Generator: 115 / 220vac at the Same Time

I have a new westerbeke 7.6 D-Net and will replace my old 7.6 Btd. The boat is wired for 115v.I recently bought a Bauer Jnr dive compressor that is 220v.Can i install it with a dedicated 220 v power supply from the genset and be able to use it by switching a breaker/switch.In other words can my genset supply 220v and 115v by throwing a switch ?I will only use the 220v for the compressor and i presume the switch will isolate the 220v poiwer to the wires/supply to the compressor only.
I am all ears sparky's
__________________

__________________
Overlord is offline   Reply With Quote
Old 04-06-2011, 20:43   #2
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: San Francisco Bay
Boat: research vessel
Posts: 10,150
Re: Generator 115/220v at same time

There are generators that can produce both 120 and 240. What are the specs for your generator? You do not need a 1:2 step up transformer if your generator can produce 240. You also want to make sure your generator has the power to operate your dive compressor. As you double your voltage your amps will halve minus the loss from inefficiency from your power supply.

On a 240 volt generator putting together the L1 and L2 legs produce 240.
__________________

__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 04-06-2011, 20:48   #3
Registered User

Join Date: Nov 2008
Posts: 407
Re: Generator 115/220v at same time

Its a 7.6 kw generator,digital.The compressor is a 2.5 kw ,220v motor
__________________
Overlord is offline   Reply With Quote
Old 04-06-2011, 20:51   #4
Registered User

Join Date: Nov 2008
Posts: 407
Re: Generator 115/220v at same time

correction , 2.2 kw compressor motor. 220v motor. How many amps will this draw ?
__________________
Overlord is offline   Reply With Quote
Old 04-06-2011, 21:20   #5
Registered User
 
Sand crab's Avatar

Join Date: Oct 2010
Location: Gig Harbor, WA
Boat: 34' Crowther tri sold 16' Kayak now
Posts: 3,157
Re: Generator 115/220v at same time

10 amps but compressors draw more on startup. Ohms law calculator here.
Electrical & Electronics, Ohm's Law, Formulas & Equations
When you double the voltage you halve the amps so you end up with about 34 amps at 220 which should kick the compressor over no problemo provided you have the correct wiring and breaker to it. The crazy thing is that a higher voltage decreases the amps which is the true juice so you can now use smaller wire, In this case 12 ga would be fine. BOB
__________________
Sand crab is offline   Reply With Quote
Old 04-06-2011, 21:27   #6
Registered User

Join Date: Nov 2008
Posts: 407
Re: Generator 115/220v at same time

Got it .Thanks.Any idea how much more the start up amps are ? Specs on generator sayWire Power Factor KW RPM Start
7.6 EDT-614* 120/240 63.3/31.7 amps 60
* Adjustable to 50 or 60 Hertz.
5.7 EDT-514* 230 24.8 amps 50
__________________
Overlord is offline   Reply With Quote
Old 04-06-2011, 21:32   #7
Elvish meaning 'Far-Wanderer'
 
Palarran's Avatar

Cruisers Forum Supporter

Join Date: Jan 2008
Location: Me - Michigan / Boat - Tenerife
Boat: 56' Fountaine Pajot Marquises
Posts: 2,641
Re: Generator 115/220v at same time

I run my Bauer Junior 220v off a 8kw with no problem at all. Don't worry.
__________________
Not all who wander are lost

http://www.sailblogs.com/member/palarran/
Palarran is offline   Reply With Quote
Old 04-06-2011, 21:40   #8
Registered User
 
Sand crab's Avatar

Join Date: Oct 2010
Location: Gig Harbor, WA
Boat: 34' Crowther tri sold 16' Kayak now
Posts: 3,157
Re: Generator 115/220v at same time

Might be up to 50% more amps. See if the compressor states it. A 20 amp 220 breaker should handle it. BOB
__________________
Sand crab is offline   Reply With Quote
Old 04-06-2011, 22:06   #9
Registered User
 
Capn Morgan's Avatar

Join Date: Jul 2009
Location: South East Asia
Boat: Hans Christian 48T
Posts: 381
Re: Generator 115/220v at same time

Quote:
Originally Posted by chris smith View Post
I have a new westerbeke 7.6 D-Net and will replace my old 7.6 Btd. The boat is wired for 115v.I recently bought a Bauer Jnr dive compressor that is 220v.Can i install it with a dedicated 220 v power supply from the genset and be able to use it by switching a breaker/switch.In other words can my genset supply 220v and 115v by throwing a switch ?I will only use the 220v for the compressor and i presume the switch will isolate the 220v poiwer to the wires/supply to the compressor only.
I am all ears sparky's
There is an interesting setup here for 110/220:

From My Design to My Installation: New AC Power System
__________________
Capn Morgan
'If you can fill the unforgiving minute with sixty seconds' worth of distance run...'
Capn Morgan is offline   Reply With Quote
Old 05-06-2011, 05:37   #10
Registered User

Join Date: Dec 2008
Location: Oriental, NC
Boat: Mainship Pilot 34
Posts: 1,429
Re: Generator 115/220v at Same Time

It can be done but it will take some rewiring of your boat. The simplest way is to configure your genset to produce 240 volts (wire the two coils in series) with a neutral so also you get 120 betweeen L1 or L2 and neutral. Currently it sounds like your genset is configured where both coils are wired in parallel to produce 120V.

