So some may have read another thread about my generator voltage, but I hope for a more focused crowd response.

My generator is putting out too low a voltage and things are pointing to the capacitor. In a couple of days I'm going to be in a town that has a chance of having a replacement capacitor so I will be "getting into" it them.

My question is how many have replaced there generator capacitor with a different rated one to increase the voltage. If you have what did you change from and to (my is spec'd for 31uF 450V), what was the voltage before and after, how long has you generator ran since the change?

I ask as there are mixed search results that say it is ok to increase the uF size to increase voltage (but a lower value than spec'd will give low voltage).

I want my voltage "right" but not at the expense of burning out the generator.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 24-06-2018, 14:31   #2
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator Capacitor

I know I answered before, but I went from a printed on the cap value of 35 to a printed on the cap value of 40, voltage went up I think about 10, maybe as much as 15. I was running low 100’s as in single digits, and am now running right at 120.
Since your last thread had me discovering that my Fluke 115 could measure UF value, which I didn’t know, I measured the original cap that I replaced and had printed on it 35 was really right at 30. It’s now in the trash.
I assume as it got old, it lost its value and of course finally got so bad I needed to do something. Maybe your is the same? Maybe take you old one with you, they may can measure it? Maybe you just need a new one, not change value? I can tell you though that my air conditioner and other electric motors seem to “like” the higher voltage and seem to run cooler and the compressors are quieter.
I have not measured the one in the generator, but it’s supposed to be a 40. Maybe if I had just put in a new 35, I would be running at 110V?
I can confirm that on my generator that increasing UF value increased voltage. If I were you I think I would get a 31 and a 35. I’d try the 31 first.
On my generator it’s real easy to change a cap. Mine did not seem to hold a charge, but of course be careful.

My generator according to Nexgen calls for a 40, but mine had a 35, leaving me to assume the actual generator manufacturer bench tests the things and maybe will “trim” each one by changing UF value a little. I bet mine with a real 35 runs just a bit low, and with a 40, just a bit high.

It’s been a couple of years and I think about 300 hours. I believe if you stay around the 110 to 120 ish V range, your in spec.
a64pilot is offline   Reply With Quote
Old 24-06-2018, 14:34   #3
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator Capacitor

Many caps are meant for HVAC use and will come as 30+5 or 40+5 etc. that extra cap, the +5 is meant I believe for the fan on a HVAC unit and I believe you can just ignore it. If your going to a real HVAC store etc., they would know for sure.
It may be a little harder to get just a 31 or 35 single motor run cap.


On edit, I know he is looking for people other than me who has changed capacitance on their cap regulated generators, so any that have please speak up. Someone else had a couple of years ago when I posted about it.
a64pilot is offline   Reply With Quote
Old 24-06-2018, 17:44   #4
S/V rubber ducky
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: heading "south"
Boat: Hunter 410
Posts: 20,362
Re: Generator Capacitor

I can measure the cap of the installed one. The purpose of the thread is to gather info because I want to fix the issue on the first try. If that means I buy a couple of captors just to throw them away that’s fine as it’s cheap compared to my time and costs of sitting around. I think my problem goes back 20 months, but I don’t recall ever seeing my generator make120V.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 24-06-2018, 17:54   #5
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,241
Re: Generator Capacitor

Be aware there is wide variation of tolerances in capacitor values. Many are + / - 20%.
Look for precision caps if you can; better than say %5.

Or take your meter with you when you buy.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 24-06-2018, 17:55   #6
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Generator Capacitor

I’d just guess that target voltage is 115 with plus or minus 5 being good.
Mine will run a little higher not under a load and drop a little as you put a load on it, the Governor isn’t perfect, it slows a little. I have forgotten how much, but its at least 1HZ. I think I run about 61 Hz unloaded and 59 loaded. I have adjusted that too, as it broke in, it slowed down some, or maybe the Governor springs just got a little weaker with age? Voltage does follow Hz, it slows down and drops voltage.
Have you measured your cap? if it’s good then I’d suggest you go up the next size, whatever that is and buy one size larger than that too.
I got lucky and a 40 worked, but I suspect that a good 35 was acceptable too, just mine went bad. I got mine on Amazon.
I have done a little reading and study in HVAC systems as I’m licensed and in that world OEM caps are often poor quality and don’t last long, get a good GE cap if you can, or I have heard a Supco isn’t bad either.
I’d take my meter with me and measure the new one too.
a64pilot is offline   Reply With Quote
Old 24-06-2018, 22:01   #7
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Generator Capacitor

My generator has several leads for the capacitor. Each lead is for a different voltage. Do you have the generator manual? It should tell you what capacitor and how to connect it to get different voltages.
transmitterdan is offline   Reply With Quote
Old 27-06-2018, 16:38   #8
S/V rubber ducky
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: heading "south"
Boat: Hunter 410
Posts: 20,362
Re: Generator Capacitor

I haven’t checked my capacitor yet because I’m still not somewhere I can get a replacement so touching it is asking for trouble. I must not be doing a good Amazon search as I expected a bunch of choices, but only seeing 2 for 31.5uF 450v ones.

