Old 06-12-2011, 18:18   #61
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,114
Re: Proper Grounding for AC and DC

Quote:
Originally Posted by Maine Sail View Post
ABYC still requires all on-board originating "sources", inverter, generator or isolation transformer to be grounded (green wire) to the ships DC grounding system. Neutral and ground are only connected at the source end..
As I read ABYC, E-11, if an inverter or generator are on board, they become the source rather than shore power, therefore neutral and ground would be bonded at source i.e. generator and or inverter
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 06-12-2011, 18:31   #62
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,114
Re: Proper Grounding for AC and DC

I've been involved in a number of lightning claims (all in fresh water) ahve have seen boats that met all the ABYC standards and one that had all the current geegaws from static disipator and ion disipator, dynaplates et al. Most that I have seen had significant hull damage from side flashes (remember fresh water hits are much different than salt).

I have come to the conclusion that regardless of any system on your boat, 60 million volts, travelling at about 90,000mph and hotter than the surface of the sun .... well, it's going wherever the hell it wants.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 06-12-2011, 19:24   #63
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Quote:
Originally Posted by boatpoker
I've been involved in a number of lightning claims (all in fresh water) ahve have seen boats that met all the ABYC standards and one that had all the current geegaws from static disipator and ion disipator, dynaplates et al. Most that I have seen had significant hull damage from side flashes (remember fresh water hits are much different than salt).

I have come to the conclusion that regardless of any system on your boat, 60 million volts, travelling at about 90,000mph and hotter than the surface of the sun .... well, it's going wherever the hell it wants.
For many it is the way to not understand it. But for many others, it is just a violent way of an electrical discharge which follows all laws of physics. Where ones sees nothing or just air, another sees a potential conductor after ionization. When something is discussed that not everybody who participates in the discussion understands, it gets messy with the voodoo and magic and what more.

Science has come a long way since the human kind believed that thunder and lightning was caused by an angry Thor. We can in fact create lightning ourselves which is done on a regular basis in laboratories to approve equipment incl. the lightning rods. That is where the 100% effective numbers come from, cold scientific method. I agree, boring, compared to voodoo.

ciao!
Nick.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 06-12-2011, 19:32   #64
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Quote:
Originally Posted by boatpoker

As I read ABYC, E-11, if an inverter or generator are on board, they become the source rather than shore power, therefore neutral and ground would be bonded at source i.e. generator and or inverter
Yes, unfortunately they do that. Remember that ABYC only makes recommendations and only for US yachts. Most other nations feel strongly different about that and do NOT endorse polarizing on-board AC sources, let alone connecting them to the DC system.

Many inverters allow you to change that neutral grounding behaviour (done by internal relais). And every genset allows you to remove the jumper that grounds the neutral.

On a sidenote, I'm starting to understand why US aluminium boats haveso many electrolysis problems... they make batteries out of them

cheers,
Nick.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 06-12-2011, 19:34   #65
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,197
Re: Proper Grounding for AC and DC

Quote:
Originally Posted by boatpoker View Post
As I read ABYC, E-11, if an inverter or generator are on board, they become the source rather than shore power, therefore neutral and ground would be bonded at source i.e. generator and or inverter
Exactly correct. Sorry if my wording was confusing. My point was that only at a "source", or more correctly inside the source, generator, inverter, isolation transformer are the green and white tied together. They are also obviously tied together at shore too as that is a "source". Once the green & white wires leave a source they are not again tied together on the boat. When wires leave an on-board "source" the green gets connected to ship DC ground to meet the current ABYC standard as does a shore power grounding conductor... White & green are only connected at a "source"..
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 07-12-2011, 01:04   #66
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Quote:
Originally Posted by Maine Sail

Exactly correct. Sorry if my wording was confusing. My point was that only at a "source", or more correctly inside the source, generator, inverter, isolation transformer are the green and white tied together. They are also obviously tied together at shore too as that is a "source". Once the green & white wires leave a source they are not again tied together on the boat. When wires leave an on-board "source" the green gets connected to ship DC ground to meet the current ABYC standard as does a shore power grounding conductor... White & green are only connected at a "source"..
Actually for on board isolated AC sources the stipulation that the dc negative and in effect ac neutral/earth are connected makes even less electrical sense.

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 01-02-2012, 06:06   #67
Senior Cruiser
 
hpeer's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: Between Caribbean and Canada
Boat: Murray 33-Chouette & Pape Steelmaid-44-Safara-both steel cutters
Posts: 8,576
Re: Proper Grounding for AC and DC

A practical question on this grounding topic.