But here is where it gets a little complicated. You now have two 120 systems. Each will produce half of the wattage of the genset. And they can't be paralleled. You have to wire each 120 system independently to your AC distribution panels and keep them separate.

Often an air conditioner is on one system and convenience outlets are on another. The idea is to try to balance the loads between the two 120 volt systems.

It is exactly like what you have on your home AC distribution system.

YOu will also need a 240 V breaker dedicated to your dive compressor.

A good marine electrician should be able to fix you up.
__________________
djmarchand is offline   Reply With Quote
Old 05-06-2011, 07:41   #11
Registered User

Join Date: Feb 2009
Posts: 1,321
Re: Generator 115/220v at Same Time

Quote:
Originally Posted by chris smith View Post
In other words can my genset supply 220v and 115v by throwing a switch ?
It all depend what type of voltage regulator your genset is fitted with.
Check with the manufacturer.
__________________
chala is offline   Reply With Quote
Old 05-06-2011, 08:54   #12
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: San Francisco Bay
Boat: research vessel
Posts: 10,150
Re: Generator 115/220v at Same Time

Chris,
Does your generator natively produce 240 or not? The answer makes a huge difference in how you would make this work.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 05-06-2011, 10:13   #13
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Cowes (Winter), Baltic (Summer) (the boat!); somewhere in the air (me!)
Boat: Cutter-Rigged Moody 54
Posts: 19,726
Re: Generator 115/220v at Same Time

Guys, make sure you consider how many phases. 240v three phase has nothing whatsoever to do with 230v or 220v single phase.

So if the generator natively produces 240v three phase (giving you 120v single phase on either phase), you will not be able to power a 230v single phase (European power) dive compressor. Or vice versa.
__________________
Dockhead is offline   Reply With Quote
Old 05-06-2011, 20:45   #14
Registered User

Join Date: Jun 2009
Location: STX and Portland, until refit finished
Boat: 1999 Steel (Tom Collin's design)
Posts: 371
Re: Generator 115/220v at Same Time

Dockhead,

240V in the US is NOT 3 phase. 3 phase has 3 hot wires, with each wire exactly 120 degrees out of phase of the other two. It also typicaly has a ground, and a neutral. It is very unusual to find a 3 phase generator on a boat. Typicaly the only reason to have 3 phase current is with VERY large electric motors.

240V in the US has only 2 hot wires. They are both hot, but have the voltage 180 degrees out of phase with each other, so that the differental is 240 volts. It also typicaly has a neutral.

According to the following website, the Westerbeke 7.6 EDT D-NET 7.5 is wired to provide 120 and 240 V US style current. It might already be wired into the boats wireing system, and just require the proper breakers and wireing in the boats main breaker box.

I can't find a specification for dive compressor. Depending on the specs, it might be quite easy. There are apperently 3 phase version, which would be very difficult to wire in. There are single phase 240V versions that might be quite easy, and 120V versions. Depending on which one you have, it could be easy, or hard.
__________________
ViribusUnitis is offline   Reply With Quote
Old 05-06-2011, 21:24   #15
Senior Cruiser
 
Lancerbye's Avatar

Cruisers Forum Supporter

Join Date: Mar 2007
Location: Ladysmith,BC, Vancouver Island , Canada
Boat: Lancer 44 Motorsailer
Posts: 1,757
Images: 32
Re: Generator 115/220v at Same Time

Quote:
Originally Posted by ViribusUnitis View Post
Dockhead,

240V in the US is NOT 3 phase. 3 phase has 3 hot wires, with each wire exactly 120 degrees out of phase of the other two. It also typicaly has a ground, and a neutral. It is very unusual to find a 3 phase generator on a boat. Typicaly the only reason to have 3 phase current is with VERY large electric motors.
Sorry I couldn't leave it alone. Most boats and cars do actually have 3 Phase generators in them. They are often called altenators. LOL You can make small ac systems by removing the rectifiers and wiring them either Delta or wye configuration.
__________________

__________________
The basis of accomplishment is in never quitting
Mengzi Meng-tse
Lancerbye is offline   Reply With Quote
Reply

Tags
generator

Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buy Owners Time Devilsrule2004 Atlantic & the Caribbean 5 04-02-2012 14:01
Time and Tide Clocks sailormoon Navigation 17 04-10-2011 14:45
Documenting Sea Service Time Mariners Commercial Posts 1 03-10-2011 09:50
Stories Lost in Time . . . Randyonr3 Off Topic Forum 13 31-07-2011 13:22



Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -7. The time now is 23:41.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.