Old 25-10-2013, 01:03   #136
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by sailorchic34 View Post
To add a earth to a IT would defeat part of the safety feature that the IT gives. Its Isolated power, not connected to shore or an earth loop, for goodness sake.
Quote:
Originally Posted by sailorchic34 View Post
That is one of the main reasons to have a isolation transformer after all.
Quote:
Originally Posted by chala View Post
Normally an isolating transformer used for personal safety consist of one isolating transformer and only one outlet then your moon rock theory may hold. One isolating transformer used to supply a complete electrical installation does not offer personal safety.
Quote:
Originally Posted by sailorchic34 View Post
Just to clarify or maybe confuse the issue more.
Please before trying to confuse the issue more try instead to make the difference between a foot and a head.
chala is offline   Reply With Quote
Old 25-10-2013, 01:23   #137
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by Oceanride007 View Post
You say they use these circuits in hospital
I suspect that Gobo got the same problem than Sa34
chala is offline   Reply With Quote
Old 25-10-2013, 01:24   #138
Registered User
 
Oceanride007's Avatar

Join Date: Jun 2013
Location: Up Qld Coast, near Yeppoon.
Boat: Passport 41, Custom Perry in steel.
Posts: 625
Re: Isolating Transformers, The Earth wire connection conundrum

Response to Flying cloud.
I for one will not tell you how to fix this problem, you know plenty. My issue is still with this conundrum thingo.
Ship regs are far tighter than shore regs anywhere. If Classification rules do not provide the safety required then usually statutory (shipstate) will.
On ship its entirely satisfactory for a potential fault to come into existence before you do something about it, and you attend to it soon after.
Class authorities evolved a system that best works for them, they are pretty consistant around the world.
The point is on ship you have means of determining such a state exists, and its not hard to implement, I’ve stated it on previous post re: earth lamps.
For others benefit, there are the usual suspects, if not, keep isolating till you find it. Once found, fix it or put a danger tag on it and make it unavailable till you get the parts/replacement.
Oceanride007 is offline   Reply With Quote
Old 25-10-2013, 01:41   #139
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by Oceanride007 View Post
Personnally I would go the Isolated Transformer way, but there are some of us who insist on RCD devices and lots of work place safety requirements mandate RCD devices to even work on a yacht.
Ocean, what does "Au" stand for in “Melbourne, Au”?
chala is offline   Reply With Quote
Old 25-10-2013, 01:49   #140
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Quote:
Originally Posted by FlyingCloud1937 View Post

I still think most miss my point. In the USA we work against "potential fault" because potentials seem to happen and then someone loses a life.

I have a boat(customer) right now that has a floating IT/Step-up with a Euro 230v range. When plugged into shore all seems to work well, no tingler.

As soon as the shore side is disconnected, and the range is powered by the Diesel-Gen going thru the same IT/Step-Up, touching any part of the range/cooker it's a tingler.

So we have a fault, ie double fault. It's the only load on that circuit, it's wired correctly.

We have a potential that is an actual working fault. go figger

Lloyd
Ground loop internal to the boat. Furthermore the it transforner should not be in front of the generator. iTs should be exclusively shore power feeds as its regarded as a power source. Also such a series connection almost guarantees a ground loop. Bad idea

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 25-10-2013, 01:50   #141
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Quote:
Originally Posted by chala View Post

I suspect that Gobo got the same problem than Sa34
Huh. I'm currently looking at one right this minute in a hospital

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 25-10-2013, 01:54   #142
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Well Chala before you got accusing a reputable person of confusion you should examine this snippet of yours
"
Originally Posted by chala
Normally an isolating transformer used for personal safety consist of one isolating transformer and only one outlet then your moon rock theory may hold. One isolating transformer used to supply a complete electrical installation does not offer personal safety."

Since a boats IT is a single item , its exactly the same as a personal safety issue. Rather then just throwing out unsupported statements you could cogently argue your viewpoint technically

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 25-10-2013, 04:24   #143
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by goboatingnow View Post
Well Chala
Gobo try harder.
chala is offline   Reply With Quote
Old 25-10-2013, 05:19   #144
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by s/v Jedi View Post
I have been writing to use gfci outlets to prevent any of the scenarios incl. the very unlikely, since way back in the thread. The only ones recognizing it are Dave and Dan, who obviously are engineers too. The rest still needs the quarter to fall, or are ignoring it because it would kill their argument they love to repeat
This will require a bonding conductor connected to one of the terminals on the output side of the isolating transformer.

