Frequecncy converter by GoHz

Has anyone installed one of these units?

10 kVA Pure Sine Wave Frequency Converter | GoHz.com.

We have a 220V 50 hz boat and want to plug into to 110 or 220 V 60 hz shore power. Also I would just like to hear from someone who has actually installed a frequency converter.
Bean Counter is offline   Reply With Quote
Old 22-03-2018, 06:36   #2
Registered User
 
Tricolor's Avatar

Join Date: Aug 2016
Location: Brazil, Spain, The Netherlands
Boat: Boatless at the moment
Posts: 381
Re: Frequecncy converter by GoHz

Quote:
Originally Posted by Bean Counter View Post
Has anyone installed one of these units?

10 kVA Pure Sine Wave Frequency Converter | GoHz.com.

We have a 220V 50 hz boat and want to plug into to 110 or 220 V 60 hz shore power. Also I would just like to hear from someone who has actually installed a frequency converter.
Maybe call GoHz and ask for (Yacht) references. I received the tip from a serious shipbuilder in The Netherlands.
__________________
Ranulph Fiennes — 'There is no bad weather, only inappropriate clothing.'
Tricolor is offline   Reply With Quote
Old 22-03-2018, 06:39   #3
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Frequecncy converter by GoHz

I have not installed one in a boat. But I have used something very similar on land. They are more expensive than a simple inverter designed for a boat. Plus they generate a lot of heat (think several fans).

You can get the same thing by using a marine inverter to create 50Hz 220V and charge the batteries with a standalone 60Hz high current charger plugged in to shore power. Plus you have the benefit of some run time when unplugged from shore. That's essentially what is inside the GoHZ box minus the batteries.
transmitterdan is offline   Reply With Quote
Old 22-03-2018, 06:43   #4
Registered User

Join Date: Jul 2012
Location: Switzerland
Boat: So many boats to choose from. Would prefer something that is not an AWB, and that is beachable...
Posts: 1,324
Re: Frequecncy converter by GoHz

Quote:
Originally Posted by transmitterdan View Post
You can get the same thing by using a marine inverter to create 50Hz 220V and charge the batteries with a standalone 60Hz high current charger plugged in to shore power. Plus you have the benefit of some run time when unplugged from shore. That's essentially what is inside the GoHZ box minus the batteries.
Even better would be to just use a standalone universal charger that takes both 110V/60Hz and 220V/50Hz, and indeed run everything of the inverter. Added advantage is that your shore connection only needs to carry the average load, and no longer the peak loads generated by your boat.
K_V_B is offline   Reply With Quote
Old 22-03-2018, 09:44   #5
Registered User

Join Date: Mar 2014
Location: Oz
Posts: 1,042
Re: Frequecncy converter by GoHz

Thank you all, but if a boat has 4 air conditioners that use 240 V 50 hz with locked rotor amps of 6 - that is 240 * 6 * 4 = 5.76KVA - An inverter that size would be heavy and expensive even if you could find one. I know there are soft start solutions etc etc but I just want a simple plug in answer that will run everything on the boat just like our 11 KVA generator does at 240 V 50 hz.
Bean Counter is offline   Reply With Quote
Old 22-03-2018, 10:31   #6
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Frequecncy converter by GoHz

Quote:
Originally Posted by Bean Counter View Post
Thank you all, but if a boat has 4 air conditioners that use 240 V 50 hz with locked rotor amps of 6 - that is 240 * 6 * 4 = 5.76KVA - An inverter that size would be heavy and expensive even if you could find one. I know there are soft start solutions etc etc but I just want a simple plug in answer that will run everything on the boat just like our 11 KVA generator does at 240 V 50 hz.
Buy a tapped transformer. 50 or 60 cycles is not likely to make a difference when the voltage is right.
Cadence is offline   Reply With Quote
Old 22-03-2018, 11:03   #7
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Frequecncy converter by GoHz

Quote:
Originally Posted by Bean Counter View Post
Thank you all, but if a boat has 4 air conditioners that use 240 V 50 hz with locked rotor amps of 6 - that is 240 * 6 * 4 = 5.76KVA - An inverter that size would be heavy and expensive even if you could find one. I know there are soft start solutions etc etc but I just want a simple plug in answer that will run everything on the boat just like our 11 KVA generator does at 240 V 50 hz.


