Generator: 115 / 220vac at the Same Time

I have a new westerbeke 7.6 D-Net and will replace my old 7.6 Btd. The boat is wired for 115v.I recently bought a Bauer Jnr dive compressor that is 220v.Can i install it with a dedicated 220 v power supply from the genset and be able to use it by switching a breaker/switch.In other words can my genset supply 220v and 115v by throwing a switch ?I will only use the 220v for the compressor and i presume the switch will isolate the 220v poiwer to the wires/supply to the compressor only.
I am all ears sparky's
Overlord is offline   Reply With Quote
Old 04-06-2011, 19:43   #2
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Generator 115/220v at same time

There are generators that can produce both 120 and 240. What are the specs for your generator? You do not need a 1:2 step up transformer if your generator can produce 240. You also want to make sure your generator has the power to operate your dive compressor. As you double your voltage your amps will halve minus the loss from inefficiency from your power supply.

On a 240 volt generator putting together the L1 and L2 legs produce 240.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 04-06-2011, 19:48   #3
Marine Service Provider

Join Date: Nov 2008
Posts: 482
Re: Generator 115/220v at same time

Its a 7.6 kw generator,digital.The compressor is a 2.5 kw ,220v motor
Overlord is offline   Reply With Quote
Old 04-06-2011, 19:51   #4
Marine Service Provider

Join Date: Nov 2008
Posts: 482
Re: Generator 115/220v at same time

correction , 2.2 kw compressor motor. 220v motor. How many amps will this draw ?
Overlord is offline   Reply With Quote
Old 04-06-2011, 20:20   #5
Registered User
 
Sand crab's Avatar

Join Date: Oct 2010
Location: Gig Harbor, WA
Boat: 34' Crowther tri sold 16' Kayak now
Posts: 5,067
Re: Generator 115/220v at same time

10 amps but compressors draw more on startup. Ohms law calculator here.
Electrical & Electronics, Ohm's Law, Formulas & Equations
When you double the voltage you halve the amps so you end up with about 34 amps at 220 which should kick the compressor over no problemo provided you have the correct wiring and breaker to it. The crazy thing is that a higher voltage decreases the amps which is the true juice so you can now use smaller wire, In this case 12 ga would be fine. BOB
Sand crab is offline   Reply With Quote
Old 04-06-2011, 20:27   #6
Marine Service Provider

Join Date: Nov 2008
Posts: 482
Re: Generator 115/220v at same time

Got it .Thanks.Any idea how much more the start up amps are ? Specs on generator sayWire Power Factor KW RPM Start
7.6 EDT-614* 120/240 63.3/31.7 amps 60
* Adjustable to 50 or 60 Hertz.
5.7 EDT-514* 230 24.8 amps 50
Overlord is offline   Reply With Quote
Old 04-06-2011, 20:32   #7
Elvish meaning 'Far-Wanderer'
 
Palarran's Avatar

Join Date: Jan 2008
Location: Boat - Greece - Me - Michigan
Boat: 56' Fountaine Pajot Marquises
Posts: 3,489
Re: Generator 115/220v at same time

I run my Bauer Junior 220v off a 8kw with no problem at all. Don't worry.
__________________
Our course is set for an uncharted sea
Dante
Palarran is offline   Reply With Quote
Old 04-06-2011, 20:40   #8
Registered User
 
Sand crab's Avatar

Join Date: Oct 2010
Location: Gig Harbor, WA
Boat: 34' Crowther tri sold 16' Kayak now
Posts: 5,067
Re: Generator 115/220v at same time

Might be up to 50% more amps. See if the compressor states it. A 20 amp 220 breaker should handle it. BOB
Sand crab is offline   Reply With Quote
Old 04-06-2011, 21:06   #9
Registered User
 
Capn Morgan's Avatar

Join Date: Jul 2009
Location: South East Asia
Boat: Hans Christian 48T
Posts: 381
Re: Generator 115/220v at same time

Quote:
Originally Posted by chris smith View Post
I have a new westerbeke 7.6 D-Net and will replace my old 7.6 Btd. The boat is wired for 115v.I recently bought a Bauer Jnr dive compressor that is 220v.Can i install it with a dedicated 220 v power supply from the genset and be able to use it by switching a breaker/switch.In other words can my genset supply 220v and 115v by throwing a switch ?I will only use the 220v for the compressor and i presume the switch will isolate the 220v poiwer to the wires/supply to the compressor only.
I am all ears sparky's
There is an interesting setup here for 110/220:

http://www.cruisersforum.com/forums/...tem-29667.html
__________________
Capn Morgan
'If you can fill the unforgiving minute with sixty seconds' worth of distance run...'
Capn Morgan is offline   Reply With Quote
Old 05-06-2011, 04:37   #10
Registered User

Join Date: Dec 2008
Location: Oriental, NC
Boat: Mainship Pilot 34
Posts: 1,461
Re: Generator 115/220v at Same Time

It can be done but it will take some rewiring of your boat. The simplest way is to configure your genset to produce 240 volts (wire the two coils in series) with a neutral so also you get 120 betweeen L1 or L2 and neutral. Currently it sounds like your genset is configured where both coils are wired in parallel to produce 120V.

