Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 26-04-2016, 14:38   #1
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Generator starter allowable voltage drop

I'm installing a 4 KW generator. The manual lied to me about the starter ampere, so even though I used a size larger than what based on the manual it is too small.

Anyone have a idea of what starter voltage drop is allowable? I want to calculate for the right cable (not too small, but not too large).

The supplier is now saying the starter is 1.1 KW so that would be 90 amps and I would need a 1 AWG cable to keep voltage drop to under 3%. That seems like a big cable for a little generator.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 26-04-2016, 14:51   #2
Registered User

Join Date: Jul 2015
Posts: 41
Re: Generator starter allowable voltage drop

About 10 volts at the starter during cranking. Any less will affect starter life, more is better.
1 AWG isn't large by battery cable standards. It may be 1.1kw rated but how much is it loaded? 60% ? 80%?
dave948 is offline   Reply With Quote
Old 26-04-2016, 14:58   #3
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Generator starter allowable voltage drop

Quote:
Originally Posted by dave948 View Post
1 AWG isn't large by battery cable standards. It may be 1.1kw rated but how much is it loaded? 60% ? 80%?
Not by battery cable standards, but pretty big for a little generator starter. Apparently it is a secret as to what the load is.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 26-04-2016, 16:44   #4
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator starter allowable voltage drop

Well if it's that important, you can use jumper cables and a clamp on multimeter to measure load.
I would have guessed 100 amps myself, but that's for just a few seconds and you have to assume if it's a single cylinder like mine, it stopped on compression, meaning of course the starter may not get a running start, but immediately have to deal with compression and accelerate the mass of the motor and generator, big flywheel momentum at the same time.

My windlass is I believe 1200 W or 1.2 KW for example.


Sent from my iPad Pro using Cruisers Sailing Forum
a64pilot is offline   Reply With Quote
Old 26-04-2016, 17:54   #5
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Generator starter allowable voltage drop

Quote:
Originally Posted by a64pilot View Post
Well if it's that important, you can use jumper cables and a clamp on multimeter to measure load.
You have a pair of 15' jumper cables?


Back to the question, is there an accepted allowable voltage drop for a starter circuit?
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 26-04-2016, 19:44   #6
Registered User

Join Date: Nov 2013
Location: Slidell, La.
Boat: Morgan Classic 33
Posts: 2,845
Re: Generator starter allowable voltage drop

Don't know an actual number, but in my experience, for a 12V system, I'd say that at somewhere in the range of a .3 -.4 v less than 12.5, you're gonna start getting slow cranking speeds or worse, that dreaded clicking sound...

I'm pretty sure you're supposed to use round trip lengths when calculating wire size, so 1/0 for 91.66 amps at 30 feet doesn't seem so big. This is a very intermittent circuit, so maybe you could get away with something a little smaller, but it starts to look like a false economy pretty quickly.

Can you move the generator starting battery closer?
jimbunyard is offline   Reply With Quote
Old 26-04-2016, 20:16   #7
Registered User
 
leftbrainstuff's Avatar

Join Date: May 2011
Location: San Diego CA
Boat: Liberty 458
Posts: 2,205
Re: Generator starter allowable voltage drop

You may see instantaneous starting voltage drop below 10V.

Loaded starter speed is the limiting factor. Too slow and you wont fire.

If it starts and temp in the starter cables are not greater than ambient will be fine.


Sent from my SM-N900T using Cruisers Sailing Forum mobile app
leftbrainstuff is offline   Reply With Quote
Old 27-04-2016, 03:47   #8
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,448
Images: 241
Re: Generator starter allowable voltage drop

If the available voltage at the starter is not within 0.5 to 1.0 volt of battery voltage, there is excessive voltage drop in the circuit.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 27-04-2016, 04:02   #9
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Generator starter allowable voltage drop

Well I did a few Google searches, rewording the search to get different answers, and read the best sounding hits for the first 4 pages of results. I couldn't really find a actual answer, just "noise". So since this is a critical electrical load I'm going to say the allowable voltage drop is 3% at the max power of the starter (I have the curve).
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 27-04-2016, 04:17   #10
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator starter allowable voltage drop

Quote:
Originally Posted by sailorboy1 View Post
You have a pair of 15' jumper cables?





