Ground fault on shore power trips

I have a 2002 novatec sundeck trawler.
Have never had a problem with plugging into shore power.
Just had my home dock rebuilt and new wiring code requires a ground fault breaker (in house at breaker box)
Now when I plug in, ground fault blows immediately.
This is with the power selector (in the boat between gen and shore power) turned to off and all breakers in the boat turned off.

Temporarily replaced the new ground fault breaker with a regular one and back to normal.

Thoughts and help appreciated!
Thanks
Panacea2183 is offline   Reply With Quote
Old 13-09-2016, 18:41   #2
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Ground fault on shore power trips

I think the first thing I would check is if the neutral and ground on the yacht are isolated. Unplug the shore power cable from its feed and check between the ground contact and the neutral contact on the shore power cable end. Look up the contact identification on google. Typically L5-30 for a 30 amp 120 volt connection.
Frankly is offline   Reply With Quote
Old 13-09-2016, 22:45   #3
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,661
Re: Ground fault on shore power trips

if it is blowing with the shore power breaker off, assuming you have a double pole breaker. then you have something weird going on, but it should be easy to find as it'll be between the plug and switch / breaker. or it's in the dock wiring.

you should find and fix the problem not just leave the breaker. that means you are leaking power into the water.

if it happened only with the main on then you'd have a lot more to look through on the boat.

I'm thinking it could be a netraul to ground cables swaped somewhere in the dock. and the n from the house is being connected to the ground of the boat.
smac999 is offline   Reply With Quote
Old 13-09-2016, 22:53   #4
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,661
Re: Ground fault on shore power trips

Quote:
Originally Posted by Frankly View Post
I think the first thing I would check is if the neutral and ground on the yacht are isolated. Unplug the shore power cable from its feed and check between the ground contact and the neutral contact on the shore power cable end. Look up the contact identification on google. Typically L5-30 for a 30 amp 120 volt connection.
if he had a N-G bond on the boat it would most likly be after the main breaker, and not show up or cause issues with a double pole switch / breaker off.
smac999 is offline   Reply With Quote
Old 14-09-2016, 05:16   #5
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,339
Re: Ground fault on shore power trips

This may help tracking it down

https://gilwellbear.wordpress.com/20...sts-for-boats/
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 14-09-2016, 05:44   #6
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,394
Images: 241
Re: Ground fault on shore power trips

GFCIs will trip when the load side neutral and equipment grounding conductors are joined, even if there is no ground fault.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 14-09-2016, 07:02   #7
Registered User
 
Steve_C's Avatar

Join Date: Apr 2009
Location: La Rochelle, France
Boat: L42
Posts: 530
Re: Ground fault on shore power trips

Quote:
Originally Posted by GordMay View Post
GFCIs will trip when the load side neutral and equipment grounding conductors are joined, even if there is no ground fault.
As usual GordMay is correct.

If I understand correctly, the new GFCI is located before the main panel on your vessel?

The Neutral and ground are probably tied to a common buss on your boats panel where the main and load breakers are located. These would need to be separated and the Neutral buss cannot be grounded.
__________________
_________________
Steve
www.svfreebird.com
Steve_C is offline   Reply With Quote
Old 14-09-2016, 09:31   #8
Registered User
 
ralter's Avatar

Join Date: Apr 2015
Location: Fort Lauderdale
Boat: Nautor 50 Motorsailer
Posts: 5
Re: Ground fault on shore power trips

My guess beyond those that have been mentioned already is that there is probably a "ground fault buzzer" (or maybe just a light) onboard the boat. What either of those is is a load in the normally unusual place between the grounding (green) and grounded (white) leads on the boat. All that load does is ring a buzzer (or light the light) when there is voltage between those two legs, which there normally should not be. That load however will likely appear to the shoreside GFI breaker as just the kind of leakage that breaker is designed to complain about, and it did. If you have such a buzzer or light, just open-circuit it temporarily to prove that is the problem. If a light, remove the bulb; if a buzzer, lift one leg of it. Then plug in the boat and all should be well.

The only permanent solution I can think of that will maintain compatibility with other places you might want to plug the boat into would be to place a switch in series with that light or buzzer. Then label that switch "Ground fault test". Whenever you plug in, just close that switch temporarily. If the buzzer or light activate, you have a fault. If not, you're fine. If the shore breaker pops, open the switch, reset the shoreside breaker, and trust it for the protection you're looking for.

That's my $.02. Good Luck!
ralter is offline   Reply With Quote
Old 14-09-2016, 14:53   #9
Registered User
 
Panacea2183's Avatar

Join Date: May 2016
Location: Cape Cora, Fl
Boat: 2002 Novatec 42 Sundeck Trawler
Posts: 131
Images: 1
Re: Ground fault on shore power trips

Thanks for all the info
Have not had a chance to trouble shoot yet
But to clear up a few things.
The GFI is in the house at the main panel, it was just installed by the same company that wired the house, very well known co in this area.
I do have a reverse polarity light, and galvanic isolater
New magnasine inverter with neutral switching installed by a pro.

Yes it trips with gen/shore power selector turned to off and main double pole breaker turned off on boat panel, (trips as soon as it is plugged in). That's the weird part as you would think with it off no current would flow?

