Grounding

Power question. I have a big 3000w inverter and 420 amp hour battery's. When I am at the dock the boat is grounded through the shore power cord. When I'm away from the dock, where does the ground current go? Should I be dropping something on the water (fresh water) to better ground? In a residential situation there is a copper rod driven into the ground and connected to the panel box.
amanphoto is offline   Reply With Quote
Old 30-04-2014, 17:17   #2
Registered User

Join Date: Feb 2013
Location: Oregon
Boat: Seafarer36c
Posts: 5,563
Re: Grounding

Quote:
Originally Posted by amanphoto View Post
Power question. I have a big 3000w inverter and 420 amp hour battery's. When I am at the dock the boat is grounded through the shore power cord. When I'm away from the dock, where does the ground current go? Should I be dropping something on the water (fresh water) to better ground? In a residential situation there is a copper rod driven into the ground and connected to the panel box.
What do you need a ground for? You are out there all on your own, self contained. An SSB and perhaps lightning protection would be your only need for a ground. Then of course you have your Zink..
model 10 is offline   Reply With Quote
Old 30-04-2014, 17:20   #3
Registered User

Join Date: Apr 2013
Location: So Cal
Boat: Catalina 387
Posts: 967
Re: Grounding

There should never be _any_ current on ground. It's there for safety. So it pretty much doesn't matter electrically.

Now bonding to thru-hulls and connecting to the 12v system is a different question. (Which has multiple opinions).
jeepbluetj is offline   Reply With Quote
Old 30-04-2014, 17:22   #4
Registered User
 
Reefmagnet's Avatar

Join Date: May 2008
Location: puɐןsuǝǝnb 'ʎɐʞɔɐɯ
Boat: Nantucket Island 33
Posts: 4,864
Re: Grounding

No. There is no such thing as "ground current" in the context of the inverter output. The inverter will most probably have what is referred to as a "floating earth". There are arguments to running an earth wire to, well, the Earth but the cons would at least match the pros, if not exceed them IMO.
Reefmagnet is offline   Reply With Quote
Old 30-04-2014, 17:53   #5
Registered User

Join Date: Mar 2012
Location: Webster, NY, USA
Boat: Monterey, 250CR, 27'
Posts: 28
Re: Grounding

My boat has gfi's. Don't they measure the resistance between neutral and ground to trip them? I just want to make sure I'm not leaking power through my outdrive and desolving it.
amanphoto is offline   Reply With Quote
Old 30-04-2014, 18:05   #6
Registered User
 
Terra Nova's Avatar

Join Date: Apr 2007
Location: Marina del Rey, California
Boat: President 43 Sportfish
Posts: 4,105
Re: Grounding

You don't need to throw a ground rod over the side. A very sensitive voltmeter will tell you if there is potential at your outdrive.
__________________
1st rule of yachting: When a collision is unavoidable, aim for something cheap.
"whatever spare parts you bring, you'll never need"--goboatingnow
"Id rather drown than have computers take over my life."--d design
Terra Nova is offline   Reply With Quote
Old 30-04-2014, 18:13   #7
Registered User
 
Reefmagnet's Avatar

Join Date: May 2008
Location: puɐןsuǝǝnb 'ʎɐʞɔɐɯ
Boat: Nantucket Island 33
Posts: 4,864
Re: Grounding

Quote:
Originally Posted by amanphoto View Post
My boat has gfi's. Don't they measure the resistance between neutral and ground to trip them? I just want to make sure I'm not leaking power through my outdrive and desolving it.
Ground fault interrupters are the tail wagging the dog. They are needed BECAUSE your normal household circuit HAS an inherent unsafe condition in that one of the live wires of your circuit (the neutral) is connected to earth out of necessity. If your boat is constructed of metal or some other conducting material, then there is an argument for doing the same onboard, otherwise a floating earth is just as safe.

I should note that you can think of a "floating earth" as a double insulated circuit. Many appliances are double insulated, having no earth wire connected to their circuits or chassis. I think many would agree that double insulated appliances are safer than the equivalent earthed versions.
Reefmagnet is offline   Reply With Quote
Old 30-04-2014, 18:14   #8
Registered User

Join Date: Feb 2013
Location: Oregon
Boat: Seafarer36c
Posts: 5,563
Re: Grounding

Quote:
Originally Posted by Terra Nova View Post
You don't need to throw a ground rod over the side. A very sensitive voltmeter will tell you if there is potential at your outdrive.
Aluminum boat guys use, I think, something like a silver iode or some such, to make good contact with the water, not the meter lead itself.
model 10 is offline   Reply With Quote
Old 30-04-2014, 20:21   #9
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,390
Re: Grounding

If you have an all chain anchor rode, just connect it to the inboard end of the chain and the anchor will provide a suitable ground back along the seabed.
Can't use while underway of course...





