wm-img...-Propane-1.jpg
sabray is offline   Reply With Quote
Old 09-02-2013, 20:30   #17
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Quick Gas Question.

Quote:
Originally Posted by sabray View Post
Okay so why is this on the West marine site. I always had the solenoid past the regulator. Just cause that's how I did it. Could be wrong,http://content.westmarine.com/wm-img...-Propane-1.jpg

Is there any gas fitters out there than can answer this one?
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 09-02-2013, 20:44   #18
Registered User
 
sabray's Avatar

Join Date: Aug 2008
Location: Wash DC
Boat: PETERSON 44
Posts: 3,165
I'll take a stab at why the solenoid is after the regulator. The tank valve is positive off. The regulator maintains a pressure after the tank. The solenoid valve can't guarantee against a high pressure passing through its seat.
So first valve is on the tank pressure is reduced at the regulator and the solenoid handles low pressure gas.
Not a gas fitter but if you think about what is sealing the gas from coming into the boat it makes sense.
sabray is offline   Reply With Quote
Old 10-02-2013, 02:34   #19
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Quick Gas Question.

Put it back together with new thread tape and then soaped it all up. We have a leak just past the solenoid. So I will by some new fittings tomorrow as there is a little bit of thread damage on the fitting. I am going to replace the hose as well, the O ring looks a bit sad. Better safe than sorry.
Jeff
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 10-02-2013, 06:55   #20
Registered User

Join Date: May 2010
Location: Elsewhere on the Water
Posts: 579
Re: Quick Gas Question.

The question of putting the solenoid valve before or after the regulator seems to have conflicting guidance information from device manufacturers. West Marines data presented earlier suggest it being after. Fireboy - Xantrex says the opposite. This is from their owner's manual:
"Electrical Solenoid Valve SV-1
A. LPG Installation The electrical solenoid valve should be mounted on the tank side of the LPG regulator, as close to the tank as practical. The tank itself should be mounted outside the cabin or crew quarters to avoid the possibility of gas accumulation due to a leak between the tank and solenoid valve.

B. CNG Installation Because of the higher tank pressure of CNG, the valve must be installed after the CNG regulator and as close to the regulator as possible. The tank itself should be mounted outside the cabin or crew quarters to avoid the possibility of gas accumulation due to a leak. "

Clearly the benefit to having it at the tank is that it then protects possible leaks in the line from the tank. And, the benefit of having it after the regulator is that it is not subjected to the higher pressure.

LPG vapor pressure is 100-200 psi, and CNG vapor pressure is 2900–3600 psi.
St. Elsewhere is offline   Reply With Quote
Old 10-02-2013, 07:09   #21
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,678
Re: Quick Gas Question.

Wire up the solenoid after your main battery switch so when you leave the boat it is automatically turned off.
noelex 77 is offline   Reply With Quote
Old 10-02-2013, 07:30   #22
Registered User
 
Kettlewell's Avatar

Join Date: Jul 2006
Location: Massachusetts
Boat: Finnsailer 38
Posts: 5,077
Re: Quick Gas Question.

Quote:
Wire up the solenoid after your main battery switch so when you leave the boat it is automatically turned off.
^^+1^^.
__________________
JJKettlewell
Kettlewell is offline   Reply With Quote
Old 10-02-2013, 14:25   #23
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Quick Gas Question.

Quote:
Originally Posted by St. Elsewhere View Post
The question of putting the solenoid valve before or after the regulator seems to have conflicting guidance information from device manufacturers. West Marines data presented earlier suggest it being after. Fireboy - Xantrex says the opposite. This is from their owner's manual:
"Electrical Solenoid Valve SV-1
A. LPG Installation The electrical solenoid valve should be mounted on the tank side of the LPG regulator, as close to the tank as practical. The tank itself should be mounted outside the cabin or crew quarters to avoid the possibility of gas accumulation due to a leak between the tank and solenoid valve.

B. CNG Installation Because of the higher tank pressure of CNG, the valve must be installed after the CNG regulator and as close to the regulator as possible. The tank itself should be mounted outside the cabin or crew quarters to avoid the possibility of gas accumulation due to a leak. "

Clearly the benefit to having it at the tank is that it then protects possible leaks in the line from the tank. And, the benefit of having it after the regulator is that it is not subjected to the higher pressure.

LPG vapor pressure is 100-200 psi, and CNG vapor pressure is 2900–3600 psi.
Hmm. I will leave things as they are for now, I am using LPG, so the pressure is lower.
The power does turn off when the main switch is shut off but, currently I usually leave the boat with the power on for auto bilge pumps, right or wrong. I have a wind generator & small 60watt solar that charge 24/7 but as far as I am aware the wind gen mast be switched to the batteries that I want charged. By default, this turns the power on.
At the risk of opening a can of worms. What is the problem with leaving the power on while the boat is unattended?
Jeff
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 10-02-2013, 14:40   #24
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Quick Gas Question.

Hi Ron.
I can see you.
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 10-02-2013, 14:40   #25
Registered User

Join Date: May 2010
Location: Elsewhere on the Water
Posts: 579
Re: Quick Gas Question.

If you arrange it so that you limit what is on to the essential items, there should be no problem. If you are depending on wind or solar instead of shore power, you will need to be concerned about keeping the batteries charged.
St. Elsewhere is offline   Reply With Quote
Old 10-02-2013, 14:57   #26
Registered User
 
44'cruisingcat's Avatar

Join Date: Sep 2006
Posts: 9,398
Images: 69
Re: Quick Gas Question.

