Question: Batteries in Parallel, all loads from main + & -

Not sure how best to put this...

I have 4 group 31 batteries wired together in parallel. The positive of battery #1 is the main positive and the negative of number 4 is the main ground.

All major charging and loads are connected to the main positive, but my question is; can I connect light loads like a bilge pump etc. anywhere along the line, maybe to battery #2 in the system..???

Or, should ALL positive connections be to the positive of Number one? The main reason is I have a ton of cables going to just one terminal and I want to spread out some of the connections because the leads are too short or it takes too much cable to split it the 4-5 feet between the + & - terminals...

Hope that makes sense & I really appreciate any help!
__________________

__________________
Happy Sailing!
Mr Big is offline   Reply With Quote
Old 13-10-2015, 03:49   #2
Certifiable Refitter/Senior Wannbe
 
Wotname's Avatar

Cruisers Forum Supporter

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: Van DeStat Super Dogger 31'
Posts: 7,334
Re: Question: Batteries in Parallel, all loads from main + & -

A more usual arrangement would be to use bus bars for both +ve and -ve loads.
__________________

__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 13-10-2015, 04:26   #3
Senior Cruiser
 
StuM's Avatar

Cruisers Forum Supporter

Join Date: Nov 2013
Location: Port Moresby,Papua New Guinea
Boat: FP Belize Maestro 43
Posts: 6,713
Re: Question: Batteries in Parallel, all loads from main + & -

Don't take feeds from different batteries.

Here's a very good article. SmartGauge Electronics - Interconnecting multiple batteries to form one larger bank

It answers your specific question:
"Finally, if your battery bank has various take off points on different batteries, change it now! It is extremely bad practice. Not only does it mess up the battery balancing, it also makes trouble shooting very much more complicated and looks awful. "

And also discusses various methods of connecting four parallel batteries.

You are implementing Method 2, it's not the worst way to do it, but it's not the best either. Implement Method 4 if you can - combined with Wotname's recommended bus bars.
__________________
StuM is offline   Reply With Quote
Old 13-10-2015, 04:41   #4
Registered User

Join Date: Apr 2014
Posts: 39
Re: Question: Batteries in Parallel, all loads from main + & -

Thanks!

Here is my set up back when we were installing it. It has a box built around it now and straps to hold everything down.

Starting from the left are the 4 house batteries and the last batt. on the right is a separate start battery that shares the ground with the house bank.

You can see my + & - terminals are pretty loaded up...On the positive terminal, the yellow cable is the windlass, the fused red is the alt. and the main red runs through the 1/2/off switch to the fusebox.

The yellow arrow is the positive for the bilge pump on battery 2.



So, it would be better to run both a positive and negative bus bar and run all the leads off there?

Something like these & just mount them to the wall of the bilge...?



Thanks for your help this is new to me.
__________________
Happy Sailing!
Mr Big is offline   Reply With Quote
Old 13-10-2015, 04:52   #5
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Toronto, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 2,593
Re: Question: Batteries in Parallel, all loads from main + & -

I don't see a fuse in that positive conductor, you might want to think about that.
__________________
That hysterical laughter you hear as you sail a way in your "new" boat ..... is the seller.
boatpoker is offline   Reply With Quote
Old 13-10-2015, 04:56   #6
Moderator
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Albany Ga.
Boat: Island Packet 38
Posts: 17,062
Re: Question: Batteries in Parallel, all loads from main + & -

Run a pos and negative bus, just like you picture, just remember bigger is better.
Mount it to a wall is fine, a current limiting device on the Pos side isn't a bad idea either.
If you can get a little airspace between each battery that helps cooling during charging
__________________
a64pilot is offline   Reply With Quote
Old 13-10-2015, 08:37   #7
Registered User
 
hamburking's Avatar

Join Date: Feb 2013
Location: Kingston Ont Canada
Boat: Looking for my next boat!
Posts: 2,149
Re: Question: Batteries in Parallel, all loads from main + & -

The positive should run to a DC distribution panel (possibly through a selector switch if you have 2 banks). That way you can select what's on or not. If you have a panel, and just didn't mention it, then the bar bus is the way to go. This would be for the circuits you want ON all the time, like bilge pumps and maybe VHF radio. Everything else should be on the panel.
__________________
hamburking is offline   Reply With Quote
Old 13-10-2015, 10:06   #8
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Douglas 32 Mk II
Posts: 1,923
Re: Question: Batteries in Parallel, all loads from main + & -

Definitely put a current limiting device on every house bank take-off.


A battery terminal fuse is an effective and inexpensive solution. However, a breaker is better in that if it ever trips, AFTER you solve the problem, you only need to reset the breaker rather than find and replace the fuse. Either should be sized to suit the rating of the cable running to, or the distribution panel, whichever is less.


Every additional connection on any one terminal increases risk of a bad connection. ABYC standards prohibit having more than 4 connections on any battery terminal. I generally recommend no more than 2.


I am not aware of any ABYC standard prohibiting take-offs from other than the "end" battery terminal in a bank.


I don't see a bilge pump or VHF on a mid bank battery having a huge impact on charge balancing, but as others have said, using a bus bar or power post for all take-offs is a cleaner solution which makes battery servicing (pulling caps off for checking/filling and removal/replacement) much easier.


Many people are injured every year from improper battery handling. Just because it can't electrocute you, doesn't mean it can't hurt you.


Whenever working around batteries, always follow good safety practices, (remove all jewellery, wear protective clothing and googles, disconnect all charge sources and loads, and operate blower before disconnecting battery terminals, take care not to short terminals, etc.)


