Old 07-09-2018, 17:28   #46
Registered User
 
Delfin's Avatar

Join Date: Aug 2010
Location: Anacortes, WA
Boat: 55' Romsdal
Posts: 2,103
Re: "Floating" LFP batteries

Quote:
Originally Posted by Maine Sail View Post
Where we cruise, Maine & Maritimes, there are so few marinas it's a non issue. That said flipping off the LFP and then flipping on the lead bank takes but a few seconds. It's more work getting out the shore power cable & plugging it in. The last time we used a marina we never plugged in at all. With lead I would have jumped at the opportunity to plug in. With LFP I just poured another cocktail and sat back and relaxed.......
Ditto. I use the ACR switch to direct charge current to the starter bank.

Step 1: Flip toggle on the ACR from Auto Combine to Manual Combine.
Step 2: Turn off BMS
Step 3: Prepare adult beverage

When this proves too much effort, I'll be ready for adult diapers.
__________________
https://delfin.talkspot.com
I can picture in my head a world without war, a world without hate. And I can picture us attacking that world, because they'd never expect it. - Jack Handey
Delfin is offline   Reply With Quote
Old 07-09-2018, 18:24   #47
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: "Floating" LFP batteries

Quote:
Originally Posted by tanglewood View Post
Does a week at 100% SOC reduce life, or does it make no difference if you then fully cycle the battery?
Absolutely.

Minutes count, much less hours.

Not saying we know exactly how much lifetime is reduced, too many variables.

Also, one super important note: people toss around SoC% levels as if they have an objective meaning.

They don't.

_______
At the bottom, maybe we can all agree on 12V resting as a common definition of Zero SoC, as we do with lead at 10.5V.

Since going much lower **in voltage** risks instant scrapification, as MS indicated above, it would be useless to assign SoC% values down there.

Now assuming this is a good quality 12V/400AH rated bank with a CEF of 1.05.

Take it from a 0% SoC state, and:

Case A. add 420AH to it at a 200A rate at 14.6V

Case B. add 420AH at a 40A rate at 14.6V

Case C. bring it up to 13.75V and Just Stop (no Absorb)

Case D. bring it up to 13.8V and Absorb until endAmps of 12A is reached

Case E. charge to 14.6V and Absorb as with D

Assume E is the cell maker's published spec for 100% Full, but you agree with me that this is "pushing into the shoulder" **so far** as to drastically reduce longevity,

perhaps so the owner only gets the rated lifetime, rather than its far higher true potential, even if the bank is coddled every other way.

So why call that SoC 100%, if you're never going to go there in normal daily operations?

I personally use Case D as **my definition** of 100% Full when precision is required, e.g. calibrating a SoC gauge.

Case C is my charge-stopping point for day to day cycling usage, and I intentionally vary it a bit in case the memory effect is real. It is usually above 98% SoC compared to D.

Some people here are under the impression that Case C & D are far lower SoC compared to E, even talking cray-cray low numbers like 80-90% SoC.

It is a difference far less than that.

And my 100% SoC at Case D is higher than A or B (in every case so far), "just how much exactly?" seems a bit of a silly question to me.

If you want to go to the trouble of finding out, post back here and let us know.

Now, back to my larger point.

Can you understand why I feel how silly statements like

"LFP should be cycled between 20% and 80%, and therefore you are losing 40% of capacity"

are?

Or attempts to correlate precise working voltage in the mid ranges to varying arbitrary definitions of SoC?

Given the above example, I just reset my coulomb counter to 100% at Case D. That **is** 100%.

It then counts down using a 400AH capacity setting so I can see **roughly** where my SoC is at.

Since my entertainment circuit alarms then LVD cuts out at around 12.5V, other non-essential big-amp load circuits at say 12.3V,

only essential safety/navigation systems are left going down to single-digit SoC readings, and their "user space LVD" cuts out at 12.1V.

The lowest failsafe "BMS" level never needs to isolate the bank completely at 11.9V, unless those higher-level protections fail.

I in fact have greater than rated AH capacity using **those** admittedly arbitrary definitions of 0-100% SoC, in my case prioritizing longevity.

And even if I didn't, I just don't care how much capacity I might be "wasting", compared to what? damaging voltages?

