Onan genset keeps stopping fault code 13

We have a onan genset MDKAW 9.5 kva unit.
After about 15 seconds of running it turns off with fault 13.
It is a low voltage read fault.
We just replaced the ecu $1500 and the fuel pump.
The engine side runs fine so we think its the power generation side?
Anyone had this issue that may be able to advise a fix?
It is in Indonesia so calling the Onan service tech is not really an option.
harvey hellman is offline   Reply With Quote
Old 30-05-2017, 05:12   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,384
Images: 241
Re: Onan genset keeps stopping fault code 13

“... UNDERVOLTAGE FAULT—CODE NO. 13 (Controller unable to maintain rated voltage)
Corrective Action:
Reduce the number of connected appliances, especially when air conditioners and battery chargers are running ...”

https://manuals.heartlandowners.org/...ng%20Codes.pdf
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 30-05-2017, 05:12   #3
Registered User

Join Date: May 2006
Posts: 1,139
Re: Onan genset keeps stopping fault code 13

Quote:
Originally Posted by harvey hellman View Post
We have a onan genset MDKAW 9.5 kva unit.
After about 15 seconds of running it turns off with fault 13.
It is a low voltage read fault.
We just replaced the ecu $1500 and the fuel pump.
The engine side runs fine so we think its the power generation side?
Anyone had this issue that may be able to advise a fix?
It is in Indonesia so calling the Onan service tech is not really an option.
Maybe the error 13 is just because the engine slowed and has nothing to do with the generator unit.


Does it stop suddenly or over 3 seconds first slowing a bit.
if first slowing a bit then it might be fuel. maybe a filter or blocked line.
I am sure a good generator diesel mechanic can solve it better than asking on here.
We don't have enough info and will spend Ages asking you lots of questions.
Maybe try replacing all filters and then running from a liter of diesel feeding the fuel pump with a new 20cm long pipe.


Try switching the main breaker off on the generator and running it.
Fuss is offline   Reply With Quote
Old 30-05-2017, 05:57   #4
Registered User

Join Date: May 2017
Location: Geelong
Boat: Lagoon 440
Posts: 22
Re: Onan genset keeps stopping fault code 13

All power appliances are disconnected so no power draw from the unit,
New fuel filters, new fuel pump,fuel flow perfect.
The fault is in the power generating half of the genset.
I wish a service tech could fix it but they dont really exist in the remote 3rd world tropics where we are. These things only fail when you are no where near a service centre
harvey hellman is offline   Reply With Quote
Old 30-05-2017, 06:01   #5
Registered User

Join Date: May 2017
Location: Geelong
Boat: Lagoon 440
Posts: 22
Re: Onan genset keeps stopping fault code 13

Quote:
Originally Posted by Fuss View Post
Maybe the error 13 is just because the engine slowed and has nothing to do with the generator unit.


Does it stop suddenly or over 3 seconds first slowing a bit.
if first slowing a bit then it might be fuel. maybe a filter or blocked line.
I am sure a good generator diesel mechanic can solve it better than asking on here.
We don't have enough info and will spend Ages asking you lots of questions.
Maybe try replacing all filters and then running from a liter of diesel feeding the fuel pump with a new 20cm long pipe.


Try switching the main breaker off on the generator and running it.


Main breaker off, fuel filters and pump replaced, fuel run from container with hose all works fine,the engine runs great for about 10-20 seconds and then the ecu turns it off suddenly.
Replaced with new ecu as we thought it was faulty but still shuts down due to low voltage.
Start battery is new too.
Seems it must be on the power generating side?
harvey hellman is offline   Reply With Quote
Old 30-05-2017, 06:55   #6
Registered User
 
Captain Bill's Avatar

Join Date: Apr 2008
Location: Punta Gorda, Fl
Boat: Endeavourcat Sailcat 44
Posts: 3,176
Re: Onan genset keeps stopping fault code 13

I have a 5kw mdkau so my experience may not directly apply. If the ECU does not see 120v +- in about 15 seconds it shuts the engine down. The generator applies a small voltage to the coils to start building the magnetic field and this builds to 120v pretty quickly. All of this goes through the brushes on the rotor. If the brushes are bad then the magnetic field cannot be established in the coils and 120v will not be generated. Brushes wear out and sometimes damage the contact rings when they do. I got 2300 hours on my first set of brushes but only 1050 on my second set because there was a small area on the contact ring that abraded the graphite brush. I replaced then replaced both pieces.

The circuit applying and controlling this voltage is called the field flash circuit and the only moving parts (hence likeliest to fail) are the contactor rings and the brushes. I would look at the brushes first. Since you have already replaced the ECU where all of the electronics are located you have likely eliminated that as a problem. The remaining parts are voltage sensing coils which are a serious problem because they are embedded in the coils of the generator.

Like I said this information is for a 5kw mdkau and may not apply to your genset.
Captain Bill is online now   Reply With Quote
Old 30-05-2017, 08:57   #7
Registered User

Join Date: Jan 2013
Posts: 347
Re: Onan genset keeps stopping fault code 13

Ya know,an old salor once said sailing is about fixing your stuff with having to make due with whatever you have in exotic locations. well it sounds like you've succeeded. Sorry I can't help.
Kita is offline   Reply With Quote
Old 30-05-2017, 09:19   #8
Registered User
 
SeeMonstrEd's Avatar

Join Date: Dec 2014
Location: St Thomas USVI
Boat: Jeaneau, International 50
Posts: 89
Images: 3
Re: Onan genset keeps stopping fault code 13

also check for loose connections and broken wires. I ended up rewiring my entire genset because the plastic POS junction for the control wires had so many bad connection. It was mounted on the case the vibrations just killed it. I replaced it and all the wires then relocated it on a bulkhead.

