Old 04-04-2011, 11:09   #16
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

Thanks for your answers!

I took off all other loads, and also tried to hook up the compressor directly to the generator with a 50amp breaker. The breaker doesn't trip, but the comressor stops after a couple of seconds.
I also thought that I might have used too small gauge wires as it is a long run from the generator to the compressor (35 feet of AWG 10), but after I hooked up directly without the long wire and it's still the same...

Before purchasing the compressor I've checked the current rating, which is 29 amps, so even if the starting current is double, my 6KW genset should be enough...

I'm browsing on the internet for solutions and I might have found something:
Elimia Air Compressor Motor Starter 5 15 20 HP 240V 36A - eBay (item 110656443587 end time May-01-11 14:02:07 PDT)
Anybody knows how this thing works? Is there a chance that this will eliminate my problem?

I also read that it's possible to change the capacitors in the generator for bigger ones, so it will be able to hold the starting current needed...

I appreciate all advice!!!

Thanks,
Tamas
tomicante is offline   Reply With Quote
Old 04-04-2011, 11:31   #17
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

About the inverter...
How can I sync the inverter and the genset?
I thought the inverter will shut down if power comes from the generator.

I have 2 inverters:
1.) MAGNUM true sine wave charger/inverter (100amp/2000W)
2.) XANTREX 1800W inverter

Thanks,
Tamas
tomicante is offline   Reply With Quote
Old 04-04-2011, 11:32   #18
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,339
Images: 241
Re: Need Help! Fischer Panda Generator

Quote:
Originally Posted by tomicante View Post
... Before purchasing the compressor I've checked the current rating, which is 29 amps, so even if the starting current is double, my 6KW genset should be enough ...
Compressor motor starting currents are generally 6 - 8 times running current.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 04-04-2011, 12:24   #19
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

Wow...

The compressor has a capacitor too which probably lowers the needed staring current, so it looks like I just need a little more boost. Playing with it for a day now it started twice. Once it starts no problem with running.

Thanks,
T.
tomicante is offline   Reply With Quote
Old 04-04-2011, 12:50   #20
Registered User

Join Date: Mar 2008
Location: Easton, CT
Boat: MJM 50 Z
Posts: 343
Re: Need Help! Fischer Panda Generator

29A ? Thats huge!
Starting an AC unit that draws 12A would make the 6kw Panda grunt for a second.
That motor is almost 2 HP! I think 16A is about 1HP.
Just too big!
Highlander40 is offline   Reply With Quote
Old 04-04-2011, 13:01   #21
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

It's 2,2KW (about 3HP)...

I've found this on the Fischer-Panda site:

ASB-Automatic Start Booster
An electronically controlled high starting current in the control box. Suitable for all Panda asynchronous generators, to compensate the high starting current of electric motors (i.e air conditioning units etc). ASB should always be chosen if a generator is to be driven by an inductive load (electric motors, air-conditioning units etc). All generators from Panda 8000 up to Panda 14.000 are fitted, as a rule, with ASB as standard.

Mine is a smaller unit (Panda 6000), so originally it's not fitted with this booster. I will see if it's compatible with my unit...

Thanks!
tomicante is offline   Reply With Quote
Old 04-04-2011, 13:14   #22
Senior Cruiser
 
atoll's Avatar

Cruisers Forum Supporter

Join Date: Mar 2010
Location: gettin naughty on the beach in cornwall
Boat: 63 custom alloy sloop,macwester26,prout snowgoose 37 elite catamaran!
Posts: 10,594
Images: 75
Re: Need Help! Fischer Panda Generator

6kw/240 v=25 amps
29 amps/240 v= 6950 watts plus shunt =+/- 12000 watts.
get a bigger genset
atoll is offline   Reply With Quote
Old 04-04-2011, 13:27   #23
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

It's 6KW/120V=50A.
tomicante is offline   Reply With Quote
Old 04-04-2011, 13:32   #24
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

...and the 3HP motor is only 2,2KW = 18A (startup maybe double)...
The factory current rating is 29A, but it doesn't say if it's continous. For me it seems that 29A would be the startup current and I calculate 18A continous.
What do you think?
tomicante is offline   Reply With Quote
Old 04-04-2011, 15:18   #25
Registered User

Join Date: May 2008
Posts: 3,536
Re: Need Help! Fischer Panda Generator

The inverter solution would be to replace one of your inverters with something like the Victron Multiplus inverter/charger. Depending on size about $1600-$2500. These allow the genset power to pass through and when the AC load exceeds a user setting the batteries instantly provide additional amps via the inverter. This can be an additional 3000 watts added to whatever the genset is providing.