Ramblin Rod
www.sheenmarine.com
__________________
ramblinrod is offline   Reply With Quote
Old 13-10-2015, 10:40   #9
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,060
Re: Question: Batteries in Parallel, all loads from main + & -

Quote:
Originally Posted by ramblinrod View Post
Definitely put a current limiting device on every house bank take-off.


A battery terminal fuse is an effective and inexpensive solution. However, a breaker is better in that if it ever trips, AFTER you solve the problem, you only need to reset the breaker rather than find and replace the fuse. Either should be sized to suit the rating of the cable running to, or the distribution panel, whichever is less.


Breakers can be handy but any breaker used as primary bank protection should meet the minimum ABYC AIC rating for the bank it is protecting.

For a bank such as the one pictured this requires minimum AIC rating of 5000A... While the Blue Sea 187 series breakers do meet 5000A AIC at 12V they only go to 200A, which can get marginal if the house bank could ever be called upon to start the motor.

If the bank size exceeds 500Ah or 2200 CCA I don't know of a marine duty circuit breaker that would meet the ABYC standard. Over 500Ah and you're usually into a 20,000 AIC Class T fuse...
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 13-10-2015, 11:34   #10
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: Freya 39 cutter- Terra Nova
Posts: 3,652
Re: Question: Batteries in Parallel, all loads from main + & -

The paralleling cables appear to be at least twice as long as necessary, have no shrink sleeve to seal the connections, and appear to be improperly crimped. Did you do these yourself?
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 13-10-2015, 11:43   #11
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 6,389
Re: Question: Batteries in Parallel, all loads from main + & -

It also appears that the right two or three batteries are right next to your exhaust riser. Heat is not good for batteries. Do you have somewhere else to put them on the boat?
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, (Maple Bay Marina) SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 13-10-2015, 11:58   #12
Registered User
 
leftbrainstuff's Avatar

Join Date: May 2011
Location: San Francisco and Australia
Boat: Liberty 458
Posts: 1,979
Re: Question: Batteries in Parallel, all loads from main + & -

Quote:
Originally Posted by Mr Big View Post
Not sure how best to put this...

I have 4 group 31 batteries wired together in parallel. The positive of battery #1 is the main positive and the negative of number 4 is the main ground.

All major charging and loads are connected to the main positive, but my question is; can I connect light loads like a bilge pump etc. anywhere along the line, maybe to battery #2 in the system..???

Or, should ALL positive connections be to the positive of Number one? The main reason is I have a ton of cables going to just one terminal and I want to spread out some of the connections because the leads are too short or it takes too much cable to split it the 4-5 feet between the + & - terminals...

Hope that makes sense & I really appreciate any help!
Fit a bus bar. Size the posts and therefore the terminals for each load.

As a rule I never fit more than 2 eye terminals together. We have some exceptions where space for a bigger bus bar is an issue.

Some of our bus bars impede on access to other systems. These might have 3 or more terminals together. Only light loads that arent mission or safety critical are ganged together.

Fault finding and resistance checking is easier if you group terminals logically. For example bilge pump power is alone while several light terminals can be ganged together.

I dont place any terminals, other than the main power feed direct to the battery. This way when you remove or replace the battery you're not flexing and squashing wires and connectors. Battery access for topups and hydrometer testing is generally easier. Less excuse not to check them then.

Sent from my SM-N900T using Cruisers Sailing Forum mobile app
__________________
leftbrainstuff is offline   Reply With Quote
Old 13-10-2015, 12:16   #13
Registered User

Join Date: May 2008
Posts: 1,971
Re: Question: Batteries in Parallel, all loads from main + & -

Someone who knows more than me, like MainSail, should comment -- but I think the batteries will charge and discharge more equally if the positive and negative feeds are at opposite ends of the bank. Or you could move just the alternator positive to the opposite end to get some benefit and reduce the number of connections.

BlueSea makes a nifty multiple connection battery fuse holder:

https://www.bluesea.com/products/215...k_-_30_to_300A
__________________
CarlF is offline   Reply With Quote
Old 13-10-2015, 12:32   #14
Registered User

Join Date: Nov 2014
Posts: 15
Re: Question: Batteries in Parallel, all loads from main + & -

To answer your exact question, no. It wont make any difference. Everything connected to that parallel "node" sees the same voltage. Current will flow determined by resistive loads, not placement. Making the bus bars is the same theory and easier to work with but you asked Can I and yes you can.
__________________
bluegreen is offline   Reply With Quote
Old 13-10-2015, 12:48   #15
Registered User
 
deblen's Avatar

Join Date: Oct 2014
Location: Grand Manan,N.B.,Canada N44.40 W66.50
Boat: Mascot 28 pilothouse motorsailer 28ft
Posts: 1,405
Images: 1
Re: Question: Batteries in Parallel, all loads from main + & -

Click image for larger version

Name:	Bat. Bank <a title=Wiring & Switching.jpg Views: 161 Size: 421.3 KB ID: 110924" style="margin: 2px" />

A suggested method.
/ Len
__________________

__________________
My personal experience & humble opinions-feel free to ignore both
deblen is online now   Reply With Quote
Reply

Tags
loa

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
6 Batteries in Parallel - Good Idea or Bad? Optimas solecollector Electrical: Batteries, Generators & Solar 12 14-08-2013 13:03
1 alternator, 2 new starter batteries + parallel switch - will it work?? svstrider Electrical: Batteries, Generators & Solar 5 27-01-2013 23:07
Main Sail Reefing system loads.... NCountry Construction, Maintenance & Refit 1 06-03-2012 09:08
Four Solar Panels - Parallel , Series or Series-Parallel west coaster Electrical: Batteries, Generators & Solar 76 07-07-2011 15:35
Isolate Shore Power Loads from Inverter Loads RoyHB Electrical: Batteries, Generators & Solar 4 19-04-2010 06:02



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 12:46.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.