Back to the question, is there an accepted allowable voltage drop for a starter circuit?

Yes, actually 25' but they were used for farm equipment where you couldn't always get that close. Last truck, I had a large deans connector in the grill so I didn't even have it open the hood, but neither here or there, but if you have cables, they need to be long enough I believe to reach the furthest thing that may need them.
Your generator is 15' from your engine? Cause I'd tap 12v off of the starter solenoid of the big engine as opposed to going all the way back to the bank, plus by tapping off of the solenoid, then your connected to whichever bank the battery switch has selected.
Many will tell you that you need a separate bank for the generator, but those same would tell me I need a separate bank for my Windlass too, and four banks on a 38' boat is I believe excessive.

My run to my 1200W windlass is probably 40' total and #2 wire seems to hold that load fine if that helps.


Sent from my iPad Pro using Cruisers Sailing Forum
a64pilot is offline   Reply With Quote
Old 27-04-2016, 04:28   #11
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Generator starter allowable voltage drop

[QUOTE=a64pilot;2107451]
Your generator is 15' from your engine? Cause I'd tap 12v off of the starter solenoid of the big engine as opposed to going all the way back to the bank, /QUOTE]

closer to 12' by the time it gets neatly routed, and that is tapping off the engine starter
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 27-04-2016, 05:29   #12
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Generator starter allowable voltage drop

Sounds like your getting close
Although I feel guilty about running mine silly as that sounds, it does make things significantly different in the boat, my belief is it makes the boat a whole lot more self sufficient.
a64pilot is offline   Reply With Quote
Old 27-04-2016, 09:55   #13
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Generator starter allowable voltage drop

Quote:
Originally Posted by sailorboy1 View Post
Not by battery cable standards, but pretty big for a little generator starter. Apparently it is a secret as to what the load is.
I can not imagine that type of draw on a starter for a gen. of that size. As fare as load, you don't start a gen. under load. JMHO
Cadence is offline   Reply With Quote
Old 27-04-2016, 14:06   #14
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,419
Re: Generator starter allowable voltage drop

Well it was really 33' round trip. Used 1 AWG cabling and it turns over just fine and started up, then died, started then died, started then died, started then died, started then died. So I started thinking fuel problem and went on a tighten hoses mission. Then it started and got to speed and died, started and died, started then died. So I drained the fuel separator/filter since it is early spring and it always has some water after sitting all winter. Then it started and ran almost 10 seconds at speed, then died, started then died, didn't start, didn't start, didn't start.

So I got pissed off and decided to come home.

I don't know if the line to generator got water in it or what so I'm going to hook a fresh pail and see what will happen. Looking through the manual again it may be that I'm at the extreme limit of the fuel line length. I didn't really notice that as I figured as long as the suction lift wasn't a problem it would be OK, but who knows.

But I've drifted way off topic and am venting
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 27-04-2016, 15:12   #15
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Generator starter allowable voltage drop

Some have a low oil switch, both pressure and quantity if it's not fuel delivery issues.
I first tapped fuel supply into the extra bungs in my fuel tank, it would always start, then run slowly for awhile and maybe die and have to be restarted and on the second attempt continue to run.
I have since tied into the main fuel Racor filter which cut fuel line length in half and since then it starts and runs like it should.
I think installing an electric fuel pump as a boost pump will confirm if it's just too long a fuel line run.


Sent from my iPad Pro using Cruisers Sailing Forum
a64pilot is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Allowable Ship Stores while in CUBA Nomad 1 Atlantic & the Caribbean 15 17-12-2015 13:30
78 pearson 30 maximum allowable prop size simplynick912 Propellers & Drive Systems 8 26-02-2013 16:11
Cutlass bearing shot, what is max shaft wear allowable ? Jd1 Engines and Propulsion Systems 7 23-07-2012 19:20
Allowable Chart Folder / Subfolder Structure paul2 OpenCPN 6 27-12-2010 22:32
Windchargers and Voltage Drop Question 4 Experts. dkall Electrical: Batteries, Generators & Solar 6 25-03-2008 21:34

Advertise Here


All times are GMT -7. The time now is 16:40.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.