Boat is a 44' STEEL cutter.

The PO had a Paneltronics 4401 series panel installed in 2006.

Diagram here: http://paneltronics.com/technical/Wi...eluxe/4401.pdf

Note that they have two DC buses:

1: DC Grounding Bus - this has 2 about #10AWG wires dissapearing into the wiring harness. I'll dive after this connection soon.

2: DC Negative Bus - this goes to the negative side of the battery.

They are NOT connected and have about 5 volts between them.

Clearly this is an engineered solution and there is some good reason for it. What?
hpeer is offline   Reply With Quote
Old 01-02-2012, 07:00   #68
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,001
Re: Proper Grounding for AC and DC

Quote:
Originally Posted by hpeer View Post
Clearly this is an engineered solution and there is some good reason for it. What?
Isolating DC negative from ground is great and the standard for metal boats. It eliminates electrolysis.

The ground wires will attach to some underwater metal part.

ciao!
Nick.
s/v Jedi is offline   Reply With Quote
Old 01-02-2012, 08:00   #69
Registered User

Join Date: Mar 2006
Posts: 1,594
Re: Proper Grounding for AC and DC

On our 25D with a diesel, years ago I separated the DC gnd from the AC ground because of an issue with stray currents and tripping my GFIs.. The ONLY place that our AC circuits connect to ground is at the SUPPLY PANEL on shore. No AC generation equip on board.
__________________
Randy

Cape Dory 25D Seraph
rtbates is offline   Reply With Quote
Old 01-02-2012, 14:31   #70
Senior Cruiser
 
hpeer's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: Between Caribbean and Canada
Boat: Murray 33-Chouette & Pape Steelmaid-44-Safara-both steel cutters
Posts: 8,576
Re: Proper Grounding for AC and DC

Quote:
Originally Posted by s/v Jedi View Post
Isolating DC negative from ground is great and the standard for metal boats. It eliminates electrolysis.

The ground wires will attach to some underwater metal part.

ciao!
Nick.
Nick - thanks for answer.

1. I can understand isolating Battery negative from ground/hull. Good idea.
2. I can understand having some connection from the hull to the electrical panel so that you can test to assure you don't have an inadvertent ground connection.
3. I can appreciate that this panel is designed for fiberglass boats and not steel.

What I don't get is why to parallel each Bat neg bus with a DC ground bus of the same size and capacity for either FG or metal.

Why would they do that?
hpeer is offline   Reply With Quote
Old 02-02-2012, 02:16   #71
Registered User

Join Date: Apr 2011
Location: Cooktown,Australia.(only to collect my mail)
Boat: Fastback 32 cat.
Posts: 158
Re: Proper Grounding for AC and DC

by aussiegeoff.
AFAIK, unlike caravans, there's no Australian regulations for mains power on boats, and Australian Standards only seem to cover commercial power.

There are regulations on all boats,each state has it's own regs.
Mains power is not a definition that applies,any low voltage eg 110 or 240 volt from any source (generators etc)is regulated.12 volt is extra low voltage.
Here is some info from Queensland transport .http://www.msq.qld.gov.au/~/media/ba...s_licences.pdf
Ian R is offline   Reply With Quote
Old 02-02-2012, 09:28   #72
Ike
Registered User
 
Ike's Avatar

Join Date: Oct 2008
Location: Pacific Northwest, USA
Boat: FL12 12 ft rowboat, 8 foot sailing dink, 18 foot SeaRay I/O
Posts: 325
Re: Proper Grounding for AC and DC

Australian and New Zealand National standards for recreational boats are found here. The document in Ian R's post is a little out of date.
:: National Marine Safety Committee ::: ::
Put your cursor over Standards And Publications, Select National Standards, Scroll down to Recreational Boat Standards.
__________________
Ike
"Dont tell me I can't, tell me how I can"
Ike is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
DC Generator - The Smart Way to Go ColdEH Electrical: Batteries, Generators & Solar 107 18-01-2024 15:07
Save the Anchorage In Washington, DC ANCHOR DC Cruising News & Events 129 01-08-2012 08:00
OpenGL for OpenCPN bdbcat OpenCPN 72 15-11-2011 00:17
Liveaboard Boatyard Annapolis , Commute to DC? virginia boy General Sailing Forum 12 08-07-2011 15:37

Advertise Here