With a bank from a quality maker, it's bound to be an insignificant amount anyway.
john61ct is offline   Reply With Quote
Old 07-09-2018, 19:02   #48
Registered User
 
Delfin's Avatar

Join Date: Aug 2010
Location: Anacortes, WA
Boat: 55' Romsdal
Posts: 2,103
Re: "Floating" LFP batteries

Quote:
Originally Posted by tanglewood View Post
Does a week at 100% SOC reduce life, or does it make no difference if you then fully cycle the battery? What about a month? Or a year?
See MaineSail's test of the loss of capacity for a battery stored for a year at 100% SoC. From memory, a loss of a bit under 12% over that time period. I have no clue if this is a linear function, and I suspect it is not, but assuming that it is, on a 100 amp bank, a day stored full is going to cost you 1/3 of an amp in lost capacity. The minutes John is concerned about may reduce the capacity by .000023 amp per minute.

The week you asked about would reduce your bank by 1/4 of an amp. To avoid this precipitous loss of capacity, folks who actually know what they are talking about recommend storing the batteries at 50% SoC, in the sweet spot of lowest impedance.
__________________
https://delfin.talkspot.com
I can picture in my head a world without war, a world without hate. And I can picture us attacking that world, because they'd never expect it. - Jack Handey
Delfin is offline   Reply With Quote
Old 07-09-2018, 19:16   #49
Registered User
 
Delfin's Avatar

Join Date: Aug 2010
Location: Anacortes, WA
Boat: 55' Romsdal
Posts: 2,103
Re: "Floating" LFP batteries

Incidentally, Lithionics recommends storing their product at 100% SoC for periods less than 3 months, and at 50% SoC for periods greater than 3 months.

http://lithionicsbattery.com/wp-cont...cations-R0.pdf
__________________
https://delfin.talkspot.com
I can picture in my head a world without war, a world without hate. And I can picture us attacking that world, because they'd never expect it. - Jack Handey
Delfin is offline   Reply With Quote
Old 07-09-2018, 19:27   #50
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: "Floating" LFP batteries

Quote:
Originally Posted by Delfin View Post
Ditto. I use the ACR switch to direct charge current to the starter bank.



Step 1: Flip toggle on the ACR from Auto Combine to Manual Combine.

Step 2: Turn off BMS

Step 3: Prepare adult beverage



When this proves too much effort, I'll be ready for adult diapers.


So you charge your lead bank at the same voltage as your LFP?
a64pilot is offline   Reply With Quote
Old 07-09-2018, 20:04   #51
Registered User
 
Delfin's Avatar

Join Date: Aug 2010
Location: Anacortes, WA
Boat: 55' Romsdal
Posts: 2,103
Re: "Floating" LFP batteries

Quote:
Originally Posted by a64pilot View Post
So you charge your lead bank at the same voltage as your LFP?
Yes. The starter bank delivers current for an instant to start the engines. Underway, the bulk voltage setting of 28 v is more than enough to replace that. Minimum absorption, then float at 26.6, which supplies house loads underway through the inverter drawing off the LA bank. I installed today a Smart Gauge to check SoC of that starter bank and may adjust float up a bit. Since I disconnect charging of the Lithium bank when the acceptance rate drops to around 5%C, I could set float to what the LA bank needs, but just to be safe I keep it at a harmless rate for Li if I forget to throw a switch when the Li bank is full.
__________________
https://delfin.talkspot.com
I can picture in my head a world without war, a world without hate. And I can picture us attacking that world, because they'd never expect it. - Jack Handey
Delfin is offline   Reply With Quote
Old 07-09-2018, 23:05   #52
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: "Floating" LFP batteries

Quote:
Originally Posted by Delfin View Post
a day stored full is going to cost you 1/3 of an amp in lost capacity. The minutes John is concerned about may reduce the capacity by .000023 amp per minute.
Talk about WAGing 8-)

And capacity is not measured in amps. . .
john61ct is offline   Reply With Quote
Old 07-09-2018, 23:08   #53
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: "Floating" LFP batteries

Quote:
Originally Posted by Delfin View Post
Incidentally, Lithionics recommends storing their product at 100% SoC for periods less than 3 months, and at 50% SoC for periods greater than 3 months.

http://lithionicsbattery.com/wp-cont...cations-R0.pdf
Well that's clearly wrong.

I think the guideline for LFP in general needs to be, ignore all advice from vendors 8-)
john61ct is offline   Reply With Quote
Old 08-09-2018, 05:28   #54
Registered User

Join Date: Feb 2015
Posts: 1,227
Images: 1
Re: "Floating" LFP batteries

Quote:
Originally Posted by Delfin View Post
See MaineSail's test of the loss of capacity for a battery stored for a year at 100% SoC. From memory, a loss of a bit under 12% over that time period. I have no clue if this is a linear function, and I suspect it is not, but assuming that it is, on a 100 amp bank, a day stored full is going to cost you 1/3 of an amp in lost capacity. The minutes John is concerned about may reduce the capacity by .000023 amp per minute.

