This world wide reference table illustrates that a cruising yacht must deal with a variety of different electrical standards and plugs.
Mains electricity by country - Wikipedia, the free encyclopedia

And this present thread http://www.cruisersforum.com/forums/...on-137145.html illustrates problems and dangers with modifying AC connecters and plugs.

This got me to thinking, maybe there is a better way to improve on how we connect to different marinas in different countries and verify solution, WITHOUT being dependent on running everything thru a Victron Type Multiplus (whose failure just complicates everything).

I am not a qualified electrician, so feel free to correct me on my rationalization and thinking as to a better but simple system assuming you have an installed AC Generator onboard.

For example my Northern Lights M843NW3:12/10 kW is set up as 4 lead, 1 phase, 50Hz output standard @ 1500 RPM
  • Your onboard AC wiring system and onboard consumers is really designed to handle what your Generator delivers.
  • So you are stuck with that and if moving to different Marina locations, just accept that some stuff will not work unless you have capacity to run thru your invertor or accept as is my case in the Philippines that Hz difference is not that critical (Philippines is strange)
Improving on testing and changing
  • I believe the weak link in connecting to Marina shore power is the closed water-resistant type plugs that are used at Marina Pedestals and the Hubble type fittings we connect to on deck.
  • While we have little choice but to modify our shore cable connection and change plug to fit the Marina’s pedestal, I think the onboard Hubble plug restricts and complicates managing different Marina Supplies.
  • The Hubble type is also the common failure point for heat and arcing of loose connections, deck wash short-outs and is often a vulnerable connection for stepping on.
WHAT IF:
  • You just terminate your inboard shore cable with 4 heavy duty lugs as shown.
  • Then do away with the on deck Hubble plug (Male/ Female) and instead run your shore cable down thru an engine room vent to a protected terminal block and breaker, which is prewired to the Isolation Transformer.
  • As the shore side connection varies, you have the option to connect the 4 or 3 wires as is needed to match what the Isolation Transformer can handle.
  • Once connected and tested hot and correct from the shore supply, you can flip the Mains breaker that feeds to the Isolation Transformer and Main AC Distribution panel.
Obviously this is not as handy a solution for the day sailor who wants to quickly get out for the day and reconnect, but is it something that benefits a transient who will plug in for a month?

Am I missing something?
Attached Thumbnails
Click image for larger version

Name:	PpdLCA3.jpg
Views:	192
Size:	12.3 KB
ID:	92555  
Pelagic is offline   Reply With Quote
Old 29-11-2014, 20:05   #2
Registered User

Join Date: Jul 2008
Location: East about Circumnavigation
Boat: Spray Replica
Posts: 144
Re: Improving on Shore Power Connections

This is the method that ships use when berthed. It actually makes perfect sense. The box could be placed in any waterproof locker with an easy to remove cover.

Garry
sv Spirit of Sobraon
Home Page | Spirit of Sobraon's Travel Log
sobraon is offline   Reply With Quote
Old 30-11-2014, 03:19   #3
Registered User

Join Date: Apr 2006
Posts: 4,413
Re: Improving on Shore Power Connections

Sensible but not practical for those who move about and plug in. (I don't)
Sandero is offline   Reply With Quote
Old 30-11-2014, 04:32   #4
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 33,873
Re: Improving on Shore Power Connections

I think it's an eminently sensible idea . Hard wire the shore power cable to eliminate a big point of failure.

A variant on that would to put the Hubble plug inside your lazarette out of the elements.

In either case, strain relief would be a very important consideration.
Dockhead is offline   Reply With Quote
Old 30-11-2014, 05:04   #5
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Re: Improving on Shore Power Connections

Permanently connect the shipboard end and install one of these: CM-7 - Glendinning Products, LLC.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 30-11-2014, 05:37   #6
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 33,873
Re: Improving on Shore Power Connections

Quote:
Originally Posted by colemj View Post
Permanently connect the shipboard end and install one of these: CM-7 - Glendinning Products, LLC.

Mark
A beautiful thing, but hellish to retrofit. Better suited, I would think, to an original build.
Dockhead is offline   Reply With Quote
Old 30-11-2014, 07:21   #7
Registered User
 
Dennis.G's Avatar

Join Date: May 2011
Location: Sea of Cortez and the U.P. of Michigan
Boat: Celestial 48
Posts: 904
Re: Improving on Shore Power Connections

One problem is that this does nothing about issue of how to plug into the dock end outlet, which still requires the proper plug on the end on the far end of the cable. Still need either a bunch of different cables or adapters onboard anyway.

Although a hassle in some cases, 90% of time plugging in is no issue for my boat. To me, having to hard wire the boat end of cable every time connecting sounds like a hassle and something that presents its own problems (possible hot connection lugs dangling about if other end of cable still energized being one).
Dennis.G is offline   Reply With Quote
Old 30-11-2014, 07:32   #8
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Improving on Shore Power Connections

Quote:
Originally Posted by Dockhead View Post
...... Hard wire the shore power cable to eliminate a big point of failure...............
Perhaps, but this will severely limit your cruising range.

