Re: Is it OK to combine different size batteries in the same bank?

Quote:
Originally Posted by wesevans View Post
NO! all the batteries in the same bank need to be the same size and type. If not the batteries will not recharge properly. Also if you have more than one bank it is best to charge them separately unless you have separate charging circuits.
WHY?

Sorry, Wesevans, you are another victim of this often repeated misconception. It is important for batteries in SERIES to be the same size and type and matched as close as possible but it does not apply to batteries in PARALLEL.

Do you have some scientific basis for the statement or did someone mis-advise you too and you feel obliged to pass it on?
__________________

__________________
Andina Marie is offline   Reply With Quote
Old 21-02-2015, 22:13   #17
Senior Cruiser
 
Randyonr3's Avatar

Cruisers Forum Supporter

Join Date: Nov 2007
Boat: Beneteau FIRST 42
Posts: 1,836
Re: Is it OK to combine different size batteries in the same bank?

My understanding is that in charging the batteries, if mis matched, they will only charge to the holding of the smallest battery in the bank.
__________________

__________________
Randyonr3 is offline   Reply With Quote
Old 22-02-2015, 01:11   #18
Marine Service Provider

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 395
Re: Is it OK to combine different size batteries in the same bank?

Quote:
Originally Posted by Randyonr3 View Post
My understanding is that in charging the batteries, if mis matched, they will only charge to the holding of the smallest battery in the bank.
Yes, that misunderstanding carries over from SERIES charging where the same current flows through all the batteries. But the current when charging PARALLEL batteries does not divide 50/50 for two batteries, or 33.3/33.3/33.3 for 3 batteries. In fact each battery only takes current in proportion to its capacity.

In parallel they are all at the SAME voltage. If one gets to fully charged at say 14.2 volts, the other battery has to be at 14.2 volts too.

Think of it as filling a 100 gallon (amp hour) tank connected in PARALLEL at the bottom to a 10 gallon (amp hour) tank that have the same height (voltage). As you fill (charge) them they both remain at the same depth (voltage) until eventually both are full even though one needed 10 times as much CURRENT as the other.
__________________
Andina Marie is offline   Reply With Quote
Old 22-02-2015, 05:59   #19
Registered User
 
TeddyDiver's Avatar

Join Date: Aug 2010
Location: Arctic Ocean
Boat: Under construction 35' ketch
Posts: 1,826
Images: 2
Re: Is it OK to combine different size batteries in the same bank?

Depends.. The difference of the internal resistance of the batteries will ruin the battery bank. If the difference is minor and you have less duty cycles in the time you expect batteries to live then it doesn't matter so much. But be aware..
__________________
TeddyDiver is offline   Reply With Quote
Old 22-02-2015, 06:25   #20
Marine Service Provider

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 395
Re: Is it OK to combine different size batteries in the same bank?

Quote:
Originally Posted by TeddyDiver View Post
Depends.. The difference of the internal resistance of the batteries will ruin the battery bank. If the difference is minor and you have less duty cycles in the time you expect batteries to live then it doesn't matter so much. But be aware..
How can you justify that statement? How will it "ruin" the bank? Batteries don't even "know" that they are in parallel with another, they each respond individually to the voltage on its terminals and carry a load, or charge, at a level corresponding to their internal resistance. They don't get lazy or change capacity just because there happens to be another battery in parallel.

As any battery gets older its internal resistance increases. Corresponding to that its capacity decreases. Eventually you have to make a decision about when to replace it due to loss of capacity. But so long as it is contributing significant capacity you don't replace it because that capacity is less than others in parallel.

A legitimate criticism of batteries in parallel is it is more difficult to know which of the batteries is no longer supplying sufficient capacity to justify its weight and space so a means of isolating them for testing is good practice.
__________________
Andina Marie is offline   Reply With Quote
Old 22-02-2015, 06:49   #21
Moderator
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: North Mississippi
Boat: 48 Wauquiez Pilot Saloon-C22 Chrysler Sunpiper- 19 Potter-Preparing to cruise w/my girl
Posts: 5,980
Re: Is it OK to combine different size batteries in the same bank?

RUDIMENTARY Visualization of parallel v series connection
Attached Thumbnails
Click image for larger version

Name:	Batt connection diagram.jpg
Views:	81
Size:	37.6 KB
ID:	97687  
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Old 22-02-2015, 07:17   #22
Marine Service Provider

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 395
Re: Is it OK to combine different size batteries in the same bank?

Quote:
Originally Posted by HappyMdRSailor View Post
RUDIMENTARY Visualization of parallel v series connection
That's pretty cool but not correct. The parallel drawing is correct but series is not.

When current passes through batteries in series (charging or discharging) it is an equal amount in ALL the batteries. It has to be because there are no exits, what goes in one end must come out the other since there is only one path.

