Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 20-10-2015, 19:40   #1
Registered User

Join Date: Oct 2011
Posts: 3,604
Fuse Or Breaker For Inverter?

Would you want to install an inverter to a breaker if you had one to spare? Or would it be better to install some kind of in-line fuse instead? Seems like you should do one or the other.

I'm not super strong on electric but trying to learn so thanks in advance for your thoughts.
Delancey is offline   Reply With Quote
Old 20-10-2015, 20:02   #2
Registered User

Join Date: Feb 2013
Location: Oregon
Boat: Seafarer36c
Posts: 5,563
Re: Fuse Or Breaker For Inverter?

Breaker for sure. If you could find one that re-sets automatically that would be even better. I often overload our inverter. A fuse would be a pain.
model 10 is offline   Reply With Quote
Old 20-10-2015, 20:19   #3
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Fuse Or Breaker For Inverter?

If you do choose to use a breaker, it must be one of the new ones with an AIC greater than 5,000 amps. Most breakers don't have this capability and should not be connected directly to a large house bank.

A well-designed inverter would itself have fuse or other circuit protection against overloads, and should not blow the fuse between the inverter and the house batteries.

Most installations with large inverters use Class-T fuses. ANLs or MRBF fuses would be OK for medium-sized inverters.



Bill
btrayfors is offline   Reply With Quote
Old 20-10-2015, 20:52   #4
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Fuse Or Breaker For Inverter?

On my boat:
On the AC side, lock out breaker style for
SHORE
GENERATOR
INVERTOR
so that only one can be engaged at a time

On the DC side Large Class T Fuse before Master switch which supplies DC buss bar that supplies Invertor.

I see no problem with this
Pelagic is offline   Reply With Quote
Old 20-10-2015, 21:03   #5
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,174
Re: Fuse Or Breaker For Inverter?

My inverter has fuses on the DC side and a gfci pushbutton on the ac side.
newhaul is offline   Reply With Quote
Old 20-10-2015, 21:57   #6
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,664
Re: Fuse Or Breaker For Inverter?

Depends on the size on inverter. A normal size (2000w). You'd have a class t directly between inverter and battery.

On a very small one (200-300w) you may get away running from the DC panel off a breaker.
smac999 is offline   Reply With Quote
Old 21-10-2015, 03:51   #7
Registered User

Join Date: Oct 2011
Posts: 3,604
Re: Fuse Or Breaker For Inverter?

FWIW I'm thinking 600w to use mainly for charging a laptop and occasional use with a stick blender.

Thanks for the feedback, I'll research your recommendations.
Delancey is offline   Reply With Quote
Old 21-10-2015, 07:28   #8
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,174
Re: Fuse Or Breaker For Inverter?

If just to charge a laptop and run a stick blender then you could even get by with a 200 watt unit that plugs into the power tap ( CIG lighter) laptops usually draw about 65 watts and a stick blender draws about 150 to 175 watts at 120 volts. I used to run a 400 watt unit like that in my truck to charge all manor of lil stuff.
newhaul is offline   Reply With Quote
Old 21-10-2015, 07:34   #9
Registered User
 
Ironman162's Avatar

Join Date: Oct 2012
Location: Sydney Harbour
Boat: Coronet Oceanfarer30
Posts: 168
Re: Fuse Or Breaker For Inverter?

My inverter has fuses built in
Havent had to replace them at all this far. Guess I will have to vote for fuses against that background.
Fuses are quicker than circuit breakers if well sized.
Ironman162 is offline   Reply With Quote
Old 21-10-2015, 08:21   #10
Registered User

Join Date: Oct 2012
Location: Seattle
Boat: Tayana Mariner 36
Posts: 122
Re: Fuse Or Breaker For Inverter?

For my 1000w inverter, I use a 150A Blue Sea 285 series breaker mounted in the cavity behind my breaker panel. I know this requires an extra step to reset, but I want it that way, since if this breaker trips, there's an interesting reason why that I need to investigate before I or someone else randomly resets it.
bauer965 is offline   Reply With Quote
Old 21-10-2015, 08:40   #11
Registered User
 
ColdEH's Avatar

Join Date: Feb 2007
Location: Toronto Canada
Boat: Bristol 45.5
Posts: 848
Images: 1
Re: Fuse Or Breaker For Inverter?