Hard wiring the boat end of the shorepower cable is reasonable (but it complicates things if the cord gets damaged because you can't just go to the marina store and buy a replacement and plug it in), but I think most marinas would get pretty upset if you took the dock pedestal apart and hard wired your power cord in, bypassing the receptacle.

This would also prevent moving your boat quickly in an emergency like a fire on the boat in the next slip.

Sometimes we get what seem to be great ideas but forget or don't understand why things are done the way they are done.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 30-11-2014, 10:58   #9
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Improving on Shore Power Connections

All good points rwidman and I already felt that this was more suited to a roaming cruiser .

I agree you are pretty much forced to buy the matching marina's male plug for their pedestal and rewire your shore side..... But doing away with the exposed boat side large plug is what I hoped to achieve.

This plug always seems to develop internal damages over the years of handling and I thought reducing physical size so that cable with lugs can be run thru a small dorade vent into a dry observable connection point is worth considering.
I felt that this also makes it easier to verify with a meter... that the new marina side plug has been properly wired.

The fire scenario also depends on how you run and secure your shore cable...(bow in or out?) so in my "bow in" case , shore cable runs via pulpit over deck to cockpit plug.

I would always be forced to quickly disconnect from shore side or rip out pedastal plug in an emergency and take my cable with me.
Pelagic is offline   Reply With Quote
Old 30-11-2014, 19:56   #10
Registered User
 
DeepFrz's Avatar

Cruisers Forum Supporter

Join Date: Mar 2006
Location: Winnipeg
Boat: None at this time
Posts: 8,462
Re: Improving on Shore Power Connections

Many large power boats use the Glendinning system. I have often wondered why it isn't incorporated more often in sail boats.
DeepFrz is offline   Reply With Quote
Old 30-11-2014, 20:20   #11
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Improving on Shore Power Connections

On the Superyachts (+50m) we use a power reel like that but much larger to handle +350amps 3 phase 220-440V connected to a step up/down transformer and frequency controller.

One interesting caution was that the Chief Engineer always flaked the cable off of the spool before energizing because of heat and I think winding concerns.

The same problem of matching the shore side plug was even more critical as you could tell by the condition of them that previous customers had bad connections there... creating heat.

My excellent engineer often talked the Marina into bypassing their plug and wiring direct using his own custom waterproof connection box.
Pelagic is offline   Reply With Quote
Old 30-11-2014, 20:47   #12
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Improving on Shore Power Connections

For us non-megayacht guys who only need 30 or 50 amps the Smartplug will solve the boat side of the problem. SmartPlug Systems - Shore Power Products and Accessories

Been using mine for about 3 years and perfect so far. If there is a problem it will be on the dock side connection so at least the fire won't be starting on your boat.

Instead of adapters you can just wire a new plug on the dockside when visiting area with power different than your home country. Of course the boat side will have to go through appropriate electronics to make it work for your system.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 30-11-2014, 21:46   #13
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Improving on Shore Power Connections

That Smart plug is a definite improvement over the twist type that I hate.... Thanks for sharing
Pelagic is offline   Reply With Quote
Old 01-12-2014, 08:01   #14
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Improving on Shore Power Connections

Quote:
Originally Posted by Pelagic View Post
That Smart plug is a definite improvement over the twist type that I hate.... Thanks for sharing
If the Smartplug need any further endorsement, CF member Maine Sail who is almost obsessive about quality and reliability, has endorsed Smartplug.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 01-12-2014, 09:50   #15
Registered User

Join Date: Apr 2013
Posts: 11,002
Re: Improving on Shore Power Connections

If you are parked for months at a time, never leaving the slip, you probably don't need to adapt to other shore power sources...because you never cruise far enough to come across other power sources.

If you actually cruise with any regularity, it's going to be a big hassle rewire the cord every time you move unless you add some type of reel system, which tends to be expensive and bulky on smaller cruisng boats.

Finally the plug is usually the not the primary issue when you come up against a variety of volt/hz combinations.
valhalla360 is offline   Reply With Quote
Reply

Tags
shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Improving Quality of DC Power to Electronics Patrick_DeepPlaya Electrical: Batteries, Generators & Solar 14 16-06-2018 23:56
Leopard 38: Shore Power Connections hikersailor Leopard Catamarans, Robertson & Caine 0 16-08-2014 16:48
Improving Insulation on Existing Fridge / Freezer sailorgal Plumbing Systems and Fixtures 1 17-04-2010 06:21
Looking for Ideas on Improving the Old Ice Box sailvayu Construction, Maintenance & Refit 20 16-11-2009 03:30
Improving Capsize Ratings? Rvrratt Monohull Sailboats 32 25-08-2009 22:12

Advertise Here


All times are GMT -7. The time now is 01:08.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.