So if you put 50 amps into 3 batteries in series for 2 hours, each battery adds 100 amp hours to its capacity. THIS is where matching of capacity is important because the 100 amp hour battery will become fully charged, the 245 amp hour battery will be only 41% charged and the 65 amp hour battery will be overcharged and gassing excessively as current is forced through it on its way to charging the other two.

The situation is even more critical on discharging.

The 65 amp hour battery will be fully discharged before the other two. When the remaining two continue to force current through the discharged battery you end up reversing the polarity on its weakest cell with -34 volts and rapidly destroying it.

By matching you "hope" they will all discharge uniformly so that they will all be fully discharged at the same time and no cells have enough charge left to destroy another. This NEVER happens and that is why you should never discharge batteries fully so the weakest cell in the chain is fully discharged. When the first cell in the chain is discharged on a 12 volt battery there is 10 volts left to destroy it. But when that happens on a 24 or 36 volt battery there is 22 or 34 volts still available to kill the weakest one.

The chance of matching all 18 cells in a 36 volt battery is much less likely so following the 50% maximum discharge rule to get maximum life is much more important for higher voltage batteries.
__________________
Andina Marie is offline   Reply With Quote
Old 22-02-2015, 07:21   #23
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,060
Re: Is it OK to combine different size batteries in the same bank?

Quote:
Originally Posted by Andina Marie View Post
That's pretty cool but not correct. The parallel drawing is correct but series is not.

When current passes through batteries in series (charging or discharging) it is an equal amount in ALL the batteries. It has to be because there are no exits, what goes in one end must come out the other since there is only one path.

So if you put 50 amps into 3 batteries in series for 2 hours, each battery adds 100 amp hours to its capacity. THIS is where matching of capacity is important because the 100 amp hour battery will become fully charged, the 245 amp hour battery will be only 41% charged and the 65 amp hour battery will be overcharged and gassing excessively as current is forced through it on its way to charging the other two.

The situation is even more critical on discharging.

The 65 amp hour battery will be fully discharged before the other two. When the remaining two continue to force current through the discharged battery you end up reversing the polarity on its weakest cell with -34 volts and rapidly destroying it.

By matching you "hope" they will all discharge uniformly so that they will all be fully discharged at the same time and no cells have enough charge left to destroy another. This NEVER happens and that is why you should never discharge batteries fully so the weakest cell in the chain is fully discharged. When the first cell in the chain is discharged on a 12 volt battery there is 10 volts left to destroy it. But when that happens on a 24 or 36 volt battery there is 22 or 34 volts still available to kill the weakest one.

The chance of matching all 18 cells in a 36 volt battery is much less likely so following the 50% maximum discharge rule to get maximum life is much more important for higher voltage batteries.

+1 Bingo!!!
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 22-02-2015, 09:42   #24
cruiser

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 4,669
Re: Is it OK to combine different size batteries in the same bank?

Quote:
Originally Posted by Andina Marie View Post
That's pretty cool but not correct. The parallel drawing is correct but series is not....................
__________________
rwidman is offline   Reply With Quote
Old 22-02-2015, 11:21   #25
Registered User
 
TeddyDiver's Avatar

Join Date: Aug 2010
Location: Arctic Ocean
Boat: Under construction 35' ketch
Posts: 1,826
Images: 2
Re: Is it OK to combine different size batteries in the same bank?

Quote:
Originally Posted by Andina Marie View Post
How can you justify that statement? How will it "ruin" the bank? Batteries don't even "know" that they are in parallel with another, they each respond individually to the voltage on its terminals and carry a load, or charge, at a level corresponding to their internal resistance. They don't get lazy or change capacity just because there happens to be another battery in parallel.

As any battery gets older its internal resistance increases. Corresponding to that its capacity decreases. Eventually you have to make a decision about when to replace it due to loss of capacity. But so long as it is contributing significant capacity you don't replace it because that capacity is less than others in parallel.

A legitimate criticism of batteries in parallel is it is more difficult to know which of the batteries is no longer supplying sufficient capacity to justify its weight and space so a means of isolating them for testing is good practice.
Something right and something wrong as allways
__________________

__________________
TeddyDiver is offline   Reply With Quote
Reply

Tags
size

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Same Chemistry, Same Age, Different AH Thin Line Electrical: Batteries, Generators & Solar 13 23-02-2015 08:28
Different size batteries in new bank? fallingeggs Electrical: Batteries, Generators & Solar 11 08-12-2014 11:56
Distance of Batteries in the Same Bank S/VSkylark Electrical: Batteries, Generators & Solar 3 31-05-2010 10:46
Same old, same old in the polar regions knottybuoyz Polar Regions 4 07-03-2008 18:44



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 16:42.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.