Old 03-12-2018, 21:06   #16
er9
cruiser

Join Date: Sep 2014
Boat: 1980 (Canning) Mariner36
Posts: 834
Re: Pairing circuit breaker to wire to load

Quote:
Originally Posted by patrickbarbary View Post
Is it 12 or 24V? I would measure how much amps max and get a lower fuse. Also, ALWAYS tighten the wires to your fuses VERY tightly and check twice a year. I almost had a fire because of a loose wire in the fuse panel.
12volt
er9 is offline   Reply With Quote
Old 03-12-2018, 21:14   #17
er9
cruiser

Join Date: Sep 2014
Boat: 1980 (Canning) Mariner36
Posts: 834
Re: Pairing circuit breaker to wire to load

Quote:
Originally Posted by KP44 View Post
The smallest wire in the circuit needs to be protected by the breaker.

Even if your main wire is 14 ga, the fixture(s) wires are probably 18 ga and is rated to carry 5 amps before danger of melting or burning. So a 5 amp circuit breaker is correct.

Since you only expect 3 amps, this will not be a problem.

Do not use 15 amp unless 14 ga is the smallest wire in the circuit, including the interior circuits of the lights.

Or you could use a 15 amp breaker and a 3 amp in-line fuse at each light fixture.
Thanks for all the replies and info....much appreciated.

Iv'e been doing a lot more research past few days and this is the conclusion iv'e also arrived at, to protect the smallest wire in the circuit which coming from the fixture is pretty small...i'm guessing 18 GA.

Each fixture has a voltage regulator and will work happily within a fairly wide range of voltage.

The only issue is trying to replace the 15 amp circuit breaker on my 1980 DC panel could prove to be a challenge. If i decided to leave the breaker in could i just put a 5 amp fuse inline on the +wire after it leaves the panel to the lights to protect them at a lower amperage?
er9 is offline   Reply With Quote
Old 03-12-2018, 21:20   #18
er9
cruiser

Join Date: Sep 2014
Boat: 1980 (Canning) Mariner36
Posts: 834
Re: Pairing circuit breaker to wire to load

Quote:
Originally Posted by KP44 View Post
The smallest wire in the circuit needs to be protected by the breaker.

Even if your main wire is 14 ga, the fixture(s) wires are probably 18 ga and is rated to carry 5 amps before danger of melting or burning. So a 5 amp circuit breaker is correct.

Since you only expect 3 amps, this will not be a problem.

Do not use 15 amp unless 14 ga is the smallest wire in the circuit, including the interior circuits of the lights.

Or you could use a 15 amp breaker and a 3 amp in-line fuse at each light fixture.
Has to be at each light? wow i think i would rather replace the entire distribution panel than to remove all those ceiling panels again. I invented new forms of bodily contortion i prefer to never repeat again getting to some fixtures.
er9 is offline   Reply With Quote
Old 06-12-2018, 08:19   #19
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 361
Re: Pairing circuit breaker to wire to load

After reading here all about voltage drop, wire capacity, and do smaller fuses have more voltage drop? I guess the original lights did not glow.
I would have thought 18AWG marine grade would carry 15 amps with no trouble.
Zil is offline   Reply With Quote
Old 06-12-2018, 08:31   #20
Registered User

Join Date: Dec 2010
Location: W Carib
Boat: Wildcat 35, Hobie 33
Posts: 13,486
Re: Pairing circuit breaker to wire to load

Quote:
Originally Posted by Zil View Post
After reading here all about voltage drop, wire capacity, and do smaller fuses have more voltage drop? I guess the original lights did not glow.
I would have thought 18AWG marine grade would carry 15 amps with no trouble.
Fuses/breakers dont normally create any significant voltage drop. The voltage drop is created by resistance in the wire.

Amps alone is not enough to determine correct wire gauge. You also need to know length of wire run, voltage, and target voltage drop.

Here is an online calculator:

https://www.calculator.net/voltage-d...s=15&x=78&y=28
belizesailor is offline   Reply With Quote
Old 06-12-2018, 08:50   #21
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Pairing circuit breaker to wire to load

The Blue Sea Circuit Wizard app lets you take other relevant variables into account.

Every connection / gadget in the path adds to voltage drop.

Different owners and use cases affect what is "significant."
john61ct is offline   Reply With Quote
Old 06-12-2018, 10:46   #22
֍֎֍֎֍֎֍֎֍֎

Join Date: Apr 2006
Posts: 15,136
Re: Pairing circuit breaker to wire to load

All fuses have some voltage drop, typically so small that for all practical purposes it is ignored.