This would also let you set the maximum load on the genset to something less than 100% rating which will extend the genset's life.

The Victrons have a lot of other interesting features but it's a fairly pricey solution. Might still be the best idea in the long run. It's top quality gear.

MultiPlus 800VA - 5kVA - Victron Energy


Carl
CarlF is offline   Reply With Quote
Old 04-04-2011, 16:02   #26
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

Thanks, but I've just installed a new charger/inverter, so that would be too pricy solution...
What about a hard start kit (capacitor and relay): Search hard start Hard Start Kits%2C - Grainger Industrial Supply
Do you think it might work?
tomicante is offline   Reply With Quote
Old 04-04-2011, 16:25   #27
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

The compressor manufacturer says that it should run from a 4Kw genset as it has an in buildt capacitor for the startup...
tomicante is offline   Reply With Quote
Old 05-04-2011, 02:42   #28
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 18,951
Re: Need Help! Fischer Panda Generator

Just don't get me started on Fisher Panda gensets... mechanics didn't even want to come near it when mine needed repair. In the end, I had to pay to get it removed from the boat, instead of trading it in for the new Northern Lights ! (this will surely get the pro-FP crowd to post and tell us how good and advanced these units are :-)

I completely agree with CarlF... get a Victron charger/inverter.

You write you don't want a Victron because you just bought something else... but at some point you must start to understand that it's just not gonna work with stuff like what you have/buy. A 6kW Northern Lights genset will run your compressor... your Fisher Panda helped by a Victron "Power Assist" unit (with decent battery bank) will run your compressor. That's two solutions to your problem; I'm afraid there's not gonna be a solution where you don't have to change anything.

ciao!
Nick.
s/v Jedi is offline   Reply With Quote
Old 06-04-2011, 05:33   #29
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,534
Re: Need Help! Fischer Panda Generator

Quote:
...and the 3HP motor is only 2,2KW = 18A (startup maybe double)...
As Gord and others have said, start-up current of a electric motor is an instantaneous 6 to 8 times the full load amps (FLA) rating.

This high current can be mitigated by the addition of a starting capacitor that is in the circuit as the motor starts and comes up to speed and then is switched out of the circuit by a centrifugal switch. A separate run capacitor is always in the circuit to reduce the effects of the running inductive load on the generator.

There are "permanent capacitors" that perform both the start and run functions but these are used on fractional hp motors.

My guess is that the compressor motor has a run capacitor, not a start capacitor. If this is true then changing this capacitor will have no effect on the start up behavior.

The least expensive way out of the generator/compressor mismatch may be to simply change out the compressor motor for one with both a starting and running capacitors.

Quote:
The compressor manufacturer says that it should run from a 4Kw genset as it has an in buildt capacitor for the startup...
Based on the fact that the compressor won't start when power is provided by a genset that meets the compressor mfgr's. specs., I do not think that you have a starting capacitor but you have been given some misinformation from the mfgr. Does the motor have two capacitors mounted on it?

Have you attempted to start the compressor while on shore power? What were the results?

Do you have access to a clamp on ammeter with surge capture capability?

What is the mfgr. and model number of the compressor?

Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 06-04-2011, 13:45   #30
Registered User

Join Date: Nov 2009
Location: circumnavigating
Boat: Dean 5000 sailing catamaran
Posts: 47
Re: Need Help! Fischer Panda Generator

First of all thanks a lot for everybody trying to help me out with this problem! I really appreciate it!

So the comressor is a Coltri Sub MCH-6 EM, 115VAC, single phase, 3HP, 29 Amps continous and 87Amps starting current. and it has 2 capacitors (160mF and 315mF).
My genset's peak is about 80A for a short time, so it's pretty close...
See manufacturer's site: Aerotecnica Coltri - Portable Compressors - MCH-6/EM
I've tried to run it from shore power and it works fine, but from the generator it only moves for a couple of seconds.
I've checked many options on the net, and my last hope is a soft starter. The problem with it that there aren't many single phase soft starters on the market, or they are pretty expensive. The cheapest one is around 1000$.

Thanks,
Tamas
tomicante is offline   Reply With Quote
Reply

Tags
generator, Fischer Panda

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical question Ray Durkee Our Community 7 11-07-2019 04:54
Fischer Panda Owner's Forum geoffschultz Construction, Maintenance & Refit 1 05-03-2011 20:27
Propeller generator Stevek Electrical: Batteries, Generators & Solar 14 22-09-2006 09:35
Portable Generator How-to? Amfivena Electrical: Batteries, Generators & Solar 14 26-07-2006 05:49

Advertise Here


All times are GMT -7. The time now is 15:39.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.