I suspect my problem lies with the selector switch as it does not appear to change the neutral wire (very hard to see where it is located)
Will dive into it more when I have time.

For now just replaced the breaker in the house with a non GFI unit. (It's been this way for 14 yrs with no problems)
Have a pro scheduled to come out in a week or 2
Panacea2183 is offline   Reply With Quote
Old 14-09-2016, 14:58   #10
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Ground fault on shore power trips

Quote:
Originally Posted by Panacea2183 View Post
Thanks for all the info
Have not had a chance to trouble shoot yet
But to clear up a few things.
The GFI is in the house at the main panel, it was just installed by the same company that wired the house, very well known co in this area.
I do have a reverse polarity light, and galvanic isolater
New magnasine inverter with neutral switching installed by a pro.

Yes it trips with gen/shore power selector turned to off and main double pole breaker turned off on boat panel, (trips as soon as it is plugged in). That's the weird part as you would think with it off no current would flow?

I suspect my problem lies with the selector switch as it does not appear to change the neutral wire (very hard to see where it is located)
Will dive into it more when I have time.

For now just replaced the breaker in the house with a non GFI unit. (It's been this way for 14 yrs with no problems)
Have a pro scheduled to come out in a week or 2
As I suggested on the other forum, the problem could be with the reverse polarity indicating circuit. Remove the bulbs if possible, otherwise, disconnect them. See if that solves your problem.

Most of these indicating circuits are a ground fault by design. A lamp connected between the hot wire and ground to indicate proper polarity.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 14-09-2016, 15:02   #11
Registered User
 
Panacea2183's Avatar

Join Date: May 2016
Location: Cape Cora, Fl
Boat: 2002 Novatec 42 Sundeck Trawler
Posts: 131
Images: 1
Re: Ground fault on shore power trips

Quote:
Originally Posted by rwidman View Post
As I suggested on the other forum, the problem could be with the reverse polarity indicating circuit. Remove the bulbs if possible, otherwise, disconnect them. See if that solves your problem.

Most of these indicating circuits are a ground fault by design. A lamp connected between the hot wire and ground to indicate proper polarity.
Question is if the selector switch is turned to OFF how can any power flow into the boat to trip the GFI?
Panacea2183 is offline   Reply With Quote
Old 14-09-2016, 15:13   #12
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Ground fault on shore power trips

Quote:
Originally Posted by Panacea2183 View Post
Question is if the selector switch is turned to OFF how can any power flow into the boat to trip the GFI?

I think it's because the breaker removes power, yet leaves ground and neutral connected


Sent from my iPad Pro using Cruisers Sailing Forum
a64pilot is offline   Reply With Quote
Old 14-09-2016, 15:37   #13
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Ground fault on shore power trips

Quote:
Originally Posted by Panacea2183 View Post
Question is if the selector switch is turned to OFF how can any power flow into the boat to trip the GFI?
Usually the reverse/no-reverse lights are wired ahead of the selector switch. This is done so you can decide yes or no before final connection using the selector switch in case of a reversal.
DotDun is offline   Reply With Quote
Old 14-09-2016, 16:13   #14
Registered User
 
Panacea2183's Avatar

Join Date: May 2016
Location: Cape Cora, Fl
Boat: 2002 Novatec 42 Sundeck Trawler
Posts: 131
Images: 1
Re: Ground fault on shore power trips

Quote:
Originally Posted by DotDun View Post
Usually the reverse/no-reverse lights are wired ahead of the selector switch. This is done so you can decide yes or no before final connection using the selector switch in case of a reversal.
Good thought I'll check that as well. Although I believe it's wired at the panel.
Panacea2183 is offline   Reply With Quote
Old 15-09-2016, 00:50   #15
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,661
Re: Ground fault on shore power trips

Quote:
Originally Posted by a64pilot View Post
I think it's because the breaker removes power, yet leaves ground and neutral connected


Sent from my iPad Pro using Cruisers Sailing Forum
both his main breaker and Gen / shore switch will cut off both the hot and nuetreal. if wired right. which will also eleminate seeing a N-G issue on the boat... you can't see an N-G bond on that boat if the N is open.

so the issue should be between the house breaker and the boat main breaker or selector switch, and not past that in the boat

the rev light is before the main breaker (though probabbly after his selector switch which is off. also they are supposed to be atleast 10,000 ohms and shouldn't interfere with a GFI.
smac999 is offline   Reply With Quote
Reply

Tags
shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shore Power Problem - Ground Fault or Other Issue ? SailFastTri Electrical: Batteries, Generators & Solar 29 19-03-2017 20:51
GFCI - Ground Fault Breaker Rex Delay Electrical: Batteries, Generators & Solar 26 17-03-2016 13:45
Prosine 2 Ground Fault so34chi Electrical: Batteries, Generators & Solar 0 26-02-2015 19:40
For Sale: Fall Cleaning Sale Marinco Shore Power and Ground Plate velero Classifieds Archive 2 17-10-2013 19:44
Ground fault protector problems tsl Electrical: Batteries, Generators & Solar 6 12-04-2013 15:51

Advertise Here


All times are GMT -7. The time now is 05:25.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.