"If i decided to leave the breaker in could i just put a 5 amp fuse inline on the +wire after it leaves the panel"
You could do it that way, but having fuses/breakers in series that way tends to come back to bite you, when you're trying to figure out why a circuit has gone dead and "the" fuse/breaker is good, and you've forgotten about the other one. Also, the very short length of the 18g section of wire usually means that it can carry a higher load than a longer run of the same gauge wire would, so it should not be a significant worry. But that's your call, either approach would work safely, IMO.
hellosailor is offline   Reply With Quote
Old 06-12-2018, 11:21   #23
Registered User

Join Date: Dec 2010
Location: W Carib
Boat: Wildcat 35, Hobie 33
Posts: 13,486
Re: Pairing circuit breaker to wire to load

Quote:
Originally Posted by hellosailor View Post
All fuses have some voltage drop, typically so small that for all practical purposes it is ignored.

"If i decided to leave the breaker in could i just put a 5 amp fuse inline on the +wire after it leaves the panel"
You could do it that way, but having fuses/breakers in series that way tends to come back to bite you, when you're trying to figure out why a circuit has gone dead and "the" fuse/breaker is good, and you've forgotten about the other one. Also, the very short length of the 18g section of wire usually means that it can carry a higher load than a longer run of the same gauge wire would, so it should not be a significant worry. But that's your call, either approach would work safely, IMO.
Yeah, I really dislike inline fuses for this reason...and its one more spare to keep on hand.
belizesailor is offline   Reply With Quote
Old 06-12-2018, 11:44   #24
֍֎֍֎֍֎֍֎֍֎

Join Date: Apr 2006
Posts: 15,136
Re: Pairing circuit breaker to wire to load

Spares, yeah. I've learned to keep a 7-day pill dispenser, the kind like a strip from an ice cube tray, for those. One for glass, one for ATO/ATC, it makes it easier to keep them all together and sorted that way.

Headed out to a race early one morning on a nearly new boat and the boss asks me how's the fuel. I said the gauge shows empty, and he says impossible. And flipping the breaker does nothing to change that, so I pull a panel and start worming behind a bulkhead to access the back of the gauge, thinking maybe it hadn't been wired up tightly. What do I find? Oh, yeah, about 18" away from the gauge, firmly buried (but unattached, just floating in the air) behind the bulkhead, there's a ****ing glass inline fuse that had failed. Totally out of sight and hey, who the hell would bury a fuse that way?!

Or the double headlight fuse that bit me on an older GM product. One fuse in the car for the headlights, a second fuse under the hood for the "headlights and stuff" circuit. And the one in the car had blown because someone had dropped a spring the headlight switch and just left it in there, so every time it rolled out of the grease...bzzzt! and the fuse would blow for 'no' reason.

I can understand why serial fuses are SOMETIMES a rational idea, sometimes even a good one. But if there's no big red sign that says "HEY, THERE'S A MAN BEHIND THE CURTAIN, LOOK THIS WAY" then they certainly can baffle you.
hellosailor is offline   Reply With Quote
Old 07-12-2018, 18:57   #25
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 361
Re: Pairing circuit breaker to wire to load

Yes, fuses do have a voltage drop. Smaller amp fuses have more voltage drop than higher amp. That is another argument for using the larger fuse sized to the gauge of the wire. mainesail has page about this.
Zil is offline   Reply With Quote
Old 07-12-2018, 20:00   #26
er9
cruiser

Join Date: Sep 2014
Boat: 1980 (Canning) Mariner36
Posts: 834
Re: Pairing circuit breaker to wire to load

Quote:
Originally Posted by hellosailor View Post
All fuses have some voltage drop, typically so small that for all practical purposes it is ignored.

"If i decided to leave the breaker in could i just put a 5 amp fuse inline on the +wire after it leaves the panel"
You could do it that way, but having fuses/breakers in series that way tends to come back to bite you, when you're trying to figure out why a circuit has gone dead and "the" fuse/breaker is good, and you've forgotten about the other one. Also, the very short length of the 18g section of wire usually means that it can carry a higher load than a longer run of the same gauge wire would, so it should not be a significant worry. But that's your call, either approach would work safely, IMO.
much thanks...i think im going to just leave the 15amp breaker in for the time being, no inline fuse. i will be installing a completely new distribution panel some time late next year so i think i will wait and make the switch to a smaller breaker then.
er9 is offline   Reply With Quote
Old 08-12-2018, 04:19   #27
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,440
Images: 241
Re: Pairing circuit breaker to wire to load

Greetings and welcome aboard the CF, patrickbarbary.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Reply

Tags
loa


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pairing a Raymarine wireless wind transducer Peregrine1983 Marine Electronics 8 27-06-2018 09:48
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Earth Leak Circuit Breaker Wire Overheating...! raya Electrical: Batteries, Generators & Solar 8 27-05-2010 21:22
Fuse or Circuit Breaker ? ggray Electrical: Batteries, Generators & Solar 5 15-10-2009 15:41
parallel a circuit breaker skyking2 Electrical: Batteries, Generators & Solar 13 03-11-2006 22:00

Advertise Here