Capt Ed
SeeMonstrEd is offline   Reply With Quote
Old 30-05-2017, 18:05   #9
Registered User

Join Date: Dec 2009
Location: Cruising, now in USVIs
Boat: Taswell 43
Posts: 1,038
Re: Onan genset keeps stopping fault code 13

We have an Onan genset, 6/5kva, and have had similar problems. We put a digital voltmeter+ freq meter on the output, and discovered the genset governor had gotten out of adjustment. I loosened both the over and underspeed set screws(bolt heads), and reset the eng speed so it was putting out the required voltage(230v) and 50Hz required for our system. Of course it slowed a bit when under heavy load, so I reset the governor to be a little over a no load and a little under at heavy load....and then reset the over and under set screws(bolts). I checked the wires to the control transformer in the control box before I ever started, so I knew they were on the correct taps, to ensure they were solidly in place. Worked for us!
sailcrazy is offline   Reply With Quote
Old 31-05-2017, 08:20   #10
Registered User

Join Date: Sep 2015
Location: East Coast Florida
Boat: Chris Craft 38 Commander 1965
Posts: 482
Re: Onan genset keeps stopping fault code 13

I second those comments by Captain Bill. I have a Generac 8KW that had similar but not exactly the same problem a couple of years ago. Part of my solution was adding an accessory part called a Field Boost Kit that made sure 12volts was fed directly to the generator field and brushes. Without it it was very erratic and difficult to start.
also depending on the hours on the genset - as he said if the problem is in the filed windings then that means a whole now generator portion of the genset will need replacing as parts are not available for just that..
Squanderbucks is offline   Reply With Quote
Old 31-05-2017, 08:38   #11
Registered User

Join Date: Feb 2016
Location: So Cal
Boat: Lancer 44 Motor Sailer
Posts: 560
Re: Onan genset keeps stopping fault code 13

Quote:
Originally Posted by Squanderbucks View Post
I second those comments by Captain Bill. I have a Generac 8KW that had similar but not exactly the same problem a couple of years ago. Part of my solution was adding an accessory part called a Field Boost Kit that made sure 12volts was fed directly to the generator field and brushes. Without it it was very erratic and difficult to start.
also depending on the hours on the genset - as he said if the problem is in the filed windings then that means a whole now generator portion of the genset will need replacing as parts are not available for just that..
Have to also agree. I have a 7.5 KW Onan on the boat (runs good) I bought a used Kabota GL 6.5 KW for the house. When starting the Kabota it would run fine for 10-15 seconds and then shut down. Turned out to be a defective voltage regulator. I found one on E-Bay for about $65.00 and that fixed the problem. Apparently the ECM senses low voltage and goes into a shut down mode. You can apply a low voltage to the exciter ring brush leads and bypass the regulator to test if it makes power. I did and got to careless and got hit with 240 VAC. Ouch! Be carefull if you try this and have someone there to do CPR. Hope it works out for you.
Diesel Bill is offline   Reply With Quote
Old 09-06-2017, 08:47   #12
Registered User
 
Emerald Sea's Avatar

Join Date: Feb 2013
Location: Live-aboard Cruiser
Boat: Lagoon 450
Posts: 628
Re: Onan genset keeps stopping fault code 13

Harvey. Have you got to the bottom of this? What was the problem amd how did you fix it?
Thanks, Steve
__________________
Steve
SV Emerald Sea
L450
Emerald Sea is offline   Reply With Quote
Old 10-06-2017, 07:23   #13
Registered User

Join Date: May 2017
Location: Geelong
Boat: Lagoon 440
Posts: 22
Re: Onan genset keeps stopping fault code 13

Still trying, ecu replaced but was not the issue, it is in the coil area and a work in progress
harvey hellman is offline   Reply With Quote
Old 12-06-2017, 23:26   #14
Registered User

Join Date: Feb 2015
Posts: 1,227
Images: 1
Re: Onan genset keeps stopping fault code 13

Have you been able to put a meter on the AC output to see what it actually measures, both in voltage and frequency?

Is this a 230V 50hz unit? 120/240V 60hz split phase? 120V 60hz?
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 25-06-2019, 16:17   #15
Registered User

Join Date: Jun 2019
Posts: 1
Re: Onan genset keeps stopping fault code 13

I just had a brand new Onan installed and after 20 hours having a similar problem but it runs for 45 minutes and then dies. The Cummins tech has replaced the fuel pump so far and still working. I did see online error code 13 as being fuel related. The person that installed it suggested isolating the generator by using an external fuel supply and then work back.
Royal Virgos is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Universal M3-20B keeps stopping sailingdoc Engines and Propulsion Systems 2 07-08-2016 16:21
Xantrex Prosine 2.0 fault code 3073 lunasea.ds Electrical: Batteries, Generators & Solar 3 05-04-2014 09:02
My 20 Amp Breaker Keeps Popping and Shutting Down Genset Turtlep Electrical: Batteries, Generators & Solar 4 26-07-2012 13:23
For Sale: 7.5kw Onan Marine Genset Dune Classifieds Archive 4 02-04-2011 10:09

Advertise Here


All times are GMT -7. The time now is 17:54.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.