But here is where it gets a little complicated. You now have two 120 systems. Each will produce half of the wattage of the genset. And they can't be paralleled. You have to wire each 120 system independently to your AC distribution panels and keep them separate.

Often an air conditioner is on one system and convenience outlets are on another. The idea is to try to balance the loads between the two 120 volt systems.

It is exactly like what you have on your home AC distribution system.

YOu will also need a 240 V breaker dedicated to your dive compressor.

A good marine electrician should be able to fix you up.
djmarchand is offline   Reply With Quote
Old 05-06-2011, 06:41   #11
Registered User

Join Date: Feb 2009
Posts: 1,315
Re: Generator 115/220v at Same Time

Quote:
Originally Posted by chris smith View Post
In other words can my genset supply 220v and 115v by throwing a switch ?
It all depend what type of voltage regulator your genset is fitted with.
Check with the manufacturer.
chala is offline   Reply With Quote
Old 05-06-2011, 07:54   #12
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Generator 115/220v at Same Time

Chris,
Does your generator natively produce 240 or not? The answer makes a huge difference in how you would make this work.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 05-06-2011, 09:13   #13
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 33,865
Re: Generator 115/220v at Same Time

Guys, make sure you consider how many phases. 240v three phase has nothing whatsoever to do with 230v or 220v single phase.

So if the generator natively produces 240v three phase (giving you 120v single phase on either phase), you will not be able to power a 230v single phase (European power) dive compressor. Or vice versa.
Dockhead is offline   Reply With Quote
Old 05-06-2011, 19:45   #14
Registered User

Join Date: Jun 2009
Location: STX and Portland, until refit finished
Boat: 1999 Steel (Tom Collin's design)
Posts: 371
Re: Generator 115/220v at Same Time

Dockhead,

240V in the US is NOT 3 phase. 3 phase has 3 hot wires, with each wire exactly 120 degrees out of phase of the other two. It also typicaly has a ground, and a neutral. It is very unusual to find a 3 phase generator on a boat. Typicaly the only reason to have 3 phase current is with VERY large electric motors.

240V in the US has only 2 hot wires. They are both hot, but have the voltage 180 degrees out of phase with each other, so that the differental is 240 volts. It also typicaly has a neutral.

According to the following website, the Westerbeke 7.6 EDT D-NET 7.5 is wired to provide 120 and 240 V US style current. It might already be wired into the boats wireing system, and just require the proper breakers and wireing in the boats main breaker box.

I can't find a specification for dive compressor. Depending on the specs, it might be quite easy. There are apperently 3 phase version, which would be very difficult to wire in. There are single phase 240V versions that might be quite easy, and 120V versions. Depending on which one you have, it could be easy, or hard.
ViribusUnitis is offline   Reply With Quote
Old 05-06-2011, 20:24   #15
Registered User
 
Lancerbye's Avatar

Join Date: Mar 2007
Location: Cormorant Island, BC, Canada
Boat: Lancer 44 Motorsailer
Posts: 1,877
Images: 38
Re: Generator 115/220v at Same Time

Quote:
Originally Posted by ViribusUnitis View Post
Dockhead,

240V in the US is NOT 3 phase. 3 phase has 3 hot wires, with each wire exactly 120 degrees out of phase of the other two. It also typicaly has a ground, and a neutral. It is very unusual to find a 3 phase generator on a boat. Typicaly the only reason to have 3 phase current is with VERY large electric motors.
Sorry I couldn't leave it alone. Most boats and cars do actually have 3 Phase generators in them. They are often called altenators. LOL You can make small ac systems by removing the rectifiers and wiring them either Delta or wye configuration.
__________________
The basis of accomplishment is in never quitting
Mengzi Meng-tse
Lancerbye is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buy Owners Time Devilsrule2004 Atlantic & the Caribbean 5 04-02-2012 13:01
Time and Tide Clocks sailormoon Navigation 17 04-10-2011 13:45
Stories Lost in Time . . . Randyonr3 Flotsam & Sailing Miscellany 13 31-07-2011 12:22

Advertise Here


All times are GMT -7. The time now is 06:06.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.