But a quick math check shows that 31.5 @ +5% labeled and a 35 labeled @ -5% are almost the same.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 27-06-2018, 17:16   #9
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator Capacitor

I see many 30 and 35, seems 31 or 31.5 to be an unusual spec.

I think unless your going to be somewhere for long enough to be Amazon delivery, a good HVAC supply house is your best bet. These things are motor run capacitors and are very common in HVAC systems, used usually for the compressor and often the condenser fan.
If you end up with one with three posts and called say a 30 +5. The three posts should be labeled herm, C, and fan.
The one labeled fan, ignore, it’s for the fan motor on a HVAC system, the C and herm connect to the compressor and are the ones you want to connect to. A cap with a +5 or +3 or whatever is actually two caps in one tube, but as that is what is usually called for, it may not be easy to find a single cap, you may have to settle with a dual cap and ignore the fan connector.
a64pilot is offline   Reply With Quote
Old 27-06-2018, 18:22   #10
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator Capacitor

This may be if some interest to you. I was curious as to what the voltage at the outlet inside of a home in the US is supposed to be, cause we call it 110,115, and 120 interchangeably.
Click image for larger version

Name:	IMG_0392.jpg
Views:	456
Size:	192.2 KB
ID:	172615
a64pilot is offline   Reply With Quote
Old 27-06-2018, 18:42   #11
S/V rubber ducky
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: heading "south"
Boat: Hunter 410
Posts: 20,362
Re: Generator Capacitor

Yeah but my generator is going below 95 and that causes my battery charger to cycle
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 27-06-2018, 22:03   #12
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Generator Capacitor

Try putting a resistive load such as a water heater or toaster on when the charger is running. Does the voltage go up or down?
transmitterdan is offline   Reply With Quote
Old 28-06-2018, 00:35   #13
Marine Service Provider

Join Date: Nov 2017
Posts: 18
Re: Generator Capacitor

Because capacitors are pure capacitive loads, capacitive currents raise the voltage at the capacitor terminals (the so-called "lift" phenomenon). So the rated voltage of the capacitor is higher than the voltage of the system.


In practice, when the current increases, the prime mover will increase the input energy, and the generator excitation current will continue to increase, keeping the voltage unchanged, when the prime mover exceeds the maximum power, or when the excitation current reaches the maximum, The current can no longer be increased, otherwise the voltage will decrease, the frequency will drop, and the serious will have to load or shut down, because the generator does not meet the load of electricity, is not allowed. That will lead to abnormal measuring instruments and electrical equipment, serious possible accidents, so the state has regulations, power plants must be in accordance with the national standard of power generation.
shelleyWendert is offline   Reply With Quote
Old 28-06-2018, 04:04   #14
S/V rubber ducky
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: heading "south"
Boat: Hunter 410
Posts: 20,362
Re: Generator Capacitor

Quote:
Originally Posted by transmitterdan View Post
Try putting a resistive load such as a water heater or toaster on when the charger is running. Does the voltage go up or down?
Voltage goes up with just a resistance load. I just looked at the spreadsheet of my readings again and I think the voltage is running lower than when I took them a few weeks ago.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 28-06-2018, 10:17   #15
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Generator Capacitor

Quote:
Originally Posted by sailorboy1 View Post
Voltage goes up with just a resistance load. I just looked at the spreadsheet of my readings again and I think the voltage is running lower than when I took them a few weeks ago.
Then most likely the capacitor you have now is drifting down in capacitance. You should try to find the exact type as original and replace the one that is failing apparently rapidly.

There are 2 things that murder capacitors in generators. The first is heat, the second is voltage. The voltage on the capacitor is not the same as the output voltage of the generator. It is much higher than that. Be sure you get a capacitor with the same or higher voltage and temperature rating.

It is ok to mount the capacitor somewhere outside the generator as long as you make sure no one can touch the terminals and that the capacitor case is grounded. It may help longevity to put the capacitor in a cooler place.
transmitterdan is offline   Reply With Quote
Reply

Tags
generator

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What Does the Capacitor in a Generator Do? scoobert Electrical: Batteries, Generators & Solar 16 28-07-2013 03:21
Start-up Capacitor for Honda Genset ? Chief Engineer Electrical: Batteries, Generators & Solar 8 27-11-2011 05:05
Zener Diode or Capacitor with mcck Onan Control-o-Matic Genset? sdowney717 Electrical: Batteries, Generators & Solar 0 22-11-2011 09:02
Need a new capacitor in Panama Meck Electrical: Batteries, Generators & Solar 4 19-03-2011 18:38
Split Capacitor on Windlass Motor Terminals - Why? Zul Anchoring & Mooring 2 16-11-2009 08:14

Advertise Here


All times are GMT -7. The time now is 20:52.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.