The week you asked about would reduce your bank by 1/4 of an amp. To avoid this precipitous loss of capacity, folks who actually know what they are talking about recommend storing the batteries at 50% SoC, in the sweet spot of lowest impedance.

MainSail's test is an excellent data point, but without knowing the actual mechanism of capacity loss, I don't think we can conclude that it's a day for day linear loss for every day at 100% SOC. That may be exactly right. But at the same time maybe it's like LA where there is a chemical reaction that is completely reversible unless it's left sitting for too long? I just wonder if we really know, or if we are connecting dots that might not actually connect in a straight line. There may well be some scientific papers that have looked into this, but I haven't found them yet.
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 08-09-2018, 05:31   #55
Registered User

Join Date: Feb 2015
Posts: 1,227
Images: 1
Re: "Floating" LFP batteries

Quote:
Originally Posted by john61ct View Post
Absolutely.

Minutes count, much less hours.

Not saying we know exactly how much lifetime is reduced, too many variables.

Do we really know this? I would love to see the studies behind it. Have you found any? I'm not saying it's incorrect. I'm just trying to validate some of these beliefs/assertions.
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 08-09-2018, 05:40   #56
Registered User

Join Date: Feb 2015
Posts: 1,227
Images: 1
Re: "Floating" LFP batteries

Quote:
Originally Posted by john61ct View Post
_______
At the bottom, maybe we can all agree on 12V resting as a common definition of Zero SoC, as we do with lead at 10.5V.

Since going much lower **in voltage** risks instant scrapification, as MS indicated above, it would be useless to assign SoC% values down there.

Now assuming this is a good quality 12V/400AH rated bank with a CEF of 1.05.

Take it from a 0% SoC state, and:

Case A. add 420AH to it at a 200A rate at 14.6V

Case B. add 420AH at a 40A rate at 14.6V

Case C. bring it up to 13.75V and Just Stop (no Absorb)

Case D. bring it up to 13.8V and Absorb until endAmps of 12A is reached

Case E. charge to 14.6V and Absorb as with D

Assume E is the cell maker's published spec for 100% Full, but you agree with me that this is "pushing into the shoulder" **so far** as to drastically reduce longevity,

perhaps so the owner only gets the rated lifetime, rather than its far higher true potential, even if the bank is coddled every other way.

So why call that SoC 100%, if you're never going to go there in normal daily operations?

I personally use Case D as **my definition** of 100% Full when precision is required, e.g. calibrating a SoC gauge.

Case C is my charge-stopping point for day to day cycling usage, and I intentionally vary it a bit in case the memory effect is real. It is usually above 98% SoC compared to D.

Some people here are under the impression that Case C & D are far lower SoC compared to E, even talking cray-cray low numbers like 80-90% SoC.

It is a difference far less than that.

And my 100% SoC at Case D is higher than A or B (in every case so far), "just how much exactly?" seems a bit of a silly question to me.

If you want to go to the trouble of finding out, post back here and let us know.

Now, back to my larger point.

Can you understand why I feel how silly statements like

"LFP should be cycled between 20% and 80%, and therefore you are losing 40% of capacity"

are?

Or attempts to correlate precise working voltage in the mid ranges to varying arbitrary definitions of SoC?

Given the above example, I just reset my coulomb counter to 100% at Case D. That **is** 100%.

It then counts down using a 400AH capacity setting so I can see **roughly** where my SoC is at.

Since my entertainment circuit alarms then LVD cuts out at around 12.5V, other non-essential big-amp load circuits at say 12.3V,

only essential safety/navigation systems are left going down to single-digit SoC readings, and their "user space LVD" cuts out at 12.1V.

The lowest failsafe "BMS" level never needs to isolate the bank completely at 11.9V, unless those higher-level protections fail.

I in fact have greater than rated AH capacity using **those** admittedly arbitrary definitions of 0-100% SoC, in my case prioritizing longevity.

And even if I didn't, I just don't care how much capacity I might be "wasting", compared to what? damaging voltages?

With a bank from a quality maker, it's bound to be an insignificant amount anyway.

I get your SOC point.


I think most people start with the battery manufacturers definition of Capacity and SOC, and work from there. I expect manufacturer's capacities will be on the high side, charging and discharging to aggressive limits so they can claim higher capacities. But those numbers are also paired with an expected cycle life, so they don't want to be too aggressive or their advertised cycle life will suffer.