If you don't like this idea, then take the advice of the more helpful posters above






Just in case someone actually wants to do this - don't - it's silly .
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is online now   Reply With Quote
Old 01-05-2014, 01:06   #10
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,659
Re: Grounding

gfi's measure current between hot and N. they work with no ground.

the ground returns back to the inverter where it is connected to N at the inverter. same as a house is more or less.
smac999 is offline   Reply With Quote
Old 01-05-2014, 01:48   #11
Registered User
 
Reefmagnet's Avatar

Join Date: May 2008
Location: puɐןsuǝǝnb 'ʎɐʞɔɐɯ
Boat: Nantucket Island 33
Posts: 4,864
Re: Grounding

Quote:
Originally Posted by smac999 View Post
gfi's measure current between hot and N. they work with no ground.

the ground returns back to the inverter where it is connected to N at the inverter. same as a house is more or less.

GFI's measure the differential current between A & N. The differential comes from current from A finding another path to ground. This means they don't physically need to connect to earth to detect faults.

I find it hard to believe, but I could very well be wrong, that an inverter would have an internal connection between the earth pin and a live wire (there is no real "neutral" output terminal in the sense of that of a poly phase AC neutral) unless it was also fitted with a built in RCD device. To do so would make the inverter borderline dangerous imo.
Reefmagnet is offline   Reply With Quote
Old 03-05-2014, 15:04   #12
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,659
Re: Grounding

Quote:
Originally Posted by Reefmagnet View Post
I find it hard to believe, but I could very well be wrong, that an inverter would have an internal connection between the earth pin and a live wire (there is no real "neutral" output terminal in the sense of that of a poly phase AC neutral) unless it was also fitted with a built in RCD device. To do so would make the inverter borderline dangerous imo.

this is a requirement for north America for marine inverters. it's the same as gennys. they are connected ground to N at the gen.

every source of power.

transfer switches only allow which ever source is being used to have that connection. inverters open and close that connection internally themselves based on weather they are inverting or passing through shore power. because if on shore power the N to G connection is already at the dock. which is the source of power
smac999 is offline   Reply With Quote
Old 04-05-2014, 18:31   #13
Registered User
 
Reefmagnet's Avatar

Join Date: May 2008
Location: puɐןsuǝǝnb 'ʎɐʞɔɐɯ
Boat: Nantucket Island 33
Posts: 4,864
Re: Grounding

Quote:
Originally Posted by smac999 View Post
this is a requirement for north America for marine inverters. it's the same as gennys. they are connected ground to N at the gen.

every source of power.

transfer switches only allow which ever source is being used to have that connection. inverters open and close that connection internally themselves based on weather they are inverting or passing through shore power. because if on shore power the N to G connection is already at the dock. which is the source of power
Well I can't speak for inverters, but I worked for a US company on this side of the globe as an engineer at a time we were being made to do the same thing with alternator generators. We ended up in the ridiculous situation of having to make machines less safe then they previously were because the regulators were, allegedly, unable to get their heads around the concept of "floating earth". To be fair, if you take a single phase generator and shove a whopping great earth stake into the ground beside it that is attached to what now becomes the pseudo neutral, and then test that the stake's electrical resistance is at or below mandated maximums then yes, it is safer. If, on the other hand, you do what most people do with portable equipment and jus' forget about it then you end up with a less safe system. In any event, as manufacturers, we had to include an RCD device into the machine as part of the deal as we were effectively connecting one of the live wires to the chassis and earth of the machines.
Reefmagnet is offline   Reply With Quote
Old 04-05-2014, 20:32   #14
Registered User
 
delmarrey's Avatar

Join Date: Mar 2003
Location: Philippines in the winters
Boat: It’s in French Polynesia now
Posts: 11,368
Images: 122
Re: Grounding

On metal boats you could run the ground to the hull. For plastic boats you have to wet your finger and stick it in the a.
__________________
Faithful are the Wounds of a Friend, but the Kisses of the Enemy are Deceitful! ........
The measure of a man is how he navigates to a proper shore in the midst of a storm!
delmarrey is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
grounding fuel tank capt lar Engines and Propulsion Systems 1 01-09-2005 03:09
Radar Arch Grounding svcattales Marine Electronics 17 22-08-2005 20:43
Fuel Fill Grounding - Imprtant Safety Notice GordMay Electrical: Batteries, Generators & Solar 0 11-08-2005 10:47
Seminar - Grounding vs Bonding GordMay The Library 3 23-07-2005 13:11
Things I learnt from my grounding svstrider The Sailor's Confessional 1 14-10-2003 04:37

Advertise Here


All times are GMT -7. The time now is 02:56.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.