Quote:
Originally Posted by s/v Jedi View Post
I can't bring up the incentive to discuss this silly repeat of having to ground a leg from a transformer or genset and live with a neutral. I will only say that this is the result of ignorance; this has been discussed to death too often now and many boats are 100% safe without a neutral and thus a floating system with two hot's.
In other word this new wiring could be described as having a one Active (Hot1), a Neutral, and an Earth wire.
And if so this will be the result of ignorance. Welcome to the team.
chala is offline   Reply With Quote
Old 25-10-2013, 05:49   #145
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,000
Quote:
Originally Posted by chala View Post
This will require a bonding conductor connected to one of the terminals on the output side of the isolating transformer. In other word this new wiring could be described as having a one Active (Hot1), a Neutral, and an Earth wire. And if so this will be the result of ignorance. Welcome to the team.
Omg Chala. You really have no clue!
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 25-10-2013, 06:28   #146
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by Tantalus View Post
Ya know....you guys are actually agreeing....
On what?
chala is offline   Reply With Quote
Old 25-10-2013, 07:11   #147
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by s/v Jedi View Post
Omg Chala. You really have no clue!
So you got the clue.
Here are two GFCI as you may notice each one have 3 wires. How do you connect them to yours two wires floating wiring?
Attached Thumbnails
Click image for larger version

Name:	GFCI-2.JPG
Views:	177
Size:	18.6 KB
ID:	69276   Click image for larger version

Name:	gfci a.JPG
Views:	150
Size:	39.9 KB
ID:	69277  

chala is offline   Reply With Quote
Old 25-10-2013, 07:46   #148
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by goboatingnow View Post

Its clear that (3) is the preferred ( ABYC) US approach, yet such an approach adds earth as a fault path. ( note not a fault path TO earth). with this system if the secondary HOT ( L) touches anything on the boat and the user touches that, then a fault path to the neutral side of the transformer exists via seawater which causes a shock. ( this assumes the 'thing' is not connected to the protective wire).

What I dont understand is , by deliberately defeating the isolation it reintroduces the swimmer in freshwater risk, as fault currents can now flow through seawater , ie out of one underwater fiting and back through another, especially if the protective wire is poor made or connected.

ABYC, does not like (1) above and to be fair , several other code bodies do not like floating 1:1 POWER transformers. Why?

(b) A rather strange concern ( as Calder as described) of the floating HOT touching an appliance, and raising the potential of that appliance unbeknownst to teh occupant, then a subsequent fault on the other HOT causes the occupant to be inserted into the circuit.

Now this is rather a bizarre claim, and seems to completely ignore two things
(a) A RCD on the secondary side covers this

Which in reality is right.
For an Electrical Engineer you really surprise me. You are supposed to know and understand the above. Not have to ask a forum of cruisers.

Quote:
Originally Posted by goboatingnow View Post
In a true floating system,
, the rcd will do little.
In a full floating system RCDS do virtually nothing
Gobo have you made up your mind, do little or do virtually nothing?

Whatever the answer, you seem to have found a reason for that “ bizarre claim”.
Maybe the ABYC knew that a RCD would do little or virtually nothing.
chala is offline   Reply With Quote
Old 25-10-2013, 08:35   #149
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Isolating Transformers, The Earth wire connection conundrum

Quote:
Originally Posted by transmitterdan View Post
If a contentious owner has multiple such crummy appliances and they are still extremely worried about safety then individual GFI circuits for each appliance will solve this problem.
Any appliance that requires to be earthed may leak or leak continuously. If that appliance cannot leak then the potential of that appliance will raise and so will anything else that is conductive and in contact with the appliance.
Quote:
Originally Posted by goboatingnow View Post
(b) A rather strange concern ( as Calder as described) of the floating HOT touching an appliance, and raising the potential of that appliance unbeknownst to teh occupant, then a subsequent fault on the other HOT causes the occupant to be inserted into the circuit.
chala is offline   Reply With Quote
Old 25-10-2013, 09:12   #150
Registered User

Join Date: Aug 2009
Location: White Stone, VA
Boat: Cabo Rico 38 / Bayfield 32
Posts: 624
Images: 1
Re: Isolating Transformers, The Earth wire connection conundrum

The thing about these threads that I'm sure is very frustrating to many readers is who do you believe? Anybody can say what they like on this forum. However, as I like to remind the junior engineers in my department, though you may be entitled to your own opinions, you're not entitled to your own facts! To Chala, you are disagreeing with a number of electrical engineers with quite a bit of experience in the field. You also make statements which clearly show your lack of understanding. Perhaps it's just terminology differences, but if so, you need to fix your terminology. Some of us have designed power systems in safety critical medical applications (myself for one). Others just seem to have opinions based on what they've seen or based on their own misunderstanding of the subject. Dave (GBN), Jedi, and myself all see the relative merits of a totally isolated AC power system. ABYC is concerned with a much broader audience than electrical engineers. Their standards must reflect that. They must prescribe techniques that provide the safest approach for the broadest audience. This implies simple. In absolute terms, the totally isolated approach is the safest. In broader terms, some analysis may be required to determine that a potential problem exists or what to do about it. ABYC cannot prescribe analysis. They can only prescribe process. For example, if an isolated system yields "tingling" when touched, it's not really isolated (completely). There may be a problem with the transformer, but it's likely a wiring error. There is a leakage path somewhere that is going to require some analysis to nail down. That analysis is difficult to do via internet forum, and even more so via prescribed process. I believe that is the reasoning behind ABYC's standard. As the equipment and methods gain acceptance and standardization, I believe ABYC will come around.

As a follow on discussion, some of us are simply unwilling to add 60 lb. chunk of iron to our boats that is only useful in the planned somewhat rare occasion we are on dock power. For us, I think the best, safest method is whole boat RCD, GFCI's on every branch circuit, no ground to seawater. Opinions?
Saltyhog is offline   Reply With Quote
Reply

Tags
rum


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 21:05.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.