On our boat we have a control box that prevents multiple ac units starting at the same time. Maybe not an option for you but something to look into.

Locked rotor amps will be 20% less on 60Hz. But I think there may be an error in your numbers. Locked rotor amps should be something like 15-20A for your AC compressor without a soft start device. My 16K BTU 110V AC has about 45A locked rotor current.

11KVA is a really big inverter system. It will not be cheap.

Marine rated step-up transformer will be the least expensive and most reliable. It will weight about 40kG I guess. You don’t really need all the electronics in the GoHZ gizmo. I would not want to have that much electronics involved when simply going from 50->60Hz. Some vendors under specify transformers for boats. See if you can find a suitable 15kva rated 110-220 transformer.
transmitterdan is offline   Reply With Quote
Old 22-03-2018, 12:07   #8
Registered User

Join Date: Mar 2014
Location: Oz
Posts: 1,042
Re: Frequecncy converter by GoHz

Quote:
Originally Posted by transmitterdan View Post
On our boat we have a control box that prevents multiple ac units starting at the same time. Maybe not an option for you but something to look into.

Locked rotor amps will be 20% less on 60Hz. But I think there may be an error in your numbers. Locked rotor amps should be something like 15-20A for your AC compressor without a soft start device. My 16K BTU 110V AC has about 45A locked rotor current.

11KVA is a really big inverter system. It will not be cheap.

Marine rated step-up transformer will be the least expensive and most reliable. It will weight about 40kG I guess. You don’t really need all the electronics in the GoHZ gizmo. I would not want to have that much electronics involved when simply going from 50->60Hz. Some vendors under specify transformers for boats. See if you can find a suitable 15kva rated 110-220 transformer.

Sorry, yes you are right I was looking at FLA which is full load amps, Locked rotor is 28 amps, I guess that is why the Aircon system has delayed starting sequence.

Charles do a 12KVA transformer internet special for $2k
https://www.boundlessoutfitters.com/...ixfmr12t-a.htm, weight 235lbs, I was looking for a more precise solution.
Bean Counter is offline   Reply With Quote
Old 22-03-2018, 15:09   #9
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Frequecncy converter by GoHz

The delay start is necessary because if the power fails and comes back on within a few seconds then the AC compressor will not start at all. The compressor motor is not big enough to start against a full high pressure head. It takes about 30-60 seconds for the pressure at the compressor inlet and outlet to equalize.

If you go with either the transformer or GoHZ solution be sure to provide plenty of fresh air for cooling. These things get hot without air flow.
transmitterdan is offline   Reply With Quote
Old 22-03-2018, 15:55   #10
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 33,750
Re: Frequecncy converter by GoHz

Quote:
Originally Posted by Bean Counter View Post
Sorry, yes you are right I was looking at FLA which is full load amps, Locked rotor is 28 amps, I guess that is why the Aircon system has delayed starting sequence.

Charles do a 12KVA transformer internet special for $2k
https://www.boundlessoutfitters.com/...ixfmr12t-a.htm, weight 235lbs, I was looking for a more precise solution.
This begs the question, however -- where will you get 12KVA of shore power? Just because the transformer will handle it, doesn't mean you've got it coming in. I've never seen a shore power connection that size in any marina. That's 109 amps at 110v.

Most inverters will handle about 2x their rated capacity for start-up. So a 5kW inverter might be able to run that. The sustained power needs to be somewhat less than the fine print rated max power (note that they are heavily derated at higher temperatures).
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is offline   Reply With Quote
Old 22-03-2018, 16:38   #11
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Frequecncy converter by GoHz

Quote:
Originally Posted by Dockhead View Post
This begs the question, however -- where will you get 12KVA of shore power? Just because the transformer will handle it, doesn't mean you've got it coming in. I've never seen a shore power connection that size in any marina. That's 109 amps at 110v.