From the mfg defines capacity and SOC, each of us decides how far we want to discharge and charge with a goal of longer battery life, and lower risk of overshoot and damage. That yields a smaller "working capacity" and a new "working SOC" range, with new "working" discharge and charge IV points.


I agree with you that in practice, these new, personalized "working" parameters become the only ones that matter, and are inherently our "new" 0-100% SOC range.
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 08-09-2018, 07:07   #57
Registered User
 
Delfin's Avatar

Join Date: Aug 2010
Location: Anacortes, WA
Boat: 55' Romsdal
Posts: 2,103
Re: "Floating" LFP batteries

Quote:
Originally Posted by tanglewood View Post
MainSail's test is an excellent data point, but without knowing the actual mechanism of capacity loss, I don't think we can conclude that it's a day for day linear loss for every day at 100% SOC. That may be exactly right. But at the same time maybe it's like LA where there is a chemical reaction that is completely reversible unless it's left sitting for too long? I just wonder if we really know, or if we are connecting dots that might not actually connect in a straight line. There may well be some scientific papers that have looked into this, but I haven't found them yet.
I suspect it isn't, but don't know that it is not linear, as I noted. As I understand it, the chemical reaction is a loss of Li ions which reduces capacity, but I have no way of knowing the ramp of that process. One would assume it is not linear based on Lithionics data, who recommend storing at full charge, but only for 3 months, then at 50% thereafter with periodic cycling. Unless you believe, as some apparently do, that manufacturers think it is in their best interest to kill their products by recommending practices that will ruin their brand, I would assume Lithionics knows something more about the subject than I do. That said, it is easy to just not charge the Li bank on the day we return to the dock from the previous day's usage, so storing them at half SoC is no issue, so why not? Further, that is the recommendation of MaineSail who has probably spent more time at the test bench actually gaining empirical data on the batteries as well as using them personally than all of us put together. Seems a better source of information than from people whose sole source of information appears to be their alimentary canal.

You might give the Lithionics engineers a call. I found them very forthright and willing to tell you what they know and don't know and they might be able to point you in the direction of outside research on subjects of interest. After all, it's what they do for a living. I learned a lot from them.
__________________
https://delfin.talkspot.com
I can picture in my head a world without war, a world without hate. And I can picture us attacking that world, because they'd never expect it. - Jack Handey
Delfin is offline   Reply With Quote
Old 08-09-2018, 07:11   #58
Registered User
 
Delfin's Avatar

Join Date: Aug 2010
Location: Anacortes, WA
Boat: 55' Romsdal
Posts: 2,103
Re: "Floating" LFP batteries

Quote:
Originally Posted by john61ct View Post
Talk about WAGing 8-)

And capacity is not measured in amps. . .
Thank you for the correction John. I should have written amp hour, not used shorthand to avoid confusion.
__________________
https://delfin.talkspot.com
I can picture in my head a world without war, a world without hate. And I can picture us attacking that world, because they'd never expect it. - Jack Handey
Delfin is offline   Reply With Quote
Old 14-09-2018, 13:27   #59
Registered User

Join Date: Jun 2018
Posts: 2
Re: "Floating" LFP batteries

The arguments seem to be irrelevant because lead acid batteries and lithium batteries are so poles apart in both expense and life. Safety requirements in Australia stipulate AGM for Cat 4 and above.. I have Varta (German) deep cycle house batteries that are in their 10th year still going strong. The boat is on a swing mooring, has no solar, no generator and uses shore power overnight each week after a days racing or after a weekend use. The batteries never lose charge at rest even for long periods.
magnificat is offline   Reply With Quote
Old 14-09-2018, 14:18   #60
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: "Floating" LFP batteries

Well getting on shore power every night is very different from the use cases discussed here.

No challenge at all.
john61ct is offline   Reply With Quote
Reply

Tags
loa


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Get radical by getting simple: a 32kWh LFP house energy system nebster Electrical: Batteries, Generators & Solar 24 17-08-2018 14:56
LFP system design approach - comments welcome tanglewood Electrical: Batteries, Generators & Solar 18 06-06-2018 11:35
US source for CALB CA180 LFP batteries? tanglewood Electrical: Batteries, Generators & Solar 23 04-06-2018 17:08
[B]Best practice charging for LFP & LFMP bank?[/B] BigBeakie Electrical: Batteries, Generators & Solar 71 16-12-2017 14:42
LFP Cell or BMS Failure CharlieJ Electrical: Batteries, Generators & Solar 21 15-09-2016 19:48

Advertise Here


All times are GMT -7. The time now is 12:35.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.