Quote:
Originally Posted by Hoohaa View Post
We have a solenoid and DVK Monitoring system with a on demand switch which turns the solenoid on "open" and when switched off, cuts the power to the solenoid "closed".
Arrived back to the boat after 2 weeks away and found that the gas had all leaked out (very dangerous I know).
It turns out that the wife had turned the gas on instead of turning it off when we left the boat and the solenoid was left on purpose, on.

The worrying thing, and yes there are many. is that the solenoid was warm when I felt it, was also a bit loose which is where I think the leak occurred. Note the leak seems to have contained to the self draining locker.

Should the solenoid get warm?
I will attach a couple of pics of the set up.
Why did you leave the solenoid on "on purpose"?

JMO, but apart from defeating the purpose of having a solenoid valve, leaving it on for weeks at a time would seem likely to shorten the life of the solenoid. Waste of electricity too.

Anyway, it's normal for it to get a little warm if it's left on a for a long time. We only switch ours on when we're actually using the gas.
44'cruisingcat is offline   Reply With Quote
Old 10-02-2013, 16:53   #27
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Quick Gas Question.

Quote:
Originally Posted by 44'cruisingcat View Post
Why did you leave the solenoid on "on purpose"?

JMO, but apart from defeating the purpose of having a solenoid valve, leaving it on for weeks at a time would seem likely to shorten the life of the solenoid. Waste of electricity too.

Anyway, it's normal for it to get a little warm if it's left on a for a long time. We only switch ours on when we're actually using the gas.
Yes, Left it on on purpose.
Had some dum notion that the gas detector needed to be on 24/7.
Won't happen again and the gas will always be turned off when not in use.

St. Elsewhere
Yes I am not hooked up to shore power.
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 10-02-2013, 16:59   #28
Registered User
 
Kettlewell's Avatar

Join Date: Jul 2006
Location: Massachusetts
Boat: Finnsailer 38
Posts: 5,077
Re: Quick Gas Question.

I have my boat set up so that I can turn off the main power switch and almost everything in the boat is cut off, but there is a small auxiliary fuse box that is close to the batteries and fused individually for each circuit for things I want to be on 24/7. Those include the bilge pumps, the solar power, and the small exhaust fan for the composting toilet (which has been running 24/7 since 2007).
__________________
JJKettlewell
Kettlewell is offline   Reply With Quote
Old 10-02-2013, 18:26   #29
Registered User

Join Date: Dec 2006
Location: Seattle
Boat: Cal 40 (sold). Still have a Hobie 20
Posts: 2,944
Images: 7
Re: Quick Gas Question.

ABYC says the valve can be installed on either the high or low pressure side.

1.7.3
The C-Brats :: - ABYC Propane Standards

The only thing you need to worry about is that the valve is rated for the pressure if you put it on the high pressure side.




Quote:
Originally Posted by St. Elsewhere View Post
The question of putting the solenoid valve before or after the regulator seems to have conflicting guidance information from device manufacturers. West Marines data presented earlier suggest it being after. Fireboy - Xantrex says the opposite. This is from their owner's manual:
"Electrical Solenoid Valve SV-1
A. LPG Installation The electrical solenoid valve should be mounted on the tank side of the LPG regulator, as close to the tank as practical. The tank itself should be mounted outside the cabin or crew quarters to avoid the possibility of gas accumulation due to a leak between the tank and solenoid valve.

B. CNG Installation Because of the higher tank pressure of CNG, the valve must be installed after the CNG regulator and as close to the regulator as possible. The tank itself should be mounted outside the cabin or crew quarters to avoid the possibility of gas accumulation due to a leak. "

Clearly the benefit to having it at the tank is that it then protects possible leaks in the line from the tank. And, the benefit of having it after the regulator is that it is not subjected to the higher pressure.

LPG vapor pressure is 100-200 psi, and CNG vapor pressure is 2900–3600 psi.
cal40john is offline   Reply With Quote
Old 10-02-2013, 23:48   #30
Registered User
 
44'cruisingcat's Avatar

Join Date: Sep 2006
Posts: 9,398
Images: 69
Re: Quick Gas Question.

Quote:
Originally Posted by Hoohaa View Post
Yes, Left it on on purpose.
Had some dum notion that the gas detector needed to be on 24/7.
Won't happen again and the gas will always be turned off when not in use.

St. Elsewhere
Yes I am not hooked up to shore power.
You can leave the gas detector on, but still have the solenoid valve shut. You just switch the "On Demand" switch off.

That's the normal situation on our boat, the GA286 is powered up, but the solenoid valve is shut. Although If I was leaving the boat, I'd power it off.

If it's not convenient to power it off at the distribution panel, there is an on/off switch on the unit.
44'cruisingcat is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
CNG / Natural Gas Distributor List way-happy Cooking and Provisioning: Food & Drink 12 24-07-2015 14:25
Cooking gas bottles seanie20 Atlantic & the Caribbean 2 29-03-2012 06:16
Quick Welding Question santa clara Construction, Maintenance & Refit 10 18-11-2011 06:25
Quick Question sona1111 Liveaboard's Forum 12 13-09-2011 20:02
Crew Question: Logistics Pleione General Sailing Forum 5 24-06-2011 19:31

Advertise Here


All times are GMT -7. The time now is 03:45.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.