generator question 230v 50htz gen to 110 system?

Boat is a leopard38 the panel is a factoryupgraded panel with 2 30Amp cords on the panel it has shore 1 and shore 2 and generator 1&2. We have a 6kw mastervolt whispergen on our new boat. The tag says it is a 230v 50 htz generator. When running it and we switch over the panel to generator itis putting out 105-110 on each side. Spoke to the makers of the generator amd they say its impossible for a 230v 50htz gen to power a 110 system. So either the gen is tagged wrong or they are wrong. Does anyone have another idea? I just want to makesure everything copasthetic. The webasto ac units say they can run on 50 htz no problem
Dulcesuenos is offline   Reply With Quote
Old 20-03-2014, 05:49   #2
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: generator question 230v 50htz gen to 110 system?

Well it is possible to get 110V from a 230V 50 Hz generator but would require a separate AC transformer. You cannot get 110 directly from the generator.

The European 230V is one hot wire and one neutral wire. The US "220V" is two hot wires and one neutral. Each hot wire is 110V between that hot wire and neutral or 220V between the two hot wires. So US 220 can be split but European 230 cannot.

I would get a meter and frequency counter to check the generator output but seems unlikely that the name plate on the generator would be wrong. Is it possible the boat has a transformer that converts the 230 to 110?
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 20-03-2014, 09:01   #3
Registered User
 
Lancerbye's Avatar

Join Date: Mar 2007
Location: Cormorant Island, BC, Canada
Boat: Lancer 44 Motorsailer
Posts: 1,877
Images: 38
Re: generator question 230v 50htz gen to 110 system?

Changing the 50Hz to 60 Hz is a matter of adjusting the speed control to produce 60Hz. Once you have done that you will also notice a higher output. 110 will approach 120. Using a 240 to 240 secondary center tapped you will basically have the same set up as what is delivered in North America. The downside is that when you run appliances on 120 rather than 240 the current required to do the same work doubles and the wiring to your recepticles may be too light. On the other hand many generators have tap outs that can be changed to get different voltages. So if you are measuring it , someone may have already changed it and not changed the tag.
__________________
The basis of accomplishment is in never quitting
Mengzi Meng-tse
Lancerbye is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
230v to 12v 100A+ bulk charger on the cheap SVI Electrical: Batteries, Generators & Solar 0 22-09-2013 14:35
12v Freezer; 230v Watermaker DAVID SHAW Plumbing Systems and Fixtures 0 02-09-2012 16:45
For Sale or Trade: Generator 1cyl. 230v-50htz rossny Classifieds Archive 1 27-06-2012 09:52
230v & 120v Inverter/Chargers nhschneider Electrical: Batteries, Generators & Solar 1 22-03-2012 14:14
120V-230V Installation sanity check pbouchar Electrical: Batteries, Generators & Solar 9 14-01-2008 11:12

Advertise Here


All times are GMT -7. The time now is 20:53.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.