Your inverter will have a fuse inside some where , so that will protect the inverter. What you need to protect, is the wire going from the battery bank to the inverter , so you want a fuse there as close to the battery as possible.

Regards
ColdEH is offline   Reply With Quote
Old 21-10-2015, 10:31   #12
Registered User

Join Date: Mar 2014
Location: Anacortes
Boat: previous - Whitby 42 new - Goldenwave 44
Posts: 1,835
Re: Fuse Or Breaker For Inverter?

Quote:
Originally Posted by btrayfors View Post
If you do choose to use a breaker, it must be one of the new ones with an AIC greater than 5,000 amps. Most breakers don't have this capability and should not be connected directly to a large house bank.

A well-designed inverter would itself have fuse or other circuit protection against overloads, and should not blow the fuse between the inverter and the house batteries.

Most installations with large inverters use Class-T fuses. ANLs or MRBF fuses would be OK for medium-sized inverters.
Bill
Ditto on what Bill says
exMaggieDrum is offline   Reply With Quote
Old 21-10-2015, 10:47   #13
Registered User

Join Date: Aug 2012
Posts: 811
Re: Fuse Or Breaker For Inverter?

Quote:
Originally Posted by Delancey View Post
FWIW I'm thinking 600w to use mainly for charging a laptop and occasional use with a stick blender.

Thanks for the feedback, I'll research your recommendations.
I run a 370w pure sine wave inverter mainly for charging MacBook, iPad and phones. That is wired off a breaker. I found the important thing is to have heavy DC cables in keeping with the inverter terminals. Avoid lighter plug DC connections as they wont pass enough current to charge a laptop even if the inverter is rated suitably high. That was my experience anyway.


I earlier tried a cheaper non sine wave (square wave) inverter for charging the MacBook and I had battery problems with the MacBook. Fortunately that self corrected; so I'd advise a pure sine wave inverter for laptop charging. Mine also has a useful USB charging port for phones, iPad as well as the usual AC out. I'm not sure how much power your blender uses.
GrahamHO is offline   Reply With Quote
Old 21-10-2015, 11:00   #14
Registered User
 
Panope's Avatar

Join Date: Sep 2012
Location: Washington State
Boat: Colvin, Saugeen Witch (Aluminum), 34'
Posts: 2,276
Re: Fuse Or Breaker For Inverter?

If the Breaker is readily accessible, it can be used as your primary means of activating/deactivating an inaccessible inverter. Saves having to wire a remote switch (with yet another circuit protector).

Steve
Panope is offline   Reply With Quote
Old 21-10-2015, 11:15   #15
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,174
Re: Fuse Or Breaker For Inverter?

Quote:
Originally Posted by GrahamHO View Post
I run a 370w pure sine wave inverter mainly for charging MacBook, iPad and phones. That is wired off a breaker. I found the important thing is to have heavy DC cables in keeping with the inverter terminals. Avoid lighter plug DC connections as they wont pass enough current to charge a laptop even if the inverter is rated suitably high. That was my experience anyway.


I earlier tried a cheaper non sine wave (square wave) inverter for charging the MacBook and I had battery problems with the MacBook. Fortunately that self corrected; so I'd advise a pure sine wave inverter for laptop charging. Mine also has a useful USB charging port for phones, iPad as well as the usual AC out. I'm not sure how much power your blender uses.
I used a 400 watt Coleman inverter in my trucks for close to a million miles to charge my laptop and other toys ( cordless drills and such) plugged into the CIG lighter in the truck with no problems however I would recommend heavier wiring for much more draw than that.
newhaul is offline   Reply With Quote
Reply

Tags
inverter


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fuse/breaker question for solar set-up GeoPowers Electrical: Batteries, Generators & Solar 9 20-04-2012 04:03
Fuse and circuit breaker question gulfstar1 Electrical: Batteries, Generators & Solar 15 30-03-2011 04:35
Separate Charger and Inverter or Charger-Inverter ? SvenG Electrical: Batteries, Generators & Solar 14 15-10-2010 17:14
Calculating Amps Drawn Before Inverter and After Inverter ? impi Electrical: Batteries, Generators & Solar 23 26-09-2010 22:24
Fuse or Circuit Breaker ? ggray Electrical: Batteries, Generators & Solar 5 15-10-2009 15:41

Advertise Here


All times are GMT -7. The time now is 14:10.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.