Most inverters will handle about 2x their rated capacity for start-up. So a 5kW inverter might be able to run that. The sustained power needs to be somewhat less than the fine print rated max power (note that they are heavily derated at higher temperatures).
US 240V 50A shorepower is 12KVA.
DotDun is offline   Reply With Quote
Old 22-03-2018, 16:44   #12
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,338
Re: Frequecncy converter by GoHz

[QUOTE=Dockhead;2601854]This begs the question, however -- where will you get 12KVA of shore power? Just because the transformer will handle it, doesn't mean you've got it coming in. I've never seen a shore power connection that size in any marina. That's 109 amps at 110v.

Every marina I can think of provides 12KVA (125/250 @ 50amps) at their smaller slips and up to 480/200/3ph at their largest... times they are a changing...
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 22-03-2018, 16:56   #13
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Helsinki (Summer); Cruising the Baltic Sea this year!
Boat: Cutter-Rigged Moody 54
Posts: 33,750
Re: Frequecncy converter by GoHz

[QUOTE=Scott Berg;2601905]
Quote:
Originally Posted by Dockhead View Post
This begs the question, however -- where will you get 12KVA of shore power? Just because the transformer will handle it, doesn't mean you've got it coming in. I've never seen a shore power connection that size in any marina. That's 109 amps at 110v.

Every marina I can think of provides 12KVA (125/250 @ 50amps) at their smaller slips and up to 480/200/3ph at their largest... times they are a changing...
Not over here! And the poster's boat apparently comes from Europe.

In Europe, 16 amps x 230 v is luxury. 10 amps, 8 amps, even 4 amps is what you get in some places on the Continent. There is 400v 3 phase power in some places for commercial vessels or superyachts, but not for mere mortals -- even a 54' boat.

But wasn't the poster asking about 110v? What is the capacity of his shore power system?
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is offline   Reply With Quote
Old 22-03-2018, 17:05   #14
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Frequecncy converter by GoHz

[QUOTE=Dockhead;2601915]
Quote:
Originally Posted by Scott Berg View Post

Not over here! And the poster's boat apparently comes from Europe.

In Europe, 16 amps x 230 v is luxury. 10 amps, 8 amps, even 4 amps is what you get in some places on the Continent. There is 400v 3 phase power in some places for commercial vessels or superyachts, but not for mere mortals -- even a 54' boat.

But wasn't the poster asking about 110v? What is the capacity of his shore power system?
The US 12KVA shorepower delivers up to 100A of 120V or 50A of 240V or a combination of each equal to 12KVA.
DotDun is offline   Reply With Quote
Old 22-03-2018, 20:46   #15
Registered User

Join Date: Dec 2009
Location: Cruising, now in USVIs
Boat: Taswell 43
Posts: 1,033
Re: Frequecncy converter by GoHz

Our boat was built for Asia power (230v, 50Hz) and all the AC machines were selected accordingly. When we got to the Caribb, we ran into the power issue you describe. We bought an isolation transformer to step the 110v shore power up to 230v. All our installed machinbes work well with the 230v, 60Hz power...except 1 of our 2 aircons. It worked OK on the genset(230v 50Hz) but not on transformed 110v shorepower.....and in the marina is where we needed the aircon! After checking options, we elected to replace that aircon with a new one...a model that is both 50Hz and 60Hz power. Problem solved, and we have a new, modern aircon that works without the old issues.
sailcrazy is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC-DC Converter squarehead Electrical: Batteries, Generators & Solar 5 26-08-2009 18:34
Olin 25MM Flare Launcher Converter Notice svHyLyte Health, Safety & Related Gear 0 01-07-2009 07:45
Is a DC TO DC 12V Regulator / Converter Required? BlueSovereign Marine Electronics 4 24-05-2009 15:03
Spraying AwlCraft Using Brushing Converter? geoffschultz Construction, Maintenance & Refit 1 27-04-2009 04:50
TV Converter Box Dilemma svcattales Marine Electronics 16 19-10-2008 13:52

Advertise Here


All times are GMT -7. The time now is 00:02.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.